1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Subject: Re: A problem with modbus reading floating point numbers
From: Mark L Rivers via Tech-talk <[email protected]>
To: 高振华 <[email protected]>
Date: Wed, 17 Nov 2021 14:22:52 +0000
Hi Gao,
I think I see the problem:
file "../../db/ai.template" { pattern
{P,         R,      PORT,               OFFSET, BITS,  EGUL,  EGUF,   PREC,   SCAN}
{MOXA:,    ADC1,   MOXA_E1242_In_Word,   0,      16,   0.,    65535.,    3,      "I/O Intr"}
{MOXA:,    ADC2,   MOXA_E1242_In_Word,   1,      16,   0.,    65535.,    3,      "I/O Intr"}
You have set EGUF to 65535.  If you do that then the ai record will do a linear conversion, but the output values in EGU units will be the same as the input values in RAW units.  You should set the EGUF to be the maximum value of the ADC in the engineering units you want to use.  For example, if it is a 0 to 10V ADC then you can set EGUF=10 and then the ai record will be in the units of volts.  If it is -10V to 10V ADC you should set EGUL=-10.
Sent: Wednesday, November 17, 2021 2:36 AM
To: Mark L Rivers <[email protected]>
Cc: [email protected] <[email protected]>
Subject: A problem with modbus reading floating point numbers
Hi Mark,
I am reading the ai value of moxa E1242 multifunctional IO module and I have a problem,
Cannot display floating point numbers, only integer numbers,
cannot display decimal places.
What's the reason? thanks.
#moxa1242.cmd
#!./../../bin/linux-x86_64/modbusApp
< envPaths
dbLoadDatabase("../../dbd/modbus.dbd")
modbus_registerRecordDeviceDriver(pdbbase)
drvAsynIPPortConfigure("moxa","192.168.127.254:502",0,0,1)
asynSetOption("moxa",0, "disconnectOnReadTimeout", "Y")
modbusInterposeConfig("moxa",0,5000,0)
#read moxa E1242 AI_scaledValue,7 is little endian,8 is big endian
drvModbusAsynConfigure("MOXA_E1242_In_Word",   "moxa",    255, 4,  0x208,  0x8,    0x7,  2000,    "moxa E1242")
# Enable ASYN_TRACEIO_HEX on octet server
asynSetTraceIOMask("moxa",0,4)
# Enable ASYN_TRACE_ERROR and ASYN_TRACEIO_DRIVER on octet server
asynSetTraceMask("moxa",0,9)
dbLoadTemplate("moxa1242.substitutions")
iocInit
asynReport 1
dbl
#moxa1242.substitutions
#asyn record for the underlying asyn octet port
file "$(ASYN)/db/asynRecord.db" { pattern
{P,           R,       PORT,      ADDR,   IMAX,    OMAX}
{MOXA:    OctetAsyn,    moxa,     0,      80,      80}
#ai.template
record(ai, "$(P)$(R)_AI") {
    field(DTYP,"asynInt32")
    field(INP,"@asynMask($(PORT) $(OFFSET) $(BITS))MODBUS_DATA")
    field(LINR,"LINEAR")
#    field(LINR,"NO CONVERSION")
    field(EGUL,"$(EGUL)")
    field(EGUF,"$(EGUF)")
    field(HOPR,"$(EGUF)")
    field(LOPR,"$(EGUL)")
    field(PREC,"$(PREC)")
    field(SCAN,"$(SCAN)")
#traceIO
2021/11/17 15:41:17.075 192.168.127.254:502 write 12
01 17 00 00 00 06 ff 04 02 08 00 08
2021/11/17 15:41:17.083 192.168.127.254:502 read 25
01 17 00 00 00 13 ff 04 10 13 b0 40 f0 00 00 00 00 00 dc 3b
5c 00 a0 3b a0
#caget display
[gaozh@localhost db]$ caget MOXA:ADC1_AI
MOXA:ADC1_AI                   7
note:The actual input is 7.5V.
application environment:
EPICS 7.0.3
Asyn R4-33
Modbus R2-11
Gao Zhenhua
BSRF(Beijing Synchrotron Radiation Facility)
Email:[email protected]
Re: Re: A problem with modbus reading floating point numbers 高振华 via Tech-talk
Prev: Re: A problem with modbus reading floating point numbers Mark L Rivers via Tech-talk
Next: support for Moxa ioLogik modules Pearson, Matthew R. via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  <2021>  2022  2023  2024  2025  2026
Next: Re: Re: A problem with modbus reading floating point numbers 高振华 via Tech-talk