1994  1995  1996  1997  1998  1999  <20002001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  <20002001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Status return from EPICS device support
To: <[email protected]>
Cc: "EPICS-tech-talk" <[email protected]>
Date: Thu, 25 May 2000 12:11:42 -0600
Fritz,
One possibility: add special BI device support and
associated device addressing for a pseudo binary IO
in your device which returns the status from the last
IO request. You might have specialized information in
the parm field of INST_IO or some other addressing format which
binds with your device's status. For example, if the addressing
is typically "CARD 0 SIGNAL 4" then the addressing for
the associated device status might be "CARD 0 SIGNAL 4 <STATUS>".
The downside of course is that you would need an additional
BI record for each signal, and I understand that you have more
than a few signals there.
We could avoid this overhead by adding a new pseudo field name to
all records which does not exist in the recod but is instead fetched
through a new entry at the end of the record support entry table.
This RSET entry might then call a new entry at the end of the device
Another way to solve this problem (long term) would be to allow
certain records to be created on-the-fly from a template only
when clients are looking at them. These pseudo BI's communicating
with your device's status would therefore only exist if a client
was attached to them.
Alternatively, we could look at device support extensibility
mechanisms for the "STAT" field.
Jeff
> -----Original Message-----
> From: J. Frederick Bartlett ([email protected])
> [mailto:[email protected]]
> Sent: Thursday, May 25, 2000 11:21 AM
> To: [email protected]
> Cc: [email protected]
> Subject: Status return from EPICS device support
>   I have a question for the experts. Is there a standard field in all
> records in which detailed device status (status from device support)
> may be placed where is is accessible by a database get operation.
>   My particular difficulty appears with asynchronous device support
> for the MIL/STD1553B bus. We have a controller for the 1553 bus which
> generates an interrupt at the end of a bus transaction. The 1553 bus
> driver reschedules record "processing" (PACT is non-zero at this point) at
> interrupt time via a call to callbackRequestProcessCallback, passing a
> longword with bus I/O completion status. I need to save this status in
> a standard record field (one that all records have) so that, if there
> was an error, the application program may retrieve it. Any
> suggestions?
> 						Fritz Bartlett
Re: Status return from EPICS device support Andrew Johnson
Status return from EPICS device support J. Frederick Bartlett ([email protected])
Prev: Re: archiver record Albert
Next: Re: Status return from EPICS device support Andrew Johnson
Index: 1994  1995  1996  1997  1998  1999  <20002001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: Status return from EPICS device support J. Frederick Bartlett ([email protected])