> Has anyone created a record or simple pattern of records that acts as a
> watchdog? In other words, one that will give a signal if a response does
> not come back from a hardware device within a setable time period.
Well, kind of.
A simple calc record that decrements every scan can act as a watchdog. If
whatever you are watchdogging simply loads a constant into the val field
often enough such that it doesn't decrement to 0, then a 0 would indicate
the timeout. If you make it a calcout record, you could poke something
else with the out link when the watchdog expired.
record(calcout,"$(S):imageBusy") {
field(SCAN,"1 second")
field(CALC,"A<=0?0:A-1")
field(INPA,"$(S):imageBusy.VAL NPP NMS")
field(OUT,"$(S):imageBusyReset.PROC PP MS")
field(OOPT,"When Zero")
field(DOPT,"Use OCAL")
field(OCAL,"0")
Something better write to $(S):imageBusy.VAL before it gets to 0 ...
This can be used to determine in the database if a particular client is running.
The client simply writes a value to $(S):imageBusy.VAL periodically or the
database assumes its not active.
Ned