Hi David,
On Thursday 16 December 2010 21:06:06 David Dudley wrote:
> So....
> The big format in the bpt*.data files, as specified in section 6.17 isn't
> required? And I don't have to run the 'makeBpt' command and the stuff
> that's listed in that section?
You don't have to do that if you have your own way of generating the
breaktable(name){raw, eng, ...} that the IOC can load (see 6.11, although I
suspect you have an older copy of the AppDevGuide with different numbering).
Note that you can load a .dbd file containing break-point table data using
either dbLoadDatabase or dbLoadRecords, and the table data values can be space
or comma-separated.
The makeBpt program described in 6.15 is useful if the calibration data you
have needs to be re-sampled to provide conversions with an acceptable error,
bearing in mind that the IOC code gives you values taken from a straight line
drawn between adjacent data points. You wouldn't need to run makeBpt manually
since that's all taken care of by the build system when you tell it
BPTS += bptXxx.dbd
and give it the data table as described in a file named bptXxx.data.
- Andrew