Subject: Re: How to support a new stepper motor controller?
To: Rod Nussbaumer <[email protected]>
Cc: <[email protected]>
Date: Thu, 9 Feb 2017 12:46:34 +0530
Hello all,
            I have gone through the documentation you suggested. After understanding most of the coding I am here with some doubts.
1 >  what are controller specific parameters. ? How can I get my controller specific Parameters ?
2> in method
 asynStatus PXAxis::move(double position, int relative, double minVelocity, double maxVelocity, double acceleration)
  asynStatus status;
  // static const char *functionName = "moveAxis";
  sprintf(pC_->outString_, "%s STX P1 %f %f CR", axisName_, maxVelocity/pulsesPerUnit_, position/pulsesPerUnit_);
  status = pC_->writeController();
  return status;
How will I assign value for maxVelocity and position ???
3> which method in .cpp is responsible for communication between database(.db files) and driver. ?
4> What is importance of following code.?
asynStatus PXController::readBinaryIO()
  asynStatus status;
  // Read the binary inputs
  sprintf(outString_, "?P%d", binaryInReg_);
  status = writeReadController();
  if (!status) {
    binaryIn_ = atoi(inString_);
    setUIntDigitalParam(0, PXBinaryIn_, binaryIn_, 0xFFFFFFFF);
  // Read the binary outputs
  sprintf(outString_, "?P%d", binaryOutReg_);
  if (!status) {
    binaryOutRBV_  = atoi(inString_);
    setUIntDigitalParam(0, PXBinaryOutRBV_, binaryOutRBV_, 0xFFFFFFFF);
  callParamCallbacks(0);
  return status;
I am attaching my .cpp and .h files.
thank you in advance.
On Tue, Feb 7, 2017 at 11:55 PM, Rod Nussbaumer <[email protected]> wrote:
We've gone that route (streamDevice) for the relatively pedestrian requirements for the Galil motor controllers we use. No coordinated motion, or programmed movements; just discrete single axis motion with switches at each limit. The polling generates a lot of traffic, so we put the controllers on dedicated LANs. We did attempt to provide functionality that is similar to the motor record functions that we previously used in older applications with OMS VME motor controllers, by using logic in EPICS base records.
So far, we've only encountered a few hiccups and were able to address them easily.
Rod Nussbaumer
TRIUMF
Vancouver, Canada
On 02/07/2017 09:04 AM, Kevin Peterson wrote:
In general, the recommendation to write a model 3 driver is a good one.
Under some circumstances, however, that is far from the easiest option.
If the controller doesn't have a status command that allows queries of
the moving state, it can be awkward and inefficient to make the model 3
driver work well with the motor record, which expects the driver to
reliably set the done bit of the MSTA field.
If the goal is EPICS support and the motor record is not required, I
have found that StreamDevice support
(http://epics.web.psi.ch/software/streamdevice/) is a much better fit
and significantly easier to write.
Kevin
On 2/7/17 3:53 AM, Ralph Lange wrote:
Dear motion specialists,
I am writing on behalf of Paramveer Jain (in CC) who has contacted me
with this issue, but as I have never done motion control integration
with EPICS, I'd rather throw this ball up than send him into the wrong
direction.
He is being tasked with developing EPICS support for a locally developed
motor controller.
The hardware setup can be summarized as:
   * Moxa embedded TCP-to-serial converter (NE4110S)
   * Serial connection (RS-232)
   * Homemade motor controller (based on an AT89C52)
   * Ark Motion AMS 3630 stepper motor driver.
The controller software talks ASCII in command/response fashion, e.g.:
   * Read position (rotary encoder)
     Command: STX U<CR>
     Response: STX U pppppp<CR>
     pppppp = six digit hex (divide by 640 to get millimeter)
   * Go to position (rotary encoder)
     Command: STX P1 sss pppppp<CR>
     Response: \06 (ACK)
     sss = three digit hex (speed in mm/s multiplied by 240)
     pppppp = six digit hex (millimeter multiplied by 640)
What's the best/easiest way to do this? What are the caveats?
Is there a tutorial he could follow?
Is there existing support for another motor that he could start from?
Thanks a lot for your help!
~Ralph
With Regards,
Paramveer Jain
FILENAME... PXMotorDriver.cpp
USAGE...    Motor driver support for the Parker PX series of controllers, including the Aries.
Mark Rivers
March 4, 2011
#include <stdio.h>
#include <string.h>
#include <stdlib.h>
#include <iocsh.h>
#include <epicsThread.h>
#include <asynOctetSyncIO.h>
#include "PXMotorDriver.h"
#include <epicsExport.h>
#define CtlY 25
#define PX_TIMEOUT 1.0
static const char *driverName = "PXMotorDriver";
/** Creates a new PXController object.
  * \param[in] portName          The name of the asyn port that will be created for this driver
  * \param[in] PXPortName       The name of the drvAsynIPPPort that was created previously to connect to the PX controller
  * \param[in] numAxes           The number of axes that this controller supports
  * \param[in] movingPollPeriod  The time between polls when any axis is moving
  * \param[in] idlePollPeriod    The time between polls when no axis is moving
PXController::PXController(const char *portName, const char *PXPortName, int numAxes,
                             double movingPollPeriod, double idlePollPeriod)
  :  asynMotorController(portName, numAxes, NUM_PX_PARAMS,
                         asynInt32Mask | asynFloat64Mask | asynUInt32DigitalMask,
                         ASYN_CANBLOCK | ASYN_MULTIDEVICE,
                         1, // autoconnect
                         0, 0)  // Default priority and stack size
  int axis;
  asynStatus status;
  PXAxis *pAxis;
  static const char *functionName = "PXController";
  binaryInReg_  = 4096;
  binaryOutReg_ = 4097;
  // Create controller-specific parameters
  createParam(PXReadBinaryIOString, asynParamInt32,         &PXReadBinaryIO_);
  createParam(PXBinaryInString,     asynParamUInt32Digital, &PXBinaryIn_);
  createParam(PXBinaryOutString,    asynParamUInt32Digital, &PXBinaryOut_);
  createParam(PXBinaryOutRBVString, asynParamUInt32Digital, &PXBinaryOutRBV_);
  /* Connect to PX controller */
  status = pasynOctetSyncIO->connect(PXPortName, 0, &pasynUserPX_, NULL);
  if (status) {
    asynPrint(this->pasynUserSelf, ASYN_TRACE_ERROR,
      "%s:%s: cannot connect to PX controller\n",
      driverName, functionName);
  // Turn off command echoing
  sprintf(outString_, "BIT1792=0");
  writeController();
   // Turn off command prompt
  sprintf(outString_, "BIT1794=1");
  writeController();
  // Wait a short while so that any responses to the above commands have time to arrive so we can flush
  // them in the next writeReadController()
  epicsThreadSleep(0.5);
  // Read the binary I/O registers once
  readBinaryIO();
  // Set the output=output readback so bi records reflect current state
  setUIntDigitalParam(0, PXBinaryOut_, binaryOutRBV_, 0xFFFFFFFF);
  // Create the axis objects
  for (axis=0; axis<numAxes; axis++) {
    pAxis = new PXAxis(this, axis);
  startPoller(movingPollPeriod, idlePollPeriod, 2);
  * Configuration command, called directly or from iocsh
  * \param[in] movingPollPeriod  The time in ms between polls when any axis is moving
  * \param[in] idlePollPeriod    The time in ms between polls when no axis is moving
extern "C" int PXCreateController(const char *portName, const char *PXPortName, int numAxes,
                                   int movingPollPeriod, int idlePollPeriod)
  PXController *pPXController
    = new PXController(portName, PXPortName, numAxes, movingPollPeriod/1000., idlePollPeriod/1000.);
  pPXController = NULL;
  return(asynSuccess);
/** Reports on status of the driver
  * \param[in] fp The file pointer on which report information will be written
  * \param[in] level The level of report detail desired
  * If details > 0 then information is printed about each axis.
  * After printing controller-specific information calls asynMotorController::report()
void PXController::report(FILE *fp, int level)
  int axis;
  PXAxis *pAxis;
  fprintf(fp, "PX motor driver %s, numAxes=%d, moving poll period=%f, idle poll period=%f\n",
    this->portName, numAxes_, movingPollPeriod_, idlePollPeriod_);
  if (level > 0) {
    fprintf(fp, "  binary input = 0x%x\n", binaryIn_);
    fprintf(fp, "  binary output readback = 0x%x\n", binaryOutRBV_);
    for (axis=0; axis<numAxes_; axis++) {
      pAxis = getAxis(axis);
      fprintf(fp, "  axis %d\n"
              "  pulsesPerUnit_ = %f\n"
              "    encoder position=%f\n"
              "    theory position=%f\n"
              "    limits=0x%x\n"
              "    flags=0x%x\n",
              pAxis->axisNo_, pAxis->pulsesPerUnit_,
              pAxis->encoderPosition_, pAxis->theoryPosition_,
              pAxis->currentLimits_, pAxis->currentFlags_);
  // Call the base class method
  asynMotorController::report(fp, level);
/** Returns a pointer to an PXMotorAxis object.
  * Returns NULL if the axis number encoded in pasynUser is invalid.
  * \param[in] pasynUser asynUser structure that encodes the axis index number. */
PXAxis* PXController::getAxis(asynUser *pasynUser)
  return static_cast<PXAxis*>(asynMotorController::getAxis(pasynUser));
  * \param[in] axisNo Axis index number. */
PXAxis* PXController::getAxis(int axisNo)
  return static_cast<PXAxis*>(asynMotorController::getAxis(axisNo));
asynStatus PXController::writeUInt32Digital(asynUser *pasynUser, epicsUInt32 value, epicsUInt32 mask)
  int bit, tmask=0x1;
  asynStatus status;
  //static const char *functionName = "writeUInt32Digital";
  for (bit=0; bit<32; bit++) {
    if (mask & tmask) break;
    tmask = tmask << 1;
  sprintf(outString_, "BIT %d=%d", 32+bit, value);
  status = writeController();
  // Read the I/O back
  readBinaryIO();
  return(status);
/** Reads the binary input and binary output registers on the PX.
  * Sets the values in the parameter library.
  * Keeps track of which bits have changed.
  * Calls any registered callbacks for this pasynUser->reason and address. */
  asynStatus status;
  if (!status) {
  if (!status) {
  return status;
/** Writes a string to the PX controller.
  * Calls writeController() with a default location of the string to write and a default timeout. */
asynStatus PXController::writeController()
  return writeController(outString_, PX_TIMEOUT);
  * \param[in] output The string to be written.
  * \param[in] timeout Timeout before returning an error.*/
asynStatus PXController::writeController(const char *output, double timeout)
  size_t nwrite;
  asynStatus status;
  // const char *functionName="writeController";
  status = pasynOctetSyncIO->write(pasynUserPX_, output,
                                   strlen(output), timeout, &nwrite);
  return status ;
/** Writes a string to the PX controller and reads the response.
  * Calls writeReadController() with default locations of the input and output strings
  * and default timeout. */
asynStatus PXController::writeReadController()
  size_t nread;
  return writeReadController(outString_, inString_, sizeof(inString_), &nread, PX_TIMEOUT);
/** Writes a string to the PX controller and reads a response.
  * \param[in] output Pointer to the output string.
  * \param[out] input Pointer to the input string location.
  * \param[in] maxChars Size of the input buffer.
  * \param[out] nread Number of characters read.
  * \param[out] timeout Timeout before returning an error.*/
asynStatus PXController::writeReadController(const char *output, char *input, size_t maxChars, size_t *nread, double timeout)
  size_t nwrite;
  asynStatus status;
  int eomReason;
  // const char *functionName="writeReadController";
  status = pasynOctetSyncIO->writeRead(pasynUserPX_, output,
                                       strlen(output), input, maxChars, timeout,
                                       &nwrite, nread, &eomReason);
  return status;
// These are the PXAxis methods
/** Creates a new PXAxis object.
  * \param[in] pC Pointer to the PXController to which this axis belongs.
  * \param[in] axisNo Index number of this axis, range 0 to pC->numAxes_-1.
  * Initializes register numbers, etc.
PXAxis::PXAxis(PXController *pC, int axisNo)
  : asynMotorAxis(pC, axisNo),
    pC_(pC)
  asynStatus status;
  sprintf(axisName_, "AXIS%d", axisNo);
  encoderPositionReg_ = 12290 + 256*axisNo;
  theoryPositionReg_  = 12294 + 256*axisNo;
  limitsReg_          = 4600  + axisNo;
  flagsReg_           = 4120  + axisNo;
  // Get the number of pulses per unit on this axis
  sprintf(pC->outString_, "%s PPU", axisName_);
  status = pC->writeReadController();
  if (status) {
    setIntegerParam(pC->motorStatusProblem_, 1);
  } else {
    pulsesPerUnit_ = atof(pC->inString_);
    // We assume servo motor with encoder for now
    setIntegerParam(pC->motorStatusGainSupport_, 1);
    setIntegerParam(pC->motorStatusHasEncoder_, 1);
  callParamCallbacks();
  asynStatus status;
  return status;
asynStatus PXAxis::home(double minVelocity, double maxVelocity, double acceleration, int forwards)
  asynStatus status;
  // static const char *functionName = "homeAxis";
sprintf(pC_->outString_, "%s STX H %f CR", axisName_, maxVelocity/pulsesPerUnit_);
  return status;
/** Code for iocsh registration */
static const iocshArg PXCreateControllerArg0 = {"Port name", iocshArgString};
static const iocshArg PXCreateControllerArg1 = {"PX port name", iocshArgString};
static const iocshArg PXCreateControllerArg2 = {"Number of axes", iocshArgInt};
static const iocshArg PXCreateControllerArg3 = {"Moving poll period (ms)", iocshArgInt};
static const iocshArg PXCreateControllerArg4 = {"Idle poll period (ms)", iocshArgInt};
static const iocshArg * const PXCreateControllerArgs[] = {&PXCreateControllerArg0,
                                                           &PXCreateControllerArg1,
                                                           &PXCreateControllerArg2,
                                                           &PXCreateControllerArg3,
                                                           &PXCreateControllerArg4};
static const iocshFuncDef PXCreateControllerDef = {"PXCreateController", 5, PXCreateControllerArgs};
static void PXCreateContollerCallFunc(const iocshArgBuf *args)
  PXCreateController(args[0].sval, args[1].sval, args[2].ival, args[3].ival, args[4].ival);
static void PXMotorRegister(void)
  iocshRegister(&PXCreateControllerDef, PXCreateContollerCallFunc);
extern "C" {
epicsExportRegistrar(PXMotorRegister);
FILENAME...   PXMotorDriver.h
USAGE...      Motor driver support for the Parker ACR series of controllers, including the Aries.
Mark Rivers
March 28, 2011
#include "asynMotorController.h"
#include "asynMotorAxis.h"
/** drvInfo strings for extra parameters that the PX controller supports */
//#define PXJerkString           "PX_JERK"
#define PXReadBinaryIOString   "PX_READ_BINARY_IO"
#define PXBinaryInString       "PX_BINARY_IN"
#define PXBinaryOutString      "PX_BINARY_OUT"
#define PXBinaryOutRBVString   "PX_BINARY_OUT_RBV"
#define MAX_PX_STRING_SIZE 85
class PXAxis : public asynMotorAxis
public:
  /* These are the methods we override from the base class */
  PXAxis(class PXController *pC, int axis);
  asynStatus move(double position, int relative, double min_velocity, double max_velocity, double acceleration);
  /*asynStatus moveVelocity(double min_velocity, double max_velocity, double acceleration);*/
  asynStatus home(double min_velocity, double max_velocity, double acceleration, int forwards);
 //asynStatus stop(double acceleration);
 // asynStatus poll(bool *moving);
  //asynStatus setPosition(double position);
private:
  PXController *pC_;      /**< Pointer to the asynMotorController to which this axis belongs.
                                *   Abbreviated because it is used very frequently */
  char axisName_[10];      /**< Name of each axis, used in commands to PX controller */
  double pulsesPerUnit_;   /**< Pulses per engineering unit, which is what PX controller uses */
  int flagsReg_;           /**< Address of the flags register */
  int limitsReg_;          /**< Address of the limits register */
  int encoderPositionReg_; /**< Address of the encoder position register */
  int theoryPositionReg_;  /**< Address of the theoretical position register */
  double encoderPosition_; /**< Cached copy of the encoder position */
  double theoryPosition_;  /**< Cached copy of the theoretical position */
  int currentFlags_;       /**< Cached copy of the current flags */
  int currentLimits_;      /**< Cached copy of the current limits */
friend class PXController;
class PXController : public asynMotorController {
public:
  PXController(const char *portName, const char *PXPortName, int numAxes, double movingPollPeriod, double idlePollPeriod);
  /* These are the methods that we override from asynPortDriver */
  asynStatus writeUInt32Digital(asynUser *pasynUser, epicsUInt32 value, epicsUInt32 mask);
  /* These are the methods that we override from asynMotorDriver */
 /* asynStatus writeInt32(asynUser *pasynUser, epicsInt32 value);
  #asynStatus writeFloat64(asynUser *pasynUser, epicsFloat64 value);*/
  void report(FILE *fp, int level);
  PXAxis* getAxis(asynUser *pasynUser);
  PXAxis* getAxis(int axisNo);
  /* These are the methods that are new to this class */
  asynStatus readBinaryIO();
  asynStatus writeController();
  asynStatus writeController(const char *output, double timeout);
  asynStatus writeReadController();
  asynStatus writeReadController(const char *output, char *response, size_t maxResponseLen, size_t *responseLen, double timeout);
//protected:
  /*int PXJerk_;          **< Jerk time parameter index*/
    int PXReadBinaryIO_;
#define FIRST_PX_PARAM PXReadBinaryIO_
  //int PXReadBinaryIO_;  **< Read binary I/O parameter index */
  int PXBinaryIn_;      /**< Binary input parameter index */
  int PXBinaryOut_;     /**< Binary output parameter index */
  int PXBinaryOutRBV_;  /**< Binary output readback parameter index */
#define LAST_PX_PARAM PXBinaryOutRBV_
#define NUM_PX_PARAMS  (&LAST_PX_PARAM - &FIRST_PX_PARAM + 1)
private:
  asynUser *pasynUserPX_;
  char outString_[MAX_PX_STRING_SIZE];
  char inString_[MAX_PX_STRING_SIZE];
  int binaryIn_;
  int binaryOutRBV_;
  int binaryInReg_;
  int binaryOutReg_;
friend class PXAxis;
Re: How to support a new stepper motor controller? Mark Rivers
RE: How to support a new stepper motor controller? Mark Rivers
How to support a new stepper motor controller? Ralph Lange
Re: How to support a new stepper motor controller? Kevin Peterson
Re: How to support a new stepper motor controller? Rod Nussbaumer
Prev: Re: [epics-modules/asyn] Throw exception if we can't register interfaces (#43) Andrew Johnson
Next: Re: How to support a new stepper motor controller? Mark Rivers
Prev: Re: How to support a new stepper motor controller? Rod Nussbaumer