1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025  2026
Subject: RE: Unexpected change in behaviour of ai/ao device support
From: "michael.abbott--- via Tech-talk" <[email protected]>
To: "'Johnson, Andrew N.'" <[email protected]>, "tech-talk ([email protected])" <[email protected]>
Date: Wed, 12 Jun 2019 06:32:55 +0000
(Two meta comments: firstly, apologies for lack of proper e-mail quoting, my e-mailer makes it next to impossible, and the quoting in your e-mail is almost unreadable (nearly impossible to tell which text is quoted), possibly for the same reason.  Secondly, why on earth doesn’t “Reply All” work on this mailing list?  Is this again my crappy e-mailer, or is this some strage tech-talk configuration?)
In you anxiety to avoid the “undefined” wrapping that occurs with integer arithmetic (technically, undefined for signed, defined as modulo word size for unsigned), you changed the semantics drastically.  This doesn’t feel like a good trade off to me.
Ignoring your boundary checking and the rounding, and with extra casts inserted to make the types involved clearer, the difference between the two versions of the conversion code boils down to this:
old:
                rval = (int32_t) (double) value - (int32_t) roff;
new:
                rval = (int32_t) ((double) value - (double) (uint32_t) roff);
Now let’s look at a value of 0 being adjusted with an roff of -512 (for whatever reason, this is what the Hy8402 driver does):
old:
                rval = 512;
new:
                rval = - (uint32_t) -512 = -4294966784;
Oops.
I do wonder if it is time to act on the proposal of 1998 (a trifle before my time in this field) and remove these conversions altogether.  For my own driver support I gave up on letting EPICS do the ai/ao conversion long ago and use the unconverted val field instead.  Much simpler and more predictable!
From: [email protected] [mailto:[email protected]] On Behalf Of Johnson, Andrew N. via Tech-talk
Sent: 11 June 2019 19:51
To: [email protected]
Subject: Re: Unexpected change in behaviour of ai/ao device support
On 6/11/19 3:28 AM, Ralph Lange via Tech-talk wrote:
Use of the ROFF field has been effectively deprecated since 1998, when its functionality was taken over by the cleaner ESLO/EOFF mechanism. ROFF was mainly kept for compatibility reasons.
See https://epics.anl.gov/tech-talk/1998/msg00075.php for the announcement on Tech-Talk.
It got un-deprecated again later because there are things ROFF can do that EOFF can't (see below). The change that Michael A is objecting to happened as a result of the discussion thread starting at https://epics.anl.gov/tech-talk/2013/msg00684.php where I pointed out that we were relying on Undefined Behaviour (UB) in some cases, so that code needed to be fixed.
About the Hytec driver support, Michael wrote:
The underlying problem is that the driver support relies on being able to set the ROFF field to a negative value.  Unfortunately this is no longer possible, and the result is that ao outputs drive into maximum negative output voltage (potentially very damaging), and the ai inputs can also produce nonsense values (haven't actually tried yet, but the driver code is also now clearly broken).
In the ao record's convert() routine ROFF gets subtracted from the scaled (ESLO+EOFF) and adjusted (ASLO+AOFF) value before it gets rounded and cast to the epicsInt32 RVAL field. Subtraction of a positive number is necessary here to avoid the UB that would occur if the code relied on value wrap-around to map part of the EGUL-EGUF value range into the signed int32 range of RVAL, which I suspect the Hytec driver may be doing.
Michael: Can you trace the conversion calculations that happen when you set VAL to EGUF, 0 and EGUL to generate RVAL for that driver? Do any of those rely on scaled values greater than 0x7fffffff being wrapped to negative numbers when that negative ROFF gets subtracted and the result cast to an epicsInt32?
However, I think that not having many users being affected might be related to the ROFF deprecation 17 years before.
ROFF is still used by many device support that talk directly to ADC/DAC registers, but all the device support I have seen that use ROFF set it to a positive number when the hardware has an offset zero — that's why I didn't see much risk in making this code change back in 2015.
I disagree with Ben's suggestion of 21 years ago that ROFF can easily be replaced by modifying EOFF, for 2 main reasons:
1. EOFF is only used by the record's convert() routine when LINR is set to LINEAR or SLOPE.
2. A user can set AOFF and/or ASLO to correct their ADC/DAC's calibration, which is what those fields were designed for. Any device support that sets EOFF instead of ROFF would need to recalculate the value of EOFF after each adjustment of AOFF/ASLO. EGUL and EGUF are marked as SPC_LINCONV, but AOFF and ASLO are not, so there's nothing in the record that could trigger that recalculation to happen automatically.
- Andrew
Complexity comes for free, Simplicity you have to work for.
Re: Unexpected change in behaviour of ai/ao device support J. Lewis Muir via Tech-talk
Re: Unexpected change in behaviour of ai/ao device support Johnson, Andrew N. via Tech-talk
Unexpected change in behaviour of ai/ao device support michael.abbott--- via Tech-talk
Re: Unexpected change in behaviour of ai/ao device support Ralph Lange via Tech-talk
Prev: Re: RELEASE file Lang, Keenan C. via Tech-talk
Next: Re: RELEASE file Florian Feldbauer via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  <20192020  2021  2022  2023  2024  2025  2026
Prev: Re: Unexpected change in behaviour of ai/ao device support Johnson, Andrew N. via Tech-talk
Next: Re: Unexpected change in behaviour of ai/ao device support J. Lewis Muir via Tech-talk
ANJ, 14 Jun 2019 · Home · News · About · Talk · Base · Modules · Extensions ·