1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  <2025>  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  <2025>  2026
Subject: Re: Enable or select records
From: "Dr. Simon Friederich via Tech-talk" <[email protected]>
To: Ralph Lange <[email protected]>, EPICS Tech Talk <[email protected]>
Date: Mon, 2 Jun 2025 13:59:03 +0200
Dear Ralph,
Thank you very much for the hints and explanation. I am currently trying to implement your advice.
I got rid of the calc record, the mbbi + Raw Soft Channel works nicely.
I've started with two types of modules and created the "Disable<type>" records.
#=============== bo Disable records ===============
record(bo, "$(P)$(R)slot$(SLOT):_disable_4chunit") {
    field(DESC, "Disable 4CH UNIT records")
    field(VAL,  "1") # disabled by default
    field(ZNAM, "enable")
    field(ONAM, "disable")
record(bo, "$(P)$(R)slot$(SLOT):_disable_output") {
    field(DESC, "Disable OUTPUT records")
    field(VAL,  "1")
Unfortunately the SDIS="Disable<type> CA" does not work as expected or at least from what I see, all types are processed. Here an example
# Valid data (4CH UNIT, OUTPUT)
#=============== Read data valid ===========
record(bi, "$(P)$(R)slot$(SLOT):validdata_get") {
    field(DESC, "Read data is valid")
    field(INP, "$(P)$(R)slot$(SLOT):info_get.VAL[3] CP")
    field(ZNAM, "NO")   field(ZSV, "MAJOR")
    field(ONAM, "YES")  field(OSV, "NO_ALARM")
    field(DISV, "1") # Disable record if DISA=DISV
    field(SDIS, "$(P)$(R)slot$(SLOT):_disable_4chunit CA") # Sets DISA value
If I read the reference manual correctly it should work like this:
A not-empty SDIS-field sets the value for DISA and if DISA=DISV, then the record should be disabled, right?
Or the other way around: If DISA!=DISV, the record is enabled.
Although my bo records "_disable_4chunit" are set correct (the VAL fields are 0 for this modules and 1 else), the DISA is 1 for all my slots and hence all "validdata_get" are enabled.
What am I missing?
Best regards
Simon
Am 27.05.2025 um 09:24 schrieb Ralph Lange:
Hi Simon,
Without going into the specifics of your application...
Device type mapping:
No need for the calc - the mbbi can do the mapping itself. Use the "Raw Soft Channel" device support (in Base) to have the mbbi do RVAL-to-index mapping.
Disabling:
There are several ways, of course ... I would indeed use disabling.
Add one "Disable<type>" bo record to each per-device-type database, with a default setting of 1=disabled. Point all hardware-connected records of that device type to this Disable<type> using SDIS="Disable<type> CA". (CA option to avoid pulling all records into the same lock set.)
The missing link:
Connecting its SELL to your mapping mbbi, use e.g. a dfanout record with SELM=specified to write a 0 (=enabled) to the Disabled<type> record of the recognized card type. (Don't forget the PP flag to process the Disabled<type>.)
The whole thing is a template per slot that you instantiate for each slot that is used. (Or the max number of slots if you don't care about unconnected records.)
Cheers,
~Ralph
ps. Database links work only locally, Channel Access links work locally and remotely.
CP on input links means "set up a monitor and process me when the value changes" - which is perfectly legal in any case.
Re: Enable or select records Ralph Lange via Tech-talk
Enable or select records Dr. Simon Friederich via Tech-talk
Prev: Re: External: Re: Communicating with Bechoff I/O through EPICS Timo Korhonen via Tech-talk
Next: Job Openings at BESSY/HZB Gotz, Malte via Tech-talk
Index: 1994  1995  1996  1997  1998  1999  2000  2001  2002  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  <2025>  2026
Prev: Re: Enable or select records Ralph Lange via Tech-talk
Next: Re: Enable or select records Ralph Lange via Tech-talk