1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <2016>  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <2016>  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: RE: Cost effective solution for monitor a large number of temperatures w EPICS
To: "[email protected]" <[email protected]>, "[email protected]" <[email protected]>
Date: Thu, 14 Jan 2016 09:47:20 +0000
Hi Mauro
If you seek more distributed and perhaps effortless solution, MOXA ioLogik E1260 is 6x RTD , incl. PT100, box which talks MODBUS/TCP. (http://www.moxa.com/product/ioLogik_E1260.htm ).
We have an EPICS IOC to read the sensors. Feel free to ask for sources. So far, we use it as a bench-top device. Additionally, temperatures are published on E1260 internal web-server.
For, lets say, more serious stuff, guys next door developed a PCB with Temp&Humi sensor which is then read by an industrial analog input 0--10Volts (NI C-RIO in our case).
Tomas
Od: [email protected] [[email protected]] za uživatele [email protected] [[email protected]]
Odesláno: 13. ledna 2016 12:46
Komu: [email protected]; [email protected]
Předmět: RE: Cost effective solution for monitor a large number of      temperatures w EPICS
Hi Mauro,
100 sensors is quite a large number to handle. One of your problems might be cabling density. Are all the signals coming from one relatively contained area, or are they widely distributed? Could you consider distributed I/O and divide the problem in that way? Are you planning 2, 3 or 4 wire measurement connections - how long will your cabling be? You did not comment on required instrumentation accuracy. As you comment, cost and reliability questions also come into the decision making process. Would multiplexed readings be appropriate, rather than 100 direct connections to the instrumentation?
Anyway some ideas:
VME crate, carrier cards, ADC IP modules and PT100 PIMS. I am guessing that there are quite a few ADC/PIM combinations used by other facilities. We use Hytec Electronics modules for this, but never at the density you suggest. Depending on components used, you should be able to find EPICS support.
Beckhoff solutions - but I am not familiar with their range for this type of application and number of signals.
Agilent meters offer some multiplexed solutions, but again, not at this signal density.
Finally, you might consider using a PLC to marshal your inputs. We use Omron PLCs and they have 6 channel modules, but at 100 signals this might be difficult.
If you could distribute the I/O then all the above have merits.
I look forward to hearing how you solved this.
Austen Rose
(x8495)
I'm looking to find something that works out of the box. The PT100 is a requirements.
Beckhoff has a KL320X, I thought someone has experienced on that...
I've to balance the cost and the reliability of this solution.
Thansk,
-Mauro
Re: Cost effective solution for monitor a large number of temperatures w EPICS Jack
RE: Cost effective solution for monitor a large number of temperatures w EPICS austen.rose
Prev: Dynamically refresh CSS BOY runtime OPI Zhang Yuliang
Next: Galil Motor Tutorial? Mark Clift
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <2016>  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: RE: Cost effective solution for monitor a large number of temperatures w EPICS austen.rose
Next: Re: Cost effective solution for monitor a large number of temperatures w EPICS Jack
ANJ, 15 Jul 2016 · Home · News · About · Talk · Base · Modules · Extensions ·
