Subject: RE: EtherIP EPICS Support: Invalid Service 0x52
From: "Guerra, Roy Ignacio via Tech-talk" <[email protected]>
To: "Kasemir, Kay" <[email protected]>, "[email protected]" <[email protected]>
Date: Wed, 15 Jan 2020 23:06:01 +0000
Thanks for the suggestions!
I’ve been able to narrow down the problem to a group of tags associated with faults for a gate valve.
The group of tags are prefixed with “GV1.Fault.<name>”, where <name> is the specific fault being monitored.
There are ten tags with this prefix. Three of these tags must be commented out in order for the EIP driver to load without error.
When all the tags are included, the error displayed on IOC shell from EIP_verbosity = 10 is:
EncapsulationHeader:
    UINT  command   = 0x6F (SendRRData)
    UINT  length    = 0
    UDINT session   = 0x11029111
    UDINT status    = 0x00000065  (invalid data length)
    USINT context[8]= 'Funstuff'
    UDINT options   = 0x00000000
Received RR Data
    UDINT interface handle  0
    UINT timeout            0
    UINT count (addr+data)  2
    UINT address_type       0x0 (UCMM)
    UINT address_length     0
    UINT data_type          0xB2 (Unconnected Message)
    UINT data_length        514
2020/01/15 13:52:59.7118 EIP process_ScanList: Error in response
Tag 0: 'GV1.Fault.Opened_Switch'
Tag 1: 'GV1.Fault.Fail_to_Open'
Tag 2: 'GV1.Fault.Fully_Open'
Tag 3: 'GV1.Fault.Fully_Close'
Tag 4: 'GV1.Fault.Beam_Exposure'
Tag 5: 'GV1.Fault.No_Switch'
Tag 6: 'Flow1.Below_Set_Point_Trip'
Tag 7: 'Flow2.Below_Set_Point_Trip'
Tag 8: 'Flow3.Below_Set_Point_Trip'
Tag 9: 'Flow4.Below_Set_Point_Trip'
Tag 10: 'Flow5.Below_Set_Point_Trip'
Tag 11: 'Flow6.Below_Set_Point_Trip'
Tag 12: 'Flow7.Below_Set_Point_Trip'
Tag 13: 'Flow8.Below_Set_Point_Trip'
CIP_MultiRequest reply: invalid service 0x52
It appears to be a problem with data length?
Sent: Wednesday, January 15, 2020 7:40 AM
To: [email protected]; Guerra, Roy Ignacio <[email protected]>
Subject: Re: EtherIP EPICS Support: Invalid Service 0x52
Seems strange.
> CIP_MultiRequest reply: invalid service 0x52..
> found some info online stating CIP service code 0x52 is an Allen-Bradley proprietary “read tag fragmented service”
We send a request with 'MultiRequest (0x0A)' content, somewhat like this:
MultiRequest (0x0A):
   ReadData(0x4C) 'tag 1'
   ReadData(0x4C) 'tag 2'
   ReadData(0x4C) 'tag 3'
For a reply, we expect this:
MultiRequest reply (0x0A|0x80):
   ReadData reply (0x4C|0x80) data for tag 1
   ReadData reply (0x4C|0x80) data for tag 2
   ReadData reply (0x4C|0x80) data for tag 3
Instead of 0x0A|0x80 = 0x8A we seem to get 0x52. That's a request, not a reply.
To debug this, I would start small.
Put only one record into your database, set the EIP_verbosity high enough, and you should see that the driver sends a MultiRequest for reading just that one tag.
Add more records back in, observe how the driver sends MultiRequests for more tags. Eventually either the request or the expected response size exceeds the EIP_buffer_limit, so now it sends several
MultiRequests. At some point you should then get the error, so try to figure out when.
Is it when you add records that read tagx[0], tagx[1], tagx[2], ..tagx[100], ... so when the driver tries to read the tagx array, 100 elements, the package size is too big?
The usual response from the PLC should be 'Buffer too small, partial data only', but maybe you get a different type of error.
-Kay
From: Tech-talk <[email protected]> on behalf of Guerra, Roy Ignacio via Tech-talk <[email protected]>
Sent: Tuesday, January 14, 2020 3:35 PM
To:
[email protected] <[email protected]>
Subject: [EXTERNAL] EtherIP EPICS Support: Invalid Service 0x52
Hi all,
I am setting up an IOC to interface with a Control Logix 5000 PLC using the EtherIP EPICS support.
I’ve successfully set everything up and can read all but three tags from the PLC.
For the three tags that are not working, when I include them in the substitution file, I get an error displayed to the IOC shell every few seconds:
EIP connecting bleps
< list of tags >
2020/01/14 14:14:34.5732 EIP disconnecting bleps
(‘bleps’ is the name of the PLC, and I’ve removed the list of PLC tags).
I’ve checked that the three tags which are causing the “invalid service” error exist and respond using the ether_ip_test utility, and all the tags can be queried using caget, so communication through the EtherIP support is successful.
The problem at hand is on my MEDM display screen, red/green ovals for bool-type alarm tags show as white (color mode is set to alarm), and their “Alarm” state is “INVALID”.
Simply not including the three tags that cause the problem alleviates the invalid alarm states, and the display works correctly.
I’ve found some info online stating CIP service code 0x52 is an Allen-Bradley proprietary “read tag fragmented service”; does the EtherIP support not support this service, and if this is the case, does anyone have experience reconfiguring the tags so they do not use this service?
Thanks!
Roy Guerra
Pronouns: they, them, theirs
Control System Applications Assistant
Beamline Controls and Data Acquisition, X-Ray Science Division, Advanced Photon Source
Re: EtherIP EPICS Support: Invalid Service 0x52 Kasemir, Kay via Tech-talk
EtherIP EPICS Support: Invalid Service 0x52 Guerra, Roy Ignacio via Tech-talk
Prev: Re: Killing caRepeater on Windows 10 Hill, Jeff via Tech-talk
Next: Fw: Multiline statement in iocsh Mark Rivers via Tech-talk
Prev: Re: EtherIP EPICS Support: Invalid Service 0x52 Kasemir, Kay via Tech-talk
Next: Re: EtherIP EPICS Support: Invalid Service 0x52 Kasemir, Kay via Tech-talk