Hi Stuart, Laurence,
I don't know if this is related to some problems I found in
drvLinuxGpib.c (asyn) recently. See thread "Reading scope waveforms with
StreamDevice + asyn".
1. Under certain circumstances, drvLinuxGpib uses '\0' (null byte) as a
terminator instead of '' (no terminator). This happens when setEos is
called with eoslen=0 and eos!=NULL. This is not conform with asyn.
2. When the terminator or EOI has been received, eomReason should be set
by the driver. This does not happen. This is probably what you mean with
'does not recognise "\n" as an EOS signal'.
Your problems that the first character is '\0' may be related to global
variables used by linux-gpib. The number of received characters is
stored in the global variable ibcnt. This does not look thread safe to
me. If more that one interface is in use, the "other one" may set it to
0 before drvLinuxGpib terminates the received string with 'data[ibcnt] =
0'. Do you have multiple interfaces in use?
I had fixed problem 1 and 2 before and now tries to fix your problem,
too. Please try the attached version of drvLinuxGpib.c.
Dirk
Feng Laurence wrote:
Hi Stuart!
I had meet the same problem as yours. I have an Agilent 82357B
USB-GPIB converter plugged in a Linux PC, and I use
Linux-GPIB/StreamDevice to communication with an Agilent frequency
counter.
The portName problems had troubled me for some days, and then I dig in
the source and found the same solution as yours.
For the primary address problem, StreamDevice User's Guide had
mentioned a bus address parameter in the record file, I guest this may
be the solution~
"@file protocol bus [address [parameters]]"
http://epics.web.psi.ch/software/streamdevice/doc/setup.html#rec
As for the last problem you mentioned, Linux-GPIB does work on my
machine, except that the 82357B USB-GPIB converter does not recognise
"\n" as an EOS signal. And the driver keep printing the EOS error.
Have you debugged the driver? Or maybe you can just modify the
StreamDevice format string to go around this problem?
Best wishes
On Mon, Jan 9, 2012 at 9:28 PM, Wilkins, Stuart <[email protected]> wrote:
Hi!
I have been using linux-gpib and asyn (and StreamDevice) for communication
with Keithley Electrometers. I have one comment on the documentation and one
bug which I would like to see if anyone else has seen.
Firstly, according to the asyn documentation the following command at the
iocsh sets up the board.
GpibBoardDriverConfig(portName,autoConnect,BoardIndex,timeout,priority)
From this documentation, it looks like you assign the GPIB board with the
integer "board index", however after about 2 hrs of trying to get this
working, I delved into the souce code for this driver. In fact, this is not
the behavior in the code, the port driver tries to open the gpib card with
the same name as the portName as defined in /etc/gpib.conf. I think
(although in places the code is fairly cryptic) it is only if you open a
certain gpib address that it uses board index, but I cannot find the config
to give the primary and secondary address at the iocsh. It might be a good
idea to update this in the asyn documentation (or at least clarify it!)
Having got past this stage, I noticed that some of my communications are
being garbled, with replies returning where the first character is NULL
[chr$(0)] instead of the correct character. Has anyone seen this behavior. I
am not sure if it is due to the linux-gpib driver, asyn or the Keithley. I
plan to put another device on the bus to see if it is just this combination.
Is anyone out there using this combination?
Best wishes,
Stuart
/* drvLinuxGpib.c */
* Copyright (c) 2004 by Danfysik and Cosylab (Danfysik has funded the work
* performed by Cosylab).
* linux-gpib port driver is distributed subject to a Software License Agreement
* found in file LICENSE that is included with this distribution.
/* Author: Gasper Jansa, Cosylab */
/* date: 18AUG2006
date: 19OCT2006 - changed get/set options to check the option key and value
date: 07APR2008 - added support for secondary address, address 30 bugfix
date: 20JUN2008 - modified time of start of the poll_worker thread - after iocInit*/
#include <signal.h>
#include <errno.h>
#include <osiUnistd.h>
#include <stdlib.h>
#include <stddef.h>
#include <string.h>
#include <stdio.h>
#include <string.h>
#include <epicsTypes.h>
#include <epicsEvent.h>
#include <epicsThread.h>
#include <epicsInterrupt.h>
#include <iocsh.h>
#include <callback.h>
#include <cantProceed.h>
#include <epicsTime.h>
#include <devLib.h>
#include <taskwd.h>
#include <initHooks.h>
#include <gpib/ib.h>
#include <epicsExport.h>
#include "asynDriver.h"
#include "asynOctet.h"
#include "asynOption.h"
#include "asynGpibDriver.h"
#define DEBUG 0
typedef struct GpibBoardPvt {
char *portName;
void *asynGpibPvt;
int ud;
int uddev[31][31];
int ibsta;
int iberr;
int sad;
int boardIndex;
int timeout;
epicsBoolean srqEnabled;
CALLBACK callback;
epicsBoolean srqHappened;
pid_t worker_pid;
asynInterface option;
}GpibBoardPvt;
GpibBoardPvt *pGlobalGpibBoardPvt;
static void report(void *pdrvPvt,FILE *fd,int details);
static asynStatus connect(void *pdrvPvt,asynUser *pasynUser);
static asynStatus disconnect(void *pdrvPvt,asynUser *pasynUser);
/*asynOctet methods */
static asynStatus gpibRead(void *pdrvPvt,asynUser *pasynUser,char
*data,int maxchars,int *nbytesTransfered,int *eomReason);
static asynStatus gpibWrite(void *pdrvPvt,asynUser *pasynUser,
const char *data,int numchars,int *nbytesTransfered);
static asynStatus gpibFlush(void *pdrvPvt,asynUser *pasynUser);
static asynStatus setEos(void *pdrvPvt,asynUser *pasynUser,const char *eos,int eoslen);
static asynStatus getEos(void *pdrvPvt,asynUser *pasynUser,
char *eos, int eossize, int *eoslen);
/*asynGpib methods*/
static asynStatus addressedCmd (void *pdrvPvt,asynUser *pasynUser,
const char *data, int length);
static asynStatus universalCmd (void *pdrvPvt, asynUser *pasynUser, int cmd);
static asynStatus ifc (void *pdrvPvt,asynUser *pasynUser);
static asynStatus ren (void *pdrvPvt,asynUser *pasynUser, int onOff);
static asynStatus srqStatus (void *pdrvPvt,int *isSet);
static asynStatus srqEnable (void *pdrvPvt, int onOff);
static asynStatus serialPollBegin (void *pdrvPvt);
static asynStatus serialPoll (void *pdrvPvt, int addr, double timeout,int *status);
static asynStatus serialPollEnd (void *pdrvPvt);
/*local methods*/
static asynStatus checkError(void *pdrvPvt,asynUser *pasynUser,int addr);
unsigned int sec_to_timeout( double sec );
/*interrupt handlers*/
static void srqCallback(CALLBACK *pcallback);
/*EPICSTHREADFUNC poll_worker(GpibBoardPvt *pGpibBoardPvt);*/
void getAddr(int addr,int *primAddr,int *secAddr);
static asynGpibPort GpibBoardDriver = {
report,
connect,
disconnect,
gpibRead,
gpibWrite,
gpibFlush,
setEos,
getEos,
addressedCmd,
universalCmd,
ifc,
ren,
srqStatus,
srqEnable,
serialPollBegin,
serialPoll,
serialPollEnd
static asynStatus gpibPortSetPortOptions(void *pdrvPvt,asynUser *pasynUser,
const char *key, const char *val);
static asynStatus gpibPortGetPortOptions(void *pdrvPvt,asynUser *pasynUser,
const char *key, char *val, int sizeval);
static asynOption GpibBoardOption = {
gpibPortSetPortOptions,
volatile int work;
void signal_handler(int signum){
if(signum==SIGUSR1)
work=0;
static void poll_worker(GpibBoardPvt *pGpibBoardPvt)
/*mask for srq bit*/
int mask=SRQI;
struct sigaction new_action,old_action;
work = 1;
new_action.sa_handler=signal_handler;
sigemptyset(&new_action.sa_mask);
new_action.sa_flags=0;
pGpibBoardPvt->worker_pid=getpid();
sigaction(SIGUSR1,&new_action,&old_action);
while(work){
ibwait(pGpibBoardPvt->ud,mask);
callbackRequest(&pGpibBoardPvt->callback);
epicsThreadSleep(0.001);
/* poll_worker is started after iocInit finishes */
void poll_worker_starter(initHookState state)
if(state == initHookAtEnd)
/*create thread only if not yet created*/
if((!epicsThreadGetId("PollThread")))
epicsThreadCreate("PollThread", epicsThreadPriorityMedium,
epicsThreadGetStackSize(epicsThreadStackSmall),
(EPICSTHREADFUNC)poll_worker,pGlobalGpibBoardPvt);
GpibBoardPvt *pGpibBoardPvt = (GpibBoardPvt *)pdrvPvt;
if(DEBUG) printf("drvGpibBoard:report!!\n");
fprintf(fd,"GpibBoard port %s, boardIndex %d,timeout %d.\n",
pGpibBoardPvt->portName,pGpibBoardPvt->boardIndex,pGpibBoardPvt->timeout);
int addr = 0;
int primaryAddr = 0;
int secondaryAddr = 0;
asynStatus status;
if(DEBUG) printf("drvGpibBoard:connect!!\n");
status = pasynManager->getAddr(pasynUser,&addr);
if(status!=asynSuccess) return status;
asynPrint(pasynUser, ASYN_TRACE_FLOW,
"%s addr %d connect\n",pGpibBoardPvt->portName,addr);
if(DEBUG) printf("ADDR: %d\n", addr);
if(addr==-1){
pGpibBoardPvt->ud=ibfind(pGpibBoardPvt->portName);
if(DEBUG) printf("DESCRIPTOR: %d\n",pGpibBoardPvt->ud);
if(pGpibBoardPvt->ud<0){
status=checkError(pdrvPvt,pasynUser,addr);
if(status!=asynSuccess)return status;
/*disable autopolling*/
ibconfig(pGpibBoardPvt->ud,IbcAUTOPOLL,0);
/*set general timeout for board*/
ibtmo(pGpibBoardPvt->ud,pGpibBoardPvt->timeout);
else{
getAddr(addr,&primaryAddr,&secondaryAddr);
/*third argument:secondary address,last two arguments are:set EOI line and set eos*/
if((primaryAddr>=0 && primaryAddr<=30) && (secondaryAddr>=0 && secondaryAddr<=30)){
pGpibBoardPvt->uddev[primaryAddr][secondaryAddr]=ibdev(pGpibBoardPvt->boardIndex,primaryAddr,secondaryAddr + 96,pGpibBoardPvt->timeout,1,0);
if(DEBUG) printf("DESCRIPTOR: %d\n",pGpibBoardPvt->uddev[primaryAddr][secondaryAddr]);
if(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr]<0){
else{
asynPrint(pasynUser,ASYN_TRACE_ERROR,
"%s addr %d connect illegal primary or secondary address (primary:%d,secondary %d)\n",
pGpibBoardPvt->portName,addr,primaryAddr,secondaryAddr);
return asynError;
pasynManager->exceptionConnect(pasynUser);
return asynSuccess;
int addr=0;
int secondaryAddr = 0; ;
asynStatus status;
if(DEBUG) printf("drvGpibBoard:disconnect!!\n");
"%s addr %d disconnect\n",pGpibBoardPvt->portName,addr);
/*disconnect device or board*/
if(addr==-1){
ibonl(pGpibBoardPvt->ud,0);
/*destroy poll_worker*/
kill(pGpibBoardPvt->worker_pid,SIGUSR1);
else{
ibonl(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],0);
pasynManager->exceptionDisconnect(pasynUser);
return asynSuccess;
int option,value;
int addr=0,j=0;
char cset[] = "1234567890ABCDEFabcdefxX";
asynStatus status;
int parseStatus;
if(DEBUG) printf("drvGpibBoard:gpibPortSetPortOptions!!\n");
asynPrint(pasynUser,ASYN_TRACE_FLOW,"%s gpibPortSetPortOptions\n",
j = strspn (key,cset);
if((*key != '0') || ((*(key+1) != 'x') && (*(key+1) != 'X')) || ( j != strlen(key))){
"%s addr %d gpibPortSetPortOptions illegal option: %s\n",
pGpibBoardPvt->portName,addr,key);
return asynError;
parseStatus = sscanf(key,"%x",&option);
if(parseStatus != 1){
return asynError;
parseStatus = sscanf(val,"%d",&value);
"%s addr %d gpibPortSetPortOptions illegal option value: %s\n",
pGpibBoardPvt->portName,addr,val);
return asynError;
if(DEBUG) printf("option %d set with value %d\n",option,value);
if(addr==-1){
ibconfig(pGpibBoardPvt->ud,option,value);
else{
ibconfig(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],option,value);
return asynSuccess;
int value,option;
int addr=0,j=0;
asynStatus status;
int parseStatus = 0;
if(DEBUG) printf("drvGpibBoard:gpibPortGetPortOptions!!\n");
asynPrint(pasynUser,ASYN_TRACE_FLOW,"%s gpibPortGetPortOptions\n",
*pGpibBoardPvt->portName);
"%s addr %d gpibPortGetPortOptions illegal option: %s\n",
return asynError;
parseStatus=sscanf(key,"%x",&option);
return asynError;
if(addr==-1){
ibask(pGpibBoardPvt->ud,option,&value);
else{
ibask(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],option,&value);
sprintf(val,"%d",value);
if(DEBUG) printf("option %d get with value %d\n",option,value);
return asynSuccess;
int addr=0;
asynStatus status=asynSuccess;
double timeout = pasynUser->timeout;
int ibsta;
int ibcnt;
if(DEBUG) printf("drvGpibBoard:gpibRead!!\n");
epicsThreadSleep(epicsThreadSleepQuantum());
asynPrint(pasynUser,ASYN_TRACE_FLOW,"%s addr %d gpibRead\n",
/*set timeout*/
ibtmo(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],sec_to_timeout(timeout));
/*read data*/
ibsta = ibrd(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],data,maxchars);
/*ibcnt holds number of bytes transfered*/
*nbytesTransfered=ibcnt=ThreadIbcnt();
if (eomReason != NULL)
*eomReason = 0;
if (ibsta & END) *eomReason = ASYN_EOM_END;
if (ibcnt == maxchars) *eomReason = ASYN_EOM_CNT;
if(status!=asynSuccess){
epicsSnprintf(pasynUser->errorMessage,pasynUser->errorMessageSize,
"%s readGpib failed %s\n",pGpibBoardPvt->portName,gpib_error_string(pGpibBoardPvt->iberr));
return status;
asynPrintIO(pasynUser,ASYN_TRACEIO_DRIVER,data,ibcnt,"%s addr %d gpibPortRead\n",pGpibBoardPvt->portName,addr);
/*if last response is shorter than previous*/
if(ibcnt<maxchars) data[ibcnt] = 0;
if(DEBUG) printf("DATA READ: %s\n",data);
return status;
int addr=0;
int ibcnt;
if(DEBUG){
printf("drvGpibBoard:gpibWrite!!\n");
printf("WRITING STRING: %s \n",data);
asynPrint(pasynUser,ASYN_TRACE_FLOW,"%s addr %d gpibWrite nchar %d\n",
pGpibBoardPvt->portName,addr,numchars);
/*set timeout*/
/*write data*/
ibwrt(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],data,numchars);
"%s writeGpib failed %s\n",pGpibBoardPvt->portName,gpib_error_string(pGpibBoardPvt->iberr));
return status;
data,ibcnt,"%s addr %d gpibPortWrite\n",pGpibBoardPvt->portName,addr);
return status;
if(DEBUG)
printf("drvGpibBoard:gpibFlush!!\n");
/*nothing to do*/
return asynSuccess;
int addr = 0;
asynStatus status;
if(DEBUG) printf("drvGpibBoard:setEos!!\n");
"%s addr %d setEos eoslen %d\n",pGpibBoardPvt->portName,addr,eoslen);
if(eoslen>1 || eoslen<0){
"%s addr %d gpibBoard:setEos illegal eoslen %d\n",
return asynError;
if(eoslen==1){
ibconfig(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],IbcEOScmp,1);
ibconfig(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],IbcEOSchar,*eos);
ibconfig(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],IbcEOSrd,1);
if(DEBUG)
printf("Seting EOS: %u\n",*eos);
else{
pGpibBoardPvt->ibsta=ibconfig(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],IbcEOSrd,0);
if(DEBUG) printf("Disabling EOS\n");
return asynSuccess;
int addr = 0;
asynStatus status;
int ieos;
"%s addr %d gpibPortGetEos\n",pGpibBoardPvt->portName,addr);
if(DEBUG) printf("drvGpibBoard:getEos!!\n");
if(eossize<1) {
"%s addr %d getEos eossize %d too small\n",
pGpibBoardPvt->portName,eossize);
*eoslen = 0;
return asynError;
ibask(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],IbaEOSrd,&ieos);
if(ieos==0){
*eoslen = 0;
if(DEBUG) printf("EOS disabled\n");
else {
*eoslen = 1;
ibask(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],IbaEOSchar,&ieos);
if(DEBUG) printf("EOS: %d\n",ieos);
eos[0]=ieos;
return asynSuccess;
int addr = 0;
asynStatus status;
if(DEBUG) printf("drvGpibBoard:addressedCmd!!\n");
asynPrint(pasynUser,ASYN_TRACE_FLOW,"%s addr %d addressedCmd nchar %d\n",
pGpibBoardPvt->portName,addr,length);
/*set timeout*/
if(DEBUG) printf("DATA: %s\n", data);
Send(pGpibBoardPvt->ud,MakeAddr(primaryAddr,secondaryAddr),data,strlen(data),1);
return asynSuccess;
static asynStatus universalCmd(void *pdrvPvt, asynUser *pasynUser, int cmd)
int addr=0;
asynStatus status;
char chcmd[20];
asynPrint(pasynUser,ASYN_TRACE_FLOW,"%s universalCmd %2.2x\n",
pGpibBoardPvt->portName,cmd);
if(DEBUG){
printf("drvGpibBoard:universalCmd!!\n");
printf("CMD integer: %d\n",cmd);
sprintf(chcmd,"\\%x",cmd);
if(DEBUG)printf("CMD string: %s\n",chcmd);
ibcmd(pGpibBoardPvt->ud,chcmd,strlen(chcmd));
return asynSuccess;
static asynStatus ifc(void *pdrvPvt,asynUser *pasynUser)
int addr=0;
asynStatus status;
if(DEBUG)printf("drvGpibBoard:ifc!!\n");
"%s ifc\n",pGpibBoardPvt->portName);
ibsic(pGpibBoardPvt->ud);
return asynSuccess;
static asynStatus ren(void *pdrvPvt,asynUser *pasynUser, int onOff)
int addr=0;
asynStatus status;
if(DEBUG)printf("drvGpibBoard:ren!!\n");
"%s ren %s\n",pGpibBoardPvt->portName,(onOff ? "On" : "Off"));
ibsre(pGpibBoardPvt->ud,onOff);
return asynSuccess;
if(DEBUG)printf("drvGpibBoard:srqStatus!!\n");
*isSet=pGpibBoardPvt->srqHappened;
pGpibBoardPvt->srqHappened = epicsFalse;
return asynSuccess;
if(DEBUG)printf("drvGpibBoard:srqEnable\n");
pGpibBoardPvt->srqEnabled = (onOff ? epicsTrue : epicsFalse);
return asynSuccess;
/*not used*/
return asynSuccess;
static asynStatus serialPoll (void *pdrvPvt, int addr, double timeout,int *statusByte)
char serialPollByte = 0;
int ibsta;
if(DEBUG){
printf("drvGpibBoard:serialPoll!!\n");
printf("ADDR: %d\n",addr);
printf("uddev: %d\n",pGpibBoardPvt->uddev[primaryAddr][secondaryAddr]);
/*set timeout*/
ibsta=ibtmo(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],sec_to_timeout(timeout));
if(ibsta&TIMO)
return asynTimeout;
if(ibsta&ERR)
return asynError;
/*serial poll*/
ibsta=ibrsp(pGpibBoardPvt->uddev[primaryAddr][secondaryAddr],&serialPollByte);
if(ibsta&TIMO)
return asynTimeout;
if(ibsta&ERR)
return asynError;
*statusByte = (int)serialPollByte;
return asynSuccess;
/*not used*/
return asynSuccess;
pGpibBoardPvt->ibsta=ThreadIbsta();
pGpibBoardPvt->iberr=ThreadIberr();
if(DEBUG){
printf("drvGpibBoard:checkIberr\n");
printf("ibsta: %d\n",pGpibBoardPvt->ibsta);
if(pGpibBoardPvt->ibsta & DCAS)
printf("IBSTA bit 0\n");
if(pGpibBoardPvt->ibsta & DTAS)
printf("IBSTA bit 1\n");
if(pGpibBoardPvt->ibsta & LACS)
printf("IBSTA bit 2\n");
if(pGpibBoardPvt->ibsta & TACS)
printf("IBSTA bit 3\n");
if(pGpibBoardPvt->ibsta & ATN)
printf("IBSTA bit 4\n");
if(pGpibBoardPvt->ibsta & CIC)
printf("IBSTA bit 5\n");
if(pGpibBoardPvt->ibsta & REM)
printf("IBSTA bit 6\n");
if(pGpibBoardPvt->ibsta & LOK)
printf("IBSTA bit 7\n");
if(pGpibBoardPvt->ibsta & CMPL)
printf("IBSTA bit 8\n");
if(pGpibBoardPvt->ibsta & EVENT)
printf("IBSTA bit 9\n");
if(pGpibBoardPvt->ibsta & SPOLL)
printf("IBSTA bit 10\n");
if(pGpibBoardPvt->ibsta & RQS)
printf("IBSTA bit 11\n");
if(pGpibBoardPvt->ibsta & SRQI)
printf("IBSTA bit 12\n");
if(pGpibBoardPvt->ibsta & END)
printf("IBSTA bit 13\n");
if(pGpibBoardPvt->ibsta & TIMO)
printf("IBSTA bit 14\n");
if(pGpibBoardPvt->ibsta & ERR)
printf("IBSTA bit 15\n");
printf("iberr: %d\n",pGpibBoardPvt->iberr);
if(pGpibBoardPvt->ibsta & TIMO){
asynPrint(pasynUser,ASYN_TRACE_ERROR,"%s addr %d : device timed out.\n",pGpibBoardPvt->portName,addr);
return asynTimeout;
if(pGpibBoardPvt->ibsta & ERR){
asynPrint(pasynUser,ASYN_TRACE_ERROR,"%s addr %d : %s.\n",pGpibBoardPvt->portName,addr,gpib_error_string(pGpibBoardPvt->iberr));
return asynError;
return asynSuccess;
if( sec <= 0 ) return TNONE;
else if( sec <= .00001 ) return T10us;
else if( sec <= .00003 ) return T30us;
else if( sec <= .0001 ) return T100us;
else if( sec <= .0003 ) return T300us;
else if( sec <= .001 ) return T1ms;
else if( sec <= .003 ) return T3ms;
else if( sec <= .01 ) return T10ms;
else if( sec <= .03 ) return T30ms;
else if( sec <= .1 ) return T100ms;
else if( sec <= .3 ) return T300ms;
else if( sec <= 1 ) return T1s;
else if( sec <= 3 ) return T3s;
else if( sec <= 10 ) return T10s;
else if( sec <= 30 ) return T30s;
else if( sec <= 100 ) return T100s;
else if( sec <= 300 ) return T300s;
else if( sec <= 1000 ) return T1000s;
return TNONE;
GpibBoardPvt *pGpibBoardPvt;
callbackGetUser(pGpibBoardPvt,pcallback);
if(!pGpibBoardPvt->srqEnabled) return;
pGpibBoardPvt->srqHappened = epicsTrue;
pasynGpib->srqHappened(pGpibBoardPvt->asynGpibPvt);
if(addr < 100){
*primAddr = addr;
return;
*primAddr = addr/100;
*secAddr = addr%100;
return;
int GpibBoardDriverConfig(char *name,int autoConnect,int boardIndex,double timeout,int priority)
int size;
asynStatus status;
if(DEBUG) printf("GpibBoardDriverConfig\n");
size=sizeof(GpibBoardPvt)+strlen(name)+1;
pGpibBoardPvt=callocMustSucceed(size,sizeof(char),"GpibBoardDriverConfig");
pGpibBoardPvt->portName =(char *) (pGpibBoardPvt+1);
strcpy(pGpibBoardPvt->portName,name);
pGpibBoardPvt->boardIndex=boardIndex;
pGpibBoardPvt->timeout=sec_to_timeout(timeout);
callbackSetCallback(srqCallback,&pGpibBoardPvt->callback);
callbackSetUser(pGpibBoardPvt,&pGpibBoardPvt->callback);
pGpibBoardPvt->asynGpibPvt =
pasynGpib->registerPort(pGpibBoardPvt->portName,
ASYN_MULTIDEVICE|ASYN_CANBLOCK,autoConnect,&GpibBoardDriver,pGpibBoardPvt,priority,0);
pGpibBoardPvt->option.interfaceType=asynOptionType;
pGpibBoardPvt->option.pinterface=(void *) &GpibBoardOption;
pGpibBoardPvt->option.drvPvt= pGpibBoardPvt;
status = pasynManager->registerInterface(pGpibBoardPvt->portName,&pGpibBoardPvt->option);
if(status==asynError){
errlogPrintf("GpibBoardDriverConfig: Can't register option.\n");
return -1;
pGlobalGpibBoardPvt = pGpibBoardPvt;
/*register for init */
initHookRegister(poll_worker_starter);
return 0;
/*register GpibBoardDriverConfig*/
static const iocshArg GpibBoardDriverConfigArg0 =
{ "portName", iocshArgString };
static const iocshArg GpibBoardDriverConfigArg1 =
{ "autoConnect", iocshArgInt };
static const iocshArg GpibBoardDriverConfigArg2 =
{ "boardIndex", iocshArgInt };
static const iocshArg GpibBoardDriverConfigArg3 =
{ "timeout", iocshArgDouble };
static const iocshArg GpibBoardDriverConfigArg4 =
{ "priority", iocshArgInt };
static const iocshArg *GpibBoardDriverConfigArgs[] = {
&GpibBoardDriverConfigArg0,&GpibBoardDriverConfigArg1,&GpibBoardDriverConfigArg2,&GpibBoardDriverConfigArg3,&GpibBoardDriverConfigArg4};
static const iocshFuncDef GpibBoardDriverConfigFuncDef = {
"GpibBoardDriverConfig",5, GpibBoardDriverConfigArgs};
static void GpibBoardDriverConfigCallFunc(const iocshArgBuf *args)
GpibBoardDriverConfig(args[0].sval,args[1].ival,args[2].ival,args[3].dval,args[4].ival);
static void GpibBoardDriverRegister(void)
static int firstTime = 1;
if (firstTime) {
firstTime = 0;
iocshRegister(&GpibBoardDriverConfigFuncDef, GpibBoardDriverConfigCallFunc);
epicsExportRegistrar(GpibBoardDriverRegister);
- linux-gpib with asyn Wilkins, Stuart
- Re: linux-gpib with asyn Feng Laurence
Cryocool LHe support? matthew.pearson
EDM file listing display... Dave Reid
<2012>
2025
2026
Re: linux-gpib with asyn Peter . Mueller
<2012>
2025
2026
