1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  <20202021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  <20202021  2022  2023  2024  2025  2026
Subject: Re: Update a record at a specific time
To: Donny Domagoj Cosic <[email protected]>
Cc: EPICS tech-talk <[email protected]>
Date: Wed, 3 Jun 2020 13:43:11 +0000
Hi Danny,
Now I think I understand what you want to do.  You want to write B if and only if A==10?
I think this will do what you want:
record(calcout, "Name"){
    field(INPA, "In_A")
    field(INPB, "In_B")
    field(CALC, "A==10")
    field(OCAL, "B"
    field(OOPT, "When Non-zero")
    field(DOPT, "Use OCAL")
    field(OUT, "Out")
The CALC is now just A==10.  OOPT tests if the CALC is non-zero (i.e. True) and only writes to the output if it is.  OCAL determines what is written, and it is set to B.  DOPT says to write OCAL, not CAL, to the output link.
From: Tech-talk <[email protected]> on behalf of Donny Domagoj Cosic via Tech-talk <[email protected]>
Sent: Wednesday, June 3, 2020 8:32 AM
To: [email protected]
Hi Mark,
Thank you for your response,
I was referring to the CALC field of the calcout record:
    field(INPA, "In_A")
    field(INPB, "In_B")
    field(CALC, "A==10?B")
    field(OUT, "Out")
the line "field(CALC, "A==10?B")" is not valid because there is no else
statement ie. "A==10?B:0". If i understood your response correctly, this
can be accomplished by setting the OOPT field to "Transition To
Non-zero" and the record will only write the output when it is non zero.
Donny
Donny Domagoj Cosic
  Institut Ruder Boskovic, Bijenicka cesta 54, 10000 Zagreb, Croatia
Dana 03.06.2020 14:03, Mark Rivers via Tech-talk je napisao(la):
>> Additionally, a simple follow up question that I
>> am not able to solve in a simple way. Is there a simple way to create
>> a
>> "if" statement without the "else" part. As in, I would like the OUT
>> record processed only then the "if" condition is met.
> I'm not positive I understand the question.  But if you can make your
> calculation "if" return 0 or non-zero then the calcout record has an
> OOPT field that can be either "Transition To Zero" or "Transition To
> Non-zero" (among other choices).  That will write the output only
> under the specified condition.  It also has a DOPT field that lets you
> write a different value from the result of the calculation if you set
> it to "Use OCAL" rather than "Use CAL".
> Mark
> ________________________________
> Sent: Wednesday, June 3, 2020 6:45 AM
> Subject: Update a record at a specific time
> Hello,
> For archiving purposes I am trying to record a value from a PV everyday
> at a specific time. I accomplished similar things using a Soft
> Timestamp
> record when a specific date/time field updates. ie:
> record(stringin, "TeslaMeters:$(position):TimeStamp"){
>      field(DTYP, "Soft Timestamp")
>      field(PINI, "YES")
>      field(INP,  "@%d")
> record(calcout, "TeslaMeters:$(position):Calc"){
>     field(INPA, "TeslaMeters:$(position):TimeStamp CP")
>     field(INPB, "TeslaMeters:$(position)")
>     field(CALC, "B")
>     field(OUT, "TeslaMeters:$(position):Midnight PP")
> record(ai, "TeslaMeters:$(position):Midnight")
>      field(PREC, "3")
>      field(EGU,  "Tesla")
>      field(PINI, "YES")
> Could I use a similar strategy to compare a time string generated by
> the
> Soft Timestamp? I see that there is a scalcout record, but i was not
> able to get it to work. Additionally, a simple follow up question that
> I
> am not able to solve in a simple way. Is there a simple way to create a
> Thank you,
> Donny
> Donny Domagoj Cosic
Re: Update a record at a specific time Donny Domagoj Cosic via Tech-talk
Re: Update a record at a specific time Mark Rivers via Tech-talk
Prev: Re: Update a record at a specific time Donny Domagoj Cosic via Tech-talk
Next: Re: Update a record at a specific time Donny Domagoj Cosic via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  <20202021  2022  2023  2024  2025  2026