At 5:24 PM -0500 2000/04/25, Porter, Rodney wrote:
>I need to monitor 24 thermocouples. Can someone suggest EPICS supported
>hardware for this application.
Our method of choice here is to hook them directly to Allen-Bradley
Flex-I/O modules which are deployed close to the sensors. These 8-channel
units handle all known types, and have cold-junction compensation
and a calibration procedure. The unit is model IT-8.
Three IT-8 units can be combined in a small DIN-rail stack. (And they can
be mixed with other units for handling pressure, flow, whatever, in a nicely
distributed manner.) With adaptor and power supply (but not including
6008 scanner) using typical discounts, it would cost about $3700
They can connect to the IOC either directly to the 6008 scanner (we are
just finishing device support) or via any A-B series PLC (in which case
the generic PLC device support already works).
We much prefer this "raw sensor" approach here to the rack-mounted/
multiplexed/bells-and-whistles/RS-485-protocol-from-hell style of the
typical catalog instrument. Your mileage may vary...
_____________________________________________________________________
Stephen A. Lewis | [email protected]
Mail Stop 71-259 | http://www.lbl.gov/~salewis
Lawrence Berkeley National Laboratory | Tel: +1.510.486.7702
Berkeley, CA 94720 USA | FAX: +1.510.486.4544
- Re: Hardware to for thermocouple readout Steve Hunt
- References:
- Hardware to for thermocouple readout Porter, Rodney
- Navigate by Date:
- Prev:
Re: Hardware to for thermocouple readout Marty Kraimer
- Next:
- Index:
1994
1995
1996
1997
1998
1999
<2000>
2001
2002
2003
2004
2005
2006
2007
2008
2009
2010
2011
2012
2013
2014
2015
2016
2017
2018
2019
2020
2021
2022
2023
2024
2025
2026
- Navigate by Thread:
- Prev:
- Next:
- Index:
1994
1995
1996
1997
1998
1999
<2000>
2001
2002
2003
2004
2005
2006
2007
2008
2009
2010
2011
2012
2013
2014
2015
2016
2017
2018
2019
2020
2021
2022
2023
2024
2025
2026