Ø
I would suggest now adding this to your startup script after creating the MISC port.
asynSetOption(“MISC”, 0, “disconnectOnReadTimeout”, “Y)
> That's better. Thanks.
initial state:
MSD_S1F_FLD_CR 2020-07-16 09:36:52.285315 STATE MAJOR
I unplug the cable:
MSD_S1F_FLD_CR 2020-07-16 09:37:25.876095 TIMEOUT INVALID
MSD_S1F_FLD_CR 2020-07-16 09:37:26.376358 READ INVALID
OK, good. There is still something I am not completely happy with. Note that first you get a TIMEOUT alarm, which is correct. But once the port disconnects you get a READ alarm which is not really correct. The asynStatus should
be asynDisconnected which maps to COMM alarm. That would be more meaningful. I think this patch will fix the problem.
(sphinx) corvette:asyn/asyn/asynDriver>git diff .
diff --git a/asyn/asynDriver/asynManager.c b/asyn/asynDriver/asynManager.c
index deefbe7..911e14e 100644
--- a/asyn/asynDriver/asynManager.c
+++ b/asyn/asynDriver/asynManager.c
@@ -1829,7 +1829,7 @@ static asynStatus queueLockPort(asynUser *pasynUser)
pasynUserCopy->errorMessage);
epicsMutexUnlock(plockPortPvt->queueLockPortMutex);
pasynManager->freeAsynUser(pasynUserCopy);
- return asynError;
+ return status;
/* Wait for event from the port thread in the queueLockPortCallback function */
asynPrint(pasynUser,ASYN_TRACE_FLOW, "%s asynManager::queueLockPort waiting for event\n", pport->portName);
@@ -1840,7 +1840,7 @@ static asynStatus queueLockPort(asynUser *pasynUser)
"asynManager::queueLockPort queueRequest timed out");
- return asynError;
+ return asynTimeout;
asynPrint(pasynUser,ASYN_TRACE_FLOW, "%s asynManager::queueLockPort got event from callback\n", pport->portName);
You have already applied the second change in this patch. Could you also try the first change and see if that changes the final alarm to COMM alarm?
I unplug the cable:
2+ minutes late I plug the cable back in and it recovers promptly
MSD_S1F_FLD_CR 2020-07-16 09:40:02.911512 STATE MAJOR
I think you are seeing is due to Linux taking a really long time to realize that the device is disconnected and closing the socket. I think that eventually it would reconnect, but it can take hours. Windows is better with this.
I am very interested to know what you see when you do that.
Sent: Thursday, July 16, 2020 8:10 AM
To: Mark Rivers
Subject: Re: Modbus alarms question
Mark,
That fixed my problem. Thanks!
My test involves disconnecting the network cable from the PC hosting the simulated PLC. When I unplug the cable I now get a single transition to "TIMEOUT INVALID". When I plug the cable back in things return to normal.
In doing this testing I did notice something else I wanted to ask about. If the time the cable is unplugged is > ~ 2 minutes, the connection between the IOC and the simulated PLC is not restored when I plug the cable back in (though it is for shorter outages).
The record remains in the "TIMEOUT INVALID" state. Is this what you would expect?
John