1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>
Subject: Re: question about pvmonitor behavior
From: Alfio Rizzo via Tech-talk <tech-talk at aps.anl.gov>
To: Érico Nogueira Rolim <erico.rolim at lnls.br>, "tech-talk at aps.anl.gov" <tech-talk at aps.anl.gov>
Date: Tue, 17 Mar 2026 14:33:18 +0000
Hej Erico,
Your explanation is quite clear,
However I am confused why the .HIHI and other fields seems to be processed even if the PP attribute is missing.
I have checked a dfanout we use in some IOCs
record(dfanout, "$P$R:#FB_ProcHiValue") {    field(DESC, "Set alarm limit value")    field(DOL,  "$P$R:FB_ProcHiValue CP")    field(OMSL, "closed_loop")    field(OUTA, "$P$R:MeasValue.HIGH")   }
And according to the IOC owner, the value from $P$R:FB_ProcHiValue  is propagated to "$P$R:MeasValue.HIGH
But again, if  it is instead field(OUTA, "$P$R:MeasValue.VAL") without the PP, as you wrote, the record is not processed as expected...
Anyway, since it is not harmful to put the PP attribute, we will update that kind of records adding it in the OUTA
Best
Alfio
______________________
Alfio Rizzo
PhD / Automation Section Leader / ICS HW&I Group
European Spallation Source ERIC
P.O. Box 176, SE-221 00 Lund, Sweden
Visiting address: Partikelgatan 2, 224 84 Lund
Mobile: +46 72 179 23 42
E-mail: alfio.rizzo at ess.eu
ess.eu
From: Érico Nogueira Rolim <erico.rolim at lnls.br>
Sent: Tuesday, March 17, 2026 2:33 PM
To: Alfio Rizzo <Alfio.Rizzo at ess.eu>; tech-talk at aps.anl.gov <tech-talk at aps.anl.gov>
Hi Alfio!
To make matters clear, the issue isn't pvmonitor vs camonitor, it's your OUT link. You should be using "myaipv PP" as the output link, to tell the record to process after it receives the write. Even if "pvget myaipv" showed the updated value, any other database or device support connections wouldn't have been updated (the same way the monitor command didn't receive any changes), since the record itself wasn't processed. Most of the time, OUT links should include PP. This is documented in [1].
IIRC writing into RVAL doesn't work correctly, but I'd welcome someone clearing that up.
HIHI is quite different from VAL, regarding the field definition:
    field(VAL,DBF_DOUBLE) {
        prompt("Current EGU Value")
        promptgroup("40 - Input")
        asl(ASL0)
        pp(TRUE)
    field(HIHI,DBF_DOUBLE) {
        prompt("Hihi Alarm Limit")
        promptgroup("70 - Alarm")
        pp(TRUE)
        interest(1)
        prop(YES)       # get_alarm_double
It's possible either interest(1) or prop(YES) cause HIHI changes to be propagated to monitors (probably prop(YES), given the get_alarm_double comment). However, from my quick testing, it doesn't actually cause the record to be processed, so you still need PP to cause processing.
[1] https:// docs.epics-controls.org/en/latest/appdevguide/lockScanProcess.html#process-passive
Cheers,
Érico
On 3/17/26 07:27, Alfio Rizzo via Tech-talk wrote:
Hej
I noticed that the pvmonitor of a record value does not update  when the .VAL is  changed from the  OUT field of another record,
E.g. Using this simple db
record(ai, "myaipv"){
   field(PINI, "YES")
   field(VAL, 100)
record(ao, "myaopv") {
   field(PINI, "YES")
   field(VAL, 30)
   field(OUT, "myaipv")
If I do pvput myaovpv 1000, the myaipv.VAL is updated correctly (pvget myaipv gives back the updated value)
But this change is not shown in the pvmonitor  STDOUT
According to what I heard this is the intended behavior, but why apparently it applies only to  the .VAL field ?
I have tested the OUT with other fields like the alarm fields, or .RVAL , etc (i.e. OUT, "myaipv.HIHI") (OUT, "myaipv.RVAL")
Then if I do pvmonitor myaipv.HIHI for instance, everytime the myaopv value changes,
The pvmonitor reacts as well showing the updated .HIHI field value
Can someone give some more explanation about ?
I am using EPICS 7.0.9/6.0.0
Thanks
Best
Alfio
Alfio Rizzo
ess.eu
Aviso Legal: Esta mensagem e seus anexos podem conter informações confidenciais e/ou de uso restrito. Observe atentamente seu conteúdo e considere eventual consulta ao remetente antes de copiá-la, divulgá-la ou distribuí-la. Se você recebeu esta mensagem por engano, por favor avise o remetente e apague-a imediatamente.
Disclaimer: This email and its attachments may contain confidential and/or privileged information. Observe its content carefully and consider possible querying to the sender before copying, disclosing or distributing it. If you have received this email by mistake, please notify the sender and delete it immediately.
Re: question about pvmonitor behavior Érico Nogueira Rolim via Tech-talk
question about pvmonitor behavior Alfio Rizzo via Tech-talk
Prev: Re: question about pvmonitor behavior Érico Nogueira Rolim via Tech-talk
Next: Re: question about pvmonitor behavior Railton, Irie (STFC,RAL,CLF) via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  <2026>
Next: Re: question about pvmonitor behavior Érico Nogueira Rolim via Tech-talk
