Hi Dehong,
On 2012-03-26 Zhang, Dehong wrote:
> One of my records reads from hardware then triggers a chain of actions
> through FLNK. From time to time it can get stuck: SEVR=INVALID,
> STAT=SCAN. When it gets into this problem, it stops the FLNKing --
> which is the desired behavior, but stops forever.
> Now, when next scan is due, I would like the record to forget about
> the previous problem, and try again. If it can read (SCAN the streamdevice
> input), do everything as usual; if it fails, do not FLNK -- stop the
> chain, just forget about this cycle.
> Will this "ACKT=NO" do the trick? Please help to confirm.
No, ACKT just controls whether the record needs to have transient alarms
acknowledged through the alarm handler or not, it has no effect on the IOC
processing. If a record that has ACKT=YES goes out of alarm state before the
operators have acknowledged that alarm then they will still have to do so for
the alarm to be cleared on the ALH screen, but if ACKT=NO then unacknowledged
alarm from this record will disappear from the ALH screen as soon as the alarm
condition is removed.
The SCAN/INVALID alarm you are seeing is raised when the IOC tries to process
a record and finds the PACT field has been true for the last 10 tries. The
fact that you're getting these suggests that your database design should be
improved to prevent this happening. You would have to describe the current
processing chain for us to help you with that though.
- Andrew
Never interrupt your enemy when he is making a mistake.
-- Napoleon Bonaparte
- What will "ACKT=NO" do? Zhang, Dehong
Re: please stop Andrew Johnson