1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  <20202021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  <20202021  2022  2023  2024  2025  2026
Subject: RE: Modbus alarms question
To: 'John Dobbins' <[email protected]>
Date: Thu, 16 Jul 2020 14:36:08 +0000
Ø  I would suggest now adding this to your startup script after creating the MISC port.
asynSetOption(“MISC”, 0, “disconnectOnReadTimeout”, “Y)
> That's better. Thanks.
initial state:
MSD_S1F_FLD_CR                 2020-07-16 09:36:52.285315  STATE MAJOR
I unplug the cable:
MSD_S1F_FLD_CR                 2020-07-16 09:37:25.876095  TIMEOUT INVALID
MSD_S1F_FLD_CR                 2020-07-16 09:37:26.376358  READ INVALID
OK, good.  There is still something I am not completely happy with.  Note that first you get a TIMEOUT alarm, which is correct.  But once the port disconnects you get a READ alarm which is not really correct.  The asynStatus should be asynDisconnected which maps to COMM alarm.  That would be more meaningful.  I think this patch will fix the problem.
(sphinx) corvette:asyn/asyn/asynDriver>git diff .
diff --git a/asyn/asynDriver/asynManager.c b/asyn/asynDriver/asynManager.c
index deefbe7..911e14e 100644
--- a/asyn/asynDriver/asynManager.c
+++ b/asyn/asynDriver/asynManager.c
@@ -1829,7 +1829,7 @@ static asynStatus queueLockPort(asynUser *pasynUser)
                 pasynUserCopy->errorMessage);
             epicsMutexUnlock(plockPortPvt->queueLockPortMutex);
             pasynManager->freeAsynUser(pasynUserCopy);
-            return asynError;
+            return status;
         /* Wait for event from the port thread in the queueLockPortCallback function */
         asynPrint(pasynUser,ASYN_TRACE_FLOW, "%s asynManager::queueLockPort waiting for event\n", pport->portName);
@@ -1840,7 +1840,7 @@ static asynStatus queueLockPort(asynUser *pasynUser)
                 "asynManager::queueLockPort queueRequest timed out");
-            return asynError;
+            return asynTimeout;
         asynPrint(pasynUser,ASYN_TRACE_FLOW, "%s asynManager::queueLockPort got event from callback\n", pport->portName);
You have already applied the second change in this patch.  Could you also try the first change and see if that changes the final alarm to COMM alarm?
Sent: Thursday, July 16, 2020 8:46 AM
Subject: Re: Modbus alarms question
Mark,
initial state:
I unplug the cable:
2+ minutes late I plug the cable back in and it recovers promptly
MSD_S1F_FLD_CR                 2020-07-16 09:40:02.911512  STATE MAJOR
John
Sent: Thursday, July 16, 2020 9:19 AM
To: John Dobbins <[email protected]>
I think you are seeing is due to Linux taking a really long time to realize that the device is disconnected and closing the socket.  I think that eventually it would reconnect, but it can take hours.  Windows is better with this.
I am very interested to know what you see when you do that.
Sent: Thursday, July 16, 2020 8:10 AM
To: Mark Rivers
Mark,
That fixed my problem. Thanks!
My test involves disconnecting the network cable from the PC hosting the simulated PLC.  When I unplug the cable I now get a single transition to "TIMEOUT INVALID".  When I plug the cable back in things return to normal.
In doing this testing I did notice something else I wanted to ask about. If the time the cable is unplugged is > ~ 2 minutes, the connection between the IOC and the simulated PLC is not restored when I plug the cable back in (though it is for shorter outages). The record remains in the "TIMEOUT INVALID" state.  Is this what you would expect?
John
Re: Modbus alarms question John Dobbins via Tech-talk
Re: Modbus alarms question Mark Rivers via Tech-talk
RE: Modbus alarms question Mark Rivers via Tech-talk