1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <2016>  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <2016>  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: Device Support for I2C and GPIO -> StreamDevice
To: Mark Rivers <[email protected]>, "[email protected]" <[email protected]>, "[email protected]" <[email protected]>
Date: Tue, 19 Jan 2016 15:28:36 +0100
Hey,
I'm using version 2.6 with the 3 "official" patches from the StreamDevice webpage
which are all in deed dated from 2012...
I will switch to the version at github and test it again!
Thanks for the info!
  Florian
On 01/19/2016 02:20 PM, Mark Rivers wrote:
Hi Florian,
What version of streamDevice are you using?
I fixed the problem you are having in April 2014.  My fix is in the version on github (https://github.com/epics-modules/stream):
commit 02e5f0a2a7eda45c7e13b0d66f7c1675b671204e
Author: MarkRivers <[email protected]>
Date:   Fri Apr 11 19:03:22 2014 +0000
     Fix for infinite loop in WriteHandler for disconnected devices
This is the patch:
corvette:stream/streamDevice/src>git diff f0fe997b0dbf60285b5c7dd328805ba06105022f AsynDriverInterface.cc
diff --git a/streamDevice/src/AsynDriverInterface.cc b/streamDevice/src/AsynDriverInterface.cc
index 8f64180..1ae3e7f 100644
--- a/streamDevice/src/AsynDriverInterface.cc
+++ b/streamDevice/src/AsynDriverInterface.cc
@@ -630,6 +630,7 @@ writeHandler()
          int eomReason = 0;
          status = pasynOctet->read(pvtOctet, pasynUser,
              buffer, received, &received, &eomReason);
+        if (status == asynError) break;
  #ifndef NO_TEMPORARY
          if (received) debug("AsynDriverInterface::writeHandler(%s): flushing %ld bytes: \"%s\"\n",
              clientName(), (long)received, StreamBuffer(buffer, received).expand()());
This problem came up again in November 2015 in this tech-talk thread:
http://www.aps.anl.gov/epics/tech-talk/2015/msg01836.php
In both cases Dirk Zimoch, the author of streamDevice, was e-mailed with the patch.  Unfortunately there has not been an official release of streamDevice since 2.6, which I believe dates from 2012.
I would recommend using either the master branch or release 2-6c from the github link above.
From: [email protected] [[email protected]] on behalf of Florian Feldbauer [[email protected]]
Sent: Tuesday, January 19, 2016 6:26 AM
To: [email protected]; [email protected]
Hey,
I had a look at the code of streamDevice
If I understood it correct, the write command of the
protocol is performed by the function
  AsynDriverInterface::writeHandler()
Looking at the lines 621 and following of the source this might cause the problem:
     pasynUser->timeout = 0;
     if (pasynGpib)
          pasynOctet->flush(pvtOctet, pasynUser);
     else
     // discard any early input, but forward it to potential async records
     // thus do not use pasynOctet->flush()
     do {
         char buffer [256];
         size_t received = sizeof(buffer);
         int eomReason = 0;
#endif
     } while (status != asynTimeout);
Since  the read on the I2C bus fails,
pasynOctet->read returns asynError, and not asynTimeout...
so the break condition of the while-loop gets never satisfied.
If I change the return value to asynTimeout it works...
I'm not sure how this works an other buses/ports,
but wouldn't it make sense also to test on errors at this point
in streamDevice?
   Florian
On 01/19/2016 10:18 AM, Florian Feldbauer wrote:
Hey,
after having a look at the link provided by Guy, and
looking at which point :connect() is called, it makes sense
that the "wrong" method was called.
With Marks patch it now works!
But I get a new problem now.
I'm now trying to use my I2C asynPortDriver with StreamDevice, but somehow this doesn't work.
As a first try I want to readout the control register of my ADC (AD7998-0). Since the control register is
a 16-bit word, where each bit stands for a specific setting, I'm using a mbbiDirect record.
I also tried using a longin instead. Same effect.
record( mbbiDirect, "AD7998:$(ID):CTRLREGISTER:READ" ) {
   field( DTYP, "stream" )
   field( INP,  "@ad7998.proto rCtrl($(ID)) I2C" )
And the protocol file:
Terminator   = "";
MaxInput     = 2;
ExtraInput   = Error;
rCtrl {
   #out ${1} 2;
   out 33 2;
   in  "%02r";
I put a printf in the writeOctet and readOctet functions, to see what happens.
epics> dbpf AD7998:33:CTRLREGISTER:READ.PROC 1
I2C: drvAsynI2C::readOctet: maxChars=256
DBR_UCHAR:          1         0x1
epics> I2C: drvAsynI2C::readOctet: maxChars=256
This output continues endlessly...
I cannot see the printf from the writeOctet call, and the readOctet seems
to be called in an infinite loop with maxChars=256, although I set MaxInput=2
Am I missing something?
The record above is the only one in my IOC.
Thanks for the help!
   Florian
On 01/19/2016 01:40 AM, Mark Rivers wrote:
Hi Florian,
I now understand the problem.  If an asynPort has autoConnect=true then the pasynCommon->connect() function is called as soon as the asynCommon interface is registered.  For ports created with asynPortDriver this happens in the base class constructor.  At that time your derived classes virtual methods have not yet been registered, so it calls asynPortDriver::connect, not your derived class connect() method.
So I have now learned that if your derived class implements the connect() method and if autoConnect is true, then you must do the following in your derived class constructor:
- Call pasynManager->disconnect, because the base class connect method will have succeeded, and asynManager will think the port is connected
- Call your derived class connect() method directly
I have modified your driver to do this:
diff -U2 drvAsynI2c/drvAsynI2CApp/src/drvAsynI2C.cpp drvAsynI2c_new/drvAsynI2CApp/src/
--- drvAsynI2c/drvAsynI2CApp/src/drvAsynI2C.cpp 2016-01-18 03:52:49.000000000 -0600
+++ drvAsynI2c_new/drvAsynI2CApp/src/drvAsynI2C.cpp     2016-01-18 18:20:07.361358828 -0600
@@ -376,4 +376,5 @@
asynStatus drvAsynI2C::connect( asynUser *pasynUser ) {
+printf("%s: drvAsynI2C::connect entry, device=%s\n", portName, _deviceName);
    if( _fd >= 0 ) {
      epicsSnprintf( pasynUser->errorMessage,pasynUser->errorMessageSize,
@@ -434,7 +435,21 @@
                      0 ) // Default stack size
+  asynStatus status;
    _deviceName = epicsStrDup( ttyName );
    _fd = -1;
    _slaveAddress = 0;
+  if (autoConnect) {
+    // If autoConnect is true then asynPortDriver::connect will have been called by the asynPortDriver
+    // constructor and asynManager will think the port is connected.  Must disconnect and then call
+    // our connect() method
+    pasynManager->exceptionDisconnect(pasynUserSelf);
+    status = this->connect(pasynUserSelf);
+    if (status) {
+      asynPrint(pasynUserSelf, ASYN_TRACE_ERROR,
+        "drvAsynI2C::drvAsynI2C, error calling connect %s\n", pasynUserSelf->errorMessage);
  //  createParam( SLAVEADDRESS_STRING, asynParamInt32, &_paramSlaveAddress );
This is what I then get when I run the IOC.  Note that on my system connect() will fail because I don't have an I2C device.
drvAsynI2CConfigure( "I2C", "/dev/i2c-1", 1 )
I2C: drvAsynI2C::connect entry, device=/dev/i2c-1
2016/01/18 18:20:51.369 drvAsynI2C::drvAsynI2C, error calling connect I2C: Can't open /dev/i2c-1: No such file or directory
dbLoadRecords("/home/epics/devel/asyn/db/asynRecord.db", "P=test:,R=asyn,OMAX=80,IMAX=80,PORT=I2C,ADDR=0")
iocInit()
Starting iocInit
## EPICS R3.14.12.5 $Date: Tue 2015-03-24 09:57:35 -0500$
## EPICS Base built Dec  9 2015
2016/01/18 18:20:51.370 test:asyn: queueRequest failed
The final message is because autoConnect is true and the initial connect failed.  asynManager will keep periodically trying to connect the device.
-----Original Message-----
Sent: Monday, January 18, 2016 9:57 AM
To: Mark Rivers; [email protected]<mailto:[email protected]>
Hey
On 01/18/2016 03:07 PM, Mark Rivers wrote:
The error you were getting was in the pasynOctet->write() method.  But was that method actually being called from the asynRecord, i.e. were you using the asynRecord to do the write operation to the driver?  If so, how did you do that?  Or were you using some other device support like streamDevice or devGpib?
I've used the asynRecord. The records looks like this:
record( asyn, "TEST" ) {
    field( DTYP,  "asynRecordDevice" )
    field( PORT,  "I2C" )
    field( ADDR,  "0" )
    field( IFACE, "asynOctet" )
    ## AsynOctet output
    field( OEOS,  "" )
    field( OFMT,  "Binary" )
    field( OMAX,  "6" )
    ## AsynOctet input
    field( IEOS,  "" )
    field( IFMT,  "Binary" )
    field( IMAX,  "2" )
    field( NRRD,  "2" )
To write to the device I run the command `caput -a TEST.BOUT 2 33 2`
Regarding autoConnect, please put a simple printf at the start of your ::connect() function so you can see if it is being called.  When you run asynReport does asynManager say the port is connected when the only thing that should have been run is autoConnect, i.e. you do not manually connect it?  If asynReport says the port is connected then I find it hard to believe that your ::connect method was not called.
Ok. I now put in the line
     printf( "%s: Open connection to %s\n", portName, _deviceName );
as the first line of my connect funciton.
For some reason asynReports says the device is connected, but the printf
is not present in the shell.
The output from both, autoConnect on and off, are below:
dbLoadRecords("/home/debian/i2cTest/db/asyn.db")
iocInit()
Starting iocInit
## EPICS R3.14.12.5-3.14.12.5-3~jessie $Date: Tue 2015-03-24 09:57:35 -0500$
## EPICS Base built Aug 31 2015
asynReport 1 I2C
I2C multiDevice:No canBlock:Yes autoConnect:Yes
      enabled:Yes connected:Yes numberConnects 1
      nDevices 0 nQueued 0 blocked:No
      asynManagerLock:No synchronousLock:No
      exceptionActive:No exceptionUsers 1 exceptionNotifys 0
      traceMask:0x8 traceIOMask:0x8 traceInfoMask:0x1
Port: I2C
    Timestamp: <undefined>
    Input EOS[0]:
    Output EOS[0]:
Parameter list 0
Number of parameters is: 0
When manually connecting:
drvAsynI2CConfigure( "I2C", "/dev/i2c-1", 0 )
iocInit()
Starting iocInit
asynReport 1 I2C
I2C multiDevice:No canBlock:Yes autoConnect:No
      enabled:Yes connected:No numberConnects 0
Port: I2C
    Input EOS[0]:
    Output EOS[0]:
Parameter list 0
epics> dbpf TEST.CNCT "Connect"
I2C: Open connection to /dev/i2c-1
2016/01/18 15:52:11.712 I2C: Open connection to /dev/i2c-1
DBR_STRING:          "Connect"
    Florian
From: Florian Feldbauer [<mailto:[email protected]>[email protected]<mailto:[email protected]>]
Sent: Monday, January 18, 2016 4:00 AM
To: Mark Rivers; <mailto:[email protected]> <mailto:[email protected]> [email protected]<mailto:[email protected]>
Hey Marc,
as far is I have seen, the asynRecord is not printing the error message
to the iocsh,
put is storing it inside the ERRS field.
I have now found another ADC with uses the same supply voltage as the
BeagleBone,
so now I can communicate with it.
The only thing which still does not work, is the autoConnect.
When setting autoConnect to 1, the device seems to never connect.
I uploaded the latest version of my code here
http://www.ep1.rub.de/~florian/drvAsynI2c.tar.gz<http://www.ep1.rub.de/%7Eflorian/drvAsynI2c.tar.gz>
in case someone wants to look at it....
Cheers,
    Florian
On 01/14/2016 10:01 PM, Mark Rivers wrote:
So the asynOctet/asynRecord do not print the error Message of the asynUser?
Yes, it should print the error message
The asynRecordThe asynRecord::performOctetIO function calls asynRecord::reportError passing pasynUser->errorMessage if the write returns an error.  reportError calls asynPrint.
Here is the code snippet from performOctetIO:
               status = pasynRecPvt->pasynOctet->write(pasynRecPvt->asynOctetPvt,
                                   pasynUser, outptr, nwrite, &nbytesTransfered);
               if (saveEosLen)
                   pasynRecPvt->pasynOctet->setOutputEos(pasynRecPvt->asynOctetPvt,
                                                         pasynUser,saveEosBuf,saveEosLen);
           } else {
               /* ASCII or Hybrid mode */
           pasynRec->nawt = (int)nbytesTransfered;
           asynPrintIO(pasynUser, ASYN_TRACEIO_DEVICE, outptr, nbytesTransfered,
              "%s: nwrite=%lu, status=%d, nawt=%lu\n", pasynRec->name, (unsigned long)nwrite,
                       status, (unsigned long)nbytesTransfered);
           if(status != asynSuccess || nbytesTransfered != nwrite) {
               /* Something is wrong if we couldn't write everything */
               reportError(pasynRec, status, "Write error, nout=%d, %s",
                           nbytesTransfered, pasynUser->errorMessage);
I suspect your problem is that you are not calling the pasynOctet->write() method from the asynRecord, you are calling it from some other device support?  What device support are you using?  streamDevice or devGpibio?  They call the driver, and it is their responsibility to print the error message, including pasynUser->errorMessage.
If you actually did the I/O from the asynRecord (which you inquired about earlier) then I think you would see the correct error message.
You could probably also use the standard asyn device support for the asynOctet interface with a stringout or waveform record and that should also print the correct error message.
From: Florian Feldbauer [<mailto:[email protected]><mailto:[email protected]>mailto:[email protected]]
Sent: Thursday, January 14, 2016 11:32 AM
To: Mark Rivers; 'Pete Jemian'; [email protected]<mailto:[email protected]>
I guess I found the source of that write failing error. I have connected
an ADC to the I2C bus.
But the BeagleBone uses 3.3V as high level....according to the data
sheet this is the threshold for
a high level, because the ADC works normally with 5V.
Looking at the scope, the ADC doesn't send a ACK bit to the BeagleBone.
I will place a level shifter between both ics and try again.
Could an error like this also cause the autoConnect to fail?
Best regards,
Florian
On 01/14/2016 03:44 PM, Mark Rivers wrote:
     epicsSnprintf does not print a message.  It places the error message in pasynUser->errorMessage.  It is then the responsibility of the calling code (e.g. device support, etc.) to print the message if so desired.
Sent: Thursday, January 14, 2016 8:38 AM
Hey again,
somehow the error message from
           if( 0 > thisWrite && ( errno != EWOULDBLOCK )
                             && ( errno != EINTR )
                             && ( errno != EAGAIN ) ) {
                            "%s: %s write error: %s",
                            portName, _deviceName, strerror( errno ) );
             status = asynError;
             break;
this block is not printed. I replaced the epicsSnprintf call with asynPrint
and then I get the following:
2016/01/14 14:35:07.229 I2C: /dev/i2c-1 write error: Remote I/O error
2016/01/14 14:35:07.231 I2C: wrote 1 bytes to /dev/i2c-1, return asynError
So there is still a problem accessing the device itself...I will test
this furher outside
EPICS with a standalone C program, to see why this Remote I/O error occures.
Many thanks for your help so far!!
       Florian
On 01/14/2016 03:01 PM, Mark Rivers wrote:
Hi Florian,
If you set autoConnect=1 then after iocInit please send the output of
asynReport 1 I2C
Your driver printed this:
2016/01/14 13:11:54.967 I2C: wrote 1 bytes to /dev/i2c-1, return asynError
Why is it returning asynError if the write was successful?
I have a question concerning the asynRecord.
To read out the control register of my ADC I have to send the two bytes 0x42 0x02.
Is this possible using the asyn record with OFMT="Binary" ?
How would the corresponding put to the BOUT field look like?
Yes, this is possible.  If you are doing the put from a programming language (C, Python, etc.) you would just send a byte array of length 2 containing those bytes.
>From the command line you can do this with caput.  I don't think you can use hex notation, but the following appears to work using decimal notation:
corvette:~>caput -a quadEMTest:TetrAMM:Asyn.BOUT 2 66 2
Old : quadEMTest:TetrAMM:Asyn.BOUT 80 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0
New : quadEMTest:TetrAMM:Asyn.BOUT 80 66 2 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0
From: Florian Feldbauer [[email protected]<mailto:[email protected]>]
Sent: Thursday, January 14, 2016 7:33 AM
Hey,
concerning the compiler error, I uploaded the unfinished version from my
desktop PC instead of
the one used on the Beagle Bone...I now uploaded the correct version.
Link is still the same.
Sorry for the mistake!
I also tested the asynRecord. This is my record:
        field( ADDR,  "0" )
        ## AsynOctet output
        field( OEOS,  "" )
        ## AsynOctet input
        field( IEOS,  "" )
in the IOC I checked the following:
dbgf TEST.PCNCT
dbgf TEST.CNCT
dbgf TEST.ENBL
DBR_STRING:          "Enable"
dbgf TEST.AUCT
DBR_STRING:          "autoConnect"
dbgf TEST.ERRS
DBR_CHAR[100]:       "" +      ""
dbpf TEST.NOWT 1
DBR_LONG:           1         0x1
dbpf TEST.BOUT B
DBR_CHAR[2]:         "B"
dbgf TEST.ERRS
DBR_CHAR[100]:       "error  nread 0 I2C: /dev/i2c-1 disconnected:" +  ""
"I2C: /dev/i2c-1 disconnected:" is the error message when
asynOctet->read is called,
but the file handle (drvAsynI2c::_fd) is negative, so either ::connect()
was not called,
or the connect failed without printing the error message.
I set autoConnect to false in my code, and tried it again:
dbgf TEST.PCNCT
dbgf TEST.CNCT
DBR_STRING:          "Disconnect"
dbgf TEST.ENBL
dbgf TEST.AUCT
DBR_STRING:          "noAutoConnect"
2016/01/14 13:11:54.957 I2C: Open connection to /dev/i2c-1
dbgf TEST.ERRS
dbpf TEST.NOWT 1
DBR_LONG:           1         0x1
dbpf TEST.BOUT B
2016/01/14 13:11:54.964 I2C: read 0 bytes from /dev/i2c-1, return asynError
2016/01/14 13:11:54.965 drvAsynI2C::writeOctet: trying to send 2 bytes
drvAsynI2C::writeOctet: sending: 0x420x00
2016/01/14 13:11:54.969 I2C: read 0 bytes from /dev/i2c-1, return asynError
DBR_CHAR[2]:         "B"
dbgf TEST.ERRS
DBR_CHAR[100]:
       "error  nread 0 I2C: /dev/i2c-1 read error: Remote I/O error" +       ""
So with this second test, writing works, but reading not. The beaglebone
doesn't continue the clock for reading...
I will further study the problem...
I have a question concerning the asynRecord. To read out the control
Is this possible using the asyn record with OFMT="Binary" ? How would
Cheers
Florian
On 01/12/2016 09:02 PM, Mark Rivers wrote:
You can also load an asynRecord in your IOC.  With that you can turn AutoConnect on and off, and you can manually force calls to ::connect() and ::disconnect() from medm.  If you do that then do you see your methods being called?
Sent: Tuesday, January 12, 2016 8:58 AM
Hey,
the current version of my code can be found here:
<http://www.ep1.rub.de/%7Eflorian/drvAsynI2C.tar.gz> <http://www.ep1.rub.de/%7Eflorian/drvAsynI2C.tar.gz> http://www.ep1.rub.de/~florian/drvAsynI2C.tar.gz
The value for the writeOctet and readOctet is expected to be
a bitstream.
Currently I tried to use StreamDevice as the interface between records
and asynPortDriver...
         Florian
On 01/12/2016 01:22 PM, Mark Rivers wrote:
Your derived method's connect function should be called.  Can you send your code?  I'll take a look and see if I can spot anything wrong.
Sent: Tuesday, January 12, 2016 4:38 AM
Hey Marc, hey all!
unfortunately, I did not had the time to write and test the I2C device
support last year.
But now I have the time and I'm currently facing a problem:
My I2C device support is written as a class derived from the asynPortDriver,
reimplementing writeOctet, readOctet, connect and disconnect.
When calling the ctor of asynPortDriver I set the "autoConnect" flag to 1,
but the connect function of my class is never called, thus the file
handle for the
I2C interface is never opened.
Is there something I'm missing?
I thought autoConnect means that the connect function is automatically
called?
Cheers
Florian
On 11/25/2015 06:24 PM, Mark Rivers wrote:
The I2C asyn driver could be considered for going into asyn itself, since it is conceptually similar to the serial, IP, GPIB, USBTMC, and VXI11 drivers.
Note that "ip" is really not for software related to Industry Pack modules any more.   Most industry pack drivers now have their own modules (ip330, ipUnidig, dac128V, softGlue, ipac for ipOctal).  "ip" is really now software for asynOctet devices (serial, GPIB, TCP) that do not have another home like "vac" and "delayGen".  "ip" is no longer a good name for it.
Similarly "std" was originally the home for a lot "standard" beamline control stuff.  Most of this has now been moved to other modules (calc, busy, optics, sscan), so "std" is more like "misc" now.
From: <mailto:[email protected]> <mailto:[email protected]> [email protected]<mailto:[email protected]> [mailto:[email protected]] On Behalf Of Pete Jemian
Sent: Wednesday, November 25, 2015 11:10 AM
To: <mailto:[email protected]> <mailto:[email protected]> [email protected]<mailto:[email protected]>
Michael describes a good procedure for completely new functionality.
New modules should provide support distinct from other modules.
This _might_ have a place in one of the existing synApps modules.  This
is not "ip" functionality (related to Industry Pack modules), not
"calc", not "optics", perhaps "std" is the catchall module for new
synApps support?
On 11/25/2015 9:08 AM, Michael Davidsaver wrote:
On 11/25/2015 03:08 AM, Florian Feldbauer wrote:
I would like to upload the sources to github. Is it possible to upload
it to the "epics-modules" group?
At this point there isn't any established criteria for when/if
repositories in this group are created.
It would suggest starting with a repository under your own account (what
I do), then think about moving to epics-modules at some later date,
which isn't difficult.
That said, if you want to go straight to epics-modules I'm inclined to
just add it.  Let me know if you want to do this and I'll do this in a
day or so, assuming no one objects.  Of course, first you need to solve
the hard problem, the repository name ;)
Michael
| Dr. Florian Feldbauer                |
| Helmholtz-Institut Mainz /           |
| Johannes Gutenberg-Universität Mainz |
| Johann-Joachim-Becher-Weg 36         |
| D-55128 Mainz                        |
| Office: SB1 / 00-213                 |
| Phone:  (+49)6131 / 39-29605         |
| D-55128 Mainz                        |
| D-55128 Mainz                        |
| D-55128 Mainz                        |
| D-55128 Mainz                        |
| D-55128 Mainz                        |
| D-55128 Mainz                        |
| D-55128 Mainz                        |
| D-55128 Mainz                        |
Re: Device Support for I2C and GPIO -> StreamDevice Florian Feldbauer
Re: Device Support for I2C and GPIO Florian Feldbauer
RE: Device Support for I2C and GPIO Mark Rivers
RE: Device Support for I2C and GPIO -> StreamDevice Mark Rivers
Prev: Software engineer position at FRIB/MSU Shen, Guobao
Next: Re: Re: Re:Re: Re:Re: EPICS Multiple Archiver Appliance problem Shankar, Murali
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  <2016>  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Prev: RE: Device Support for I2C and GPIO -> StreamDevice Mark Rivers
Next: Re: Device Support for I2C and GPIO -> StreamDevice Florian Feldbauer
ANJ, 15 Jul 2016 · Home · News · About · Talk · Base · Modules · Extensions ·