Hej again,
while thinking about it:
It could be that we have another race condition here:
The call to
pmacSetCoordStepsPerUnit("$(PPMAC_CS1_PORT)", 1, 1000)
(Sometimes with problems)
vs
pmacSetCoordStepsPerUnit("$(PPMAC_CS1_PORT)", 1, 10000)
(Solved the problem)
In this case the call
pmacSetCoordStepsPerUnit()
needs to make it's way into the PMAC, and back into the IOC,
where the poller is picking it up.
Then it could be interesting to see what asynReport says before and
after pmacSetCoordStepsPerUnit()
In this case I would not expect undedined here:
Parameter 8 type=asynFloat64, name=MOTOR_POSITION, value is undefined
Parameter 9 type=asynFloat64, name=MOTOR_ENCODER_POSITION, value is
... but rather a value which is off by factor 10, as you reported.
The good news:
The epicsThreadSleep() just before the iocInit() should help
here as well.
On 2022-09-30 17:35, Marco A. Barra Montevechi Filho wrote:
Thanks, we will test with epicsThreadSleep and asynReport, then.
It makes sense that its a concurrency situation since its the first time
that we observe the situation in this kind of IOC and this IOC's .cmd
file in particular seems to execute much less functions between the call
to pmacSetCoordStepsPerUnit, dbLoadRecords and iocInit than other cmd's
that use this same Pmac version we have here. So maybe this concurrency
was being hidden until now.
Will report test results in this same thread later.
Cheers,
Marco
*Sent:* 30 September 2022 10:10
*To:* Marco A. Barra Montevechi Filho <[email protected]>
*Cc:* [email protected] <[email protected]>; Augusto Yoshio
Horita <[email protected]>; SOL <[email protected]>
*Subject:* Re: Suspicious behavior of Pmac 2-5-16 IOC. .RBV and .VAL
showing wrong values.
Hej Marco,
This is a tricky thing.
I have heard about those “weird values” at startup before,
and we had them on a PMAC once.
After a lot of digging, I found that there is a possible race condition.
And did changes to overcome them, mainly in motorRecord.cc
If my theory is right, it may help, if you put a
epicsThreadSleep 4
just before iocInit, and then the driver has more time to talk to the
controller and read the motor position, before the record needs it.
It could even be the case, the the asynReport delays execution
similar to the epicsThreadSleep, so that the problem is worked around.
Or it could be a complete different problem.
Without having a hardware to play with, it is hard to tell,
and easy to speculate.
The “sometimes” in your report indicates that there is something
shaky, so lets hope that we can figure out, what it is.
BR
/Torsten
On 30 Sep 2022, at 14:43, Marco A. Barra Montevechi Filho <[email protected]> wrote:
Hy, Torsten! Thanks for the answer!
Although I have time to try this, the beamline that uses these particular motors does not, at least not today. We have never observed this behavior in any motor before, so i believe it would be unproductive to test this elsewhere.
I believe next week i might have some free beamline time to test this. Let me see if i understood what you meant:
If the race condition messes with us and causes this weird behavior, then putting asynReport 10 <PORTNAME> will result in messages such as
"MOTOR_POSITION, value is undefined" when i get wrong values (e.g.: multiplied by 10, in my case), and will not result in these messages when i get my values right.
Is that it? If yes, i can make this test next week and report here.
Marco
Sent: 30 September 2022 02:56
To: Marco A. Barra Montevechi Filho <[email protected]>; [email protected] <[email protected]>
Cc: Augusto Yoshio Horita <[email protected]>
Subject: Re: Suspicious behavior of Pmac 2-5-16 IOC. .RBV and .VAL showing wrong values.
Hej Marco,
There is a possible race condition, when the IOC starts:
The record tries to read the position of the motor
from the driver, but the driver has not yet been able
to fully talk to the controller.
If I run
asynReport 10 MCU1
just before iocInit in st.cmd, I see things like this:
undefined
(and may be have a look at
MOTOR_REC_RESOLUTION as well)
(You asynReport needs probably another name)
Before we dig into a possible solution:
Do you have time to try this ?
BR
/Torsten
On 2022-09-29 19:43, Marco A. Barra Montevechi Filho via Tech-talk wrote:
> Hello all. We were having problems with Pmac 2-5-16 here at LNLS. The
> problem was solved by Augusto Horita (in copy), but the behavior was
> weird and we though maybe someone here knows why it is like that or
> maybe reporting it in tech-talk would be useful for other people.
> The IOC was compiled with EPICS base 3.15.6.
> The particular instance that we were having trouble with had a set of
> axis in the PVs such as:
> BL:H:PB02:CS1:m1
> the axis was configured with
> and its MRES was set to 10E-3.
> When initialized, the IOC sometimes showed the right values for .RBV and
> .VAL fields, but sometimes showed values 10 times bigger than what
> should be. Sometimes the *10 factor was only in .RBV, sometimes only in
> .VAL and sometimes in both.
> Augusto suspected this was due to failure in pmacSetCoordStepsPerUnit
> since the default scale factor is 10000 (ten times bigger than what we
> were using). So we suspected that the function was failing for whatever
> reason and defaulting the scale factor to 10000 while MRES remained in
> 10E-3. Indeed, changing MRES to 10E-4 and
> to
> Solved the problem.
> In the middle of the debug process, we struggled to find any error
> message about the suspected failure in pmacSetCoordStepsPerUnit.
> Is this absence of error message intentional? Is there a particular
> debug method we should have used?
> Has this been reported before?
> Thanks for the attention. Best regards,
> Marco
- Re: Suspicious behavior of Pmac 2-5-16 IOC. .RBV and .VAL showing wrong values. Marco A. Barra Montevechi Filho via Tech-talk
- Suspicious behavior of Pmac 2-5-16 IOC. .RBV and .VAL showing wrong values. Marco A. Barra Montevechi Filho via Tech-talk
- Re: Suspicious behavior of Pmac 2-5-16 IOC. .RBV and .VAL showing wrong values. Torsten Bögershausen via Tech-talk
RE: EPICS mrfioc2 and new mtca card EVRTM-300 GAGET Alexis via Tech-talk
<2022>
2025
2026
<2022>
2025
2026