Hi Tom,
You can control the scan rate of the record via caput's directly:
caput <record_name>.SCAN <scan_rate>
where the scan rate can be a string or an number value that represents
the string (more details here:
https://epics.anl.gov/base/R7-0/5-docs/menuScan.html)
If you want to control this from another record you could use an AO
record and link the OUT of this record to SCAN field of the CALC record
record(ao, "scan:ao1") {
field(VAL, 7)
field(OUT, "scan:calc.SCAN PP")
record(calc, "scan:calc") {
field(SCAN, "1 second") # valid only until scan:ao1 gets processed
field(CALC, "<calculation>")
The values for the AO record must be between 0 and 9 for the default
menuScan.dbd.
Another option a bit more verbose would be to use an MBBO record, where
you can implement the menuScan from the link above and use strings for
control but this would be the same as writing to the SCAN field (maybe
useful if you want to change SCAN field of multiple records at the same
time ...
record(mbbo, "scan:menu") {
field(FLNK, "scan:dfanout")
field(ZRVL, "0")
field(ZRST, "Passive")
field(ONVL, "1")
field(ONST, "Event")
field(TWVL, "2")
field(TWST, "I/O Intr")
field(THVL, "3")
field(THST, "10 second")
field(FRVL, "4")
field(FRST, "5 second")
field(FVVL, "5")
field(FVST, "2 second")
field(SXVL, "6")
field(SXST, "1 second")
field(SVVL, "7")
field(SVST, ".5 second")
field(EIVL, "8")
field(EIST, ".2 second")
field(NIVL, "9")
field(NIST, ".1 second")
record(dfanout, "scan:dfanout") {
field(DOL, "scan:menu")
field(OMSL, "closed_loop")
field(OUTA, "scan:calc.SCAN PP")
field(OUTB, ...)
field(SCAN, "1 second") # valid only until scan:menu gets processed
Now the last database will only work as expected if the menuScan.dbd
hasn't been modified...
Best regards,
Žiga
On 19. 05. 2021 14:20, Stainer Tom via Tech-talk wrote:
Dear Epics Community,
I have a simple problem that I am sure has been asked before but my previous searches came up blank on tech-talk, so please forgive me if it is trivial.
I have a simple database, consisting of two records, as shown below. This works fine, and is one of the most elementary databases you can conceive of, however, you will notice the two commented out lines.
My desire is to have the SCAN field controlled by the "scan:ai1" PV, so I can do some *caput*s to control the scan, say to go from 0.1 second to 2 seconds.
My commented out lines obviously don't work, but I wondered how this would be possible using the database file.
Does anyone have any tips on how to solve this problem? (Or please point me to previous/similar solutions.)
# mydb.db
record(ai, "scan:ai1") {
field(INP, ".1")
record(calcout, "scan:calc1"){
# field(SCAN, "B second")
# field(INPB, "scan:ai1")
field(SCAN, ".5 second")
field(INPA, "scan:calc1.VAL")
field(CALC, "(A<20)?(A+1):0")
Kind regards,
Tom
- RE: Control SCAN field with ai record Stainer Tom via Tech-talk
- Control SCAN field with ai record Stainer Tom via Tech-talk
Re: Control SCAN field with ai record Ralph Lange via Tech-talk
<2021>
2025
2026
<2021>
2025
2026