Subject: Re: Modbus alarms question
From: John Dobbins via Tech-talk <[email protected]>
Cc: EPICS tech-talk <[email protected]>
Date: Wed, 8 Jul 2020 18:58:54 +0000
Thanks. I'll start by upgrading to latest version and do a new test.  After the test I'll send all the details.
John
Sent: Wednesday, July 8, 2020 1:38 PM
To: John Dobbins <[email protected]>
Hi John,
Some questions:
- What version of asyn are you using?
- Are you using relative or absolute Modbus addressing?
- Is this Modbus TCP over Ethernet?
- For the records that generate the alarm, what is:
    - The record type
    - The Modbus function code
    - The SCAN rate
    - The polling rate of the modbus driver
    - The time between alarm status changes
- Is it possible for you update to modbus R3-0 and see if the problem persists?  It will make it easier for me to fix if you are running the latest release.
The alarm status is set according to the status returned by the function doModusIO().  The driver should only do callbacks with a new alarm status when that status return changes.
It would probably be a good idea to turn on asynTrace of the underlying asynIPPort driver and see if its status is changing.
From: Tech-talk <[email protected]> on behalf of John Dobbins via Tech-talk <[email protected]>
Sent: Wednesday, July 8, 2020 11:54 AM
To: [email protected]
Subject: Modbus alarms question
All,
We have a PLC from which data is read by an IOC via Modbus (R2-11).  The PLC was turned off and while the PLC was off the IOC generated a stream of alarm messages from the Alarm Server (BEAST) while the PVs toggled between
SEVERITY: INVALID           STATUS: READ_ALARM
and
SEVERITY:  INVALID           STATUS: TIMEOUT_ALARM
Aside from configuring these alarms to be latching in the Alarm Server configuration is there some other way to make it so this state (loss of modbus communication) doesn't generate a stream of alarms?
John Dobbins
Research Support Specialist
Cornell High Energy Synchrotron Source
Cornell University
www.chess.cornell.edu
Modbus alarms question John Dobbins via Tech-talk
Re: Modbus alarms question Mark Rivers via Tech-talk
Prev: Re: Asyn/StreamDevice for HP3458A through Agilent E5810 LAN/GPIB Gateway Michael Davidsaver via Tech-talk
Next: RE: Process at Init of mbbo-record Mark Rivers via Tech-talk
Prev: Re: Modbus alarms question Mark Rivers via Tech-talk
Next: RE: Modbus alarms question Mark Rivers via Tech-talk
