1994  1995  1996  1997  1998  <19992000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  <19992000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: devVXStats.c corrupts Intel floating point unit
To: "EPICS-tech-talk (E-mail)" <[email protected]>
Date: Fri, 12 Mar 1999 17:56:08 -0700
All,
This message is in reference to "devVXStats" which is not a part of
EPICS base but may nevertheless be in use at a number of EPICS
sites. This code is EPICS device support which is used to monitor an
IOC's state of health.
Symptom:
Mysterious floating point value corruption in an analog input record
which initially defies any rational explanation.
Cause:
After some considerable effort I have discovered that a floating point
value corruption occurring in our Intel-based IOCs was caused by a
missing function prototype for the function "sqrt()" in devVXStats.c.
It appears the Intel floating point unit became corrupted in a task
spawned off by devVXStats.c for the purpose of calculating the IOC's
CPU consumption. The "sqrt()" call was used by devVXStats.c to
consume CPU and thereby estimate CPU consumption in a low priority
task, and so the code was not interested in the result from "sqrt()".
The compiler assumed that the function returned type "int" when in fact
a double precision floating point number was returned, and this
appears to have corrupted the floating point unit. The result was that
another task in the system produced a not-a-number IEEE floating point
value in the ESLO field of an analog input record during EPICS
initialization. When the record processed the NaN value was propagated
to the VAL field of the ai record.
Resolution:
Here is the patch we applied which eliminated the problem:
D:\hill\leda\share\rp\src>cvs diff -r 1.2 -r 1.1 devVXStats.c
Index: devVXStats.c
RCS file: /usr/local/cvsroot/share/rp/src/devVXStats.c,v
retrieving revision 1.2
retrieving revision 1.1
diff -r1.2 -r1.1
24d23
< #include <math.h>
Jeff
______________________________________________________
Jeffrey O. Hill                      Internet     [email protected]
LANL MS H820                    Voice         505 665 1831
Los Alamos NM 87545 USA   FAX          505 665 5107
Prev: EPICS on x86 john sinclair
Next: Re: EPICS on x86 Ralph Lange
Index: 1994  1995  1996  1997  1998  <19992000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Re: EPICS on x86 Brian McAllister
Next: pcompress->alg == compressALG_N_to_1_Median William Lupton