1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Asyn/Modbus Delay
To: "Robert Emery" <[email protected]>, <[email protected]>, "Yves Lussignol" <[email protected]>
Date: Wed, 9 Mar 2011 08:19:18 -0600
Hi Rob,
I see the source of the 20ms delay.  It is in modbusInterpose.c:
static asynStatus writeIt(void *ppvt, asynUser *pasynUser,
                          const char *data, size_t numchars,
                          size_t *nbytesTransfered)
    modbusPvt  *pPvt = (modbusPvt *)ppvt;
    asynStatus status = asynSuccess;
    epicsThreadSleep(0.02);
That delay was added in this commit to the code:
r9770 | rivers | 2009-11-27 10:36:51 -0600 (Fri, 27 Nov 2009) | 1 line
Move slave address from interpose layer to modbus packet layer, allowing multiple slave address per asyn IP or serial port; add 20 ms delay per Modbus spec; changes made by Yves Lussignol
I made the commit, but the changes were actually done by Yves Lussignol when he got Modbus RTU running with multiple slave addressess on a single serial line.  His comment says that the 20ms delay is "per Modbus spec".
I have not actually tried to find that in the Modbus spec.  Can Rob or Yves you have a look and see if it is in the spec for all transports (TCP, RTU, ASCII) or perhaps just for the RTU and/or ASCII?  If the spec says it is transport dependent it is easy to make that change in modbusInterpose.c.  The Modbus specs are in the documentation in the module, I just don't have time to work on it today.
Sent: Tue 3/8/2011 6:10 PM
To: 'Robert Emery'; [email protected]
This is the first I have heard of this.
Here is the first thing to do.  Set the asynTraceMask to 0x9 on the underlying asyn TCP port (AcromagDO1), and send the asyn output to a file with asynSetTraceFile.  Then look at the timestamps to see if you learn anything.  You can also then set the asynTraceMask on the asyn Modbus port (CCC:ACROMAGDO1:Modbus:Output) and send its output to a file.  By sending the asynTrace output to a file you hopefully won't mess up the timing too much, though 20ms is still a pretty short delay to be tracking down.
-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of Robert Emery
Sent: Tuesday, March 08, 2011 6:01 PM
To: [email protected]
Subject: Asyn/Modbus Delay
We are using Modbus/Asyn to talk to a Acromag ES2113 digital I/O
device.  Since updating our controller software (Linux 2.6.24 to 2.6.32,
EPICS 3.14.8.2 to 3.14.12, Asyn 4.8 to 4.15, Modbus 1.1 to 2.1) the
Modbus/Asyn communication has slowed down.  There is now a .02 sec delay
in messages sent out (see below).  To illustrate this I ran a simple db
with 4 linked longout records writing to the Modbus/Asyn port and looked
at the timing with wireshark.
Any ideas why the delay and how I can get around it?
Thanks
Rob Emery
UW Medical Center
Original Timing
Time        Source     Destination           Protocol Info
0.000000    .0.33          .0.31          Modbus/TCP    query
0.002218    .0.31          .0.33          Modbus/TCP response
0.002229    .0.33          .0.31          TCP      53105 > 502 [ACK]
0.002288    .0.33          .0.31          Modbus/TCP    query
0.005003    .0.31          .0.33          Modbus/TCP response
0.005166    .0.33          .0.31          Modbus/TCP    query
0.007680    .0.31          .0.33          Modbus/TCP response
0.008171    .0.33          .0.31          Modbus/TCP    query
0.010342    .0.31          .0.33          Modbus/TCP response
New Timing
0.002168   .0.31          .0.33          Modbus/TCP response
0.003864   .0.33          .0.31          TCP      59583 > asa-appl-proto
[ACK]
0.024044   .0.33          .0.31          Modbus/TCP    query
0.026214   .0.31          .0.33          Modbus/TCP response
0.046431   .0.33          .0.31          Modbus/TCP    query
0.048319   .0.31          .0.33          Modbus/TCP response
0.068693   .0.33          .0.31          Modbus/TCP    query
0.071181   .0.31          .0.33          Modbus/TCP response
Port Configuration
## Create the Asyn IP ports
drvAsynIPPortConfigure("AcromagDO1","192.168.0.31:502",0,0,1)
## Apply The Modbus Configuration to the IP ports
modbusInterposeConfig("AcromagDO1",0,1000)
## Create Test Port
drvModbusAsynConfigure("CCC:ACROMAGDO1:Modbus:Output","AcromagDO1",0,6,59,
6,   0,  0, "Acro Test")
Test db
record(longout, Tuning:Asyn:Timing:Test:LongOut) {
   field(SCAN, "Passive")
   field(DTYP, "asynUInt32Digital")
   field(FLNK, "Tuning:Asyn:Timing:Test:LongOut2")
   field(OUT, "@asynMask(CCC:ACROMAGDO1:Modbus:Output 0 0xFFFF)")
   field(OMSL, "supervisory")
   field(VAL, "101")
record(longout, Tuning:Asyn:Timing:Test:LongOut2) {
   field(FLNK, "Tuning:Asyn:Timing:Test:LongOut3")
   field(OUT, "@asynMask(CCC:ACROMAGDO1:Modbus:Output 1 0xFFFF)")
   field(VAL, "102")
record(longout, Tuning:Asyn:Timing:Test:LongOut3) {
   field(FLNK, "Tuning:Asyn:Timing:Test:LongOut4")
   field(OUT, "@asynMask(CCC:ACROMAGDO1:Modbus:Output 2 0xFFFF)")
   field(VAL, "103")
record(longout, Tuning:Asyn:Timing:Test:LongOut4) {
   field(OUT, "@asynMask(CCC:ACROMAGDO1:Modbus:Output 3 0xFFFF)")
   field(VAL, "104")
Re: Asyn/Modbus Delay Robert Emery
RE: Asyn/Modbus Delay Mark Rivers
Prev: Re: question about previous value of ai Ralph Lange
Next: Re: question about previous value of ai Steven M. Hartman
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  <2011>  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: RE: Asyn/Modbus Delay Mark Rivers
Next: Re: Asyn/Modbus Delay Robert Emery