>* The Equipment Protection System (EPS) Status will be sent to EPICS via a
>6008-SV1R VME Allen Bradley Remote I/O Scanner. The scanner (i.e. a
>6008-SV1R) actually talks to the SLC 500 remote I/O via a Direct
>Communications Module (i.e. a 1747-DCM).
The communication between the PEP-II high voltage power supply system and
our RF EPICS system will be done in exactly the same manner. We also use
the 16 bit binary device support and set up the the database using the
same formula as you. In addition to binaries, we had the need to send and
receive analog values from HVPS so we developed devABANALOG.c (very similar
to devABBINARY.c) which provide device support for longins/outs and
analogins/outs and assumes 16 bit raw values.
This could be added to the standard distribution if anyone is interested.