Hi Emmanuel, you just need an Ethernet module for the S7. All the libraries for the S7 PLC side are provided with the Step7 software, the one you need anyway to program the PLC. You specify a data block for reading and one for writing. The communication is via Tcp/IP sockets. The S7PLC driver just opens the socket to the PLC and maps the data blocks on the IOC to EPICS channels. The same socket protocol is used for inter-PLC communication, too. We use VME CPUs with a second Ethernet interface (mv5100) as IOC and keep the PLC network separated from the slow control network. The set-up runs very reliably at PSI and it is used for many systems (Machine Interlock System, Equipment Protection System, Vacuum Control System, Insertion Device Control, ...) Dirk already mentioned the link http://epics.web.psi.ch/software/s7plc In addition I found an old document in German for the PLC programming http://people.web.psi.ch/luedeke/public/TM-93-00-04.pdf It contains examples how to set-up the PLC. I'll ask our PLC developer if there's more or newer documentation. I hope this helps for a start. Regards Andreas Emmanuel Mayssat wrote: Andreas, You are mentioning that you have no special hardware or proprietary software. Are you sure? Recently I investigated several ways to communicate with the PLC. I even met with Siemens sales reps. -- Dr. Andreas Luedeke, SLS Operations Manager, Tel:+41-56-3104002 mailto:[email protected], http://people.web.psi.ch/luedeke