1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>
Subject: Re: problems with SNL - sevr=minor ca_array_get_callback [...]: Virtual circuit disconnect
From: Dariush Hampai via Tech-talk <tech-talk at aps.anl.gov>
To: Žiga Oven <ziga.oven at cosylab.com>, "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>
Date: Fri, 9 Jan 2026 08:42:52 +0100
Hi Ziga,
I tried and after calling "seqcar 2” before assigning the variables it works for a while… then it stops again…
It seems the problem is rabdom!!!
After calling “status_mode=4"
*** Prepare Loop ***
motor to move = 0
start[0]= 1000.000000
1 ### These numbers are flags for debug
2
3
motor to move = 1
start[1]= 1500.000000
1
2
3
sevr=minor ca_array_get_callback( typeToCA(type), count, var->chid, pvCaGetHandler, arg): Virtual circuit disconnect
However I’ll report the output of seqcar 2 before and after the PV assignment
##### BEFORE:
Program "xena_sncscan"
    Variable "name_exp_pv" connected to PV "xena:experiment"
    Variable "status_mode" connected to PV "xena:status"
    Variable "actual_status" connected to PV "xena:state"
    Variable "scan_busy" connected to PV "xena:scan_busy"
    Variable "scan_pause" connected to PV "xena:scan_pause"
    Variable "scan_restart" connected to PV "xena:scan_restart"
    Variable "scan_abort" connected to PV "xena:scan_abort"
    Variable "num_mot" connected to PV "xena:num_motor"
    Variable "num_det" connected to PV "xena:num_detector"
    Variable "start" connected to PV "xena:start"
    Variable "end" connected to PV "xena:end"
    Variable "step" connected to PV "xena:step"
    Variable "total_points" connected to PV "xena:total_points"
    Variable "current_point" connected to PV "xena:current_point"
    Variable "scan_progress" connected to PV "xena:scan_progress"
    Variable "motor" connected to PV "xena:motor"
    Variable "mot_command" connected to PV "xena:motor_command"
    Variable "detector" connected to PV "xena:detector"
    Variable "det_command" connected to PV "xena:detector_command"
    Variable "motget" not assigned to PV
    Variable "motset" not assigned to PV
    Variable "detget" not assigned to PV
    Variable "detset" not assigned to PV
    Variable "motor_mr[0]" not assigned to PV
    Variable "motor_mr[1]" not assigned to PV
    Variable "motor_mr[2]" not assigned to PV
    Variable "motor_mr[3]" not assigned to PV
    Variable "motor_mr[4]" not assigned to PV
    Variable "motor_mr[5]" not assigned to PV
    Variable "motor_mr[6]" not assigned to PV
    Variable "motor_mr[7]" not assigned to PV
    Variable "motor_mr[8]" not assigned to PV
    Variable "motor_mr[9]" not assigned to PV
    Variable "motor_mr[10]" not assigned to PV
    Variable "motor_mr[11]" not assigned to PV
    Variable "motor_mr[12]" not assigned to PV
    Variable "motor_mr[13]" not assigned to PV
    Variable "motor_mr[14]" not assigned to PV
    Variable "motor_mr[15]" not assigned to PV
    Variable "motor_mr[16]" not assigned to PV
    Variable "motor_mr[17]" not assigned to PV
    Variable "motor_mr[18]" not assigned to PV
    Variable "motor_mr[19]" not assigned to PV
    Variable "motor_ma[0]" not assigned to PV
    Variable "motor_ma[1]" not assigned to PV
    Variable "motor_ma[2]" not assigned to PV
    Variable "motor_ma[3]" not assigned to PV
    Variable "motor_ma[4]" not assigned to PV
    Variable "motor_ma[5]" not assigned to PV
    Variable "motor_ma[6]" not assigned to PV
    Variable "motor_ma[7]" not assigned to PV
    Variable "motor_ma[8]" not assigned to PV
    Variable "motor_ma[9]" not assigned to PV
    Variable "motor_ma[10]" not assigned to PV
    Variable "motor_ma[11]" not assigned to PV
    Variable "motor_ma[12]" not assigned to PV
    Variable "motor_ma[13]" not assigned to PV
    Variable "motor_ma[14]" not assigned to PV
    Variable "motor_ma[15]" not assigned to PV
    Variable "motor_ma[16]" not assigned to PV
    Variable "motor_ma[17]" not assigned to PV
    Variable "motor_ma[18]" not assigned to PV
    Variable "motor_ma[19]" not assigned to PV
    Variable "motor_reqmov[0]" not assigned to PV
    Variable "motor_reqmov[1]" not assigned to PV
    Variable "motor_reqmov[2]" not assigned to PV
    Variable "motor_reqmov[3]" not assigned to PV
    Variable "motor_reqmov[4]" not assigned to PV
    Variable "motor_reqmov[5]" not assigned to PV
    Variable "motor_reqmov[6]" not assigned to PV
    Variable "motor_reqmov[7]" not assigned to PV
    Variable "motor_reqmov[8]" not assigned to PV
    Variable "motor_reqmov[9]" not assigned to PV
    Variable "motor_reqmov[10]" not assigned to PV
    Variable "motor_reqmov[11]" not assigned to PV
    Variable "motor_reqmov[12]" not assigned to PV
    Variable "motor_reqmov[13]" not assigned to PV
    Variable "motor_reqmov[14]" not assigned to PV
    Variable "motor_reqmov[15]" not assigned to PV
    Variable "motor_reqmov[16]" not assigned to PV
    Variable "motor_reqmov[17]" not assigned to PV
    Variable "motor_reqmov[18]" not assigned to PV
    Variable "motor_reqmov[19]" not assigned to PV
    Variable "motor_mov[0]" not assigned to PV
    Variable "motor_mov[1]" not assigned to PV
    Variable "motor_mov[2]" not assigned to PV
    Variable "motor_mov[3]" not assigned to PV
    Variable "motor_mov[4]" not assigned to PV
    Variable "motor_mov[5]" not assigned to PV
    Variable "motor_mov[6]" not assigned to PV
    Variable "motor_mov[7]" not assigned to PV
    Variable "motor_mov[8]" not assigned to PV
    Variable "motor_mov[9]" not assigned to PV
    Variable "motor_mov[10]" not assigned to PV
    Variable "motor_mov[11]" not assigned to PV
    Variable "motor_mov[12]" not assigned to PV
    Variable "motor_mov[13]" not assigned to PV
    Variable "motor_mov[14]" not assigned to PV
    Variable "motor_mov[15]" not assigned to PV
    Variable "motor_mov[16]" not assigned to PV
    Variable "motor_mov[17]" not assigned to PV
    Variable "motor_mov[18]" not assigned to PV
    Variable "motor_mov[19]" not assigned to PV
    Variable "motor_reqpos[0]" not assigned to PV
    Variable "motor_reqpos[1]" not assigned to PV
    Variable "motor_reqpos[2]" not assigned to PV
    Variable "motor_reqpos[3]" not assigned to PV
    Variable "motor_reqpos[4]" not assigned to PV
    Variable "motor_reqpos[5]" not assigned to PV
    Variable "motor_reqpos[6]" not assigned to PV
    Variable "motor_reqpos[7]" not assigned to PV
    Variable "motor_reqpos[8]" not assigned to PV
    Variable "motor_reqpos[9]" not assigned to PV
    Variable "motor_reqpos[10]" not assigned to PV
    Variable "motor_reqpos[11]" not assigned to PV
    Variable "motor_reqpos[12]" not assigned to PV
    Variable "motor_reqpos[13]" not assigned to PV
    Variable "motor_reqpos[14]" not assigned to PV
    Variable "motor_reqpos[15]" not assigned to PV
    Variable "motor_reqpos[16]" not assigned to PV
    Variable "motor_reqpos[17]" not assigned to PV
    Variable "motor_reqpos[18]" not assigned to PV
    Variable "motor_reqpos[19]" not assigned to PV
    Variable "motor_pos[0]" not assigned to PV
    Variable "motor_pos[1]" not assigned to PV
    Variable "motor_pos[2]" not assigned to PV
    Variable "motor_pos[3]" not assigned to PV
    Variable "motor_pos[4]" not assigned to PV
    Variable "motor_pos[5]" not assigned to PV
    Variable "motor_pos[6]" not assigned to PV
    Variable "motor_pos[7]" not assigned to PV
    Variable "motor_pos[8]" not assigned to PV
    Variable "motor_pos[9]" not assigned to PV
    Variable "motor_pos[10]" not assigned to PV
    Variable "motor_pos[11]" not assigned to PV
    Variable "motor_pos[12]" not assigned to PV
    Variable "motor_pos[13]" not assigned to PV
    Variable "motor_pos[14]" not assigned to PV
    Variable "motor_pos[15]" not assigned to PV
    Variable "motor_pos[16]" not assigned to PV
    Variable "motor_pos[17]" not assigned to PV
    Variable "motor_pos[18]" not assigned to PV
    Variable "motor_pos[19]" not assigned to PV
    Variable "detector_reqstart[0]" not assigned to PV
    Variable "detector_reqstart[1]" not assigned to PV
    Variable "detector_reqstart[2]" not assigned to PV
    Variable "detector_reqstart[3]" not assigned to PV
    Variable "detector_reqstart[4]" not assigned to PV
    Variable "detector_reqstart[5]" not assigned to PV
    Variable "detector_reqstart[6]" not assigned to PV
    Variable "detector_reqstart[7]" not assigned to PV
    Variable "detector_reqstart[8]" not assigned to PV
    Variable "detector_reqstart[9]" not assigned to PV
    Variable "detector_reqstart[10]" not assigned to PV
    Variable "detector_reqstart[11]" not assigned to PV
    Variable "detector_reqstart[12]" not assigned to PV
    Variable "detector_reqstart[13]" not assigned to PV
    Variable "detector_reqstart[14]" not assigned to PV
    Variable "detector_reqstart[15]" not assigned to PV
    Variable "detector_reqstart[16]" not assigned to PV
    Variable "detector_reqstart[17]" not assigned to PV
    Variable "detector_reqstart[18]" not assigned to PV
    Variable "detector_reqstart[19]" not assigned to PV
    Variable "detector_reqready[0]" not assigned to PV
    Variable "detector_reqready[1]" not assigned to PV
    Variable "detector_reqready[2]" not assigned to PV
    Variable "detector_reqready[3]" not assigned to PV
    Variable "detector_reqready[4]" not assigned to PV
    Variable "detector_reqready[5]" not assigned to PV
    Variable "detector_reqready[6]" not assigned to PV
    Variable "detector_reqready[7]" not assigned to PV
    Variable "detector_reqready[8]" not assigned to PV
    Variable "detector_reqready[9]" not assigned to PV
    Variable "detector_reqready[10]" not assigned to PV
    Variable "detector_reqready[11]" not assigned to PV
    Variable "detector_reqready[12]" not assigned to PV
    Variable "detector_reqready[13]" not assigned to PV
    Variable "detector_reqready[14]" not assigned to PV
    Variable "detector_reqready[15]" not assigned to PV
    Variable "detector_reqready[16]" not assigned to PV
    Variable "detector_reqready[17]" not assigned to PV
    Variable "detector_reqready[18]" not assigned to PV
    Variable "detector_reqready[19]" not assigned to PV
    Variable "detector_ready[0]" not assigned to PV
    Variable "detector_ready[1]" not assigned to PV
    Variable "detector_ready[2]" not assigned to PV
    Variable "detector_ready[3]" not assigned to PV
    Variable "detector_ready[4]" not assigned to PV
    Variable "detector_ready[5]" not assigned to PV
    Variable "detector_ready[6]" not assigned to PV
    Variable "detector_ready[7]" not assigned to PV
    Variable "detector_ready[8]" not assigned to PV
    Variable "detector_ready[9]" not assigned to PV
    Variable "detector_ready[10]" not assigned to PV
    Variable "detector_ready[11]" not assigned to PV
    Variable "detector_ready[12]" not assigned to PV
    Variable "detector_ready[13]" not assigned to PV
    Variable "detector_ready[14]" not assigned to PV
    Variable "detector_ready[15]" not assigned to PV
    Variable "detector_ready[16]" not assigned to PV
    Variable "detector_ready[17]" not assigned to PV
    Variable "detector_ready[18]" not assigned to PV
    Variable "detector_ready[19]" not assigned to PV
    Variable "detector_reqdata[0]" not assigned to PV
    Variable "detector_reqdata[1]" not assigned to PV
    Variable "detector_reqdata[2]" not assigned to PV
    Variable "detector_reqdata[3]" not assigned to PV
    Variable "detector_reqdata[4]" not assigned to PV
    Variable "detector_reqdata[5]" not assigned to PV
    Variable "detector_reqdata[6]" not assigned to PV
    Variable "detector_reqdata[7]" not assigned to PV
    Variable "detector_reqdata[8]" not assigned to PV
    Variable "detector_reqdata[9]" not assigned to PV
    Variable "detector_reqdata[10]" not assigned to PV
    Variable "detector_reqdata[11]" not assigned to PV
    Variable "detector_reqdata[12]" not assigned to PV
    Variable "detector_reqdata[13]" not assigned to PV
    Variable "detector_reqdata[14]" not assigned to PV
    Variable "detector_reqdata[15]" not assigned to PV
    Variable "detector_reqdata[16]" not assigned to PV
    Variable "detector_reqdata[17]" not assigned to PV
    Variable "detector_reqdata[18]" not assigned to PV
    Variable "detector_reqdata[19]" not assigned to PV
    Variable "detector_data[0]" not assigned to PV
    Variable "detector_data[1]" not assigned to PV
    Variable "detector_data[2]" not assigned to PV
    Variable "detector_data[3]" not assigned to PV
    Variable "detector_data[4]" not assigned to PV
    Variable "detector_data[5]" not assigned to PV
    Variable "detector_data[6]" not assigned to PV
    Variable "detector_data[7]" not assigned to PV
    Variable "detector_data[8]" not assigned to PV
    Variable "detector_data[9]" not assigned to PV
    Variable "detector_data[10]" not assigned to PV
    Variable "detector_data[11]" not assigned to PV
    Variable "detector_data[12]" not assigned to PV
    Variable "detector_data[13]" not assigned to PV
    Variable "detector_data[14]" not assigned to PV
    Variable "detector_data[15]" not assigned to PV
    Variable "detector_data[16]" not assigned to PV
    Variable "detector_data[17]" not assigned to PV
    Variable "detector_data[18]" not assigned to PV
    Variable "detector_data[19]" not assigned to PV
    Variable "detector_type[0]" not assigned to PV
    Variable "detector_type[1]" not assigned to PV
    Variable "detector_type[2]" not assigned to PV
    Variable "detector_type[3]" not assigned to PV
    Variable "detector_type[4]" not assigned to PV
    Variable "detector_type[5]" not assigned to PV
    Variable "detector_type[6]" not assigned to PV
    Variable "detector_type[7]" not assigned to PV
    Variable "detector_type[8]" not assigned to PV
    Variable "detector_type[9]" not assigned to PV
    Variable "detector_type[10]" not assigned to PV
    Variable "detector_type[11]" not assigned to PV
    Variable "detector_type[12]" not assigned to PV
    Variable "detector_type[13]" not assigned to PV
    Variable "detector_type[14]" not assigned to PV
    Variable "detector_type[15]" not assigned to PV
    Variable "detector_type[16]" not assigned to PV
    Variable "detector_type[17]" not assigned to PV
    Variable "detector_type[18]" not assigned to PV
    Variable "detector_type[19]" not assigned to PV
### AFTER:
    Variable "motor_mr[0]" connected to PV "mm4006_1_1_1:setmr"
    Variable "motor_mr[1]" connected to PV "mm4006_1_1_2:setmr"
    Variable "motor_ma[0]" connected to PV "mm4006_1_1_1:setma"
    Variable "motor_ma[1]" connected to PV "mm4006_1_1_2:setma"
    Variable "motor_reqmov[0]" connected to PV "mm4006_1_1_1:reqmoving"
    Variable "motor_reqmov[1]" connected to PV "mm4006_1_1_2:reqmoving"
    Variable "motor_mov[0]" connected to PV "mm4006_1_1_1:moving"
    Variable "motor_mov[1]" connected to PV "mm4006_1_1_2:moving"
    Variable "motor_reqpos[0]" connected to PV "mm4006_1_1_1:reqpos"
    Variable "motor_reqpos[1]" connected to PV "mm4006_1_1_2:reqpos"
    Variable "motor_pos[0]" connected to PV "mm4006_1_1_1:pos"
    Variable "motor_pos[1]" connected to PV "mm4006_1_1_2:pos"
    Variable "detector_reqstart[0]" not connected to PV "ortec_1_1_1:reqstart"
    Variable "detector_reqready[0]" not connected to PV "ortec_1_1_1:reqready"
    Variable "detector_ready[0]" not connected to PV "ortec_1_1_1:ready"
    Variable "detector_reqdata[0]" not connected to PV "ortec_1_1_1:reqdata"
    Variable "detector_data[0]" not connected to PV "ortec_1_1_1:data"
    Variable "detector_type[0]" not connected to PV "ortec_1_1_1:type"
Dr. Dariush Hampai, PhD
INFN - LNF
X-Lab Frascati
Via E. Fermi, 54 (ex 40)
I-00044 Frascati (RM)
Italy
Mail Address:
XLab-Frascati
LNF-INFN
Casella Postale 13
Frascati (RM)
Italy
Room: +39.06.9403.5248
Lab.: +39.06.9403.2286
Mob.: +39.06.9403.8025
Fax.: +39.06.9403.2597
Il giorno 8 gen 2026, alle ore 19:19, Žiga Oven <ziga.oven at cosylab.com> ha scritto:
Hi Dariush,
I would check is if the IOC that runs the sequencer has access to the PVs in the other (I assume motor) IOCs.
If you issue the command "seqcar 2" on the IOC that runs the sequencer, this should report the status of the sequencer's access to the PVs.
Sequencer does provide you option to force all PVs to be connected before it starts the program execution, by using the "+c" option during the compile time
https://epics-modules.github.io/sequencer/Compiling.html?highlight=options#compiler-options
Best regards,
Žiga
-----Original Message-----
From: Tech-talk <tech-talk-bounces at aps.anl.gov> On Behalf Of Dariush Hampai
via Tech-talk
Sent: Thursday, January 8, 2026 10:20
To: tech-talk at aps.anl.gov
Subject: problems with SNL - sevr=minor ca_array_get_callback [...]: Virtual
circuit disconnect
Caution: This email originated from outside of Cosylab.
Dear Community,
Dear Mark and Maurizio,
I'll try to explain my error from which I'm not able to resolve.
I developped a SNL sequencer ablo to make a raster scan with 20 motors (but
scalable to how many motors needed) and 20 detectors (same as motors
number...).
In the link you can find the code (up to now I only use "xena_snscan.stt", as the
other ones will be the same)
https://urldefense.us/v3/__https://github.com/Teclis77/Scan-
Program__;!!G_uCfscf7eWS!aPQyj4WdR7O49u2p_NU4H2lPpTDgz2o1XaIePmA
WaJUE8f9HK3CQHpkDwIJWzSP9xdgUviafCfyswv0QGFHqZ1y-Th_61Np0-g$
To test the scan I use procServ in order to start contemporary 3 different IOCs
(mm4006 for motors, ortec for detector and the scan). Up to here all is ok.
Using telnet I can monitor the scan IOC and after populate the
1) number of motors;
2) number of detectors;
3) name of motor IOCs involved in the scan;
4) name of detector IOCs involved in the scan;
5) start position for each motor;
6) end position for each motor;
7) step position for each motor
I prepare the the loop using difdferent status_mode value (1 for populate
motor variables in stt file, 2 for detector variables, 3 for defing the loop
parameters) When I initialize the scan (status_mode=4), I have a strange error.
Knowing that the variables (for motor_ma, but for the other are the same
procedures) are built (in xena_sncscan.stt) as
sprintf(temp_string, "%s:%s", motor[i], setma); printf("%s\n", temp_string);
pvAssign(motor_ma[i],temp_string);
sprintf(temp_string, "%s:%s", motor[i], reqmoving); printf("%s\n",
temp_string); pvAssign(motor_reqmov[i],temp_string);
sprintf(temp_string, "%s:%s", motor[i], moving); printf("%s\n", temp_string);
pvAssign(motor_mov[i],temp_string);
sprintf(temp_string, "%s:%s", motor[i], pos); printf("%s\n", temp_string);
pvAssign(motor_pos[i],temp_string);
with the output correct form "mm4006_1_1_1:setma",
"mm4006_1_1_1:reqmoving", "mm4006_1_1_1:moving" and
"mm4006_1_1_1:pos"
(these strings work right with caput command in other cmd so they are ok)
and the status_mode=4 is the following
/*=================== Preparing Scan =========================*/
/*=================== status_mode = 4 ========================*/
        state prepare_loop {
                when () {
                        for (i = 0; i < num_mot; i++) {
                                printf("motor to move = %d\n", i);
                                printf("start[%d]= %f\n", i, start[i]);
                                motor_ma[i]=start[i];
                                pvPut(motor_ma[i],SYNC);
                                motor_reqmov[i]=1;
                                pvPut(motor_reqmov[i],SYNC);
                                pvGet(motor_mov[i],SYNC);
                                while(motor_mov[i]<1) {
                                        motor_reqmov[i]=1; pvPut(motor_reqmov[i],SYNC);
                                pvGet(motor_pos[i], SYNC);
                        flags[0]=1; // Necessary to start the run
                        strcpy(actual_status, "Ready to Start");
                        pvPut(actual_status,SYNC);
                        status_mode=0;
                        pvPut(status_mode);
                } state dummy_loop
in the "telnet" prompt I have the following exit sevr=minor
coming from:
using seqChanShow xena_sncscan I obtain
#9 of 263:
  Variable name: "start"
    type = double
    count = 20
  Value = 1000 1500 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0
  Assigned to "xena:start"
  Connected
  Monitored
  Not sync'ed
  Status = 0
  Severity = 0
  Message =
  Time stamp = 2026-01-08 17:26:57.769209 Next? (+/- skip count)
and
#43 of 263:
  Variable name: "motor_ma[0]"
    type = double
    count = 1
  Value = 1000
  Assigned to "mm4006_1_1_1:setma"
  Not connected
  Monitored
  Not sync'ed
  Status = -2
  Severity = -1
  Message = disconnected
  Time stamp = <undefined>
what I'm wrong?
awaiting your replies...
Dariush
INFN - LNF
X-Lab Frascati
Italy
Mail Address:
XLab-Frascati
LNF-INFN
Casella Postale 13
Frascati (RM)
Italy
Re: problems with SNL - sevr=minor ca_array_get_callback [...]: Virtual circuit disconnect Dariush Hampai via Tech-talk
RE: problems with SNL - sevr=minor ca_array_get_callback [...]: Virtual circuit disconnect Žiga Oven via Tech-talk
Prev: The motor module is unable to control the PM600 motor. LONG FENG via Tech-talk
Next: Re: NDPluginFile question Jörn Dreyer via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>
Prev: RE: problems with SNL - sevr=minor ca_array_get_callback [...]: Virtual circuit disconnect Žiga Oven via Tech-talk
Next: Re: problems with SNL - sevr=minor ca_array_get_callback [...]: Virtual circuit disconnect Dariush Hampai via Tech-talk
