Sorry, I goofed. Asyn does, in fact, seem to be OK after a clean-rebuild against the newest streamdevice and asyn, but not against new asyn/old streamdevice. I am now trying to figure out exactly what was wrong with it.
-----Original Message-----
Sent: Monday, March 05, 2018 9:03 AM
To: Daykin, Evan <[email protected]>; Torsten Bögershausen <[email protected]>; [email protected]
Subject: Re: Asyn not automatically reconnecting
Hi Evan,
I'm a bit confused.
> Some error output that never previously occurred:
> 2018/03/05 08:26:50.500618 TEST-RF-DCU- TEST:POWR_RD_FWD: write failed because Connection to test-rf-dcu-n0001 closed.
> connection was closed by device
Do you get this message when you use the package or when you build from source? This looks like it is a jumble of 2 messages:
This one from StreamDevice:
./StreamDevice/src/AsynDriverInterface.cc: error("%s: write failed because connection was closed by device\n",
and some other message that starts with "Connection to". I cannot find the source code for that message in asyn or stream.
Last week you said that when you build asyn from source the problem went away and it behaves as expected. Is this conclusion still true?
Sent: Monday, March 5, 2018 7:42 AM
To: Mark Rivers; Torsten Bögershausen; [email protected]
Subject: RE: Asyn not automatically reconnecting
Aptitude claims the package is asyn 4-33.
Maybe it suggests this condition is not caught correctly in the package?
Sent: Friday, March 02, 2018 5:47 PM
> I have added the patch you suggested and built locally... It now works totally fine.
OK, that's good news. But I'm definitely interested to know what version you were running from the package that has this problem.
> From: Daykin, Evan [mailto:[email protected]]
> Sent: Friday, March 02, 2018 4:11 PM
> To: Mark Rivers <[email protected]>; Torsten Bögershausen
> totally fine. On Monday, I will investigate what's different between
> this asyn version and the package we have installed.
> > Can you simplify this further by removing all protocols from the
> > protocol file except
> getAmpValue?
> Terminator = LF;
> ReplyTimeout = 2000;
> getAmpValue {
> ExtraInput = Ignore;
> out "GET VALUE \$1 AMP \$2";
> in "VALUE \$1 AMP \$2 %g";
> > If this is "properly functioning" why are you getting a read error
> > and connection reset by
> peer?
> "Properly" meaning asyn is doing what it is supposed to after the client disconnects.
> Sorry, I omitted the normal output last time. Here is the record processing:
> 2018/03/02 16:32:38.225 TEST-RF-DCU-N0001 addr -1 queueRequest
> priority 0 not lockHolder
> 2018/03/02 16:32:38.225 TEST-RF-DCU-N0001 schedule queueRequest
> timeout
> 2018/03/02 16:32:38.225 asynManager::portThread port=TEST-RF-DCU-N0001
> callback
> 2018/03/02 16:32:38.226 TEST-RF-DCU-N0001 addr -1 queueRequest
> 2018/03/02 16:32:38.226 TEST-RF-DCU-N0001 schedule queueRequest
> timeout
> 2018/03/02 16:32:38.226 asynManager::portThread port=TEST-RF-DCU-N0001
> callback
> 2018/03/02 16:32:38.226 test-rf-dcu-n0001.cts:5001 read.
> 2018/03/02 16:32:38.227 TEST-RF-DCU-N0001 get Eos 0
> 2018/03/02 16:32:38.227 TEST-RF-DCU-N0001 set Eos 0
> 2018/03/02 16:32:38.227 test-rf-dcu-n0001.cts:5001 write.
> 2018/03/02 16:32:38.227 test-rf-dcu-n0001.cts:5001 write 32 GET VALUE
> AMP_PWR_FORWARD AMP 1
> GET VALUE AMP_PWR_FORWARD AMP 1\n
> 47 45 54 20 56 41 4c 55 45 20 41 4d 50 5f 50 57 52 5f 46 4f
> 52 57 41 52 44 20 41 4d 50 20 31 0a
> 2018/03/02 16:32:38.227 wrote 32 to test-rf-dcu-n0001.cts:5001, return asynSuccess.
> 2018/03/02 16:32:38.227 TEST-RF-DCU-N0001 wrote GET VALUE
> 2018/03/02 16:32:38.227 TEST-RF-DCU-N0001 addr -1 queueRequest
> priority 0 from lockHolder
> 2018/03/02 16:32:38.227 TEST-RF-DCU-N0001 schedule queueRequest
> timeout
> 2018/03/02 16:32:38.227 asynManager::portThread port=TEST-RF-DCU-N0001
> callback
> 2018/03/02 16:32:38.227 TEST-RF-DCU-N0001 set Eos 1
> \n
> 0a
> 2018/03/02 16:32:38.227 test-rf-dcu-n0001.cts:5001 read.
> 2018/03/02 16:32:38.228 test-rf-dcu-n0001.cts:5001 read 30 VALUE
> AMP_PWR_FORWARD AMP 1 0
> VALUE AMP_PWR_FORWARD AMP 1 0\n
> 56 41 4c 55 45 20 41 4d 50 5f 50 57 52 5f 46 4f 52 57 41 52
> 44 20 41 4d 50 20 31 20 30 0a
> 2018/03/02 16:32:38.228 TEST-RF-DCU-N0001 read VALUE AMP_PWR_FORWARD
> AMP 1 0
> 2018/03/02 16:32:38.228 TEST-RF-DCU-N0001 set Eos 0
> Thanks again for the help,
> -Evan
> From: Mark Rivers [mailto:[email protected]]
> Sent: Friday, March 02, 2018 4:10 PM
> Hi Evan,
> protocol file except getAmpValue?
> I don't understand the output you sent. See my comments below.
> > Sent: Thursday, March 01, 2018 3:34 PM
> > Sure,
> > Database:
> > record(asyn, "_$(HWUNIT):asyn") #resolves to PORT name {
> > field(PORT, "$(HWUNIT)")
> > field(IEOS, "\n")
> > field(OEOS, "\n")
> > field(ASG, "$(ASGEXPERT)")
> > record(ai, "TEST:POWR_RD_FWD")
> > field(DESC, "AMP_PWR_FORWARD value")
> > field(DTYP, "stream")
> > field(SCAN, "5 second")
> > field(EGU, "W")
> > field(INP, "@HBH-RF-Amp.proto getAmpValue(AMP_PWR_FORWARD,1)
> > TEST-
> > RF-DCU-N0001")
> > info(archive, " ")
> > Protocol file:
> > Terminator = LF;
> > getAmpValue {
> > getFirmwareVersionPallet {
> > out "GET VALUE VERSION_SOFTWARE AMP \$1 DRAWER \$2 PALLET \$3";
> > in "VALUE VERSION_SOFTWARE AMP \$1 DRAWER \$2 PALLET \$3 %s"; }
> > Asyn IO output (properly functioning):
> > 2018/03/01 16:17:49.155 [TEST-RF-DCU-N0001,-1,0]
> > [../../asyn/asynDriver/asynManager.c:1560]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] TEST-RF-DCU-N0001 addr -1
> > queueRequest priority 0 from lockHolder
> > [../../asyn/asynDriver/asynManager.c:1576]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] TEST-RF-DCU-N0001 schedule
> > queueRequest timeout
> > [../../asyn/asynDriver/asynManager.c:886]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] asynManager::portThread
> > port=TEST-RF-DCU-N0001 callback
> > [../../asyn/miscellaneous/asynInterposeEos.c:337]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] TEST-RF-DCU-N0001 get Eos 0
> > [../../asyn/miscellaneous/asynInterposeEos.c:295]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] TEST-RF-DCU-N0001 set Eos 1 \n 0a
> [../../asyn/drvAsynSerial/drvAsynIPPort.c:674]
> [TEST-RF-DCU-N0001,0x6d72f0,50] test-
> > 2018/03/01 16:17:50.320 [TEST-RF-DCU-N0001,-1,0]
> > [../../asyn/drvAsynSerial/drvAsynIPPort.c:203]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] Close test-rf-dcu-n0001.cts:5001
> > connection (fd 6): Read error
> > [../../asyn/asynRecord/asynRecord.c:905]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] _TEST-RF-DCU-N0001:asyn: exception
> > 0, asynExceptionConnect
> > 2018/03/01 16:17:50.319943 TEST-RF-DCU- TEST:POWR_RD_FWD: asynError
> > in
> > read: test-rf-dcu-n0001.cts:5001 read error: Connection reset by
> > peer
> > 2018/03/01 16:17:50.319959 TEST-RF-DCU- TEST:POWR_RD_FWD: I/O error
> > after
> reading 0 bytes: ""
> > 2018/03/01 16:17:50.319981 TEST-RF-DCU- TEST:POWR_RD_FWD: Protocol
> > aborted
> If this is "properly functioning" why are you getting a read error and
> connection reset by peer?
> > [TEST-RF-DCU-N0001,0x6d72f0,50] TEST-RF-DCU-N0001 set Eos 0
> > 2018/03/01 16:17:50.325 [TEST-RF-DCU-N0001,-1,0]
> > [../../asyn/asynDriver/asynManager.c:1565] [timerQueue,0x6d5fd0,60]
> > TEST-RF-DCU-N0001 addr -1 queueRequest priority 3 not lockHolder
> > [../../asyn/asynDriver/asynManager.c:807]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] asynManager connect queueCallback
> > port:TEST-RF-DCU-N0001
> > [../../asyn/drvAsynSerial/drvAsynIPPort.c:402]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] Open connection to
> > test-rf-dcu-n0001.cts:5001 reason:0 fd:-1
> > 2018/03/01 16:17:50.326 [TEST-RF-DCU-N0001,-1,0]
> > [../../asyn/drvAsynSerial/drvAsynIPPort.c:508]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] Opened connection to
> > 2018/03/01 16:17:54.153 [TEST-RF-DCU-N0001,-1,0]
> > [../../asyn/asynDriver/asynManager.c:1565] [scan-5,0x718ec0,61]
> > TEST-RF-DCU-N0001 addr -1 queueRequest priority 0 not lockHolder
> > [../../asyn/asynDriver/asynManager.c:1576] [scan-5,0x718ec0,61]
> > TEST-RF-DCU-N0001 schedule queueRequest timeout
> > 2018/03/01 16:17:54.154 [TEST-RF-DCU-N0001,-1,0]
> > [../../asyn/drvAsynSerial/drvAsynIPPort.c:744]
> > [TEST-RF-DCU-N0001,0x6d72f0,50] test-rf-dcu-n0001.cts:5001 read 50
> > FRIB Control Unit (0.4.8 GU Jan 2 2018 21:32:44)
> I don't understand. This does not appear to be the protocol
> getAmpValue. It did not send the command to read the amp value, and
> the string it received is not the one for that protocol.
> Please send the output when the record TEST:POWR_RD_FWD processes a few times.
> > Asyn output (not working):
> > 2018/03/01 16:29:14.902 [TEST-RF-DCU-N0001,-1,0]
> > [../../asyn/asynDriver/asynManager.c:1565] [scan-5,0x264e600,61]
> > [../../asyn/asynDriver/asynManager.c:1576] [scan-5,0x264e600,61]
> > [TEST-RF-DCU-N0001,0x260d420,50] asynManager::portThread
> > [TEST-RF-DCU-N0001,0x260d420,50] TEST-RF-DCU-N0001 addr -1
> > [TEST-RF-DCU-N0001,0x260d420,50] TEST-RF-DCU-N0001 schedule
> > [TEST-RF-DCU-N0001,0x260d420,50] test-rf-dcu-n0001.cts:5001 read 0
> > [TEST-RF-DCU-N0001,0x260d420,50] Close test-rf-dcu-n0001.cts:5001
> > connection (fd 18): Read from broken connection
> > [TEST-RF-DCU-N0001,0x260d420,50] _TEST-RF-DCU-N0001:asyn: exception
> > [../../asyn/miscellaneous/asynInterposeEos.c:235]
> > [TEST-RF-DCU-N0001,0x260d420,50] TEST-RF-DCU-N0001 read
> > [TEST-RF-DCU-N0001,0x260d420,50] test-rf-dcu-n0001.cts:5001 read.
> > (Repeats forever)
> Note that the next to the last line is from the asynPrintIO call in
> asynInterposeEos.c
> for (;;) {
> if ((peosPvt->inBufTail != peosPvt->inBufHead)) { ...
> status = peosPvt->poctet->read(peosPvt->octetPvt,
> pasynUser,peosPvt->inBuf,peosPvt->inBufSize,&thisRead,&eom);
> if(status==asynSuccess) {
> asynPrintIO(pasynUser,ASYN_TRACEIO_FILTER,peosPvt->inBuf,thisRead,
> "%s read\n",peosPvt->portName);
> * Read could have returned with ASYN_EOM_CNT set in eom because
> * the number of octets available exceeded inBufSize. This is not
> * a reason for us to stop reading.
> eom &= ~ASYN_EOM_CNT;
> if(status!=asynSuccess || thisRead==0) break;
> peosPvt->inBufTail = 0;
> It is acting as if it is stuck in this loop which is what is causing
> your fast stream of error messages. The peosPvt->poctet->read() call above is what calls the drvAsynIPPort driver.
> However, I don't see how it could get stuck in the loop. If the
> read() call returns asynSuccess it prints the message which you saw
> once. If status is not asynSuccess then it breaks out of the loop.
> So either we should see the message from this function many times, or it should not call peosPvt->poctet->read() multiple times.
> I'd like to see some more information from this function. Can you
> please apply the following patch before you run the test again:
> diff --git a/asyn/miscellaneous/asynInterposeEos.c
> b/asyn/miscellaneous/asynInterposeEos.c
> index c9697ad..558c0a7 100644
> --- a/asyn/miscellaneous/asynInterposeEos.c
> +++ b/asyn/miscellaneous/asynInterposeEos.c
> @@ -232,13 +232,16 @@ static asynStatus readIt(void *ppvt,asynUser *pasynUser,
> - "%s read\n",peosPvt->portName);
> + "%s read %d bytes eom=%d\n",peosPvt->portName,
> + thisRead, eom);
> + } else {
> + asynPrint(pasynUser, ASYN_TRACE_WARNING, "%s read from
> + low-level driver
> returned %d\n",
> + peosPvt->portName, status);
> Mark
> > Sent: Thursday, March 01, 2018 4:06 PM
> > Can you post the database, protocol file, and asynTrace output with all asynTrace bits on?
> > > Sent: Thursday, March 01, 2018 3:04 PM
> > > I have tried a database with only a couple of records, and the behavior persists.
> > > Sent: Tuesday, February 27, 2018 4:57 PM
> > > Can you try a very simple database with just one or two records
> > > talking to your server. See if that works when the server shuts
> > > down gracefully. If it does, but it fails with lots of records
> > > then we have a clue where
> to look.
> > > Mark
> > > ________________________________
> > > From: Daykin, Evan <[email protected]>
> > > Sent: Tuesday, February 27, 2018 3:53 PM
> > > To: Torsten Bögershausen; Mark Rivers; [email protected]
> > > >Sorry if this is the wrong question, but what is asyn 4.33-2 ?
> > > >"git tag" mentions R4-33, not "-2".
> > > That's the revision in our debian repo, it is asyn 4-33.
> > > > So from asyn everything seems to be OK.
> > > Maybe this is streamdevice and/or our vendor's software. We will
> > > investigate both
> > avenues.
> > > From: Torsten Bögershausen [mailto:[email protected]]
> > > Sent: Tuesday, February 27, 2018 3:37 PM
> > > To: Daykin, Evan <[email protected]>; Mark Rivers
> > > <[email protected]>; tech- [email protected]
> > > On 23/02/18 15:17, Daykin, Evan wrote:
> > > > Hi Mark,
> > > > Thanks for the reply. We are using asyn 4.33-2 and Stream 2.6-3.
> > > > The protocol file has a ReplyTimeout of 2000ms.
> > > And to answer the other question:
> > > >Here's something interesting: asyn behaves correctly for us
> > > *only* when the >client application is killed with SIGKILL,
> > > rather than SIGTERM. This results >in TCP retransmissions and/or
> > > refused connections, then normal operation after >a short while.
> > > Is it possible asyn is
> > [un]intentionally not retrying the >connection if it is closed gracefully?
> > > The code that I see producing "Read from broken connection" is this:
> > > /* If recv() returns 0 on a SOCK_STREAM (TCP) socket, the
> > > connection has closed
> > > if ((thisRead == 0) && (tty->socketType == SOCK_STREAM)) {
> > > epicsSnprintf(pasynUser->errorMessage,pasynUser->errorMessageSize,
> > > "%s connection closed",
> > > tty->IPDeviceName);
> > > closeConnection(pasynUser,tty,"Read from broken
> > > connection");
> > > And then
> > > closeConnection(asynUser *pasynUser,ttyController_t *tty,const char *why) {
> > > asynPrint(pasynUser, ASYN_TRACE_FLOW,
> > > "Close %s connection (fd %d): %s\n",
> > > tty->IPDeviceName,
> > > tty->fd, why);
> > > It seems that the problem described here:
> > > >2018/02/23 09:51:47.089 test-rf-dcu-n0001.cts:5001 read.
> > > >The last line then repeats rapidly forever.
> > > is caused by the caller into asyn, which is streamdevice ?
> > > There seem to be some improvements in streamdevice, but I am not
> > > familiar with the
> code.
> > > Dirk, does there ring a bell ?
- RE: Asyn not automatically reconnecting Mark Rivers
- Asyn not automatically reconnecting Daykin, Evan
- RE: Asyn not automatically reconnecting Daykin, Evan
Re: Asyn not automatically reconnecting Mark Rivers
<2018>
2025
2026
<2018>
2025
2026