1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  <2025>  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  <2025>  2026
Subject: RE: brushless dc motor MRES IS N/A
To: "Tran, Phi Dung" <[email protected]>, "Peterson, Kevin M." <[email protected]>, "[email protected]" <[email protected]>
Date: Mon, 6 Jan 2025 16:01:27 +0000
Hi Alex,
If you are using a DC motor with encoder then I recommend you set RTRY to 0.  You should let the controller do the PID, and not involve the EPICS motor record.  RTRY is useful for stepper motors with encoders, when the controller is running open-loop.  Then the motor record can attempt to correct for the errors at the end of the move.
From: Tech-talk <[email protected]> On Behalf Of Tran, Phi Dung via Tech-talk
Sent: Monday, January 6, 2025 9:15 AM
To: Peterson, Kevin M. <[email protected]>; [email protected]
Subject: Re: brushless dc motor MRES IS N/A
Hi Kevin,
Hi Kevin,
I used the ACS motion controller software to move the motors to their target positions successfully.
However, after configuring the EPICS substitution files with the following parameters:
bash
Copy code
{N,   M,       DTYP,         PORT,  ADDR,  DESC,          EGU, DIR,  VELO,  VBAS,  ACCL,  BDST,  BVEL,  BACC,  MRES,         PREC,  DHLM,  DLLM,  INIT}
# 2.54 mm/rev, 200 steps/rev, 1024 microsteps/step
{1,  "m$(N)",  "asynMotor",  ACS1,  0,     "VerY $(N)",   mm,  Pos,  2.2,    2,     4,    0,   2.2,    4,    9.765625e-07,  4,     400,    0,  ""}
I observed that the motor oscillates around the target positions until the retry limit is exceeded. I have attempted adjustments using PID and FRAC settings without success.
Could this issue be related to the VMAX parameter being set to 0? What would be the best approach to resolve this problem?
Best regards,
Alex Tran
Sent: Thursday, December 19, 2024 6:18 PM
To:
[email protected] <[email protected]>; Tran, Phi Dung <[email protected]>
There are multiple reasons why the MRES should be set to the ERES for DC brushless motors:
* The MRES, not the ERES, is used by the motor record to convert velocities and accelerations from EGU into controller units
* The MRES, not the ERES, is used to synchronize the raw limit fields with the dial and user limit fields
* The absolute value of the MRES is used as the minimum retry deadband
* The MRES, not the ERES, is used to calculate the raw position to send to the controller when the motor record's dial position is being redefined
* If a user changes UEIP to "No", the motor will still work if MRES == ERES (assuming the motor driver sets both the RMP and REP to the same value)
Kevin
[email protected]> on behalf of Tran, Phi Dung via Tech-talk <[email protected]>
Sent: Thursday, December 19, 2024 10:10 AM
To:
[email protected]
Subject: brushless dc motor MRES IS N/A
hI,
I am using a DC brushless motor with an encoder. For the motor record, I will define ERES and set UEIP to YES. That's it; my MRES is not applicable therefore, I will not include this field..
However, experts have advised that I should set MRES equal to ERES. What is the rationale behind this? Is it to ensure that when UEIP is set to NO, the motor still operates correctly?
Alex
Re: brushless dc motor MRES IS N/A Tran, Phi Dung via Tech-talk
Prev: Re: brushless dc motor MRES IS N/A Tran, Phi Dung via Tech-talk
Next: Re: Cross-compiling epics for petalinux Johnson, Andrew N. via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  <2025>  2026
Next: Re: brushless dc motor MRES IS N/A Peterson, Kevin M. via Tech-talk