1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <20232024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <20232024  2025  2026
Subject: RE: pasynOctetSyncIO error reading image status=4
To: "Sintschuk, Michael" <[email protected]>, tech-talk <[email protected]>
Date: Fri, 3 Mar 2023 18:38:56 +0000
Hi Michael,
If you look at your previous message you see things like this:
2023/03/02 16:51:48.603 PSL:getImage: error reading image, status=4, dataLen=12117504, nCopied=12117503, maxRead=1, nRead=1959
2023/03/02 16:51:55.552 PSL:getImage: error reading image, status=1, dataLen=12117504, nCopied=8333289, maxRead=2048, nRead=0
2023/03/02 16:52:05.499 PSL:getImage: error reading image, status=4, dataLen=12117504, nCopied=12117502, maxRead=2, nRead=1603
2023/03/02 16:52:10.847 PSL:getImage: error reading image, status=4, dataLen=12117504, nCopied=12117502, maxRead=2, nRead=51
I think that dataLen is the expected number of bytes to received, and nCopied is the number actually received so far.  Note that in 3 of the cases it is just 1 or 2 bytes short.  maxRead is the number of bytes it is trying to read.  But it then gets a broken connection.
Sent: Friday, March 3, 2023 11:59 AM
To: Mark Rivers <[email protected]>; tech-talk <[email protected]>
Subject: AW: pasynOctetSyncIO error reading image status=4
Hi Mark,
thanks for the explanation. With enabling the asynTraces it is visible that sometimes indeed the connection crashes. Here are the last output lines when an image was acquired without an error (and the exposure time was then set to 2.5s):
2023/03/03 16:22:16.650 hzb1.exp.helmholtz-berlin.de:50000 read 952
\305\000\310\000\304\000\303\000\306\000\312\000\273\000\271\000\273\000\313\000\277\000\303\000\306\000\307\000\303\000\312\000\270\000\304\000\314\000\300\000\315\000\304\000\272\000\324\000\311\000\274\000\311\000\320\000\307\000\307\000\323\000\305\000\275\000\307\000\302\000\303\000\303\000\312\000\307\000\273\000
2023/03/03 16:22:16.650 hzb1.exp.helmholtz-berlin.de:50000 read 1536
\305\000\301\000\304\000\277\000\314\000\301\000\322\000\304\000\316\000\314\000\312\000\304\000\276\000\314\000\273\000\316\000\276\000\307\000\300\000\276\000\303\000\304\000\272\000\261\000\311\000\275\000\307\000\301\000\321\000\276\000\310\000\310\000\307\000\271\000\324\000\277\000\334\000\301\000\313\000\312\000
2023/03/03 16:22:23.727 hzb1.exp.helmholtz-berlin.de:50000 write 15
SetExpoMS;2500\n
And here are the last output lines when an image was acquired with the described error:
2023/03/03 16:22:59.989 hzb1.exp.helmholtz-berlin.de:50000 read 952
\304\000\313\000\300\000\275\000\310\000\306\000\310\000\302\000\306\000\302\000\310\000\314\000\300\000\270\000\311\000\317\000\273\000\311\000\305\000\276\000\305\000\316\000\304\000\276\000\304\000\305\000\301\000\312\000\277\000\303\000\322\000\300\000\306\000\305\000\304\000\303\000\312\000\313\000\276\000\326\000
2023/03/03 16:22:59.989 hzb1.exp.helmholtz-berlin.de:50000 read 1536
\303\000\277\000\322\000\310\000\304\000\306\000\301\000\302\000\273\000\301\000\313\000\312\000\313\000\312\000\304\000\300\000\310\000\263\000\315\000\312\000\265\000\317\000\312\000\322\000\305\000\315\000\301\000\311\000\276\000\325\000\302\000\315\000\316\000\275\000\267\000\306\000\303\000\312\000\305\000\314\000
2023/03/03 16:23:00.004 hzb1.exp.helmholtz-berlin.de:50000 read 0
In that case „read 0“ always appears.
Here is the last output when setting “asynSetTraceMask("PSLServer",0,255)”, to show everything:
2023/03/03 16:17:32.587 hzb1.exp.helmholtz-berlin.de:50000 read.
2023/03/03 16:17:32.587 hzb1.exp.helmholtz-berlin.de:50000 read 952
\315\000\304\000\300\000\310\000\271\000\310\000\306\000\315\000\306\000\305\000\325\000\310\000\312\000\312\000\307\000\311\000\302\000\313\000\303\000\266\000\316\000\271\000\302\000\313\000\310\000\313\000\307\000\311\000\302\000\315\000\307\000\311\000\300\000\303\000\305\000\310\000\303\000\277\000\307\000\272\000
2023/03/03 16:17:32.587 PSLServer read 952 bytes eom=0
2023/03/03 16:17:32.587 asynOctetSyncIO read:
\000\313\000\306\000\320\000\301\000\267\000\306\000\312\000\313\000\305\000\303\000\301\000\305\000\275\000\323\000\325\000\317\000\307\000\274\000\315\000\303\000\313\000\301\000\305\000\312\000\275\000\300\000\312\000\304\000\313\000\302\000\303\000\264\000\303\000\304\000\301\000\301\000\276\000\303\000\310\000\305
2023/03/03 16:17:32.587 PSLServer queueUnlockPort
2023/03/03 16:17:32.587 PSLServer asynManager::queueUnlockPort waiting for event
2023/03/03 16:17:32.587 PSLServer queueUnlockPort unlock mutex 0x7f34ac000c90 complete.
2023/03/03 16:17:32.587 PSLServer asynManager::queueLockPort locking port
2023/03/03 16:17:32.587 PSLServer asynManager::queueLockPort taking mutex 0x7f34ac000c90
2023/03/03 16:17:32.587 PSLServer asynManager::queueLockPort queueing request
2023/03/03 16:17:32.587 PSLServer addr -1 queueRequest priority 0 not lockHolder
2023/03/03 16:17:32.587 PSLServer schedule queueRequest timeout in 2.000000 seconds
2023/03/03 16:17:32.587 PSLServer asynManager::queueLockPort waiting for event
2023/03/03 16:17:32.587 asynManager::portThread port=PSLServer callback
2023/03/03 16:17:32.587 PSLServer asynManager::queueLockPortCallback signaling begin event
2023/03/03 16:17:32.587 PSLServer asynManager::queueLockPortCallback waiting for mutex from queueUnlockPort
2023/03/03 16:17:32.587 PSLServer asynManager::queueLockPort got event from callback
2023/03/03 16:17:32.587 hzb1.exp.helmholtz-berlin.de:50000 read 1536
\267\000\312\000\301\000\310\000\300\000\315\000\305\000\310\000\314\000\266\000\303\000\301\000\306\000\271\000\274\000\315\000\303\000\317\000\277\000\275\000\304\000\277\000\271\000\303\000\312\000\304\000\322\000\314\000\313\000\304\000\303\000\273\000\315\000\316\000\306\000\300\000\302\000\303\000\271\000\311\000
2023/03/03 16:17:32.587 PSLServer read 1536 bytes eom=0
2023/03/03 16:17:32.605 hzb1.exp.helmholtz-berlin.de:50000 read 0
2023/03/03 16:17:32.605 Closing hzb1.exp.helmholtz-berlin.de:50000 connection (fd 3): Read from broken connection
2023/03/03 16:17:32.605 PSLServer read 0 bytes eom=4
2023/03/03 16:17:32.605 asynOctetSyncIO read:
\000\303\000\314\000\311\000\305\000\304\000\304\000\317\000\303\000\307\000\300\000\317\000\275\000\302\000\304\000\310\000\300\000\303\000\313\000\305\000\311\000\331\000\302\000\300\000\307\000\311\000\272\000\300\000\307\000\304\000\305\000\300\000\301\000\302\000\307\000\303\000\310\000\310\000\307\000\276\000\276
2023/03/03 16:17:32.605 PSLServer queueUnlockPort
2023/03/03 16:17:32.605 PSLServer asynManager::queueUnlockPort waiting for event
2023/03/03 16:17:32.605 PSLServer queueUnlockPort unlock mutex 0x7f34ac000c90 complete.
2023/03/03 16:17:32.605 PSLServer asynManager::queueLockPort locking port
2023/03/03 16:17:32.605 PSLServer asynManager::queueLockPort taking mutex 0x7f34ac000c90
2023/03/03 16:17:32.605 PSLServer asynManager::queueLockPort queueing request
2023/03/03 16:17:32.610 PSLServer addr -1 queueRequest priority 3 not lockHolder
2023/03/03 16:17:32.610 asynManager connect queueCallback port:PSLServer
2023/03/03 16:17:32.610 Attempting to connect to hzb1.exp.helmholtz-berlin.de:50000  reason:0  fd:-1
2023/03/03 16:17:32.611 Opened connection OK to hzb1.exp.helmholtz-berlin.de:50000
But for me there is no additional info in that output. Only that the connection is opened again after it broke…
Today I tried to get rid of that error by putting some epicsThreadSleeps in different code-places before actually reading the image but without luck. Next week I try to vary the size of “fromServer_[MAX_MESSAGE_SIZE]”.
But if there are some hints from you or someone else, I’m happy to try them!
Michael
Von: Mark Rivers <[email protected]>
Gesendet: Donnerstag, 2. März 2023 18:43
An: Sintschuk, Michael <[email protected]>; tech-talk <[email protected]>
Betreff: RE: pasynOctetSyncIO error reading image status=4
SICHERHEITSHINWEIS: Diese E-Mail wurde von außerhalb an die BAM gesendet. Bitte klicken Sie nicht auf Links oder öffnen Anhänge, bevor Sie nicht den Absender verifiziert haben und sicher sind, dass der Inhalt vertrauenswürdig ist.
This message was sent from outside of BAM. Please do not click links or open attachments unless you recognize the sender and know the content is trustworthy.
Hi Michael,
The message is printed here:
https://github.com/areaDetector/ADPSL/blob/b1924604516eca006cab8a63b7c9fc094df35fe2/pslApp/src/PSL.cpp#L589
The status is the return from pasynOctetSyncIO->read in this line:
https://github.com/areaDetector/ADPSL/blob/b1924604516eca006cab8a63b7c9fc094df35fe2/pslApp/src/PSL.cpp#L585
pasynOctetSyncIO->read is here, and it just returns the status from pasynOctet->read().
https://github.com/epics-modules/asyn/blob/3434727d5a1ba090bb423b4c7395fdb77a57eebd/asyn/interfaces/asynOctetSyncIO.c#L218
The asynStatus enums are defined here:
https://github.com/epics-modules/asyn/blob/3434727d5a1ba090bb423b4c7395fdb77a57eebd/asyn/asynDriver/asynDriver.h#L48
status=4 thus means asynDisconnected.  That seems to indicated that the socket between the IOC and the PSL server has disconnected.
You can turn on asynTraceIODriver on that socket and see exactly what is being sent and received.  You can uncomment and change these lines in your st.cmd:
asynSetTraceIOMask("PSLServer",0,ESCAPE)
asynSetTraceMask("PSLServer",0,ERROR|DRIVER)
asynSetTraceFile("PSLServer", 0, "PSLServer.out")
The last line will send the output to a file, which may be more convenient.  You may also need to add this line:
asynSetTraceIOTruncateSize(“PSLServer”, 0, 10000000) so that you do not limit the output to just 80 bytes.
From: Tech-talk <[email protected]> On Behalf Of Sintschuk, Michael via Tech-talk
Sent: Thursday, March 2, 2023 11:20 AM
To: tech-talk <[email protected]>
Subject: pasynOctetSyncIO error reading image status=4
Hi all,
like announced in this tech-talk:
https://epics.anl.gov/tech-talk/2021/msg02173.php
I’m now trying to setup a FDS camera from Photonic Science with the ADPSL module. After adding some slightly changes to the Keywords that are send to the PSViewer-server or received from it, I can communicate with the camera without any IOC-crashes. I forked the ADPSL-module here:
https://github.com/MichaS-git/ADPSL
However, from time to time I receive some deprecated images (some lines show ~50k counts, although it is a darkfield image and the rest image has ~200 counts) and the IOC shows this error code:
2023/03/02 16:51:43.266 PSL:getImage: error reading image, status=4, dataLen=12117504, nCopied=12117503, maxRead=1, nRead=1453
In the PSViewer (the vendor software that runs parallel) the image appears fine. It seems to appear random but I have the feeling that it happens more often when I increase the exposure time to higher than ~2s. Can anyone say what that error with status=4 actually means?
Here is my complete IOC-start with the errors:
#!../../bin/linux-x86_64/PSLioc
## You may have to change PSLioc to something else
## everywhere it appears in this file
< envPaths
epicsEnvSet("IOC","PSLioc")
epicsEnvSet("TOP","/mnt/soft-bam01/epics/IOC/PSLioc")
epicsEnvSet("SUPPORT","/soft/epics/inst-3.15.7")
epicsEnvSet("ASYN","/soft/epics/inst-3.15.7/asyn/4-40-1")
epicsEnvSet("BUSY","/soft/epics/inst-3.15.7/busy/1-7-2")
epicsEnvSet("CALC","/soft/epics/inst-3.15.7/calc/3-7-4")
epicsEnvSet("SSCAN","/soft/epics/inst-3.15.7/sscan/2-11-3")
epicsEnvSet("AUTOSAVE","/soft/epics/inst-3.15.7/autosave/5-10-1")
epicsEnvSet("AREA_DETECTOR","/soft/epics/inst-3.15.7/areaDetector-R3-11")
epicsEnvSet("ADCORE","/soft/epics/inst-3.15.7/areaDetector-R3-11/ADCore")
epicsEnvSet("ADSUPPORT","/soft/epics/inst-3.15.7/areaDetector-R3-11/ADSupport")
epicsEnvSet("ADPSL","/soft/epics/inst-3.15.7/areaDetector-R3-11/ADPSL")
epicsEnvSet("EPICS_BASE","/soft/epics/base")
dbLoadDatabase("../../dbd/PSLioc.dbd",0,0)
PSLioc_registerRecordDeviceDriver(pdbbase)
epicsEnvSet("PREFIX", "XRFDS:")
epicsEnvSet("PORT",   "PSL")
epicsEnvSet("QSIZE",  "20")
epicsEnvSet("XSIZE",  "2744")
epicsEnvSet("YSIZE",  "2208")
epicsEnvSet("NCHANS", "2048")
#epicsEnvSet("CBUFFS", "500")
# The search path for database files
epicsEnvSet("EPICS_DB_INCLUDE_PATH", "/soft/epics/inst-3.15.7/areaDetector-R3-11/ADCore/db")
# Create the asyn port to talk to the PSL server on port 50000
drvAsynIPPortConfigure("PSLServer","hzb1.exp.helmholtz-berlin.de:50000", 0, 0, 0)
asynOctetSetOutputEos("PSLServer", 0, "\n")
asynOctetSetInputEos("PSLServer", 0, "\n")
#asynSetTraceIOMask("PSLServer",0,2)
#asynSetTraceMask("PSLServer",0,255)
#asynSetTraceFile("PSLServer", 0, "PSLServer.out")
# PSLConfig(const char *portName, const char *serverPort,
#          int maxBuffers, size_t maxMemory,
#          int priority, int stackSize)
PSLConfig("PSL", "PSLServer", 0, 0)
#asynSetTraceIOMask("$(PORT)",0,2)
#asynSetTraceMask("$(PORT)",0,9)
dbLoadRecords("/soft/epics/inst-3.15.7/areaDetector-R3-11/ADCore/db/ADBase.template","P=XRFDS:,R=cam1:,PORT=PSL,ADDR=0,TIMEOUT=1")
dbLoadRecords("/soft/epics/inst-3.15.7/areaDetector-R3-11/ADCore/db/NDFile.template","P=XRFDS:,R=cam1:,PORT=PSL,ADDR=0,TIMEOUT=1")
dbLoadRecords("/soft/epics/inst-3.15.7/areaDetector-R3-11/ADPSL/db/PSL.template",   "P=XRFDS:,R=cam1:,PORT=PSL,ADDR=0,TIMEOUT=1")
# Create a standard arrays plugin
NDStdArraysConfigure("Image1", 5, 0, "PSL", 0, 0)
dbLoadRecords("/soft/epics/inst-3.15.7/areaDetector-R3-11/ADCore/db/NDPluginBase.template","P=XRFDS:,R=image1:,PORT=Image1,ADDR=0,TIMEOUT=1,NDARRAY_PORT=PSL,NDARRAY_ADDR=0")
# Make NELEMENTS in the following be a little bigger than 2744*2208
dbLoadRecords("/soft/epics/inst-3.15.7/areaDetector-R3-11/ADCore/db/NDStdArrays.template", "P=XRFDS:,R=image1:,PORT=Image1,ADDR=0,TIMEOUT=1,NDARRAY_PORT=PSL,TYPE=Int16,FTVL=SHORT,NELEMENTS=6100000")
# Create a TIFF file saving plugin
NDFileTIFFConfigure("FileTIFF1", 20, 0, "PSL", 0)
dbLoadRecords("NDFileTIFF.template",  "P=XRFDS:,R=TIFF1:,PORT=FileTIFF1,ADDR=0,TIMEOUT=1,NDARRAY_PORT=PSL")
# Create 1 statistics plugins
NDStatsConfigure("STATS1", 20, 0, "PSL", 0, 0, 0, 0, 0, 5)
dbLoadRecords("NDStats.template",     "P=XRFDS:,R=Stats1:,  PORT=STATS1,ADDR=0,TIMEOUT=1,HIST_SIZE=256,XSIZE=2744,YSIZE=2208,NCHANS=2048,NDARRAY_PORT=PSL")
NDTimeSeriesConfigure("STATS1_TS", 20, 0, "STATS1", 1, 23)
dbLoadRecords("/soft/epics/inst-3.15.7/areaDetector-R3-11/ADCore/db/NDTimeSeries.template",  "P=XRFDS:,R=Stats1:TS:, PORT=STATS1_TS,ADDR=0,TIMEOUT=1,NDARRAY_PORT=STATS1,NDARRAY_ADDR=1,NCHANS=2048,ENABLED=1")
# Load all other plugins using commonPlugins.cmd
#< $(ADCORE)/iocBoot/commonPlugins.cmd
set_savefile_path("/soft/epics/IOC/PSLioc/iocBoot/PSLioc/autosave")
set_requestfile_path("/soft/epics/inst-3.15.7/areaDetector-R3-11/ADPSL/pslApp/Db")
set_requestfile_path("/soft/epics/IOC/PSLioc/iocBoot/PSLioc")
set_requestfile_path("/soft/epics/inst-3.15.7/areaDetector-R3-11/ADCore/ADApp/Db")
set_requestfile_path("/soft/epics/inst-3.15.7/calc/3-7-4/calcApp/Db")
set_pass1_restoreFile("auto_settings.sav")
iocInit()
Starting iocInit
## EPICS R3.15.7
## EPICS Base built Dec 20 2019
reboot_restore: entry for file 'auto_settings.sav'
reboot_restore: Found filename 'auto_settings.sav' in restoreFileList.
*** restoring from '/soft/epics/IOC/PSLioc/iocBoot/PSLioc/autosave/auto_settings.sav' at initHookState 7 (after record/device init) ***
reboot_restore: done with file 'auto_settings.sav'
# save things every thirty seconds
create_monitor_set("auto_settings.req", 30,"P=XRFDS:,D=cam1:")
epics> auto_settings.sav: 352 of 352 PV's connected
2023/03/02 16:48:49.460 PSL:getImage: error reading image, status=4, dataLen=12117504, nCopied=12117502, maxRead=2, nRead=1377
epics>
epics> 2023/03/02 16:51:32.720 PSL:getImage: error reading image, status=4, dataLen=12117504, nCopied=12117503, maxRead=1, nRead=1185
2023/03/02 16:51:55.546 PSL:writeReadServer, status=1, sent
Stop
2023/03/02 16:51:55.581 PSL:writeInt32: error, status=1 function=8, value=0
2023/03/02 16:51:55.581 XRFDS:cam1:Acquire devAsynInt32::processCallbackOutput process write error
Best Regards
Michael
pasynOctetSyncIO error reading image status=4 Sintschuk, Michael via Tech-talk
RE: pasynOctetSyncIO error reading image status=4 Mark Rivers via Tech-talk
AW: pasynOctetSyncIO error reading image status=4 Sintschuk, Michael via Tech-talk
Prev: AW: pasynOctetSyncIO error reading image status=4 Sintschuk, Michael via Tech-talk
Next: RE: pasynOctetSyncIO error reading image status=4 Mark Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <20232024  2025  2026
