1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <2015>  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <2015>  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Alarm annunciation with ALH and other PC based systems
To: <[email protected]>, <[email protected]>
Date: Fri, 16 Jan 2015 10:48:19 +0000
Hi Rod,
I asked one of our electrical engineers about this kind of thing for a cryo system where we needed to protect staff in case of nitrogen leaks. I hope there are some useful comments for you:
Unfortunately with an active alarm the only way is to test periodically or at significant times, e.g. entry to a confined space.  This is how we deal with it for all the oxygen depletion systems:
Power loss - the alarm sounds.  The battery inside the control box lasts and hour.
Sensor disconnected or damaged - alarm sounds.  It's a 4-20mA loop so disconnection and over range are detectable by the control box.
Loss or damage of sounder/flasher circuit - periodic testing - we have an annual test by the supplier under a maintenance contract.  Warning circuits can be activated from the controller front panel allowing more frequent periodic testing if required.
Sensor aging or malfunction - checked at annual service.   Can be done more often if required.
The Crowcon systems we used have proved very reliable.   The only work needing to be done is changing sensor heads which deteriorate with age.   These are however dedicated processors inside sealed boxes with no configuration access when in service.   Power is fed from UPS feed via local outlets which do not have switches.
Austen Rose
(x8495)
Alarm annunciation with ALH and other PC based systems Rod Nussbaumer
RE: Alarm annunciation with ALH and other PC based systems ronaldo.mercado
Prev: RE: Alarm annunciation with ALH and other PC based systems ronaldo.mercado
Next: RE: Support for Mercury iTC tom.cobb
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  <2015>  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Next: RE: Alarm annunciation with ALH and other PC based systems Emmanuel Mayssat