1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025
Subject: RE: Weird stream device behavior when using the IOC shell's exit function
From: Abdalla Ahmad via Tech-talk <[email protected]>
To: Mark Rivers <[email protected]>, 'Dirk Zimoch' <[email protected]>
Cc: "'[email protected]'" <[email protected]>
Date: Thu, 7 Feb 2019 13:36:57 +0000
Hello Mark
Yes I noticed that and next week I will write a test program to read some parameters and see exactly how the device is actually communicating, because on a telnet session you get first a ">" prompt, when you type a command you get the output on a new line then followed by a ">" on a new line.
If you go back to the back trace, you can see that the poll is stuck with data ">", I started to suspect something is wrong with In/Out terminators. I should be able to verify the device terminator character(s?) through the test program I will write. Regarding the "cmd 61" which corresponds to the isEnabled PV, I noticed that if I reduce the number of substitutions, there is a point that the IOC exits if the is Enabled PV is commented from the DB. Nothing strange on a telnet session for any command.
Thank you for your time and efforts!
Abdalla.
-----Original Message-----
Sent: Thursday, February 07, 2019 3:30 PM
To: Abdalla Ahmad <[email protected]>; 'Dirk Zimoch' <[email protected]>
Cc: '[email protected]' <[email protected]>
Subject: Re: Weird stream device behavior when using the IOC shell's exit function
Hi Abdalla,
I see some curious things in your output.
2019/02/07 10:29:03.257 SR-IPC1:23 write 9 cmd 61 1\r
2019/02/07 10:29:03.276 SR-IPC1:23 read 1
2019/02/07 10:29:03.376 SR-IPC1:23 read 12 OK 00 YES\r\r\n
2019/02/07 10:29:03.377 SR-IPC1:23 write 9 cmd 61 2\r
2019/02/07 10:29:03.396 SR-IPC1:23 read 1
2019/02/07 10:29:03.496 SR-IPC1:23 read 12 OK 00 YES\r\r\n
2019/02/07 10:29:03.497 SR-IPC1:23 write 9 cmd 61 3\r
2019/02/07 10:29:03.516 SR-IPC1:23 read 1
2019/02/07 10:29:03.616 SR-IPC1:23 read 12 OK 00 YES\r\r\n
- Each write is followed by 2 reads.  The first read occurs 20 ms after the write. The second read occurs 100 ms after the first read.  Is that just how the device works, or does your protocol file use 2 read operations?
- Sometimes the same command is sent several times in rapid succession as above.  Do you understand why the "cmd 61" command is being sent 3 times in a row?  Are your records each individually periodically scanned, or do you use FLNK to processes them sequentially?
Can you send your database and protocol file?
> A question came up to my mind, could the standard telnet port be related to this deadlock?
I don't think that should matter.  On the IOC side it does not care what port it connected to, the Linux client is using a random high number port on its end.
Sent: Thursday, February 7, 2019 2:52 AM
To: Mark Rivers; 'Dirk Zimoch'
Hello Mark
Attached is the output of asyn trace mask on one of the controllers. The IOC is working fine even after the exit function so I had to press Ctrl-C at some point.
For your suggestion regarding different configuration: asyn 4.18 can't be built with base 3.15.6 because there is a line in the asyn Gpib module that sets an event record value (a char array) to an integer (which is what was in 3.14.12.3). And stream 2.5.1 with base 3.15.6 complains about two headers it can't find: wdlib.h and streamReferences. According to streamDevice/src/Makefile, StreamReferences should have been generated from CONFIG_STREAM but it's not.
I think for now I will stick with the old setup: base 3.14.12.3, asyn 4.18 and stream 2.5.1.
Since the same setup worked with the agilent controllers (serially interfaced and connected via terminal servers), A question came up to my mind, could the standard telnet port be related to this deadlock?
Best Regards,
Abdalla.
Sent: Wednesday, February 06, 2019 8:09 PM
The first test I would like you to run is with the recent code, ie. base 3.15.6, asyn 4.33 and stream 2.8.8. Set asynTraceIOMask=2 and asynTraceMask=9 for the TCP port.  Then we will see all communication with the device.  When that is running type "exit".  Send the complete output, for a few seconds before you type exit, and a few seconds after you type exit.
Sent: Wednesday, February 6, 2019 8:32 AM
To: 'Abdalla Ahmad' <[email protected]<mailto:[email protected]>>; Dirk Zimoch <[email protected]<mailto:[email protected]>>
Cc: [email protected]<mailto:[email protected]>
Ø  I thought the while loop is causing the block so I removed the while loop and put the poll function just like what is done in version 4.18 but I got the same behavior.
Ø  So I think that poll here never returns.
Ø  As the documentation says, poll will block if a negative timeout is provided.
Ø  So I think somehow stream device is passing a negative timeout but I could not verify the timeout value received in the readIt function.
You could edit that code to print the value of readPollmsec just before the while() statement.  That will tell you if stream device is passing a negative timeout.  The purpose of the loop is to retry the poll in case it terminates early with errno=EINTR.  But it will only loop for readPollsec ms at longest.
I suggest you also try independently changing the versions of asyn and Stream to see which has changed to cause the problem.  I suggest using these 2 configurations:
-          Base 3.15.6, asyn 4.16 Stream 2.8.8
-          Base 3.15.6, asyn 4.33, Stream 2.5.1
I have a simple StreamDevice IOC that I will test today to see if I can reproduce the problem.
From: Abdalla Ahmad <[email protected]<mailto:[email protected]>>
Sent: Wednesday, February 6, 2019 6:45 AM
To: Mark Rivers <[email protected]<mailto:[email protected]>>; Dirk Zimoch <[email protected]<mailto:[email protected]>>
Hello Mark
Just would like to share some findings:
I cloned the latest stream device 2.8.8 and I still get the same behavior. So I investigated the backtrace a little bit specifically the thread you mentioned it is causing the deadlock.
In asyn 4.33 file asyn/drvAsynSerial/drvAsynIPPort.c function "readIt", line 725 is the poll function call causing the deadlock. I thought the while loop is causing the block so I removed the while loop and put the poll function just like what is done in version 4.18 but I got the same behavior. So I think that poll here never returns.
As the documentation says, poll will block if a negative timeout is provided. So I think somehow stream device is passing a negative timeout but I could not verify the timeout value received in the readIt function.
Best Regards,
Abdalla.
Sent: Wednesday, February 06, 2019 9:12 AM
To: 'Mark Rivers' <[email protected]<mailto:[email protected]>>
Hello Mark
This is just to confirm that I re-built the old setup on CentOS 7 x64; base 3.14.12.3, asyn 4.18 and stream 2.5.1 and everything works fine. I don't even get the asynWrite error messages.
Best Regards,
Abdalla.
Sent: Tuesday, February 05, 2019 5:47 PM
To: Abdalla Ahmad <[email protected]<mailto:[email protected]>>
You can now use asynSetTraceIOMask and asynSetTraceMask to monitor the communication.  If you enable that before you type "exit" we can see what is happening.
I view the problem exiting the IOC as an annoyance but not something that has to be fixed immediately.  You can always just type CTRL-C.
Sent: Tuesday, February 5, 2019 8:17 AM
Well I never thought of checking the client, I will test it and come back.
I forgot to mention that the device is being controlled through standard telnet port 23. Does it make a difference for stream device to work with a well known port number?
Get Outlook for Android<https://aka.ms/ghei36>
On Tue, Feb 5, 2019 at 4:14 PM +0200, "Mark Rivers" <[email protected]<mailto:[email protected]>> wrote:
Is your device working correctly, or is it timing out? I wonder if the exit problem is because Stream is polling constantly and never releasing the lock so the epicsExit thread can never run?
Sent from my iPhone
> On Feb 5, 2019, at 7:23 AM, Abdalla Ahmad  wrote:
> Hello Mark
> Including asyn.dbd file did the trick. Looking forward for your thoughts on the exit issue.
> Thank you for your time.
> Abdalla.
> From: Mark Rivers [mailto:[email protected]]
> Sent: Tuesday, February 05, 2019 3:19 PM
> To: Abdalla Ahmad
> exit function
> OK, I understand the problem with the missing asyn commands.  You do have these commands in your help output:
> drvAsynIPPortConfigure          drvAsynIPServerPortConfigure
> drvAsynSerialPortConfigure
> That tells me that your application dbd file is including drvAsynIPPort.dbd and drvAsynSerialPort.dbd, but it is not including asyn.dbd.  It also explains why it used to work, and now it does not.  Previously drvAsynIPPort.dbd and drvAsynSerialPort.dbd themselves included asyn.dbd.  However, recent EPICS base releases no longer allow a dbd file to be loaded more than once, so asyn.dbd was removed from drvAsynIPPort.dbd and drvAsynSerialPort.dbd.  Now your application must explicitly include asyn.dbd.
> I think this is independent of the IOC exiting issue, but please include asyn.dbd and see if you still have that problem.
> Mark
> ________________________________
> From: Abdalla Ahmad
> Sent: Tuesday, February 5, 2019 6:34 AM
> To: Mark Rivers
> exit function
> Hi Mark
> I attached the help output in help.txt. For the database nothing is I/O scanned, standard 1 second rate as in the attached database. I also checked the protocol file but nothing seems strange.
> While writing the email I thought of increasing the scan rate to 5 seconds and it works. I still get the same asynError in write but the IOC eventually exits. Even if it exits gracefully now, it is still a problem because we need the scan rate to match the IMG ones. As I told you before it used to work on the old setup without any problems. Is there anything we can investigate?
> Best Regards,
> Abdalla.
> Sent: Tuesday, February 05, 2019 2:20 PM
> To: Abdalla Ahmad
> exit function
> Hi Abdalla,
> Your IOC is clearly built OK with asyn because you have threads that are in asyn functions.
> Thread 13 (Thread 0x7fffed943700 (LWP 29173)):
> #0  0x00007ffff6034f0d in poll () from /lib64/libc.so.6
> #1  0x00007ffff7926c14 in readIt (drvPvt=0x70eb30, pasynUser=0x79e4a8,
> data=0x70fd40 ">", maxchars=2048, nbytesTransfered=0x7fffed942ba0,
> gotEom=0x7fffed942b90)
>    at ../../asyn/drvAsynSerial/drvAsynIPPort.c:726
> #2  0x00007ffff7930886 in readIt (drvPvt=0x70fbb0, pasynUser=0x79e4a8,
> data=0x70fd40 ">", maxchars=, nbytesTransfered=0x7fffed942ba0,
> eomReason=0x7fffed942b90)
>    at ../../asyn/interfaces/asynOctetBase.c:233
> #3  0x00007ffff793a563 in readIt (ppvt=0x70fcb0, pasynUser=0x79e4a8,
> data=0x79e3a8 ">", maxchars=63, nbytesTransfered=0x7fffed942ca0,
> eomReason=0x7fffed942c70)
>    at ../../asyn/miscellaneous/asynInterposeEos.c:231
> #4  0x00007ffff7bab5f5 in AsynDriverInterface::readHandler
> (this=this@entry=0x79e2e0) at ../AsynDriverInterface.cc:960
> #5  0x00007ffff7bacd08 in handleRequest (pasynUser=) at
> ../AsynDriverInterface.cc:1503
> #6  0x00007ffff791c9f3 in portThread (pport=0x70ece0) at
> ../../asyn/asynDriver/asynManager.c:902
> #7  0x00007ffff6b6f7fc in start_routine (arg=0x70f290) at
> ../../../src/libCom/osi/os/posix/osdThread.c:403
> #8  0x00007ffff5d2ce25 in start_thread () from /lib64/libpthread.so.0
> #9  0x00007ffff603fbad in clone () from /lib64/libc.so.6
> Thread 12 (Thread 0x7fffeda44700 (LWP 29172)):
> #0  0x00007ffff5d30995 in pthread_cond_wait@@GLIBC_2.3.2 () from
> #1  0x00007ffff6b71f3b in epicsEventWait (pevent=0x70d520) at
> ../../../src/libCom/osi/os/posix/osdEvent.c:103
> #2  0x00007ffff6b6b029 in epicsEventMustWait (id=) at
> ../../../src/libCom/osi/epicsEvent.cpp:125
> #3  0x00007ffff791c40c in portThread (pport=0x70d050) at
> ../../asyn/asynDriver/asynManager.c:788
> #4  0x00007ffff6b6f7fc in start_routine (arg=0x70d590) at
> #5  0x00007ffff5d2ce25 in start_thread () from /lib64/libpthread.so.0
> #6  0x00007ffff603fbad in clone () from /lib64/libc.so.6
> I don't understand why the asyn iocsh commands would not be available.
> Please send the complete output of the iocsh "help" command.
> The hang at shutdown appears to be caused by this thread:
> Thread 1 (Thread 0x7ffff7fda740 (LWP 29161)):
> #0  0x00007ffff5d3351d in __lll_lock_wait () from
> #1  0x00007ffff5d2ee36 in _L_lock_870 () from /lib64/libpthread.so.0
> #2  0x00007ffff5d2ed2f in pthread_mutex_lock () from
> #3  0x00007ffff6b71a76 in mutexLock (id=0x70ef60) at
> ../../../src/libCom/osi/os/posix/osdMutex.c:46
> #4  epicsMutexOsdLock (pmutex=0x70ef60) at
> ../../../src/libCom/osi/os/posix/osdMutex.c:130
> #5  0x00007ffff7917e9b in lockPort (pasynUser=0x710668) at
> ../../asyn/asynDriver/asynManager.c:1741
> #6  0x00007ffff7925876 in cleanup (arg=0x70eb30) at
> ../../asyn/drvAsynSerial/drvAsynIPPort.c:246
> #7  0x00007ffff6b65ce3 in epicsExitCallAtExitsPvt (pep=) at
> ../../../src/libCom/misc/epicsExit.c:95
> #8  epicsExitCallAtExits () at
> ../../../src/libCom/misc/epicsExit.c:113
> #9  0x00007ffff6b66088 in epicsExit (status=0) at
> ../../../src/libCom/misc/epicsExit.c:181
> #10 0x000000000040544d in main (argc=, argv=) at ../iocMain.cpp:21
> So the epicsExit function is hung up in the drvAsynIPPort::cleanup function.  It has called lockPort, but cannot get that mutex.
> No other thread is waiting for a mutex, so it is not a traditional deadlock.  But it seems that some other thread does have that mutex and is blocking the epicsExit thread from continuing.
> It is probably this thread, which is in StreamDevice.
> Do you have StreamDevice records that are I/O Intr scanned?
> Mark
> From: Abdalla Ahmad
> Sent: Tuesday, February 5, 2019 5:53 AM
> To: Mark Rivers
> exit function
> Hi Mark
> No command available which starts with asyn. I cloned the latest asyn from github with the same behavior.
> For the gdb part, attached is the stack trace from gdb for all pending threads.
> Best Regards,
> Abdalla.
> Sent: Monday, February 04, 2019 4:52 PM
> To: Abdalla Ahmad
> exit function
> At the iocsh prompt when the IOC is still running type the command
> help
> It should show a complete list of commands that the iocsh understands.  See which ones start with "asyn".
> Mark
> From: Abdalla Ahmad
> Sent: Monday, February 4, 2019 8:44 AM
> To: Mark Rivers
> exit function
> Hello Mark
> I will apply the gdb tip and get back to you. For the asyn commands, I don't see any asyn command when I type exit.
> On Mon, Feb 4, 2019 at 4:33 PM +0200, "Mark Rivers" <[email protected]<mailto:[email protected]>> wrote:
> Hi Abdalla,
>> asynError in write. Asyn driver says: device:port disconnected.
> During IOC shutdown asyn does close all TCP ports.  However, record processing should have already been shut down, so I don't understand why you are getting that message from Stream.
> Another problem we are facing with this new setup is that I can't find some asyn IOC shell function like asynTraceMask for example. The IOC is configured properly in RELEASE and src/Makefile. Is there anything we miss in the new setup?
>> But eventually the IOC exits. For the gamma controllers we get something really strange.
>> There a point in the database where the IOC never exits, the exit command just freezes and Ctrl-C is the only way to shut down the IOC.
> I don't think I have seen that with Stream on any version of Stream/asyn/base that I have used.  That includes base 3.14.12, 3.15.5, 7.0.2.
> If you run the IOC with gdb then when you type exit and it hangs do the following:
> - Type Ctrl-C
> - Enter the gdb command
> thread apply all bt
> That will show you the current stack trace for all threads.  You can then see what is blocking the threads.
> The command is not "asynTraceMask" it is "asynSetTraceMask" or "asynSetTraceIOMask".
> What asyn commands do you see if you type "help" at the iocsh prompt?
> Mark
> From:
> on behalf of Abdalla Ahmad via Tech-talk
> Sent: Monday, February 4, 2019 1:41 AM
> To: [email protected]<mailto:[email protected]>
> Subject: Weird stream device behavior when using the IOC shell's exit
> function
> Hi
> We are using the following setup to test control of the agilent XGS gauge controllers and Gamma ion pump controllers:
> 1.       EPICS Base 3.15.6
> 2.       Asyn R4-33
> 3.       Stream R2-7-7c
> For agilent controllers we get the following error:
> But eventually the IOC exits. For the gamma controllers we get something really strange. There a point in the database where the IOC never exits, the exit command just freezes and Ctrl-C is the only way to shut down the IOC. For now I can see that this behavior occurs because more DB substitutions are configured which means more PVs and more controllers. But that was not the case when we had:
> 1.       EPICS Base 3.14.12.3
> 2.       Asyn R4-18
> 3.       Stream R2-5-1
> Where the IOC exits with no errors or freezing. Should we upgrade our support modules or change the EPICS base?
> Best Regards,
> Abdalla Ahmad
> Control Engineer
> SESAME
> Allan, Jordan.
> Tel: (+962-5) 3511348 , ext. 265
> Fax: (+962-5) 3511423
> Mob: (+962-7)88183296
> http://www.sesame.org.jo/
</[email protected]</[email protected]</[email protected]
Attachment: gamma-ion-pump.substitutions
Description: gamma-ion-pump.substitutions
Attachment: gamma-ion-pump.template
Description: gamma-ion-pump.template
Attachment: gamma-qpc.proto
Description: gamma-qpc.proto
RE: Weird stream device behavior when using the IOC shell's exit function Mark Rivers via Tech-talk
Weird stream device behavior when using the IOC shell's exit function Abdalla Ahmad via Tech-talk
Re: Weird stream device behavior when using the IOC shell's exit function Mark Rivers via Tech-talk
Re: Weird stream device behavior when using the IOC shell's exit function Abdalla Ahmad via Tech-talk
RE: Weird stream device behavior when using the IOC shell's exit function Abdalla Ahmad via Tech-talk
Prev: Re: Weird stream device behavior when using the IOC shell's exit function Mark Rivers via Tech-talk
Next: Re: Point Grey GigE Blackfly conflict Mark Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025
Next: RE: Weird stream device behavior when using the IOC shell's exit function Mark Rivers via Tech-talk
ANJ, 07 Feb 2019 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions ·
