Hey Urszula,
we had some Julabo chillers in our labs controlled via RS232 interfaces.
I used Stream+Asyn to controll them.
I've attached the protocol file and database files for our two Julabo chillers.
HTH,
Florian
On 5/24/21 7:12 PM, Neuman, Urszula (DLSLtd, RAL, LSCI) via Tech-talk wrote:
Hi,
Does anyone have EPICS support for Julabo chillers?
We have one - Julabo FL4003 - that we would like to control remotely.
Thanks,
Urszula
This e-mail and any attachments may contain confidential, copyright and or privileged material, and are for the use of the intended addressee only. If you are not the intended addressee or an authorised recipient of the addressee please notify us of receipt by returning the e-mail and do not use, copy, retain, distribute or disclose the information in or attached to the e-mail.
Any opinions expressed within this e-mail are those of the individual and not necessarily of Diamond Light Source Ltd.
Diamond Light Source Ltd. cannot guarantee that this e-mail or any attachments are free from viruses and we cannot accept liability for any damage which you may sustain as a result of software viruses which may be transmitted in or with the message.
Diamond Light Source Limited (company no. 4375679). Registered in England and Wales with its registered office at Diamond House, Harwell Science and Innovation Campus, Didcot, Oxfordshire, OX11 0DE, United Kingdom
Ruhr-Universität Bochum
AG der Experimentalphysik I
Dr. Florian Feldbauer
NB 2/131 / Fach 125
Universitätsstr. 150
D-44801 Bochum
Office: NB 2/134
Phone:  (+49)234 / 32-23563
Fax:    (+49)234 / 32-14170
https://paluma.ruhr-uni-bochum.de
# ### StreamDevice Protocol for             ### #
# ### Julabo FP50 / LH47                    ### #
# ### author: F.Feldbauer                   ### #
# ### Ref 1.0; 2011-05-19                   ### #
# ### Globals ### #
OutTerminator = CR;
InTerminator  = CR LF DC1;
LockTimeout   = 5000;
ReplyTimeout  = 500;
ReadTimeout   = 500;
WriteTimeout  = 300;
ExtraInput    = Ignore;
# ### Exception Handlers ### #
# ### Protocols ### #
getStatus {
  # get status message
  # Example of command:
  # field (INP, "@Julabo.proto getStatus(PANDA:$(subsys):$(sector):JuFP50:$(ID)) JuFP50_$(ID)")
  out "status";
  in  DC3,"%(\$1:StatusNumber.VAL)i %39c";
  @mismatch {
    out "status";
  @replytimeout {
    out "in_pv_00";
    in  DC3,"%f";
## pv
getBathTemp {
  # get bath temperature
  # field (INP, "@Julabo.proto getBathTemp JuFP50_$(ID)")
  out "in_pv_00";
  in  DC3,"%f";
  @mismatch {
    out "in_pv_00";
    in  DC3,"%f";
  @replytimeout {
    out "in_pv_00";
    in  DC3,"%f";
getHeatPower {
  # get used heat power
  # field (INP, "@Julabo.proto getHeatPower JuFP50_$(ID)")
  out "in_pv_01";
  in  DC3,"%f";
  @mismatch {
    out "in_pv_01";
    in  DC3,"%f";
  @replytimeout {
    out "in_pv_01";
    in  DC3,"%f";
getPT100Temp {
  # get temperature measured by external PT100
  # field (INP, "@Julabo.proto getPT100Temp JuFP50_$(ID)")
  out "in_pv_02";
  in  DC3,"%f";
  @mismatch{ in  DC3,"---.--";}
getSafetySensor {
  out "in_pv_03";
  in  DC3,"%f";
getSafeTemp {
  out "in_pv_04";
  in  DC3,"%f";
getPumpPressure { #####################
  out "in_pv_05"; #                   #
  in  DC3,"%f";  # Julabo LH47 only! #
## sp
getSetVal1 {
  out "in_sp_00";
  in  DC3,"%f";
  @mismatch {
    out "in_sp_00";
    in  DC3,"%f";
  @replytimeout {
    out "in_sp_00";
    in  DC3,"%f";
getSetVal2 {      #####################
  out "in_sp_01"; #                   #
  in  DC3,"%f";  # Julabo FP50 only! #
getSetVal3 {      #####################
  out "in_sp_02"; #                   #
getOverTemp {
  out "in_sp_03";
  in  DC3,"%f";
getSubTemp {
  out "in_sp_04";
  in  DC3,"%f";
getUnit {
  out "in_sp_06";
  in  DC3,"%i";
getPumpStage {
  out "in_sp_07";
  in  DC3,"%i";
  @mismatch {
    out "in_sp_07";
    in  DC3,"%i";
  @replytimeout {
    out "in_sp_07";
    in  DC3,"%i";
## par
getTempDiff {
  out "in_par_00";
  in  DC3,"%f";
getTimeTe {
  out "in_par_01";
  in  DC3,"%f";
getTimeSi {
  out "in_par_02";
  in  DC3,"%f";
getTimeTi {
  out "in_par_03";
  in  DC3,"%f";
getCoSpeed {
  out "in_par_04";
  in  DC3,"%f";
getPkPh0 {
  out "in_par_05";
  in  DC3,"%f";
getParXpInt {
  out "in_par_06";
  in  DC3,"%f";
getParTnInt {
  out "in_par_07";
  in  DC3,"%f";
getParTvInt {
  out "in_par_08";
  in  DC3,"%f";
getParXpCas {
  out "in_par_09";
  in  DC3,"%f";
getProSharCas {
  out "in_par_10";
  in  DC3,"%f";
getParTnCas {
  out "in_par_11";
  in  DC3,"%f";
getParTvCas {
  out "in_par_12";
  in  DC3,"%f";
getMaxIntTempCas {
  out "in_par_13";
  in  DC3,"%f";
getMinIntTempCas {
  out "in_par_14";
  in  DC3,"%f";
getBandLimitUP {
  out "in_par_15";
  in  DC3,"%f";
getBandLimitLO {
  out "in_par_16";
  in  DC3,"%f";
getSelSetpoint {
  out "in_mode_01";
  in  DC3,"%i";
getSelftuneType {
  out "in_mode_02";
  in  DC3,"%i";
getTempControl {
  out "in_mode_04";
  in  DC3,"%i";
getCircCon {
  out "in_mode_05";
  in  DC3,"%i";
getControlDyn {
  out "in_mode_08";
  in  DC3,"%i";
getMaxCoolPower {
  out "in_hil_00";
  in  DC3,"%f";
getMaxHeatPower {
  out "in_hil_01";
  in  DC3,"%f";
setSelSetpoint {
  out "out_mode_01 %i";
setSelftuneType {
  out "out_mode_02 %i";
setTempControl {
  out "out_mode_04 %i";
setCircCon {
  out "out_mode_05 %i";
  @init {
    out "in_mode_05";
    in  DC3,"%i";
setControlDyn {
  out "out_mode_08 %i";
setSetVal1 {
  out "out_sp_00 %3.2f";
setSetVal2 {
  out "out_sp_01 %3.2f";
setSetVal3 {
  out "out_sp_02 %3.2f";
setOverTemp {
  out "out_sp_03 %3.2f";
setSubTemp {
  out "out_sp_04 %3.2f";
setManVar {
  out "out_sp_06 %3.2f";
setPumpStage {
  out "out_sp_07 %i";
setCoSpeed {
  out "out_par_04 %1.1f";
setParXpInt {
  out "out_par_06 %2.1f";
setParTnInt {
  out "out_par_07 %i";
setParTvInt {
  out "out_par_08 %i";
setParXpCas {
  out "out_par_09 %2.1f";
setProSharCas {
  out "out_par_10 %2.1f";
setParTnCas {
  out "out_par_11 %i";
setParTvCas {
  out "out_par_12 %i";
setMaxIntTempCas {
  out "out_par_13 %i";
setMinIntTempCas {
  out "out_par_14 %i";
setBandLimitUP {
  out "out_par_15 %i";
setBandLimitLO {
  out "out_par_16 %i";
setMaxCoolPower {
  out "out_hil_00 -%i";
setMaxHeatPower {
  out "out_hil_01 %i";
# ### EPICS Database for               ### #
# ### Julabo FP50                      ### #
# ### Ref 2.0; 2011-12-19              ### #
# ### macros: subsys  PANDA subsystem  ### #
# ###         type    Cooling type     ### #
# ###         BUS     Asyn Interface   ### #
# ### in commands ### #
record (stringin, "PANDA:$(subsys):COOL:$(type):Status") {
  field (DTYP, "stream")
  field (INP,  "@Julabo.proto getStatus(PANDA:$(subsys):COOL:$(type)) $(BUS)")
  field (SCAN, "10 second")
  field (FLNK, "PANDA:$(subsys):COOL:$(type):BathTEMP:Tmom")
record (ai, "PANDA:$(subsys):COOL:$(type):StatusNumber") {
  # Alarm Parameters
  field (LOLO, "-1")  field (LLSV, "MAJOR")
  field (ADEL, "0")
  field (MDEL, "0")
record (ai, "PANDA:$(subsys):COOL:$(type):BathTEMP:Tmom") {
  field (INP,  "@Julabo.proto getBathTemp $(BUS)")
  field (EGU,  "degC")
  field (PREC, "2")
  field (HIHI, "-10")  field (HHSV, "MAJOR")
  field (LOLO, "-50")  field (LLSV, "MAJOR")
  field (HIGH, "-20")  field (HSV,  "MINOR")
  field (LOW,  "-40")  field (LSV,  "MINOR")
  field (ADEL, "0")
  field (MDEL, "0")
  field (FLNK, "PANDA:$(subsys):COOL:$(type):HeatPower")
record (ai, "PANDA:$(subsys):COOL:$(type):HeatPower") {
  field (EGU,  "p.c.")
  field (PREC, "0")
  field (INP,  "@Julabo.proto getHeatPower $(BUS)")
  field (FLNK, "PANDA:$(subsys):COOL:$(type):PumpStage")
record (ai, "PANDA:$(subsys):COOL:$(type):PT100:Tmom") {
  field (EGU,  "degC")
  field (PREC, "2")
  field (INP,  "@Julabo.proto getPT100Temp $(BUS)")
  field (ADEL, "0")
  field (MDEL, "0")
record (ai, "PANDA:$(subsys):COOL:$(type):Tset") {
  field (EGU,  "degC")
  field (PREC, "2")
  field (INP,  "@Julabo.proto getSetVal1 $(BUS)")
  field (PINI, "YES")
record (bi, "PANDA:$(subsys):COOL:$(type):Unit") {
  field (INP,  "@Julabo.proto getUnit $(BUS)")
  field (ZNAM, "degC")
  field (ONAM, "degF")
record (ai, "PANDA:$(subsys):COOL:$(type):PumpStage") {
  field (INP,  "@Julabo.proto getPumpStage $(BUS)")
  field (ADEL, "0")
  field (MDEL, "0")
  field (FLNK, "PANDA:$(subsys):COOL:$(type):Tset")
record (ai, "PANDA:$(subsys):COOL:$(type):ParXpInt") {
  field (PINI, "YES")
  field (INP,  "@Julabo.proto getParXpInt $(BUS)")
record (ai, "PANDA:$(subsys):COOL:$(type):ParTnInt") {
  field (PINI, "YES")
  field (INP,  "@Julabo.proto getParTnInt $(BUS)")
record (ai, "PANDA:$(subsys):COOL:$(type):ParTvInt") {
  field (PINI, "YES")
  field (INP,  "@Julabo.proto getParTvInt $(BUS)")
record (mbbi, "PANDA:$(subsys):COOL:$(type):SelftuneType") {
  field (INP,  "@Julabo.proto getSelftuneType $(BUS)")
  field (ZRST, "off")
  field (ONST, "once")
  field (TWST, "always")
  field (PINI, "YES")
record (bi, "PANDA:$(subsys):COOL:$(type):TempControl") {
  field (INP,  "@Julabo.proto getTempControl $(BUS)")
  field (ZNAM, "Internal")
  field (ONAM, "External")
  field (PINI, "YES")
record (bi, "PANDA:$(subsys):COOL:$(type):CircCon") {
  field (INP,  "@Julabo.proto getCircCon $(BUS)")
  field (ZNAM, "stop")
  field (ONAM, "start")
  field (PINI, "YES")
record (bi, "PANDA:$(subsys):COOL:$(type):ControlDyn") {
  field (INP,  "@Julabo.proto getControlDyn $(BUS)")
  field (ZNAM, "aperiodic")
  field (ONAM, "standard")
  field (PINI, "YES")
# ### out commands ### #
record (mbbo, "PANDA:$(subsys):COOL:$(type):setSelftuneType") {
  field (OUT,  "@Julabo.proto setSelftuneType $(BUS)")
  field (FLNK, "PANDA:$(subsys):COOL:$(type):SelftuneType")
  field (ZRST, "off")
record (bo, "PANDA:$(subsys):COOL:$(type):setTempControl") {
  field (OUT,  "@Julabo.proto setTempControl $(BUS)")
  field (ZNAM, "int")
  field (ONAM, "ext")
  field (FLNK, "PANDA:$(subsys):COOL:$(type):TempControl")
record (bo, "PANDA:$(subsys):COOL:$(type):setCircCon") {
  field (OUT,  "@Julabo.proto setCircCon $(BUS)")
  field (ONAM, "Start")
  field (ZNAM, "Stop")
  field (FLNK, "PANDA:$(subsys):COOL:$(type):CircCon")
record (ao, "PANDA:$(subsys):COOL:$(type):setTset") {
  field (OUT,  "@Julabo.proto setSetVal1 $(BUS)")
record (ao, "PANDA:$(subsys):COOL:$(type):setPumpStage") {
  field (VAL,  "4")
  field (OUT,  "@Julabo.proto setPumpStage $(BUS)")
  field (DRVH, "4")
  field (DRVL, "0")
  field (PREC, "0")
  field (EGU,  "a.u.")
record (ao, "PANDA:$(subsys):COOL:$(type):setParXpInt") {
  field (OUT,  "@Julabo.proto setParXpInt $(BUS)")
record (ao, "PANDA:$(subsys):COOL:$(type):setParTnInt") {
  field (OUT,  "@Julabo.proto setParTnInt $(BUS)")
record (ao, "PANDA:$(subsys):COOL:$(type):setParTvInt") {
  field (OUT,  "@Julabo.proto setParTvInt $(BUS)")
# ### Julabo LH47                      ### #
# ### Ref 2.2; 2011-12-19              ### #
record (stringin, "PANDA:$(subsys):COOL:MAIN:Status") {
  field (INP,  "@Julabo.proto getStatus(PANDA:$(subsys):COOL:MAIN) $(BUS)")
  field (FLNK, "PANDA:$(subsys):COOL:MAIN:BathTEMP:Tmom")
record (ai, "PANDA:$(subsys):COOL:MAIN:StatusNumber") {
  # Alarm Parameters
  field (ADEL, "0")
  field (MDEL, "0")
record (ai, "PANDA:$(subsys):COOL:MAIN:BathTEMP:Tmom") {
  field (EGU,  "degC")
  field (PREC, "2")
  field (ADEL, "0")
  field (MDEL, "0")
  field (FLNK, "PANDA:$(subsys):COOL:MAIN:HeatPower")
record (ai, "PANDA:$(subsys):COOL:MAIN:HeatPower") {
  field (EGU,  "p.c.")
  field (PREC, "0")
  field (ADEL, "0")
  field (MDEL, "0")
  field (FLNK, "PANDA:$(subsys):COOL:MAIN:PumpStage")
record (ai, "PANDA:$(subsys):COOL:MAIN:PT100:Tmom") {
  field (EGU,  "degC")
  field (PREC, "2")
  field (ADEL, "0")
  field (MDEL, "0")
record (ai, "PANDA:$(subsys):COOL:MAIN:Tset") {
  field (EGU,  "degC")
  field (PREC, "2")
  field (ADEL, "1")
  field (MDEL, "1")
  field (PINI, "YES")
record (bi, "PANDA:$(subsys):COOL:MAIN:Unit") {
record (ai, "PANDA:$(subsys):COOL:MAIN:PumpStage") {
  field (ADEL, "0")
  field (MDEL, "0")
  field (FLNK, "PANDA:$(subsys):COOL:MAIN:Tset")
record (ai, "PANDA:$(subsys):COOL:MAIN:P_Pump") {
  field (EGU,  "bar")
  field (PREC, "2")
  field (INP,  "@Julabo.proto getPumpPressure $(BUS)")
  field (ADEL, "0")
  field (MDEL, "0")
record (mbbi, "PANDA:$(subsys):COOL:MAIN:SelftuneType") {
  field (ZRST, "off")
  field (PINI, "YES")
record (bi, "PANDA:$(subsys):COOL:MAIN:TempControl") {
  field (PINI, "YES")
record (bi, "PANDA:$(subsys):COOL:MAIN:CircCon") {
  field (PINI, "YES")
record (bi, "PANDA:$(subsys):COOL:MAIN:ControlDyn") {
  field (PINI, "YES")
record (ai, "PANDA:$(subsys):COOL:MAIN:ParXpInt") {
  field (PINI, "YES")
record (ai, "PANDA:$(subsys):COOL:MAIN:ParTnInt") {
  field (PINI, "YES")
record (ai, "PANDA:$(subsys):COOL:MAIN:ParTvInt") {
  field (PINI, "YES")
record (mbbo, "PANDA:$(subsys):COOL:MAIN:setSelftuneType") {
  field (FLNK, "PANDA:$(subsys):COOL:MAIN:SelftuneType")
  field (ZRST, "off")
record (bo, "PANDA:$(subsys):COOL:MAIN:setTempControl") {
  field (ZNAM, "int")
  field (ONAM, "ext")
  field (FLNK, "PANDA:$(subsys):COOL:MAIN:TempControl")
record (bo, "PANDA:$(subsys):COOL:MAIN:setCircCon") {
  field (FLNK, "PANDA:$(subsys):COOL:MAIN:CircCon")
record (ao, "PANDA:$(subsys):COOL:MAIN:setTset") {
record (ao, "PANDA:$(subsys):COOL:MAIN:setPumpStage") {
  field (VAL,  "5")
  field (DRVH, "5")
  field (DRVL, "0")
  field (PREC, "0")
  field (EGU,  "a.u.")
record (ao, "PANDA:$(subsys):COOL:MAIN:setParXpInt") {
record (ao, "PANDA:$(subsys):COOL:MAIN:setParTnInt") {
record (ao, "PANDA:$(subsys):COOL:MAIN:setParTvInt") {
References:
EPICS support for Julabo chiller Neuman, Urszula (DLSLtd, RAL, LSCI) via Tech-talk
Navigate by Date:
Prev: Re: Issue with FPGA based encoder box when running with EPICS 7.0.5 Heinz Junkes via Tech-talk
Next: Re: Issue with FPGA based encoder box when running with EPICS 7.0.5 Torsten Bögershausen via Tech-talk
Navigate by Thread:
Prev: EPICS support for Julabo chiller Neuman, Urszula (DLSLtd, RAL, LSCI) via Tech-talk
Next: "Starter Kit" for learning EPICS? Feister, Scott via Tech-talk