I've got a network device that's misbehaving. It "sometimes" reports an absolutely ridiculous value. I'd like to set an alarm on this PV but I don't want the alarm sounding once or twice an hour when there's not really anything wrong. (Never cry wolf.)
In the typical failure mode it reports a "crazy" value once and then goes back to the normal value. (The device actually returns the voltage value for a channel when you ask for a current. And it formats a reply and happily returns "Current: 3600 A", which would be impressive for a supply running at 3600 V. It works out to 13 MegaWatts. The real current is just ~100 uA.)
What's the best way to deal with this?
A CALC pv that takes this value as an input but returns zero if the reading was outside of some range?
A CALC pv that counts the number of readings which are outside of the proper range? (e.g. A>1.0?(VAL+1):0 )
Are there other good mechanisms?
Paul
record(ai, "$(SYSTEM):measurement_current_$(SLOT)$(ID)")
field(DTYP, "Snmp")
field(SCAN, ".5 second")
field(PREC, "6")
field(EGU, "")
field(INP, "@$(HOST) pwd WIENER-CRATE-MIB::outputMeasurementCurrent.$(SLOT)$(ID) Float: 100")
field(ADEL, "1")
- Re: Alarm for noisy readback channel Paul Sichta
Re: Problems with priorities in epicsThreadCreate (part of the EPICS OSI software layer) Andrew Johnson
Alarm for noisy readback channel Paul Nord
<2012>
2025
2026
Re: CSS X-Y Graph John Dobbins
<2012>
2025
2026
