1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <2023>  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <2023>  2024  2025  2026
Subject: RE: Looking for a Water (LCW) Leak Sensor for machine interlock
From: "Guerrero, Christopher via Tech-talk" <[email protected]>
Date: Fri, 19 May 2023 17:38:08 +0000
Hi Han,
I saw your message about the water leak detection question. Here at NSLS-II, we are using products from Raychem Tracetek to tie the alarm status of the leak detection alarm module as a digital input signal to Allen Bradley PLC equipment protection system. You can check out the list of their products here:
https://www.nvent.com/en-us/raychem/solutions/commercial/applications/leak-detection
I would recommend using the TTSIM-1A-24VDC for the alarm module, which can hook up to 150m of TT1000 (water only) or TT3000(conductive liquid) leak detection sensing cable.
If you need more feedback, recs, or info on the water leak detection, contact me at [email protected].
Best,
Chris Guerrero
Prev: Re: Shutting down channel access clients Maren Purves via Tech-talk
Next: warning: multiple interrupt callbacks between processing when running testAsynPortDriverApp Wang, Lin via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <2023>  2024  2025  2026
Prev: Re: Looking for a Water (LCW) Leak Sensor for machine interlock Daykin, Evan via Tech-talk
Next: Phoebus Slider Leblanc, Gregory via Tech-talk