1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
<== Date ==> <== Thread ==>
Subject: Re: drvModbusAsynConfigure exception 3 when ASLO and PREC fields of PV are changed
From: "Marco A. Barra Montevechi Filho via Tech-talk" <[email protected]>
To: Mark Rivers <[email protected]>
Cc: Junior Cintra Mauricio <[email protected]>, "[email protected]" <[email protected]>, João Pedro Burle Ishida <[email protected]>
Date: Mon, 25 Apr 2022 15:13:10 +0000
Hello and good morning!
I finally managed to test our assumptions and advance a little, i think. I initialized the IOC and did caget in PNR:EU2408:P, PNR:EU2408:P.ASLO and PNR:EU2408:P:RBV.
The initial values are PNR:EU2408:P=1500, PNR:EU2408:P.ASLO=0.1 and PNR:EU2408:P:RBV=150.
The IOC initialization looks like:
iocInit
Starting iocInit
## EPICS R3.15.6
## EPICS Base built Sep 27 2021
2022/04/25 11:49:10.866 drvModbusAsyn::readInt32 port Eurotherm_EMODBUS_1_1_Wr_P function=0x6, offset=00, value=0x5dc
2022/04/25 11:49:10.867 drvModbusAsyn::readInt32 port Eurotherm_EMODBUS_1_1_Wr_I function=0x6, offset=00, value=0x1c
2022/04/25 11:49:11.369 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P WRITE_SINGLE_REGISTER address=06 value=0x3a98
iocRun: All initialization complete
## Start any sequence programs
#seq sncxxx,"user=gabrielfedelHost"
2022/04/25 11:49:11.485 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=3
2022/04/25 11:49:11.485 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
epics>
I append the full log in the end of this e-mail. What i think is important information​: after initializing the IOC, i did caput PNR:EU2408:P 160 and the IOC terminal returned:
epics> 2022/04/25 11:51:54.767 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P WRITE_SINGLE_REGISTER address=06 value=0x640
2022/04/25 11:51:54.803 drvModbusAsyn::writeInt32 port Eurotherm_EMODBUS_1_1_Wr_P function=0x6, modbusAddress=06, buffer[0]=0x640, bufferLen=1
Indeed, cagetting the P and P:RBV PVs returned the right 160 value. Caputting 1600 returned exception 3. The curious thing is: if i stop the IOC and reinitialize it, the terminal now returns:
2022/04/25 11:54:35.501 drvModbusAsyn::readInt32 port Eurotherm_EMODBUS_1_1_Wr_P function=0x6, offset=00, value=0x640
2022/04/25 11:54:35.501 drvModbusAsyn::readInt32 port Eurotherm_EMODBUS_1_1_Wr_I function=0x6, offset=00, value=0x1c
2022/04/25 11:54:36.005 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P WRITE_SINGLE_REGISTER address=06 value=0x3e80
2022/04/25 11:54:36.096 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=3
2022/04/25 11:54:36.096 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
epics>
So instead of trying to write 1500 in the modbus message, the IOC tried to write 1600 to it, which clearly means that its getting the value from some reading in the equipment and miscalculating the message. Looking at the .db file, though, i cant seem to find any reason for the IOC to "know" which value to send. I append the complete db file at the end of this email, but the PVs that i think are of interest are:
record(mbbo, "${BL}:EU2408:PREC") {
        field(ZRST, "1 Decimal Place")
        field(ONST, "2 Decimal Places")
        field(ZRVL, "1")
        field(ONVL, "2")
        field(FLNK, "${BL}:EU2408:SETASLO")
        field(RVAL, "4")
        field(PINI, "YES")
record(dfanout, "${BL}:EU2408:SETASLO") {
        field(OMSL, "closed_loop")
        field(DOL, "${BL}:EU2408:CALCASLO PP")
        field(OUTA, "${BL}:EU2408:SP.ASLO")
        field(OUTB, "${BL}:EU2408:SP:RBV.ASLO")
        field(OUTC, "${BL}:EU2408:RR.ASLO")
        field(OUTD, "${BL}:EU2408:RR:RBV.ASLO")
        field(OUTE, "${BL}:EU2408:PV:RBV.ASLO")
        field(OUTF, "${BL}:EU2408:P.ASLO")
        field(OUTG, "${BL}:EU2408:P:RBV.ASLO")
        field(FLNK, "${BL}:EU2408:SETPREC")
record(dfanout, "${BL}:EU2408:SETPREC") {
        field(DOL, "${BL}:EU2408:PREC.RVAL")
        field(OUTA, "${BL}:EU2408:SP.PREC PP")
        field(OUTB, "${BL}:EU2408:SP:RBV.PREC PP")
        field(OUTC, "${BL}:EU2408:RR.PREC PP")
        field(OUTD, "${BL}:EU2408:RR:RBV.PREC PP")
        field(OUTE, "${BL}:EU2408:PV:RBV.PREC PP")
        field(OUTF, "${BL}:EU2408:P.PREC PP")
        field(OUTG, "${BL}:EU2408:P:RBV.PREC PP")
record(ao, "${BL}:EU2408:P") {
  field(DESC, "P Param")
  field(DTYP, "asynInt32")
  field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_P,0,1000)MODBUS_DATA")
I understand that ${BL}:EU2408:PREC is causing ${BL}:EU2408:P to process at initialization, but i cant understand where ${BL}:EU2408:P is getting its initial value from. Any suggestions?
Thanks in advance,
Marco
OBS1: Full db file:
#record(ai, "${BL}:EU2408:PV:RBV") {
#  field(DESC, "Temperature Readback")
#  field(DTYP, "asynInt32")
#  field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_PV,0,1000)MODBUS_DATA")
#  field(EGU, "C")
#  field(SCAN, "I/O Intr")
#  field(ASLO, "0.1")
# Template for general controller parameters using the Modbus interface
# % macro, P, Device prefix
# % macro, Q, Device suffix
# % macro, PORT, Asyn port
# % macro, ADDR, Modbus address
# % macro, DISABLED, Start disabled?
# Autotune loop number address 3072
record(mbbo, "${BL}:EU2408:AUTOTUNELOOP") {
	field(DESC, "Autotune Loop Number")
	field(DTYP,"asynInt32")
	field(OUT,"@asyn(Eurotherm_EMODBUS_1_0_Wr_ATUNE,0,1000)MODBUS_DATA")
	field(ZRST, "Off")
	field(ZRVL, "0")
	field(ONST, "Loop 1")
	field(ONVL, "11")
	field(TWST, "Loop 2")
	field(TWVL, "21")
	field(THST, "Loop 3")
	field(THVL, "31")
# % archiver 10 Monitor
record(mbbi, "${BL}:EU2408:AUTOTUNELOOP:RBV") {
	field(DESC, "Autotune Loop Readback")
	field(INP,"@asyn(Eurotherm_EMODBUS_1_0_Rd_ATUNE,0,1000)MODBUS_DATA")
	field(ZRST, "Off")
	field(ZRVL, "0")
	field(ONVL, "11")
	field(TWVL, "21")
	field(THVL, "31")
# Autotune output high limit address 3076
record(ao, "${BL}:EU2408:AUTOTUNEOH") {
	field(DESC, "Autotune Output High Limit")
	field(OUT,"@asyn(Eurotherm_EMODBUS_1_0_Wr_ATUNE,4,1000)MODBUS_DATA")
	field(PREC, "1")
	field(ASLO, "0.1")
	field(DRVH, "100")
	field(DRVL, "0")
	field(EGU, "%")
record(ai, "${BL}:EU2408:AUTOTUNEOH:RBV") {
	field(DESC, "Autotune Output High Limit Readback")
	field(INP,"@asyn(Eurotherm_EMODBUS_1_0_Rd_ATUNE,4,1000)MODBUS_DATA")
	field(PREC, "1")
	field(ASLO, "0.1")
	field(EGU, "%")
# Autotune output low limit address 3077
record(ao, "${BL}:EU2408:AUTOTUNEOL") {
	field(DESC, "Autotune Output Low Limit")
	field(OUT,"@asyn(Eurotherm_EMODBUS_1_0_Wr_ATUNE,5,1000)MODBUS_DATA")
	field(PREC, "1")
	field(ASLO, "0.1")
	field(DRVH, "100")
	field(DRVL, "0")
	field(EGU, "%")
record(ai, "${BL}:EU2408:AUTOTUNEOL:RBV") {
	field(DESC, "Autotune Output Low Limit Readback")
	field(INP,"@asyn(Eurotherm_EMODBUS_1_0_Rd_ATUNE,5,1000)MODBUS_DATA")
	field(PREC, "1")
	field(ASLO, "0.1")
	field(EGU, "%")
record(bo, "${BL}:EU2408:DISABLE") {
  field(DESC, "Disable comms")
  field(PINI, "YES")
  field(VAL, "0")
  field(ZNAM, "Enabled")
  field(ONAM, "Disabled")
record(stringin, "${BL}:EU2408:ERR") {
  field(DESC, "Error message")
  field(PINI, "YES")
  field(VAL, "No Error")
# Template for register based communications
# Instantiate once per loop - the device prefix and suffix combination must be unique for each loop
# Notes:
# Controller must be set to full resolution (Comms->H module->Resolution)
# The desired number of decimal places must also be set on the controller (Standard I/O->PV Input->Resolution):
# either XXX.XX or XXXX.X.  This must match the setting of the PREC macro.
# The decimal point is inferred, hence 25.01 is transmitted as 2501 which is converted using ASLO factor.
# If two decimal places are required the maximum value that can be set is 327.66
# Also ensure that the Proportional Band units are set to 'Engineer units'
# % macro, LOOP, Loop number, default 1
# % macro, SPMIN, Minimum setpoint
# % macro, SPMAX, Maximum setpoint
# % macro, RRMAX, Maximum ramp rate
# % macro, PREC, Setpoint precision, must match controller setup
# % macro, EGUT, Engineering units for SP & RBV, etc, default is C
# % macro, EGU, Engineering units for ramp rate, default is C/s
# % macro, gda_name, Name to export to gda as
# % macro, gda_desc, Description for gda
# % macro, name, Object and gui association name
# This associates an edm screen with the template
# % gui, EMODBUS.LOOP1, edm, eurotherm2k_modbus.edl, P=${BL}:EU2408,Q=
# % gdatag,template,eurotherm2k,,
# should get this from eurothermModbus, but just in case define it here too...
# PV: address 1
# % gdatag,pv,ro,,PVRBV
# % archiver 1 Monitor
  field(EGU, "C")
# Target setpoint: address 2
#% gdatag,pv,rw,,SP
# % autosave 2 VAL
record(ao, "${BL}:EU2408:SP") {
  field(DESC, "Setpoint")
  field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_PV,1,1000)MODBUS_DATA")
  field(EGU, "C")
  field(DRVH, "1000")
  field(DRVL, "-273")
  field(ASLO, "0.1")
# % gdatag,pv,ro,,SPRBV
record(ai, "${BL}:EU2408:SP:RBV") {
  field(DESC, "Setpoint Readback")
  field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_PV,1,1000)MODBUS_DATA")
  field(EGU, "C")
  field(ASLO, "0.1")
# Target output power (manual mode): address 3
#% gdatag,pv,rw,,O
# % autosave 2 VAL
record(ao, "${BL}:EU2408:O") {
  field(DESC, "Output")
  field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_PV,2,1000)MODBUS_DATA")
  field(EGU, "%")
  field(DRVH, "100")
  field(DRVL, "-100")
  field(ASLO, "0.1")
  field(PREC, "1")
# % gdatag,pv,ro,,ORBV
record(ai, "${BL}:EU2408:O:RBV") {
  field(DESC, "Output Readback")
  field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_PV,2,1000)MODBUS_DATA")
  field(EGU, "%")
  field(ASLO, "0.1")
  field(PREC, "1")
# Working setpoint: address 5
# % gdatag,pv,ro,,WSPRBV
record(ai, "${BL}:EU2408:WSP:RBV") {
  field(DESC, "Working SP Readback")
  field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_WSP,0,1000)MODBUS_DATA")
  field(EGU, "C")
  field(ASLO, "0.1")
# Ramp rate: address 37
#% gdatag,pv,rw,,RR
# % autosave 2 VAL
record(ao, "${BL}:EU2408:RR") {
  field(DESC, "Ramprate")
  field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_RR,0,1000)MODBUS_DATA")
  field(EGU, "C/min")
  field(DRVH, "50")
  field(DRVL, "0")
# % gdatag,pv,ro,,RRRBV
record(ai, "${BL}:EU2408:RR:RBV") {
  field(DESC, "Ramprate Readback")
  field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_RR,0,1000)MODBUS_DATA")
  field(EGU, "C/s")
# Manual mode: address 273
# % autosave 2 VAL
record(bo, "${BL}:EU2408:MAN") {
  field(DESC, "Manual mode enable")
  field(DTYP, "asynUInt32Digital")
  field(OUT, "@asynMask(Eurotherm_EMODBUS_1_1_Wr_MAN,0,1,1000)MODBUS_DATA")
  field(ZNAM, "Automatic")
  field(ONAM, "Manual")
record(bi, "${BL}:EU2408:MAN:RBV") {
  field(DESC, "Manual mode readback")
  field(INP, "@asynMask(Eurotherm_EMODBUS_1_1_Rd_MAN,0,1,1000)MODBUS_DATA")
# Proportional gain term: address 351
# Note this must be set to operate engineering units (not %) for the precision to be correct
# otherwise it is a fixed precision of 1 decimal place
#% gdatag,pv,rw,,P
# % autosave 2 VAL
# % gdatag,pv,ro,,PRBV
record(ai, "${BL}:EU2408:P:RBV") {
  field(DESC, "P Param Readback")
  field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_P,0,1000)MODBUS_DATA")
# Integral gain term: address 352
#% gdatag,pv,rw,,I
# % autosave 2 VAL
record(ao, "${BL}:EU2408:I") {
  field(DESC, "I Param")
  field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_I,0,1000)MODBUS_DATA")
# % gdatag,pv,ro,,IRBV
record(ai, "${BL}:EU2408:I:RBV") {
  field(DESC, "I Param Readback")
  field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_I,0,1000)MODBUS_DATA")
  field(PREC, "1")
# Derivative gain term: address 353
#% gdatag,pv,rw,,D
# % autosave 2 VAL
record(ao, "${BL}:EU2408:D") {
  field(DESC, "D Param")
  field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_D,0,1000)MODBUS_DATA")
# % gdatag,pv,ro,,DRBV
record(ai, "${BL}:EU2408:D:RBV") {
  field(DESC, "D Param Readback")
  field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_D,0,1000)MODBUS_DATA")
  field(PREC, "1")
# Record to switch between full resolution (2 decimal places) and reduced resolution (1 decimal place) which
# allows values larger than 327.66 to be transferred.
# % autosave 2 VAL
	field(ZRVL, "1")
	field(ONVL, "2")
	field(RVAL, "4")
	field(PINI, "YES")
# Use ASLO of 0.01 if 2 decimal places required, otherwise 0.1
record(calcout, "${BL}:EU2408:CALCASLO") {
	field(INPA, "${BL}:EU2408:PREC.RVAL NPP")
	field(CALC, "A==1?0.1:0.01")
#PVs added in 19/04/2022 by Marco Montevechi, Junior Cintra Mauricio and Joao Pedro Burle Ishida
record(ao, "${BL}:EU2408:PROG") {
field(DESC, "Current program running (no.)")
field(OUT, "@asyn(Eurotherm_EMODBUS_1_0_Wr_PROG,0,1000)MODBUS_DATA")
# % gdatag,pv,ro,,PROG:RBV
record(ai, "${BL}:EU2408:PROG:RBV") {
field(DESC, "Current program running (no.) Readback")
field(INP, "@asyn(Eurotherm_EMODBUS_1_0_Rd_PROG,0,1000)MODBUS_DATA")
# Programmer setpoint: address 163
#% gdatag,pv,rw,,PSP
# % autosave 2 VAL
record(ao, "${BL}:EU2408:PSP") {
field(DESC, " Programmer Setpoint")
field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_PSP,0,1000)MODBUS_DATA")
field(EGU, "°C")
field(DRVH, "1000")
field(DRVL, "-273")
field(ASLO, "0.1")
record(ai, "${BL}:EU2408:PSP:RBV") {
field(DESC, "Programmer Setpoint Readback")
field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_PSP,0,1000)MODBUS_DATA")
field(EGU, "°C")
field(ASLO, "0.1")
# Number program running: address 59
#% gdatag,pv,rw,,CYC
# % autosave 2 VAL
record(ao, "${BL}:EU2408:CYC") {
field(DESC, "Program cycles remaining")
field(OUT, "@asyn(Eurotherm_EMODBUS_1_0_Wr_CYC,0,1000)MODBUS_DATA")
# % gdatag,pv,ro,,CYC:RBV
record(ai, "${BL}:EU2408:CYC:RBV") {
field(DESC, "Program cycles remaining Readback")
field(INP, "@asyn(Eurotherm_EMODBUS_1_0_Rd_CYC,0,1000)MODBUS_DATA")
# Number program running: address 56
#% gdatag,pv,rw,,SEG
# % autosave 2 VAL
record(ao, "${BL}:EU2408:SEG") {
field(DESC, "Current segment number")
field(OUT, "@asyn(Eurotherm_EMODBUS_1_0_Wr_SEG,0,1000)MODBUS_DATA")
# % gdatag,pv,ro,,SEG:RBV
record(ai, "${BL}:EU2408:SEG:RBV") {
field(INP, "@asyn(Eurotherm_EMODBUS_1_0_Rd_SEG,0,1000)MODBUS_DATA")
# Program Status number address 29
record(mbbo, "${BL}:EU2408:STYP") {
field(DESC, "Current segment type")
field(OUT,"@asyn(Eurotherm_EMODBUS_1_0_Wr_STYP,0,1000)MODBUS_DATA")
field(ZRST, "End")
field(ZRVL, "0")
field(ONST, "Ramp (Rate)")
field(ONVL, "1")
field(TWST, "Ramp (Time to target")
field(TWVL, "2")
field(THST, "Dwell")
field(THVL, "3")
field(FRST, "Step")
field(FRVL, "4")
field(FVST, "Step")
field(FVVL, "5")
field(SXST, "Call")
field(SXVL, "6")
record(mbbi, "${BL}:EU2408:STYP:RBV") {
field(INP,"@asyn(Eurotherm_EMODBUS_1_0_Rd_STYP,0,1000)MODBUS_DATA")
field(ZRST, "End")
field(ZRVL, "0")
field(ONVL, "1")
field(TWVL, "2")
field(THVL, "3")
field(FRST, "Step")
field(FRVL, "4")
field(FVST, "Step")
field(FVVL, "5")
field(SXST, "Call")
field(SXVL, "6")
# Program Status number address 23
record(mbbo, "${BL}:EU2408:STAT") {
field(DESC, "Program Status")
field(OUT,"@asyn(Eurotherm_EMODBUS_1_0_Wr_STAT,0,1000)MODBUS_DATA")
field(ZRST, "Reset")
field(ZRVL, "1")
field(ONST, "Run")
field(ONVL, "2")
field(TWST, "Hold")
field(TWVL, "4")
field(THST, "Holdback")
field(THVL, "8")
field(FRST, "Complete")
field(FRVL, "16")
record(mbbi, "${BL}:EU2408:STAT:RBV") {
field(DESC, "Program Status Readback")
field(INP,"@asyn(Eurotherm_EMODBUS_1_0_Rd_STAT,0,1000)MODBUS_DATA")
field(ZRVL, "1")
field(ONST, "Run")
field(ONVL, "2")
field(TWST, "Hold")
field(TWVL, "4")
field(THVL, "8")
field(FRVL, "16")
# Address 160
#% gdatag,pv,rw,,TGT
record(ao, "${BL}:EU2408:TGT") {
field(DESC, "Target setpoint current segment")
field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_TGT,0,1000)MODBUS_DATA")
field(EGU, "°C")
field(DRVH, "1000")
field(DRVL, "-273")
field(ASLO, "0.1")
# % gdatag,pv,ro,,TGTRBV
record(ai, "${BL}:EU2408:TGT:RBV") {
field(DESC, "Target setpoint current segment Readback")
field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_TGT,0,1000)MODBUS_DATA")
field(EGU, "°C")
field(ASLO, "0.1")
# Address 36
#% gdatag,pv,rw, SEGT
record(ao, "${BL}:EU2408:SEGT") {
field(DESC, "Segment time remaining")
field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_SEGT,0,1000)MODBUS_DATA")
# field(EGU, "min ?")
field(ASLO, "0.1")
# % gdatag,pv,ro,TGTRBV
record(ai, "${BL}:EU2408:SEGT:RBV") {
field(DESC, "Segment time remaining Readback")
field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_SEGT,0,1000)MODBUS_DATA")
field(ASLO, "0.1")
# Rate: address 161
#% gdatag,pv,rw,,RATE
# % autosave 2 VAL
record(ao, "${BL}:EU2408:RATE") {
field(DESC, "Ramp rate ")
field(OUT, "@asyn(Eurotherm_EMODBUS_1_1_Wr_RATE,0,1000)MODBUS_DATA")
field(EGU, "°C/min")
field(DRVH, "5")
field(DRVL, "0")
# % gdatag,pv,ro,,RATERBV
record(ai, "${BL}:EU2408:RATE:RBV") {
field(DESC, "Ramp rate Readback")
field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_RATE,0,1000)MODBUS_DATA")
field(EGU, "°C/s")
# Address 58
# % gdatag,pv,ro,PROTMRBV
record(ai, "${BL}:EU2408:PROTM:RBV") {
field(DESC, "Program time remaining Readback")
field(INP, "@asyn(Eurotherm_EMODBUS_1_1_Rd_PROTM,0,1000)MODBUS_DATA")
field(ASLO, "0.1")
OBS2: full IOC initialization log:
#!/usr/local/epics-nfs/apps/Eurotherm2408/1.0/bin/linux-x86_64/Eurotherm
< /usr/local/epics-nfs/apps/Eurotherm2408/1.0/iocBoot/iocEurotherm2408/envPaths
epicsEnvSet("IOC","iocEurotherm2408")
epicsEnvSet("TOP","/usr/local/epics-nfs/apps/Eurotherm2408/1.0")
epicsEnvSet("NFS","/usr/local/epics-nfs")
epicsEnvSet("SUPPORT","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support")
epicsEnvSet("ASYN","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/asyn-R4-33")
epicsEnvSet("STREAM","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/stream-R2-7-7c")
epicsEnvSet("MODBUS","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/modbus-R2-11")
epicsEnvSet("EPICS_BASE","/usr/local/epics-nfs/base/R3.15.6")
epicsEnvSet("ALIVE","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/alive-R1-1-0")
epicsEnvSet("AUTOSAVE","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/autosave-R5-9")
epicsEnvSet("BUSY","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/busy-R1-7")
epicsEnvSet("CALC","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/calc-R3-7-1")
epicsEnvSet("CAMAC","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/camac-R2-7-1")
epicsEnvSet("CAPUTRECORDER","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/caputRecorder-R1-7-1")
epicsEnvSet("DAC128V","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/dac128V-R2-9")
epicsEnvSet("DELAYGEN","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/delaygen-R1-2-0")
epicsEnvSet("DXP","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/dxp-R5-0")
epicsEnvSet("DXPSITORO","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/dxpSITORO-R1-1")
epicsEnvSet("DEVIOCSTATS","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/iocStats-3-1-15")
epicsEnvSet("IP","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/ip-R2-19-1")
epicsEnvSet("IPAC","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/ipac-2-15")
epicsEnvSet("IP330","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/ip330-R2-9")
epicsEnvSet("IPUNIDIG","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/ipUnidig-R2-11")
epicsEnvSet("LOVE","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/love-R3-2-6")
epicsEnvSet("LUA","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/lua-R1-2-2")
epicsEnvSet("MCA","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/mca-R7-7")
epicsEnvSet("MEASCOMP","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/measComp-R2-1")
epicsEnvSet("MODBUS_2_10_1","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/modbus-R2-10-1")
epicsEnvSet("MOTOR","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/motor-R6-10-1")
epicsEnvSet("OPTICS","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/optics-R2-13-1")
epicsEnvSet("QUADEM","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/quadEM-R9-1")
epicsEnvSet("SOFTGLUE","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/softGlue-R2-8-1")
epicsEnvSet("SOFTGLUEZYNQ","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/softGlueZynq-R2-0-1")
epicsEnvSet("SSCAN","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/sscan-R2-11-1")
epicsEnvSet("STD","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/std-R3-5")
epicsEnvSet("VAC","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/vac-R1-7")
epicsEnvSet("VME","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/vme-R2-9")
epicsEnvSet("YOKOGAWA_DAS","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/Yokogawa_DAS-R1-0-0")
epicsEnvSet("XXX","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/xxx-R6-0")
epicsEnvSet("AREA_DETECTOR","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/areaDetector-R3-3-1")
epicsEnvSet("ADCORE","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/areaDetector-R3-3-1/ADCore")
epicsEnvSet("ADSUPPORT","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/areaDetector-R3-3-1/ADSupport")
epicsEnvSet("ADSIMDETECTOR","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/areaDetector-R3-3-1/ADSimDetector")
epicsEnvSet("SNCSEQ","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/seq-2-2-5")
epicsEnvSet("ALLEN_BRADLEY","/usr/local/epics-nfs/modules/R3.15.6/synApps/R6.0/support/allenBradley-2-3")
epicsEnvSet("BL","PNR")
# Configuração da linha de luz
< /usr/local/epics-nfs/apps/Eurotherm2408/1.0/iocBoot/iocEurotherm2408/Eurotherm.config
epicsEnvSet("SERIAL_PORT","COM10")
epicsEnvSet("E_SHM","eurotherm")
epicsEnvSet("BAUD","9600")
epicsEnvSet("MBUS_SL_ADDR",1)
epicsEnvSet("MBUS_READ",3)
epicsEnvSet("MBUS_WRITE",6)
epicsEnvSet("MBUS_POLL",1000)
epicsEnvSet("STREAM_PROTOCOL_PATH","/usr/local/epics-nfs/apps/Eurotherm2408/1.0/db")
cd /usr/local/epics-nfs/apps/Eurotherm2408/1.0
## Register all support components
dbLoadDatabase "dbd/Eurotherm.dbd"
Eurotherm_registerRecordDeviceDriver pdbbase
## Configured by http://cars9.uchicago.edu/software/epics/modbusDoc.html
## Parameters to ModBus on /dev/ttyUSB0
## used to USB
#drvAsynSerialPortConfigure("EMODBUS","10.20.41.43:4001",0,0,0)
drvAsynIPPortConfigure("EMODBUS","10.20.41.43:4002",0,0,1)
# Set up ASYN HYPPIE ports
# pxiCreateSM(asyn, shared memory name)
# drvasynPXIConfig(port, COM port, shared memory name, serial type)
#asynSetOption("EMODBUS", 0, "${BAUD}", "9600")
#asynSetOption("EMODBUS", 0, "bits", "8")
#asynSetOption("EMODBUS", 0, "parity", "none")
#asynSetOption("EMODBUS", 0, "stop", "1")
## Configure
modbusInterposeConfig("EMODBUS",1,3000,0)
# drvModbusAsynConfigure(portName,      => create a name
#                       tcpPortName,    => defined before
#                       slaveAddress,   => defined on equipament
#                       modbusFunction, => 3 : Read Holding Register (16-bit)
#                       modbusStartAddress, => adress of register
#                       modbusLength,  => the length of data segment
#                       dataType,  => default data type
#                       pollMsec,
#                       plcType);     => Equipament name, not used
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Rd_ATUNE", "EMODBUS", 1,3, 3072, 6, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Wr_ATUNE", "EMODBUS", 1,6, 3072, 6,0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_PV", "EMODBUS", 1,3, 1, 3,0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_PV", "EMODBUS", 1, 6, 1, 3, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_WSP", "EMODBUS", 1,3, 5, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_RR", "EMODBUS", 1, 3, 35, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_RR", "EMODBUS", 1, 6, 35, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_MAN", "EMODBUS", 1, 3, 273, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_MAN", "EMODBUS", 1, 6, 273, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_PID", "EMODBUS", 1, 3, 351, 3, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_PID", "EMODBUS", 1, 6, 351, 3, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_P", "EMODBUS", 1, 3, 6, 3, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_I", "EMODBUS", 1, 3, 8, 3, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_D", "EMODBUS", 1, 3, 9, 3, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_P", "EMODBUS", 1, 6, 6, 3, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_I", "EMODBUS", 1, 6, 8, 3, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_D", "EMODBUS", 1, 6, 9, 3, 0, 1000, "");
#####ADDED FOR DEBUG. DELETE LATER###
asynSetTraceIOMask Eurotherm_EMODBUS_1_1_Wr_P -1 4
asynSetTraceMask Eurotherm_EMODBUS_1_1_Wr_P -1 9
asynSetTraceIOMask Eurotherm_EMODBUS_1_1_Wr_I -1 4
asynSetTraceMask Eurotherm_EMODBUS_1_1_Wr_I -1 9
#Commands added 19/04/2022 by Marco Montevechi, Junior Cintra and Jo  o Pedro Burle Ishida
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Rd_PROG", "EMODBUS", 1, 3, 22, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Wr_PROG", "EMODBUS", 1, 6, 22, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_PSP", "EMODBUS", 1, 3, 163, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_PSP", "EMODBUS", 1, 6, 163, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Rd_CYC", "EMODBUS", 1, 3, 59, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Wr_CYC", "EMODBUS", 1, 6, 59, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Rd_SEG", "EMODBUS", 1, 3, 56, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Wr_SEG", "EMODBUS", 1, 6, 56, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Rd_STYP", "EMODBUS", 1, 3, 29, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Wr_STYP", "EMODBUS", 1, 6, 29, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Rd_STAT", "EMODBUS", 1, 3, 23, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Wr_STAT", "EMODBUS", 1, 6, 23, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_TGT", "EMODBUS", 1, 3, 160, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_TGT", "EMODBUS", 1, 6, 160, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_SEGT", "EMODBUS", 1, 3, 36, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_SEGT", "EMODBUS", 1, 6, 36, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_RATE", "EMODBUS", 1, 3, 161, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_RATE", "EMODBUS", 1, 6, 161, 1, 0, 1000, "");
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Rd_PROTM", "EMODBUS", 1, 3, 58, 1, 0, 1000, "");
## Load record instances
dbLoadRecords("db/dbEurotherm2408.db", "BL=PNR")
#dbLoadRecords("db/xxx.db","user=gabrielfedelHost")
cd /usr/local/epics-nfs/apps/Eurotherm2408/1.0/iocBoot/iocEurotherm2408
iocInit
Starting iocInit
## EPICS R3.15.6
2022/04/25 11:51:29.912 drvModbusAsyn::readInt32 port Eurotherm_EMODBUS_1_1_Wr_P function=0x6, offset=00, value=0x5dc
2022/04/25 11:51:29.912 drvModbusAsyn::readInt32 port Eurotherm_EMODBUS_1_1_Wr_I function=0x6, offset=00, value=0x1c
2022/04/25 11:51:30.415 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P WRITE_SINGLE_REGISTER address=06 value=0x3a98
2022/04/25 11:51:30.547 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=3
2022/04/25 11:51:30.547 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
2022/04/25 11:53:46.926 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P WRITE_SINGLE_REGISTER address=06 value=0x3e80
2022/04/25 11:53:46.978 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=3
2022/04/25 11:53:46.978 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
2022/04/25 11:53:50.348 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P WRITE_SINGLE_REGISTER address=06 value=0x640
2022/04/25 11:53:50.385 drvModbusAsyn::writeInt32 port Eurotherm_EMODBUS_1_1_Wr_P function=0x6, modbusAddress=06, buffer[0]=0x640, bufferLen=1
Sent: 20 April 2022 12:50
To: Marco A. Barra Montevechi Filho <[email protected]>
Cc: Junior Cintra Mauricio <[email protected]>; João Pedro Burle Ishida <[email protected]>; [email protected] <[email protected]>
Subject: RE: drvModbusAsynConfigure exception 3 when ASLO and PREC fields of PV are changed
Hi Marco,
Your explanation of how this works is clear, the implied decimal point means that the ASLO of 0.1 or 0.01 is indeed required.
So caputting into :P variable makes the epics terminal print:
epics> 2022/04/20 08:40:18.579 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P WRITE_SINGLE_REGISTER address=06 value=0x3e80
2022/04/20 08:40:18.641 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=3
2022/04/20 08:40:18.641 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
That is a very useful diagnostic message.  It appears to me that the Modbus driver completed a valid WRITE_SINGLE_REGISTER operation to address 6.  The data it wrote was 0x3e80 = 16000 decimal.  If the implied decimal point is 2 digits that would be 160.00.   For some reason the Eurotherm is returning Modbus exception 3 when that value is written.  Is that an invalid setting for the P parameter?  If it is returning exception 3 because 160.00 is an invalid setting then they are violating the Modbus spec, because the spec says exception 3 should NOT be used to signal an invalid setting, it is only used to indicate an invalid Modbus message.  Are there values you can write to P that do not generate the exception?
Mark
From: Marco A. Barra Montevechi Filho <[email protected]>
Sent: Wednesday, April 20, 2022 9:33 AM
Hi, Mark! I corrected the asynSetTraceIOMask and asynSetTraceMask errors you pointed, thanks. About the error in the
dbLoadRecords("db/dbEurotherm2408.db", "BL=PNR"), it was a typo in one of the records, its also corrected.
I found the communication manual of the equipment to compare the accepted integer values and according to it:
"The protocol is also limited to integer communication only. Series 2000 instruments allow the user to configure
either integer or full resolution. In integer mode all parameters will be rounded to the nearest integer value,
whereas in full resolution mode the decimal point position will be implied so that 100.01 would be transmitted
as 10001."
And indeed caputting <PVPREFFIX>:P to a value such as 15001 makes caget <PVPREFFIX>:P:RBV return 150.01. So i figure making
the <PVPREFFIX>:P.ASLO field a non-integer is simply a logic error(?) that i intend to remove.
At the end of this email i append the IOC initialization log with typos corrected and TraceMasks added just to be coherent.
I also added
and
because i know this function worked well with the <PVPREFIX>:I variable.
Finally, about the PV being processed in initialization even without PINI field, i believe (although i am not sure) that it
is caused by the other records that reference the PV:
        field(ZRVL, "1")
        field(ONVL, "2")
        field(RVAL, "4")
        field(PINI, "YES")
So i think ${BL}:EU2408:PREC triggers all the process. Thanks so much for your attention! If this logic error
is indeed what is causing trouble, then i think the problem is solved.
Best regards,
Marco
OBS - IOC initialization log:
## used to USB
## Configure
#                       pollMsec,
iocInit
Starting iocInit
## EPICS R3.15.6
2022/04/20 08:37:33.100 drvModbusAsyn::readInt32 port Eurotherm_EMODBUS_1_1_Wr_P function=0x6, offset=00, value=0x5dc
2022/04/20 08:37:33.100 drvModbusAsyn::readInt32 port Eurotherm_EMODBUS_1_1_Wr_I function=0x6, offset=00, value=0x1c
2022/04/20 08:37:33.602 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P WRITE_SINGLE_REGISTER address=06 value=0x3a98
2022/04/20 08:37:33.688 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=3
2022/04/20 08:37:33.688 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
epics>
2022/04/20 08:40:47.496 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P WRITE_SINGLE_REGISTER address=06 value=0x3a98
2022/04/20 08:40:47.559 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=3
2022/04/20 08:40:47.559 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
and caputting into :I variable makes the epics terminal print:
2022/04/20 08:41:15.370 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_I WRITE_SINGLE_REGISTER address=010 value=0x1d
2022/04/20 08:41:15.406 drvModbusAsyn::writeInt32 port Eurotherm_EMODBUS_1_1_Wr_I function=0x6, modbusAddress=010, buffer[0]=0x1d, bufferLen=1
2022/04/20 08:41:20.447 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_I WRITE_SINGLE_REGISTER address=010 value=0x1c
2022/04/20 08:41:20.491 drvModbusAsyn::writeInt32 port Eurotherm_EMODBUS_1_1_Wr_I function=0x6, modbusAddress=010, buffer[0]=0x1c, bufferLen=1
Sent: 19 April 2022 16:26
Hi Marco,
Ø  Thats what seems weird to me: since the error only happens when we change the precision and ASLO, and since the exception indicates an incorrect command, can i just assume that the equipment is made to only accept commands that write the P parameter with a certain precision? In a way that when the precision is changed the equipment refuses to accept the command?
No, it cannot be the precision.  You are not sending ASCII characters with decimal digits over Modbus, you are sending 16-bit binary integers.  So the PREC field should not matter.  However the ASLO field controls the conversion from engineering units to 16-bit integer so it can change the data you are sending.
You are getting these errors when you boot:
asynSetTraceIOMask Eurotherm_EMODBUS_1_1_Wr_P -1 HEX
PNR-Eurotherm2408-B-Eurotherm01.cmd line 73: Illegal integer 'HEX'
asynSetTraceMask Eurotherm_EMODBUS_1_1_Wr_P -1 ERROR|DRIVER
PNR-Eurotherm2408-B-Eurotherm01.cmd line 75: Illegal integer 'ERROR|DRIVER'
That is because you are running asyn R4-33 and the enhancement to allow symbolic names in the asynSetTrace commands was added in R4-35 in 2019.  With this old version of asyn you need to change these commands to:
There is also an error when loading your database:
Error: syntax error
 at or before "Readback" in file "db/dbEurotherm2408.db" line 423
You should fix that.  It could even be the source of your problems, since I don’t know what records are defined after line 423.
It appears that the ao record is processing at iocInit, but the record does not have PINI=YES.  I don’t understand that.
Mark
Sent: Tuesday, April 19, 2022 2:00 PM
Hello, Mark. Thank for the constant help!
Im sorry for forgetting the complete message. The error message is:
2022/04/19 15:27:21.537 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=3
2022/04/19 15:27:21.537 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
epics>
I append the complete IOC initialization log in the end of this email. Also, i noticed something else that seems important: in the .db file, there is the following comment right next to the :P variable:
However, address 351 is not even mentioned in Eurotherm modbus communication manual and setting
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_P", "EMODBUS", 1, 6, 351, 3, 0, 1000, "");
instead of
results in
2022/04/19 15:54:43.225 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=2
2022/04/19 15:54:43.226 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
epics>
Which i think means that this address is not supposed to be accessed.
Best regards,
Marco
## used to USB
## Configure
#                       pollMsec,
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_0_Rd_ATUNE", "EMODBUS", 1,3, 3072, 6,0, 1000, "");
#####ADDED FOR DEBUG. ###
Error: syntax error
iocInit
Starting iocInit
## EPICS R3.15.6
2022/04/19 15:47:39.215 drvModbusAsyn::doModbusIO port Eurotherm_EMODBUS_1_1_Wr_P Modbus exception=3
2022/04/19 15:47:39.215 PNR:EU2408:P devAsynInt32::processCallbackOutput process error
epics>
Sent: 19 April 2022 15:12
Hi Marco,
This is an ao record and one of the links is P.ASLO.  This means that depending on whether the link is broken the actual integer value being written to the device could change, since ASLO affects that.
According to page 48 of the Modbus reference document
https://epics-modbus.readthedocs.io/en/latest/_downloads/c210fb586108fe21da5a09d202ab86d1/Modbus_Application_Protocol_V1_1b.pdf
Modbus exception 3 is “ILLEGAL DATA VALUE”.  This means:
A value contained in the query data field is not an allowable value for server (or slave). This indicates a fault in the structure of the remainder of a complex request, such as that the implied length is incorrect. It specifically does NOT mean that a data item submitted for storage in a register has a value outside the expectation of the application program, since the MODBUS protocol is unaware of the significance of any particular value of any particular register.
So according to the specification exception 3 should only be returned when the command syntax is wrong, not if the data value is outside the allowed range.  However, it is always possible that Eurotherm has not following the spec, and it is returning exception 3 for a data value outside the allowed range.
Please send the complete error message when you get the exception.
It may also be helpful to put the following 2 commands in your startup script:
That will show the Modbus messages sent to and received from the device.
Mark
From: Tech-talk <[email protected]> On Behalf Of Marco A. Barra Montevechi Filho via Tech-talk
Sent: Tuesday, April 19, 2022 11:01 AM
To: [email protected]
Subject: drvModbusAsynConfigure exception 3 when ASLO and PREC fields of PV are changed
Hello all and good evening.
We are working with a modbus IOC, the one i asked about compiling errors here previously and Mark answered about removing modbus.dbd and leaving only modbusSupport.dbd to make it work.
The IOC has several modbus functions defined in its st.cmd file like:
drvModbusAsynConfigure("Eurotherm_EMODBUS_1_1_Wr_P", "EMODBUS", ${MBUS_SL_ADDR}, ${MBUS_WRITE}, 6, 3, 0, ${MBUS_POLL}, "");
where MBUS_SL_ADDR=1, MBUS_WRITE=6 and MODBUS_POLL=1000.
EMODBUS was defined in drvAsynIPPortConfigure("EMODBUS",{EUROTHERM_IP},0,0,1)
The above modbus function is used by a PV:
record(ao, "${BL}:EU2408:P:SOMETHING") {
 and it works fine if the PV name doesnt end stop in ":P". If the PV name is only "${BL}:EU2408:P", then we get modbus exception 3 when initializing the IOC and the PV doesnt work.
I suppose this happens because some other PV has a link to it and the link breaks when the name is changed. I dont know if there could be any cause to this behaviour.
The only PVs we found refering to "${BL}:EU2408:P:SOMETHING" PV are:
        field(OUTF, "${BL}:EU2408:P.ASLO")   #HERE
and
        field(OUTF, "${BL}:EU2408:P.PREC PP")    ######HERE
so i suppose altering PVs PREC and ASLO alters the correct modbus function needed to access the parameter, but this makes no sense to me since the parameter stored in the equipment should still be the same.
Does someone know what am i missing?
Thanks in advance
Marco
Aviso Legal: Esta mensagem e seus anexos podem conter informações confidenciais e/ou de uso restrito. Observe atentamente seu conteúdo e considere eventual consulta ao remetente antes de copiá-la, divulgá-la ou distribuí-la. Se você recebeu esta mensagem por engano, por favor avise o remetente e apague-a imediatamente.
Disclaimer: This email and its attachments may contain confidential and/or privileged information. Observe its content carefully and consider possible querying to the sender before copying, disclosing or distributing it. If you have received this email by mistake, please notify the sender and delete it immediately.
RE: drvModbusAsynConfigure exception 3 when ASLO and PREC fields of PV are changed Mark Rivers via Tech-talk
References:
drvModbusAsynConfigure exception 3 when ASLO and PREC fields of PV are changed Marco A. Barra Montevechi Filho via Tech-talk
Re: drvModbusAsynConfigure exception 3 when ASLO and PREC fields of PV are changed Marco A. Barra Montevechi Filho via Tech-talk
Navigate by Date:
Prev: Re: Recsync: RecCeiver Server announcement contains Broadcast address instead of server ip address Michael Davidsaver via Tech-talk
Next: Eiger Stream API problems Miceli, Antonino via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  <2022>  2023  2024  2025  2026
Navigate by Thread:
Prev: Re: drvModbusAsynConfigure exception 3 when ASLO and PREC fields of PV are changed Marco A. Barra Montevechi Filho via Tech-talk
Next: RE: drvModbusAsynConfigure exception 3 when ASLO and PREC fields of PV are changed Mark Rivers via Tech-talk