>>> On 5/2/2002 at 13:42:32 -1000, Ian A Smith wrote:
> the snc manual says that the delay() function can only be used inside a
> when expression. Is this really true? Isn't it just a finction that
> returns true or false? I want to use it inside a for statement.
Sorry, you can't do that.
When a state containing delay() clauses is entered, a timer is started for
each one (in the context of the main sequencer task, I think) which is then
checked by the sequencer along with any other when() tests in that state.
There is a function that returns true when the timer expires, and you could
potentially make use of this mechanism by writing escaped C code, but you
would have to be very careful.
Keep in mind that if you do anything in a when() clause that blocks
execution, you will suspend *all* sequencers for that time. Using
taskDelay() will allow other tasks to continue, but not other sequencers.
Looking at the generated C code may make it clearer how this works.
Brian McAllister Controls Programmer/Beam Physicist