1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: Alarm for noisy readback channel
To: [email protected]
Date: Wed, 22 Feb 2012 17:36:17 -0500
Paul,
If you are using ALH to alarm then use the ALARMCOUNTFILTER option I
think that is it) which would suppress the ALH notification for
settable time or count-within-a-time.  Otherwise I think an AO record
has a rate-limit setting which might be used as a filter.  Your second
CALC option would work.
-ps
On Wed, Feb 22, 2012 at 17:25, Paul Nord <[email protected]> wrote:
> I've got a network device that's misbehaving.  It "sometimes" reports an absolutely ridiculous value.  I'd like to set an alarm on this PV but I don't want the alarm sounding once or twice an hour when there's not really anything wrong.  (Never cry wolf.)
> In the typical failure mode it reports a "crazy" value once and then goes back to the normal value.  (The device actually returns the voltage value for a channel when you ask for a current.  And it formats a reply and happily returns "Current: 3600 A", which would be impressive for a supply running at 3600 V.  It works out to 13 MegaWatts.  The real current is just ~100 uA.)
> What's the best way to deal with this?
>        A CALC pv that takes this value as an input but returns zero if the reading was outside of some range?
>        A CALC pv that counts the number of readings which are outside of the proper range?  (e.g. A>1.0?(VAL+1):0 )
> Are there other good mechanisms?
> Paul
> record(ai, "$(SYSTEM):measurement_current_$(SLOT)$(ID)")
>  field(DTYP, "Snmp")
>  field(SCAN, ".5 second")
>  field(PREC, "6")
>  field(EGU,  "")
>  field(INP,  "@$(HOST) pwd WIENER-CRATE-MIB::outputMeasurementCurrent.$(SLOT)$(ID) Float: 100")
>  field(ADEL, "1")
Alarm for noisy readback channel Paul Nord
Prev: Alarm for noisy readback channel Paul Nord
Next: RE: Alarm for noisy readback channel Pierrick M Hanlet
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  <20122013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Next: Alarm for noisy readback channel Paul Nord
