On 04/16/2017 10:46 AM, Michael Davidsaver wrote:
> On 04/16/2017 10:39 AM, Michael Davidsaver wrote:
>>> CAS: request from 10.1.204.140:54439 => CAS: Missaligned protocol rejected
>>> CAS: Request from 10.1.204.140:54439 => cmmd=0 cid=0x4143435f type=0 count=3100 postsize=3100
>>> CAS: Request from 10.1.204.140:54439 => available=0x4c524254 N=3 paddr=(nil)
>> The offending header was:
>>> 00000c1c 00000c1c 4143435f 4c524254
> Also the N=3 indicates that other this is the 4th message in the UDP
> packet and the the previous 3 were considered valid.
> The seems like a client is not constructing UDP packets properly.
I think I see what is happening. CA requires that every message size be
a multiple of 8 bytes. This should be done by padding with zeros and
adjusting the message size field. This CA client is inconsistent with
padding when packing multiple messages into one UDP packet.
> CAS: partial (damaged?) UDP msg of 8 bytes from 10.1.204.140:54439 ?
In this case a message size field is too short, so there are 8 bytes
left over at the end of the packet.
rejected
In this case a message size field is too long, so the preceding message
(N=2) body contained the first 8 bytes of the next message.