1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <20242025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <20242025  2026
Subject: AW: Readback of output variables in adsDriver
From: "Meyer, Markus via Tech-talk" <[email protected]>
Date: Mon, 15 Apr 2024 16:54:35 +0200
Hello Jure, Mark and Torsten,
Thank you all for your responses and explanations of the 2 cases.
> I kindly ask you to open a pair of issues on the Github repo. I can't say when we we'll be able to take a closer look (we're stretched pretty thin right now), but having open issues helps raise the priority.
I will do that and maybe I can help with some code after I have finished my evaluation of the other available drivers.
> Case 2, at least, is probably not that hard to implement. Case 1, on the other hand, is a bit thornier because of the design of the driver.
It may be OK to do the readback after iocInit only in a cyclic interval.
> We here at ESS use a different driver for ADS, and if that one can do the readback ? I haven't checked - but I highly suspect that it doesn't.
I have compiled the latest source of the driver from ESS [1] and can connect to my plc but unfortunately I get no values from the plc at all. I am still investigating what I am doing wrong here. I expect a readback because it's explicitly mentioned in the adsTestAsyn.db of adsExApp.
Markus
[1] https://urldefense.us/v3/__https://github.com/EuropeanSpallationSource/epics-twincat-ads__;!!G_uCfscf7eWS!cWY-oNbq-4U-gg1N5Q8SvI_E4DLNAd9tVgk5xrioIeV8ejfmVohmnmNpsp_rKDUJGlJGz2RJXqJ_poyPHDdx8g$
-----Ursprüngliche Nachricht-----
Von: Tech-talk <[email protected]> Im Auftrag von Jure Varlec via Tech-talk
Gesendet: Montag, 15. April 2024 12:49
An: [email protected]
Betreff: Re: Readback of output variables in adsDriver
Hello Markus,
Mark made a nice breakdown of the two cases. Right now, the adsDriver module supports neither. We are aware of this, but honestly, nobody has needed it badly enough yet :) . I kindly ask you to open a pair of issues on the Github repo. I can't say when we we'll be able to take a closer look (we're stretched pretty thin right now), but having open issues helps raise the priority.
Case 2, at least, is probably not that hard to implement. Case 1, on the other hand, is a bit thornier because of the design of the driver. It is focused on doing bulk reads, which are needed to get sufficient performance with lots of variables. But such reads can only be done after all the records are initialized and ADS variables made known to the driver. So, initial readbacks were disabled for simplicity. They can be added for sure, but it won't be a simple bolt-on.
Cheers,
Jure
On 4/12/24 18:11, Mark Rivers via Tech-talk wrote:
> Caution: This email originated from outside of Cosylab.
> Hi Markus,
> There are 2 separate cases here:
> 1) The PV value getting set to the PLC value during iocInit.
> 2) The PV value getting set to the PLC value when the PLC values changes after iocInit.
> Case 1 is handled as follows:
> - During iocInit the ao record device support (devAsynFloat64.c) does a read from the driver to get the current PLC value.  If that read operation returns asynSuccess then the PV should be set to the PLC value, otherwise it is not changed.  This definitely works fine with the Modbus driver, for example.  I am not sure about the adsDriver, since I have not used it.  You can add debugging to the driver to track that down.
> Case 2 is handled by adding the line you did to database:
>      info(asyn:READBACK, "1")
> That should make the ao record value update to match the PLC value when the PLC value is changed outside of EPICS.  Note that this line is NOT required for getting the behavior described in Case 1 above.
> Mark
> -----Original Message-----
> From: Tech-talk <[email protected]> On Behalf Of Meyer,
> Sent: Friday, April 12, 2024 10:25 AM
> To: [email protected]
> Subject: Readback of output variables in adsDriver
> Dear all,
> I am evaluating possibilities to communicate with a plc and other
> hardware from beckhoff. I have successfully build the adsDriver [1]
> device support and it seems to work very well for input variables. I
> can also write output variables, but if the value gets changed on the
> plc itself (e.g. by the interlock logic or by another connected
> protocol) it is not synced back to the pv. It also seems that the
> current value is not initially read on startup of the IOC.
> For example, this is the pv definition:
> record(ao, "$(P):IC:CB01-SSet") {
>      field(DTYP, "asynFloat64")
>      field(PREC, "2")
>      field(EGU,  "%")
>      field(DRVH, "100")
>      field(DRVL, "-100")
>      field(OUT,  "@asyn($(PORT) 0 0) REAL W P=PLC_TC3 V=HMI.IC.CB01.SSet")
> Before I start the IOC, the plc value is set to 2. If I start the IOC,
> the value of the pv is set to 0. The Timestamp is updated. The value
> in the plc gets not changed. I expected, that the pv value is also set
> to 2. Writing a value to the pv is working as expected.
> Did I miss something here? What can I do to subscribe for changes of
> output variables?
> Thanks,
> Markus
> [1]
> https://urldefense.us/v3/__https://github.com/Cosylab/adsDriver__;!!G_
> uCfscf7eWS!eovU-aYXFfsZIvbTx6Y3tTGma4zwbWLi1xy-LUyW3RghomFH88t9jP45toK
> nZq8oo1pt5gT5tQhGnPd9QXmCruzGkJg$
Re: AW: Readback of output variables in adsDriver Torsten Bögershausen via Tech-talk
Re: Readback of output variables in adsDriver Jure Varlec via Tech-talk
Prev: Re: Fw: Remote reset of MVME-2700 possible through serial console Kevin Peterson via Tech-talk
Next: Re: AW: Readback of output variables in adsDriver Torsten Bögershausen via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  <20242025  2026
Prev: Re: Readback of output variables in adsDriver Jure Varlec via Tech-talk
