1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026
Subject: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
From: Till Straumann via Tech-talk <[email protected]>
To: "Engbretson, Mark S." <[email protected]>, "Rivers, Mark L." <[email protected]>, "[email protected]" <[email protected]>
Date: Mon, 13 Jun 2022 21:49:10 +0200
On 6/13/22 21:27, Engbretson, Mark S. via Tech-talk wrote:
RE: ”By setting the mapping in the BSP correctly the PowerPC receives a different exception when that happens, which it can correctly handle.”
And how/where is that actually now being done correctly? In Epics base?
It is handled (actually: ignored) in the CPU itself. In this case the problem was associated with a jump
instruction that targeted an address in VME space. Also, a condition was tested and the jump was executed
only if the condition was true and this was never the case:
  if ( cond ) {
    fnPtr();
However, it is possible that the CPU (in an attempt to keep all its internal units as busy as possible)
starts executing the if block 'speculatively' *before* the condition is evaluated. If the address in 'fnPtr'
is either invalid (no mapping in the MMU exists) or points to an invalid instruction (in 'normal' memory)
then an exception is flagged in the CPU itself (since the MMU and instruction-decoding are part of the CPU).
When the condition eventually evaluates to 'false' then everything that was done 'speculatively' is simply
discarded (including the exception).
What I just described is the 'normal' scenario that happens all the time.
A problem arises if there *is* a mapping in the MMU which maps an address range that does *not* behave
like normal memory. This is what happened in the present case. The speculative execution of the jump
found a mapping and tried to load the target instruction from VME. Because there was nothing present,
the resulting PCI target abort caused the host bridge to assert a special interrupt line which results in a
'machine-check' exception. The CPU has no way of knowing that the reason for this machine-check
was the speculative load of the jump target and therefore cannot ignore it when the condition eventually
is evaluated as 'false'.
The solution marks the mapping of the VME address space as 'guarded' in the MMU which forbids any
type of speculative access.
HTH
- Till
From: Tech-talk <[email protected]> On Behalf Of Mark Rivers via Tech-talk
Sent: Monday, June 13, 2022 1:49 PM
To: [email protected]
Subject: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules
Folks,
I’m happy to report that after 3.5 weeks this problem is finally solved!
The bottom line is that it was an issue with the vxWorks Board Support Package (BSP) we are using at the APS.  The problem was that the mapping was not correctly configured to set the VME memory space as “guarded”.  That guarding prevents certain memory operations like speculative branch execution from happening in the VME memory space.
This BSP problem has existed for a long time, but did not manifest itself until base 7.0.6, where some changes were made to the db_field_log structure.  That structure contains a union which can either hold a record field value or a pointer to a destructor, depending on a flag bit in db_field_log.  It appears that the PowerPC processor was doing a speculative branch which called the destructor.  That was the wrong branch, because the flag said the union held a field value, not a pointer to a destructor.  If the value was a double in the range -2.0 to -0.5 then its high-order 32 bits correspond to a VME A32 address, and the speculative branch execution tried to execute the destructor at that VME address.  It then got a “machine check” with an A32 VME bus error.
Thanks very much to Till Straumann, Michael Davidsaver, Andrew Johnson, and Steven Hartman for their help in tracking this down.
Base R7.0.6.1 now runs fine on my VME IOCs that were having this problem.
Sent: Thursday, June 9, 2022 4:49 PM
To: Till Straumann <[email protected]>
Cc: [email protected]
Hi Till,
I tried your test program where I expanded to 36 NOPs.
void address_test() {
   *(volatile uint16_t*)0xfbff345e = 0;
   asm volatile( "   addi 3, 3, 0"); /* I hope I remember this correctly; this is just a NOP */
   /* copy/paste ~30 of these NOPs here */
Much to my surprise the program does not generate a bus error.  The two A16 addresses that it most frequently failed with were 0x345e and 0x347e.  Your program tests the first one.
iocexample> address_test
value = 0 = 0x0
I then tried writing to those A16 addresses manually from the vxWorks shell.  I can write to both of them with no bus error.  So I was wrong, those addresses are both readable and writeable.
iocexample> *0xfbff345e = 0
address_test + 0xf8a6281e = 0xfbff345e: value = 0 = 0x0
iocexample> *0xfbff347e = 0
address_test + 0xf8a6283e = 0xfbff347e: value = 65353 = 0xff49 = 'I'
However, if I try the next address after 7e I do get a bus error, because that is beyond the range of the IP330 module.
iocexample> *0xfbff3480 = 0
VME Bus Error accessing A16: 0x3480
machine check
Exception next instruction address: 0x001fe4f4
Machine Status Register: 0x0008b032
Condition Register: 0x88000244
0x0012489c vxTaskEntry  +0x48 : 0x0020c554 ()
0x0020c554 shellTask    +0x4a8: shellExec ()
0x0020c020 shellExec    +0x11c: 0x00201a78 ()
0x00201ca0 shellInterpCInit+0x640: shellInterpCparse ()
0x00201384 shellInterpCparse+0xa3c: 0x001fe9f4 ()
0x001fea24 shellInterpClex+0x1d6c: 0x001fe6dc ()
0x001fe7a0 shellInterpClex+0x1ae8: 0x001fe490 ()
Shell task 'tShell0' restarted...
So this leaves the question of why we get those A16 bus errors at all!
Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Michael Davidsaver via Tech-talk
Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Till Straumann via Tech-talk
RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Engbretson, Mark S. via Tech-talk
Prev: RE: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Mark Rivers via Tech-talk
Next: Problem with NTP configuration Francisco Ramos via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <20222023  2024  2025  2026
Next: Re: Bus errors accessing VME with base 7.0.6.1 and latest synApps modules Oleg Makarov via Tech-talk