Hi Geoff,
On Monday 23 November 2009 16:52:43 Geoff Savage wrote:
> Here are the details of my testing with a summary preceding.
Thanks for that very helpful and detailed bug report. For others, I'll quote
Geoff's original message to explain what's happening:
> On Friday 13 November 2009 13:38:36 Geoff Savage wrote:
>> I have a passive stringout record in IOC A whose OUTLINK references an
>> mbbo record in IOC B. When I reboot IOC B the value in the stringout
>> record is written to the mbbo record even though the stringout record
>> has not been processed.
I have confirmed that exactly the same thing occurs with the latest release,
and after studying the history of the code it looks like this behavior may
date all the way back to 1996.
The good news is that it only happens when the data type used is a string, so
if you replace your stringout with a longout or another mbbo it will stop
happening. That changes the coupling between your two IOCs slightly since
you've moved the string to state conversion, but it doesn't really increase it
because the strings had to match before anyway.
The bad news is that it looks like Marty intended this to happen for all data
types, as he went to the trouble of storing a copy of the data and recording
the fact that the link had actually been used. In practice non-string output
links don't re-send their last value on reconnection because the link flag bit
pvlOptOutNative never actually gets set anywhere in the code.
The question at this point is whether to change the current behavior for
string data. Given that EPICS users are not used to this my inclination is to
stop it happening for strings too, but I'm open to argument on that. In the
future we might add a link flag to allow the DB designer to control whether
this should occur, so I will probably leave the implementation in place anyway
and just disable it for now.
Any comments?
- Andrew
The best FOSS code is written to be read by other humans -- Harald Welte
- Re: Fwd: CA link behavior Dirk Zimoch
- Re: CA link behavior Andrew Johnson
- Fwd: CA link behavior Geoff Savage
Re: polling through the gateway Dirk Zimoch