1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024
Subject: RE: Modbus for Huber Pilotone
From: Mark Rivers via Tech-talk <tech-talk at aps.anl.gov>
To: Florian Feldbauer <florian at ep1.ruhr-uni-bochum.de>
Cc: "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>
Date: Thu, 19 May 2022 19:03:32 +0000
Hi Florian,
Ø  For reading out the status of the chiller, I have set the SCAN field of the first input record and use a chain of forward links to all the other input records.
Ø  My guess is, the forward links are processed "too fast" for the controller and it cannot reply.
Is this plausible or could this error messages have a different cause?
What would be a good idea to "slow down" the readout?
Using a seq record with delays instead of forward links?
I see you defined your driver to use absolute addressing.  That is not the way it is typically used.  If you change to relative addressing then when you process your input records they don’t actually cause any Modbus I/O, they just return the most recent poll reading from the driver.  That means there is no reason to “slow down” the readout, since it is not affecting the Modbus communications.  If your drivers are polling (not absolute addresses) then you should probably not set your input records to periodically scan, but rather set them SCAN=I/O Intr.  Then the records will only process when the polled value changes.
I am not sure why it is not sending the correct value for the temperature.
What version of the Modbus driver are you using?  If the device sends a Modbus exception then I believe some older versions of the driver would not show you that, and it would appear that you received no response.
From: Tech-talk <tech-talk-bounces at aps.anl.gov> On Behalf Of Florian Feldbauer via Tech-talk
Sent: Thursday, May 19, 2022 10:15 AM
To: tech-talk at aps.anl.gov
Subject: Modbus for Huber Pilotone
Hey all,
we have a Huber Unistat chiller with "PilotOne" Controller. The Controller has a modbus/TCP interface.
Sometimes I can see messages of the following type in my IOC:
epics> 2022/05/19 16:46:36.370 drvModbusAsyn::doModbusIO port chillerReadReg error calling writeRead, error=PilotONE-187144:502 TCP timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2022/05/19 16:46:36.370 SCATTERCHAMBER:COOLING:FillLevel devAsynInt32::processCallbackInput process read error
2022/05/19 16:46:36.469 drvModbusAsyn::doModbusIO port chillerReadReg writeRead status back to normal having had 1 errors, nwrite=6/6, nread=4
Another issue, that I have is writing the Setpoint of the device. From the manual:
The client sends the following request to the Modbus slave:
  00 02 00 00 00 06 FF 06 00 00 05 DC
The command is made up as follows:
00 02    TID (any number that can be used to assign a response to a query)
00 00    PID (always 0x0000)
00 06    The message length is 6 bytes. Of these, 1 byte is used for the unit identifier, 1 byte
          for the function code, 2 bytes for the PB address and 2 bytes are used for the value
          to be written.
FF      Unit identifier (UID, always 0xFF)
06      Function code 0x06 is used for Writing Single Holding Registers
00 00    PB address (vSP 0x00)
05 DC    The setpoint temperature is to be set to 15.00 °C. The value 1500 equals 0x05DC in
         hex notation.
The Modbus slave returns the following response:
For me it looks like this:
epics> dbpf SCATTERCHAMBER:COOLING:Setpoint 15
DBF_DOUBLE:         15
2022/05/19 17:04:09.078 drvModbusAsyn::doModbusIO port chillerWriteReg WRITE_SINGLE_REGISTER address=00 value=0x0
epics> 2022/05/19 17:04:09.078 PilotONE-187144:502 TCP write 12
a2 3e 00 00 00 06 ff 06 00 00 00 00
2022/05/19 17:04:09.078 PilotONE-187144:502 TCP read 0
2022/05/19 17:04:09.079 drvModbusAsyn::doModbusIO port chillerWriteReg called pasynOctetSyncIO->writeRead, status=3, requestSize=6, replySize=5, nwrite=6, nread=0, eomReason=0
epics>
First, the value (15) is not send, instead 00 00 is send. Second I do not get a reply from the device.
I load the driver with
drvAsynIPPortConfigure( "chiller", "PilotONE-187144:502 TCP", 0, 0, 0 )
modbusInterposeConfig( "chiller", 0, 300, 0 )
drvModbusAsynConfigure( "chillerWriteReg",  "chiller", 0xff, 6, -1, 1, "INT16", 0, "Huber PilotOne" )
The record looks like this:
record( ao, "$(H):$(N):Setpoint" ) {
  field( DTYP, "asynInt32" )
  field( OUT,  "@asyn($(PORT_W) 0x00)INT16" )
  field( EGU,  "degC" )
  field( PREC, "2" )
  field( ADEL, "1" )
  field( MDEL, "1" )
  field( ASLO, "100" )
  field( AOFF, "0" )
Any idea what am I doing wrong here?
Thanks for your help,
Florian
Ruhr-Universität Bochum
AG der Experimentalphysik I
Dr. Florian Feldbauer
NB 2/131 / Fach 125
Universitätsstr. 150
D-44801 Bochum
Office: NB 2/134
Phone:  (+49)234 / 32-23563
Fax:    (+49)234 / 32-14170
https://paluma.ruhr-uni-bochum.de
Re: Modbus for Huber Pilotone Florian Feldbauer via Tech-talk
Prev: Modbus for Huber Pilotone Florian Feldbauer via Tech-talk
Next: Re: Modbus for Huber Pilotone Florian Feldbauer via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024
ANJ, 14 Sep 2022 Valid HTML 4.01! · Home · News · About · Base · Modules · Extensions · Distributions · Download ·