Folks,
I have fixed the problem. It turns out that there were bugs both in asyn and in StreamDevice.
The bug in asyn was that it was not disconnecting the port when it detected errors in calls to fcntl and tcsetattr. Once this was fixed the asyn port correctly went into the "disconnected" state when the USB serial device was removed.
However, this did not allow correct functioning, due to a bug in StreamDevice. This bug caused StreamDevice to get into a tight infinite loop in WriteHandler if pasynOctet->read() kept returning asynError, which it does when the device is disconnected.
This is the fix for drvAsynSerialPort.c (patch also attached)
corvette:asyn/asyn/drvAsynSerial>svn diff drvAsynSerialPort.c
Index: drvAsynSerialPort.c
--- drvAsynSerialPort.c (revision 2325)
+++ drvAsynSerialPort.c (working copy)
@@ -648,6 +648,7 @@
epicsSnprintf(pasynUser->errorMessage,pasynUser->errorMessageSize,
"Can't set %s file flags: %s",
tty->serialDeviceName, strerror(errno));
+ closeConnection(pasynUser,tty);
return asynError;
@@ -735,6 +736,7 @@
return asynError;
@@ -761,6 +763,7 @@
"Can't set \"%s\" c_cc[VTIME]: %s",
return asynError;
#endif
This is the fix for StreamDevice (patch also attached)
corvette:stream/streamDevice/src>svn diff AsynDriverInterface.cc
Index: AsynDriverInterface.cc
--- AsynDriverInterface.cc (revision 15960)
+++ AsynDriverInterface.cc (working copy)
@@ -630,6 +630,7 @@
int eomReason = 0;
status = pasynOctet->read(pvtOctet, pasynUser,
buffer, received, &received, &eomReason);
+ if (status == asynError) break;
#ifndef NO_TEMPORARY
if (received) debug("AsynDriverInterface::writeHandler(%s): flushing %ld bytes: \"%s\"\n",
clientName(), (long)received, StreamBuffer(buffer, received).expand()());
With these 2 patches it behaves correctly. When the USB device is removed the port becomes disconnected, and StreamDevice prints an error message.
When the device is reconnected it continues normally.
I did my testing with a Newport CONEX-AGP motor controller. I created the following udev rule:
[epics@Colorado rules.d]$ more 81-Agilis.rules
KERNEL=="ttyUSB*", ATTRS{idVendor}=="104d", ATTRS{idProduct}=="3006", OPTIONS="ignore_remove", NAME+="ttyUSBAGP", MODE="0666"
This does 2 important things:
- Makes the device always have the same name when it is connected (ttyUSBAGP). Otherwise its name can change from ttyUSB0 to ttyUSB1, etc. each time it is connected, and then it won't work.
- Gives the device world r/w permission.
I have committed the asyn changes to SVN. Once Mazanec verifies that it fixes his problem I will release asyn R4-23.
I have also committed the StreamDevice change to the APS BCDA SVN repository, but that is just a local fix.
Sent: Friday, April 11, 2014 11:34 AM
To: Mark Rivers; Dirk Zimoch; [email protected]
Subject: RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort
This sounds like good news, thanks.
I've tried to distinguish stream and asyn behaviour.
With my IOC compiled with both asyn & stream with SynApps 5.7 and no DTYP=stream records loaded, asynRecord is not able to disconnect the PORT. Neither Asyn , if device is physically disconnected.
This might not introduce any change to IOC setup.
However, if the IOC is compiled with asyn only and still the only loaded record is asynRecord. Disconnection using PCNCT and CNCT works fine, no matter if the device is physically disconnected.
After I did read your post, I've tried to set TMOT to zero and repeated the second case (w/o stream).
Regardless that read is almost imposible with zero time-out, disconnection didn't work properly -- asynReport still showed "Yes" to connected state of the PORT even when physical device disconnected. Flush didn;t help neither.
Tomas
Od: Mark Rivers [[email protected]]
Odesláno: 11. dubna 2014 13:11
Komu: Dirk Zimoch; [email protected]; Mazanec Tomáš
Předmět: RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort
Eric reproduced the problem yesterday, and we think we understand the problem. It appears to actually be a problem with asyn, not with StreamDevice.
The problem does not occur for normal read operationgs with a non-zero timeout. In that case if read() returns an error indicating that the device is no longer available then the driver disconnects the port. For the next read or write operation asynManager will see that the port is disconnected, and will try the normal autoconnect mechanism. When the device available again it will connect.
The problem is occurring when StreamDevice calls read with a zero timeout, which it does to simulate a flush() operation. In this case the driver is calling fcntl() which is returning an error. It then returns that error to StreamDevice. But it does not disconnect the port when this occurs, like it does when a read() error occurs. It should be disconnecting the port. There may be a few other places where errors should cause the port to disconnect.
As a side note, why is StreamDevice calling read() with zero timeout, rather than calling flush()?
I think the fix should be pretty easy. I will try to reproduce the problem today, and then verify that it is fixed.
From: [email protected] [[email protected]] on behalf of Dirk Zimoch [[email protected]]
Sent: Friday, April 11, 2014 2:22 AM
To: [email protected]
Subject: Re: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort
Hi Tomáš,
I will have a look. In older versions of StreamDevice, I check the
connection state at each access and try to connect if necessary. But I
have been told that this is wrong behavior and I should better leave it
to asyn to do the auto connect. So I removed the connect code from
StreamDevice. This worked fine with sockets. But I have to investigate
what is missing with USB to serial. I also check with Mark and Eric. But
it may take a while...
Dirk
On 10.04.2014 13:24, Mazanec Tomáš wrote:
> In synApps 5.7, if the usb-serial device is physically disconnected,
> while the IOC is running, the command:
> asynReport(10, PORT) says the asyn port is still connected:
> PORT multiDevice:No canBlock:Yes autoConnect:Yes
> enabled:Yes connected:Yes numberConnects 1
> nDevices 0 nQueued 0 blocked:No
> asynManagerLock:No synchronousLock:Yes
> exceptionActive:No exceptionUsers 2 exceptionNotifys 0
> interposeInterfaceList
> asynOctet pinterface 0x7fbbfb51f6a0 drvPvt 0x1489670
> interfaceList
> asynCommon pinterface 0x7fbbfb51ca80 drvPvt 0x1486740
> asynOption pinterface 0x7fbbfb51caa0 drvPvt 0x1486740
> asynOctet pinterface 0x7fbbfb51ee40 drvPvt 0x1486740
> Serial line /dev/ttyUSBPIC: Connected
> fd: 5
> Characters written: 164
> Characters read: 287
> What also happens, and I didn't noticed, is IOC's process takes 100% CPU
> usage and traceFlow bit within traceMask in Asyn reports hundreds of
> these lines in a second:
> 2014/04/10 13:06:39.575 /dev/ttyUSBPIC read.
> However, an attempt to reconnect asyn port with asynRecord ends with no
> success and this messsage output:
> 2014/04/10 13:04:32.374 EEE:asynrec: special queueRequest timeout
> Thanks,
> Tomas
> *Od:* Mark Rivers [[email protected]]
> *Odesláno:* 8. dubna 2014 18:47
> *Komu:* Mazanec Tomáš; [email protected]
> *Předmět:* RE: Streamdevice 2.6 autoconnection failure using
> drvAsynSerialPort
> In synApps 5.7 what happens if you use an asynRecord to force the
> asynPort to reconnect. Does StreamDevice then start working?
> When the device is disconnected does asyn report that it is
> disconnected? Use the following command when the device is disconnected:
> asynReport 10 ASYN_PORT_NAME
> Mark
> *From:*Mazanec Tomáš [mailto:[email protected]]
> *Sent:* Tuesday, April 08, 2014 9:20 AM
> *To:* Mark Rivers; [email protected]
> *Subject:* RE: Streamdevice 2.6 autoconnection failure using
> drvAsynSerialPort
> Hi Mark
> Thanks for a quick response.
> The IOC runs on Scientific Linux 6.5 x86-64 and its default kernel.
> Yes, I have upgraded it (from 6.4 to 6.5) prior to SynApps upgrade.
> Linux udev system is configured in a way that my usb-serial device gets
> always the same device name (/dev/ttyUSBPIC) no matter what other
> devices are present (major, minor device numbers can change).
> I've double-checked Asyn 4.21 re-connection ability using asynRecord
> (.CNCT, .PCNCT).
> It works fine, so the issue might be a glitch in the new StreamDevice.
> Nevertheless, I've kept SynApps-5-6 installed and compared re-connection
> behavior to 5.7.
> The older version is fine -- If my usb-serial device is physically
> disconnected, IOC with SynApps-5-6 reports:
> 2014/04/07 16:55:20.994 PORT EEE:volts: connection closed in write
> 2014/04/07 16:55:25.994 PORT EEE:volts: pasynCommon->connect() failed:
> /dev/ttyUSBPIC Can't open No such device
> 2014/04/07 16:55:25.994 PORT EEE:volts: Protocol aborted
> and when the usb-serial device is connected back, R/W operations
> continue as usual.
> Whereas with the new version (5.7), IOC shell is kind of silent unless I
> try to reload StreamDevice protocol :
> epics> streamReload EEE:volts
> 2014/04/08 11:46:52.567355 _main_ StreamCore::finishProtocol(EEE:volts):
> Still waiting for writeSuccess()
> 2014/04/08 11:46:52.567398 _main_ EEE:volts: Protocol aborted
> or unless I try to use StreamDevice's connect command (through the
> EEE:CONNECT PV):
> epics> dbpf EEE:CONNECT 1
> DBR_STRING: "ON"
> epics> 2014/04/07 17:10:06.446437 timerQueue EEE:CONNECT: Connect failed
> 2014/04/07 17:10:06.446482 timerQueue EEE:CONNECT: Protocol aborted
> ?2014/04/07 17:10:07.536724 timerQueue EEE:CONNECT: Connect failed
> ?2014/04/07 17:10:07.536747 timerQueue EEE:CONNECT: Protocol aborted
> but the connection is not re-established anyway. Furthermore, protocol
> reload makes IOC shell stuck.
> There is an older post about different connection issue, but also with
> StreamDevice & Asyn.
> So, with the new version (5.7), I've checked whether the timerQueue
> thread is OK and checked for any locked mutexes.
> The thread is OK.
> There is a mutex reported as locked once the usb-serial device is
> diconnected, however it remains locked when the device is connected back.
> epics> epicsMutexShowAll 1
> ellCount(&mutexList) 112 ellCount(&freeList) 0
> epicsMutexId 0x1d5bfd0 source ../../asyn/asynDriver/asynManager.c line 1868
> No mutexes remain locked after the usb-device re-connection with the
> older version (5.6). But this could be just a result of the issue.
> Tomas
> *Od:*Mark Rivers [[email protected]]
> *Odesláno:* 7. dubna 2014 18:36
> *Komu:* Mazanec Tomáš; [email protected] <mailto:[email protected]>
> drvAsynSerialPort
> Hi Tomas,
> There were no substantive changes in the drvAsynSerialPort code between
> asyn 4.18 and asyn 4.21. SVN tag 1917 is asyn 4.18 and tag 2203 is asyn
> 4.21.
> Here are the differences:
> corvette:asyn/asyn/drvAsynSerial>svn diff -r1917:2203 drvAsynSerialPort*
> --- drvAsynSerialPort.c (revision 1917)
> +++ drvAsynSerialPort.c (revision 2203)
> @@ -103,12 +103,12 @@
> if ((ioctl(tty->fd, FIOBAUDRATE, tty->baud) < 0)
> && (ioctl(tty->fd, SIO_BAUD_SET, tty->baud) < 0)) {
> - "SIO_BAUD_SET failed: %s\n",
> strerror(errno));
> + "SIO_BAUD_SET failed: %s",
> strerror(errno));
> return asynError;
> if (ioctl(tty->fd, SIO_HW_OPTS_SET, tty->termios.c_cflag) < 0) {
> - "SIO_HW_OPTS_SET failed: %s\n",
> strerror(errno));
> + "SIO_HW_OPTS_SET failed: %s",
> strerror(errno));
> return asynError;
> #else
> @@ -116,7 +116,7 @@
> tty->termios.c_cflag |= CREAD;
> if (tcsetattr(tty->fd, TCSANOW, &tty->termios) < 0) {
> - "tcsetattr failed: %s\n",
> strerror(errno));
> + "tcsetattr failed: %s",
> strerror(errno));
> return asynError;
> #endif
> @@ -253,12 +253,12 @@
> if(cfsetispeed(&tty->termios,baudCode) < 0 ) {
> - "cfsetispeed returned %s\n",strerror(errno));
> + "cfsetispeed returned %s",strerror(errno));
> return asynError;
> if(cfsetospeed(&tty->termios,baudCode) < 0 ) {
> - "cfsetospeed returned %s\n",strerror(errno));
> + "cfsetospeed returned %s",strerror(errno));
> return asynError;
> @@ -452,7 +452,7 @@
> tcflush(tty->fd, TCOFLUSH);
> #endif
> #ifdef vxWorks
> - ioctl(tty->fd, FIOCANCEL, NULL);
> + ioctl(tty->fd, FIOCANCEL, 0);
> * Since it is possible, though unlikely, that we got here before the
> * slow system call actually started, we arrange to poke the thread
> @@ -509,14 +509,14 @@
> if ((tty->fd = open(tty->serialDeviceName,
> O_RDWR|O_NOCTTY|O_NONBLOCK, 0)) < 0) {
> - "%s Can't open %s\n",
> + "%s Can't open %s",
> strerror(errno));
> return asynError;
> #if defined(FD_CLOEXEC) && !defined(vxWorks)
> if (fcntl(tty->fd, F_SETFD, FD_CLOEXEC) < 0) {
> - "Can't set %s close-on-exec flag: %s\n",
> + "Can't set %s close-on-exec flag: %s",
> strerror(errno));
> close(tty->fd);
> tty->fd = -1;
> @@ -578,7 +578,7 @@
> asynPrint(pasynUser, ASYN_TRACE_FLOW,
> "%s write.\n", tty->serialDeviceName);
> asynPrintIO(pasynUser, ASYN_TRACEIO_DRIVER, data, numchars,
> - "%s write %d\n", tty->serialDeviceName,
> numchars);
> + "%s write %lu\n", tty->serialDeviceName,
> (unsigned long)numchars);
> if (tty->fd < 0) {
> "%s disconnected:",
> @@ -672,7 +672,7 @@
> if (maxchars <= 0) {
> - "%s maxchars %d Why
> <=0?\n",tty->serialDeviceName,(int)maxchars);
> + "%s maxchars %d Why <=0?",tty->serialDeviceName,(int)maxchars);
> return asynError;
> if (tty->readTimeout != pasynUser->timeout) {
> @@ -775,8 +775,8 @@
> data[nRead] = 0;
> else if (gotEom)
> *gotEom = ASYN_EOM_CNT;
> - asynPrint(pasynUser, ASYN_TRACE_FLOW, "%s read %d, return %d\n",
> - tty->serialDeviceName, *nbytesTransfered,
> status);
> + asynPrint(pasynUser, ASYN_TRACE_FLOW, "%s read %lu, return %d\n",
> + tty->serialDeviceName, (unsigned
> long)*nbytesTransfered, status);
> return status;
> So the changes are removing “\n” from the end of epicsSNprintf formats,
> and some other minor changes to avoid compiler warnings.
> Is this on Linux?
> Have you upgraded the OS?
> I think any change in behavior is likely due either to a change in
> StreamDevice or a change in the OS, and not due to any change in asyn.
> Mark
> *From:*[email protected]
> [mailto:[email protected]] *On Behalf Of *Mazanec Tomáš
> *Sent:* Monday, April 07, 2014 11:13 AM
> *To:* [email protected] <mailto:[email protected]>
> *Subject:* Streamdevice 2.6 autoconnection failure using drvAsynSerialPort
> Hello
> Automatic re-connection seems to be broken with recent streamdevice & asyn.
> Recently, we upgraded SynApps from 5.6 to version 5.7 and so
> streamdevice 2.5.1 & Asyn 4.18 to streamdevice 2.6 & Asyn 4.21.
> One of IOCs here is using serial port ( as /dev/ttyUSBxxx ) and device
> controlled by it disconnects often.
> With SynApps 5.6, everything ran smoothly. After the upgrade to SynApps
> 5.7, the IOC is not able to reconnect anymore.
> As far as I've tested, drvAsynIPPort reconnects well with both SynApps
> 5.6 and 5.7, so its just serial port variant which is affected.
> Could you anyone address this issue and provide some hints or fix.
> Regards,
> Tomas Mazanec
> ELI Beamlines Czech Republic
> http://www.eli-beams.eu
> +420 26605 2566
> +420 601 555 066
> Address:
> Institute of Physics, Academy of Sciences
> Na Slovance 2
> 182 21 Prague
> Czech Republic
> *** DB template file:
> record(ai, "$(NAME):volts")
> field(DTYP, "stream")
> field(INP, "@$(SCONF) get_volts $(ASYNPORT)")
> field(SCAN, "5 second")
> field(PINI, "YES")
> field(VAL, "0")
> field(PREC, "2")
> field(EGU, "V")
> record(bo, "$(NAME):CONNECT") {
> field(OUT, "@$(SCONF) connect $(ASYNPORT)")
> field(PINI, "NO")
> field(HIGH, "0.1")
> field(ZNAM, "OFF")
> field(ONAM, "ON")
> *** streamdev protocol file:
> get_volts {out "\x11\x3f\x76\x04"; in "\x76%f\x04\x00" }
> connect {
> ExtraInput = Ignore;
> connect 1000;
> *** EPICS IOC shell LOG file:
> epicsEnvSet("SYSNAME","EEE")
> # streamdevice protocol file-name
> epicsEnvSet("SYSSCONF","proto.sdp")
> # name of asyndriver port (arbitrary)
> epicsEnvSet("SYSASYNPORT","PORT")
> # For streamdevice
> epicsEnvSet STREAM_PROTOCOL_PATH :protocols:./cfg
> # Setup asyn driver
> drvAsynSerialPortConfigure ("PORT","/dev/ttyUSBPIC", 0, 1, 0)
> asynSetOption ("PORT", 0, "baud", "9600")
> asynSetOption ("PORT", 0, "bits", "8")
> asynSetOption ("PORT", 0, "parity", "none")
> asynSetOption ("PORT", 0, "stop", "1")
> asynReport(1, "PORT")
> PORT multiDevice:No canBlock:Yes autoConnect:No
> enabled:Yes connected:No numberConnects 0
> asynManagerLock:No synchronousLock:No
> exceptionActive:No exceptionUsers 1 exceptionNotifys 0
> Serial line /dev/ttyUSBPIC: Disconnected
> fd: -1
> Characters written: 0
> Characters read: 0
> asynSetTraceIOMask("PORT",0,0x4)
> asynSetTraceMask("PORT",0,0x9)
> dbLoadRecords("aaa.template","NAME=EEE, SCONF=proto.sdp, ASYNPORT=PORT")
> iocInit()
> Starting iocInit
> ## EPICS R3.14.12.4 $Date: Mon 2013-12-16 15:51:45 -0600$
> ## EPICS Base built Mar 11 2014
> iocRun: All initialization complete
> 2014/04/07 17:07:24.528 /dev/ttyUSBPIC write 4
> 11 3f 76 04
> 2014/04/07 17:07:24.542 /dev/ttyUSBPIC read 1
> 76
> 2014/04/07 17:07:24.543 /dev/ttyUSBPIC read 1
> 35
> 2014/04/07 17:07:24.544 /dev/ttyUSBPIC read 1
> 2e
> 2014/04/07 17:07:24.545 /dev/ttyUSBPIC read 1
> 31
> 2014/04/07 17:07:24.547 /dev/ttyUSBPIC read 1
> 39
> 2014/04/07 17:07:24.548 /dev/ttyUSBPIC read 1
> 04
> 2014/04/07 17:07:24.549 /dev/ttyUSBPIC read 1
> 00
> 2014/04/07 17:07:29.026 /dev/ttyUSBPIC write 4
> 11 3f 76 04
> 2014/04/07 17:07:29.039 /dev/ttyUSBPIC read 1
> 76
> 2014/04/07 17:07:29.041 /dev/ttyUSBPIC read 2
> 35 2e
> 2014/04/07 17:07:29.042 /dev/ttyUSBPIC read 1
> 31
> 2014/04/07 17:07:29.043 /dev/ttyUSBPIC read 1
> 39
> 2014/04/07 17:07:29.044 /dev/ttyUSBPIC read 1
> 04
> 2014/04/07 17:07:29.046 /dev/ttyUSBPIC read 1
> 00
> epics>
> epics>
> epics>
> epics> scanppl
> Records with SCAN = '5 second' (0 over-runs):
> EEE:volts
> epics> dbgf EEE:volts
> DBR_DOUBLE: 5.19
> epics>
> epics> dbpr EEE:volts 111
> ACKS: INVALID ACKT: YES ADEL: 0 ALST: 5.19
> AOFF: 0 ASG: ASLO: 1 ASP: (nil)
> BKPT: 00 DESC: DISA: 0 DISP: 0
> DISS: NO_ALARM DISV: 1 DPVT: 0x1911dd0 DSET:
> 0x7fa011b09a40
> DTYP: stream EGU: V EGUF: 0 EGUL: 0
> EOFF: 0 ESLO: 1 EVNT: 0 FLNK:CONSTANT 0
> HHSV: NO_ALARM HIGH: 0 HIHI: 0 HOPR: 0
> HSV: NO_ALARM HYST: 0 INIT: 0
> INP:INST_IO @proto.sdp get_volts PORT LALM: 5.19 LBRK: 0
> LCNT: 11 LINR: NO CONVERSION LLSV: NO_ALARM LOLO: 0
> LOPR: 0 LOW: 0 LSET: 0x1917c90 LSV: NO_ALARM
> MDEL: 0
> MLIS: 30 69 02 b0 9f 7f 00 00 30 69 02 b0 9f 7f 00 00 01 00 00 00
> MLOK: 40 76 90 01 00 00 00 00 MLST: 5.19 NAME: EEE:volts
> NSEV: NO_ALARM NSTA: NO_ALARM ORAW: 0 PACT: 1
> PBRK: (nil) PHAS: 0 PINI: YES PPN: (nil)
> PPNR: (nil) PREC: 2 PRIO: LOW PROC: 0
> PUTF: 0 RDES: 0x1885ff0 ROFF: 0 RPRO: 0
> RSET: 0x7fa0118c7a80 RVAL: 0 SCAN: 5 second
> SDIS:CONSTANT SEVR: INVALID SIML:CONSTANT SIMM: NO
> SIMS: NO_ALARM SIOL:CONSTANT SMOO: 0 SPVT: 0x1913f00
> STAT: SCAN SVAL: 0 TIME: 2014-04-07 17:07:34.247219579
> TPRO: 0 TSE: 0 TSEL:CONSTANT UDF: 0
> VAL: 5.19
> epics>
> epics> dbgf EEE:volts.SEVR
> DBR_STRING: "INVALID"
> epics>
> DBR_STRING: "ON"
> epics> ?[31;1m2014/04/07 17:10:06.446437 timerQueue EEE:CONNECT: Connect
> failed
> ?[0m?[31;1m2014/04/07 17:10:06.446482 timerQueue EEE:CONNECT: Protocol
> aborted
> ?[0m?[31;1m2014/04/07 17:10:07.536724 timerQueue EEE:CONNECT: Connect
> failed
> ?[0m?[31;1m2014/04/07 17:10:07.536747 timerQueue EEE:CONNECT: Protocol
> aborted
> ?[0m
> epics>
> epics> var streamDebug 1
> 2014/04/07 17:10:35.596373 _main_ StreamEpics.cc:711:
> Stream::process(EEE:CONNECT) start
> 2014/04/07 17:10:35.596411 _main_ StreamCore.cc:410:
> StreamCore::startProtocol(EEE:CONNECT, startMode=StartNormal)
> 2014/04/07 17:10:35.596426 _main_ StreamCore.cc:552:
> StreamCore::evalCommand(EEE:CONNECT): activeCommand = connect
> 2014/04/07 17:10:35.596436 _main_ AsynDriverInterface.cc:1347:
> AsynDriverInterface::connectRequest EEE:CONNECT
> 2014/04/07 17:10:35.596446 _main_ StreamEpics.cc:723:
> Stream::process(EEE:CONNECT): protocol started
> DBR_STRING: "ON"
> epics> 2014/04/07 17:10:36.591508 timerQueue
> AsynDriverInterface.cc:1473:
> AsynDriverInterface::handleTimeout(EEE:CONNECT)
> ?[31;1m2014/04/07 17:10:36.591531 timerQueue EEE:CONNECT: Connect failed
> ?[0m2014/04/07 17:10:36.591539 timerQueue StreamCore.cc:517:
> StreamCore::finishProtocol(EEE:CONNECT, status=Fault) not bus owner
> 2014/04/07 17:10:36.591545 timerQueue AsynDriverInterface.cc:1416:
> AsynDriverInterface::finish(EEE:CONNECT) start
> 2014/04/07 17:10:36.591551 timerQueue AsynDriverInterface.cc:1426:
> AsynDriverInterface::finish(EEE:CONNECT) done
> ?[31;1m2014/04/07 17:10:36.591557 timerQueue EEE:CONNECT: Protocol aborted
> ?[0m2014/04/07 17:10:36.591589 cbLow StreamEpics.cc:896:
> streamRecordProcessCallback(EEE:CONNECT) processing record
> 2014/04/07 17:10:36.591622 cbLow StreamEpics.cc:691:
> Stream::process(EEE:CONNECT) error status=UDF (17)
> 2014/04/07 17:10:36.591646 cbLow StreamEpics.cc:901:
> streamRecordProcessCallback(EEE:CONNECT) processing record done
> 2014/04/07 17:10:36.686741 cbLow StreamEpics.cc:711:
> 2014/04/07 17:10:36.686766 cbLow StreamCore.cc:410:
> 2014/04/07 17:10:36.686779 cbLow StreamCore.cc:552:
> 2014/04/07 17:10:36.686785 cbLow AsynDriverInterface.cc:1347:
> 2014/04/07 17:10:36.686796 cbLow StreamEpics.cc:723:
> 2014/04/07 17:10:37.681881 timerQueue AsynDriverInterface.cc:1473:
> ?[31;1m2014/04/07 17:10:37.681901 timerQueue EEE:CONNECT: Connect failed
> ?[0m2014/04/07 17:10:37.681909 timerQueue StreamCore.cc:517:
> 2014/04/07 17:10:37.681916 timerQueue AsynDriverInterface.cc:1416:
> 2014/04/07 17:10:37.681922 timerQueue AsynDriverInterface.cc:1426:
> ?[31;1m2014/04/07 17:10:37.681927 timerQueue EEE:CONNECT: Protocol aborted
> ?[0m2014/04/07 17:10:37.681958 cbLow StreamEpics.cc:896:
> 2014/04/07 17:10:37.681981 cbLow StreamEpics.cc:691:
> 2014/04/07 17:10:37.681994 cbLow StreamEpics.cc:901:
> epics>
> epics>
> epics>
@@ -648,6 +648,7 @@
return asynError;
@@ -735,6 +736,7 @@
return asynError;
@@ -761,6 +763,7 @@
return asynError;
#endif
@@ -630,6 +630,7 @@
int eomReason = 0;
- RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mazanec Tomáš
- Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mazanec Tomáš
- RE: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Mark Rivers
- Re: Streamdevice 2.6 autoconnection failure using drvAsynSerialPort Dirk Zimoch
Re: Sequencer build problem cygwin64 Benjamin Franksen
<2014>
2025
2026
<2014>
2025
2026
