1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <20182019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <20182019  2020  2021  2022  2023  2024  2025  2026
Subject: Re: Question about communications based on modbus tcp.
To: lzf neu <[email protected]>, "[email protected]" <[email protected]>
Date: Wed, 24 Jan 2018 12:44:07 +0000
Hi Zhefu,
If you look at the difference between the example Koyo1.cmd startup script between R1-2 and R2-9 you will see the following.  For simplicity I have removed the commented out lines that relate to serial RTU and serial ASCII since those don't apply to you.
corvette:modbus/iocBoot/iocTest>git diff -U9 R1-2 R2-9 Koyo1.cmd
diff --git a/iocBoot/iocTest/Koyo1.cmd b/iocBoot/iocTest/Koyo1.cmd
index 7a9d0f4..7434046 100755
--- a/iocBoot/iocTest/Koyo1.cmd
+++ b/iocBoot/iocTest/Koyo1.cmd
@@ -3,91 +3,94 @@
 dbLoadDatabase("../../dbd/modbus.dbd")
 modbus_registerRecordDeviceDriver(pdbbase)
 # Use the following commands for TCP/IP
 #drvAsynIPPortConfigure(const char *portName,
 #                       const char *hostInfo,
 #                       unsigned int priority,
 #                       int noAutoConnect,
 #                       int noProcessEos);
-drvAsynIPPortConfigure("Koyo1","164.54.160.158:502",0,1,1)
+drvAsynIPPortConfigure("Koyo1","164.54.160.158:502",0,0,1)
 #modbusInterposeConfig(const char *portName,
-#                      int slaveAddress,
 #                      modbusLinkType linkType,
-#                      int timeoutMsec)
-modbusInterposeConfig("Koyo1",0,0,5000)
+#                      int timeoutMsec,
+#                      int writeDelayMsec)
+modbusInterposeConfig("Koyo1",0,5000,0)
 # NOTE: We use octal numbers for the start address and length (leading zeros)
 #       to be consistent with the PLC nomenclature.  This is optional, decimal
 #       numbers (no leading zero) or hex numbers can also be used.
+#       In these examples we are using slave address 0 (number after "Koyo1").
 # The DL205 has bit access to the Xn inputs at Modbus offset 4000 (octal)
 # Read 32 bits (X0-X37).  Function code=2.
-drvModbusAsynConfigure("K1_Xn_Bit",      "Koyo1", 2,  04000, 040,    0,  100, "Koyo")
+drvModbusAsynConfigure("K1_Xn_Bit",      "Koyo1", 0, 2,  04000, 040,    0,  100, "Koyo")
So the differences are:
- In the drvAsynIPPortConfigure command in R1-2 the noAutoConnect flag was set.  This should not be set in R2-9, so you should change this:
drvAsynIPPortConfigure("Koyo3R",  "192.168.1.241:502",0,1,1)
to this:
drvAsynIPPortConfigure("Koyo3R",  "192.168.1.241:502",0,0,1)
- The arguments to modbusInterfaceConfigure were changed from this in R1-2:
                      int slaveAddress,
                      int timeoutMsec)
to this in R2-9:
                      int timeoutMsec
                      int writeDelayMsec)
So you should change this:
modbusInterposeConfig("Koyo3R",2,0,2000)
to this:
modbusInterposeConfig("Koyo3R",0,2000,0)
- Finally the drvModbusAsynConfigure command has changed from this in R1-2:
drvModbusAsynConfigure(portName,
                       tcpPortName,
                       modbusFunction,
                       modbusStartAddress,
                       modbusLength,
                       dataType,
                       pollMsec,
                       plcType);
to this in R2-9:
                       tcpPortName,
                       slaveAddress,
                       modbusFunction,
                       modbusStartAddress,
                       modbusLength,
                       dataType,
                       pollMsec,
                       plcType);
This means that the slaveAddress argument has moved from the  modbusInterposeConfig function to the drvModbusAsynConfigure function.
Since you were previously using slaveAddress=0 in modbusInterposeConfig, you should now use slaveAddress=0 in drvModbusAsynConfigure.  Thus you should change this:
drvModbusAsynConfigure("RD3R",   "Koyo3R",  3, 0, 95, 0, 1160, "rpDevice")
to this:
drvModbusAsynConfigure("RD3R",   "Koyo3R",  0, 3, 0, 95, 0, 1160, "rpDevice")
From: [email protected] <[email protected]> on behalf of lzf neu <[email protected]>
Sent: Wednesday, January 24, 2018 2:00 AM
To: [email protected]
Subject: Question about communications based on modbus tcp.
There are radiation dose monitor devices by using modbus tcp protocol to communicate.
The communications have succeeded to establish by using epics 3.14.12.5, modbusR1-2 combined with asynR4-9 (very old version) many years ago.
Therefore, I want to upgrade to the latest program by using modbusR2-9 combined with asynR4-30 and epics 3.14.12.5.
My settings are the same as the old version of modbusR1-2 in start.cmd file:
modbusInterposeConfig("Koyo3R",  2,0,2000)
drvModbusAsynConfigure("RD3R",   "Koyo3R",  3, 0, 95, 0, 1160, "rpDevice") # modbusR1-2 version
I noticed that there was a little difference of parameter settings in the command drvModbusAsynConfigure of new version (modbusR2-9). The manual says :"For TCP the slave address is used for the "unit identifier", the last field in the MBAP header.", and the last field in the MBAP header, as i know,  is the slave address (ranging from 1 to 247).   So, i randomly set:
drvModbusAsynConfigure("RD3R",   "Koyo3R",  111, 3, 0, 95, 0, 1160, "rpDevice")  # modbusR2-9 version, I randomly set 111
or:
drvModbusAsynConfigure("RD3R",   "Koyo3R",  0xFF, 3, 0, 95, 0, 1160, "rpDevice")  # use 0xFF to disable the parameter
however, I cannot establish  the communications by using the new version of modbus and I have no idea how to do.
The error messages are as follows:
epics> 2018/01/24 15:19:26.062 drvModbusAsyn::doModbusIO port RD3R is disconnected
2018/01/24 15:19:30.069 drvModbusAsyn::doModbusIO port RD3R error calling writeRead, error=192.168.1.241:502 timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
2018/01/24 15:19:31.229 drvModbusAsyn::doModbusIO port RD3R has I/O error
2018/01/24 15:19:35.234 drvModbusAsyn::doModbusIO port RD3R error calling writeRead, error=192.168.1.241:502 timeout: Resource temporarily unavailable, nwrite=6/6, nread=0
Any help will be appreciated,  and thanks in advance !
Zhefu
答复: Question about communications based on modbus tcp. lzf neu
Prev: Driver support of VMM ControlNet interface module (5136-CN-VME) 李刚
Next: Re: Driver support of VMM ControlNet interface module (5136-CN-VME) Kasemir, Kay
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  <20182019  2020  2021  2022  2023  2024  2025  2026
Prev: Question about communications based on modbus tcp. lzf neu
Next: 答复: Question about communications based on modbus tcp. lzf neu
ANJ, 25 Jan 2018 · Home · News · About · Talk · Base · Modules · Extensions ·