Hi Paul,
Not in the record, but if you are using ALH as an alarm handler, there is the ALARMCOUNTFILTER which
allows you not alarm on spurious values. A description can be found in:
http://www.slac.stanford.edu/grp/ssrl/spear/epics/extensions/alh/ALHUserGuide.html
I hope that this helps,
Pierrick
From: [email protected] [[email protected]] on behalf of Paul Nord [[email protected]]
Sent: Wednesday, February 22, 2012 4:29 PM
To: EPICS Tech Talk
Subject: Alarm for noisy readback channel
I've got a network device that's misbehaving. It "sometimes" reports an absolutely ridiculous value. I'd like to set an alarm on this PV but I don't want the alarm sounding once or twice an hour when there's not really anything wrong. (Never cry wolf.)
In the typical failure mode it reports a "crazy" value once and then goes back to the normal value. (The device actually returns the voltage value for a channel when you ask for a current. And it formats a reply and happily returns "Current: 3600 A", which would be impressive for a supply running at 3600 V. It works out to 13 MegaWatts. The real current is just ~100 uA.)
What's the best way to deal with this?
A CALC pv that takes this value as an input but returns zero if the reading was outside of some range?
A CALC pv that counts the number of readings which are outside of the proper range? (e.g. A>1.0?(VAL+1):0 )
Are there other good mechanisms?
Paul
record(ai, "$(SYSTEM):measurement_current_$(SLOT)$(ID)")
field(DTYP, "Snmp")
field(SCAN, ".5 second")
field(PREC, "6")
field(EGU, "")
field(INP, "@$(HOST) pwd WIENER-CRATE-MIB::outputMeasurementCurrent.$(SLOT)$(ID) Float: 100")
field(ADEL, "1")