1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <20232024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <20232024  2025  2026
Subject: modbus
Date: Thu, 25 May 2023 10:59:22 +0800
Hi ,
I got a question, I want to read the value of a instrument via MOXA Nport5650-16
serial device server,The EPICS server connect to the serial server through internet cable.
Now I cannot get the value,please help me to check the problem ,thank you very much!!!
Note:The Moxa team tell me the address of the firt port is 4001,the second is 4002…
Note:I can get the respond when I use a modbus tool to send the request:
[2023-05-25 10:52:43.927]# The server is connected from local 192.168.127.100:54649
[2023-05-25 10:53:05.731]# SEND HEX>
01 03 00 00 00 02 C4 0B
[2023-05-25 10:53:05.794]# RECV HEX>
01 03 04 02 60 00 F4 FA 12
[2023-05-25 10:53:06.515]# SEND HEX>
[2023-05-25 10:53:06.579]# RECV HEX>
Here is the parameter of the instrument :
Host inquiry frame structure:
Address code Function code Register start address Register length Check code low check code high
1 byte 1 byte 2 bytes 2 bytes 1 byte 1 byte
Slave response frame structure:
Address code Function code Effective number of bytes First data area Second data area Nth data area Check code
1 byte 1 byte 1 byte 2 bytes 2 bytes 2 bytes 2 bytes
4.3 Register address
Register address PLC or configuration address Content Operation
0000 H 40001 Humidity Read only
0001 H 40002 Temperature Read only
4.4 Communication Protocol Example and Explanation
Example: Read the temperature and humidity value of device address 0x01
Inquiry frame (hexadecimal):
Temperature and Humidity Transmitter Instruction Manual (Model 485) V2.1
Address code Function code Start address Data length Check code low check code high
0x01 0x03 0x00 0x00 0x00 0x02 0xC4 0x0B
Response frame (hexadecimal): (for example, the read temperature is -10.1°C and the humidity is 65.8%RH)
return valid bytes
number
Humidity value Temperature value
Check code low
check code high
0x01 0x03 0x04 0x02 0x92 0xFF 0x9B 0x5A 0x3D
Temperature calculation:
When the temperature is lower than 0 ℃, the temperature data is uploaded in the form of complement code.
Temperature: FF9B H(Hex)= -101 => Temperature = -10.1℃
Humidity calculation:
Humidity: 292 H (Hex) = 658 => Humidity = 65.8RH
# ai record template for temperature
record(longin, "$(P)$(R)_temp") {
    field(DTYP, "asynUInt32Digital")
    field(INP, "@asynMask($(PORT) 1 0xFFFF)")
    field(SCAN, "$(SCAN)")
# ai record template for humidity
record(longin, "$(P)$(R)_humidity") {
    field(INP, "@asynMask($(PORT) 0 0xFFFF)")
root@wft:/usr/local/EPICS/ioc01/iocBoot/iocmoxa01# ./st.cmd
#!../../bin/linux-x86_64/moxa01
< envPaths
epicsEnvSet("IOC","iocmoxa01")
epicsEnvSet("TOP","/usr/local/EPICS/ioc01")
epicsEnvSet("ASYN","/usr/local/EPICS/support/asyn")
epicsEnvSet("MODBUS","/usr/local/EPICS/support/modbus")
epicsEnvSet("EPICS_BASE","/usr/local/EPICS/base")
cd "/usr/local/EPICS/ioc01"
dbLoadDatabase "dbd/moxa01.dbd"
moxa01_registerRecordDeviceDriver pdbbase
drvAsynIPPortConfigure("Nport1","192.168.127.254:4001",0,0,0)
modbusInterposeConfig("Nport1" ,1,5000,0)
drvModbusAsynConfigure("port1","Nport1",1,3,040001,2,0,100,"Moxa")
## Load record instances
#dbLoadRecords("db/xxx.db","user=root")
dbLoadRecords("db/longin.template","P=M,R=V,PORT=Nport1,SCAN=1 second")
cd "/usr/local/EPICS/ioc01/iocBoot/iocmoxa01"
iocInit
Starting iocInit
## EPICS R7.0.6.1
## Rev. 2023-05-23T14:33+0800
MV_temp devAsynUInt32Digital::initCommon findInterface asynUInt32DigitalType
MV_humidity devAsynUInt32Digital::initCommon findInterface asynUInt32DigitalType
## Start any sequence programs
#seq sncxxx,"user=root"
epics> dbl
MV_temp
MV_humidity
epics> dbpr MV_temp 2
ACKS: NO_ALARM      ACKT: YES           ADEL: 0             AFTC: 0
AMSG:               ASG :               BKPT: 00            DESC:
DISA: 0             DISP: 0             DISS: NO_ALARM      DISV: 1
DTYP: asynUInt32Digital                 EGU :               EVNT:
FLNK: CONSTANT      HHSV: NO_ALARM      HIGH: 0             HIHI: 0
HOPR: 0             HSV : NO_ALARM      HYST: 0
INP : INST_IO @asynMask(Nport1 1 0xFFFF)                    LCNT: 41
LLSV: NO_ALARM      LOLO: 0             LOPR: 0             LOW : 0
LSV : NO_ALARM      MDEL: 0             NAME: MV_temp       NAMSG:
NSEV: INVALID       NSTA: LINK          PACT: 1             PHAS: 0
PINI: NO            PRIO: LOW           PUTF: 0             RPRO: 0
SCAN: 1 second      SDIS: CONSTANT      SDLY: -1            SEVR: INVALID
SIML: CONSTANT      SIMM: NO            SIMS: NO_ALARM      SIOL: CONSTANT
SSCN: <nil>         STAT: UDF           SVAL: 0             TIME: <undefined>
TPRO: 0             TSE : 0             TSEL: CONSTANT      UDF : 1
UDFS: INVALID       VAL : 0
epics> dbpr MV_humidity 2
INP : INST_IO @asynMask(Nport1 0 0xFFFF)                    LCNT: 66
LSV : NO_ALARM      MDEL: 0             NAME: MV_humidity   NAMSG:
epics> asynReport 1
Nport1 multiDevice:No canBlock:Yes autoConnect:Yes
    enabled:Yes connected:Yes numberConnects 1
    nDevices 0 nQueued 0 blocked:No
    asynManagerLock:No synchronousLock:Yes
    exceptionActive:No exceptionUsers 1 exceptionNotifys 0
    traceMask:0x1 traceIOMask:0x0 traceInfoMask:0x1
    Port 192.168.127.254:4001: Connected
port1 multiDevice:Yes canBlock:Yes autoConnect:Yes
    nDevices 1 nQueued 0 blocked:No
    asynManagerLock:No synchronousLock:No
    exceptionActive:No exceptionUsers 0 exceptionNotifys 0
    addr 0 autoConnect Yes enabled Yes connected No exceptionActive No
        exceptionActive No exceptionUsers 0 exceptionNotifys 0
        blocked No
modbus port: port1
    initialized:        true
    asynOctet server:   Nport1
    modbusSlave:        1
    modbusFunction:     3
    modbusStartAddress: 040001
    modbusLength:       02
    absoluteAddressing: false
    dataType:           0 (INT16)
    plcType:            Moxa
    I/O errors:         0
    Read OK:            569
    Write OK:           0
    pollDelay:          0.100000
    Time for last I/O   75 msec
    Max. I/O time:      80 msec
    Time per hist. bin: 1 msec
Port: port1
  Timestamp: <undefined>
  Input EOS[0]:
  Output EOS[0]:
Parameter list 0
Number of parameters is: 12
Parameter 0 type=asynInt32, name=MODBUS_DATA, value is undefined
Parameter 1 type=asynInt32, name=MODBUS_READ, value is undefined
Parameter 2 type=asynUInt32Digital, name=ENABLE_HISTOGRAM, value is undefined
Parameter 3 type=asynInt32, name=READ_HISTOGRAM, value is undefined
Parameter 4 type=asynInt32, name=HISTOGRAM_BIN_TIME, value is undefined
Parameter 5 type=asynInt32Array, name=HISTOGRAM_TIME_AXIS, value is undefined
Parameter 6 type=asynFloat64, name=POLL_DELAY, value is undefined
Parameter 7 type=asynInt32, name=READ_OK, value=569, status=0
Parameter 8 type=asynInt32, name=WRITE_OK, value=0, status=0
Parameter 9 type=asynInt32, name=IO_ERRORS, value=0, status=0
Parameter 10 type=asynInt32, name=LAST_IO_TIME, value=75, status=0
Parameter 11 type=asynInt32, name=MAX_IO_TIME, value=80, status=0
epics>
Windows 邮件发送
Re: modbus Mark Rivers via Tech-talk
Prev: RE: warning: multiple interrupt callbacks between processing when running testAsynPortDriverApp Mark Rivers via Tech-talk
Next: Re: modbus Mark Rivers via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  <20232024  2025  2026
Prev: Re:Re: Re:Re: Re:Re: Re:Re: Re:Re: some motor driver 3 questions lynn via Tech-talk
