Hi Jörn,
I think we getting the wires crossed here... the OPCUA port is 4840
but the 502 port is the normal Modbus port.
I managed to connect fine to it with other applications in the same
machine.
Kind Regards
Luis
On 24/07/2026 10:38, Jörn Dreyer wrote:
Hi Luis,
are you sure you are using the correct port?
The Beckhoff documentation tells that the OPCUA server is listening on port 4840. Did you cahnge that when installing the OPCUA Sever on the PLC?
The Ports 500 + x are normally used for the various NC applications in your PLC program.
Regards
Jörn
Am Freitag, 24. Juli 2026, 09:57:38 Mitteleuropäische Sommerzeit schrieb Luis Alberto De Sousa Moreira via Tech-talk:
Just found another application I used before as a Modbus client, called
EasyModbusClient.
It connects fine and gets data.
This is getting more intriguing...
Best Regards
Luis
On 24/07/2026 09:40, Luis Alberto De Sousa Moreira via Tech-talk wrote:
Hi Gabriel,
The firewall seems to be the culprit, but I added rules for the
application. I also just done a test where I disabled the firewall and
I get the same result.
D:\FalconDev\EPICS\modbus\iocBoot\iocTest>..\..\bin\windows-x64-mingw\modbusApp.exe
BPS_Beck.cmd
# BPS_Beck.cmd
# Just testing the modbus module with my BPS Beckhoff PLC.
# 1. Cleanly lock network routing automatically at boot
epicsEnvSet("EPICS_CA_ADDR_LIST", "10.136.0.255")
epicsEnvSet("EPICS_CA_AUTO_ADDR_LIST", "NO")
epicsEnvSet("EPICS_CAS_INTF_ADDR_LIST", "10.136.0.34")
# gvl.mb_Input_Registers[10] := GVL.d_setpoint_T1; // T1
mS
# gvl.mb_Input_Registers[11] := GVL.d_setpoint_TRamp1; // Ramp1
uS
# gvl.mb_Input_Registers[12] := GVL.d_setpoint_v1; // V1
10V
# gvl.mb_Input_Registers[13] := GVL.d_setpoint_T2; // T2
mS
# gvl.mb_Input_Registers[14] := GVL.d_setpoint_TRamp2; // Ramp2
uS
# gvl.mb_Input_Registers[15] := GVL.d_setpoint_V2; // V2
10V
# gvl.mb_Input_Registers[16] := GVL.d_setpoint_T3; // T3
mS
# gvl.mb_Input_Registers[17] := GVL.d_setpoint_TRamp3; // Ramp3
uS
# gvl.mb_Input_Registers[18] := GVL.d_setpoint_V3; // V3
10V
# gvl.mb_Input_Registers[19] := GVL.d_setpoint_pulseLength; //
PulseLength S /mS
# gvl.mb_Input_Registers[20] := GVL.d_setpoint_TRampDown; //
RampDown uS
dbLoadDatabase("../../dbd/modbusApp.dbd")
modbusApp_registerRecordDeviceDriver(pdbbase)
# Get the connection going
drvAsynIPPortConfigure("BPS_Beck", "10.136.0.30:502", 0, 0, 0)
2026/07/24 09:32:59.953 BPS_Beck -1 autoConnect could not connect:
Can't connect to 10.136.0.30:502: Unknown error
# drvAsynIPPortConfigure("BPS_Beck", "8.8.8.8:8080", 0, 0, 0)
modbusInterposeConfig("BPS_Beck", 0, 5000, 0)
asynSetOption("BPS_Beck",0, "disconnectOnReadTimeout", "Y")
# Configure Modbus Drivers Memory Blocks
# Syntax:
# drvModbusAsynConfigure("portName", "tcpPortName", slaveAddress,
modbusFunction, modbusStartAddress, modbusLength, dataType, pollMsec,
"plcType")
# drvModbusAsynConfigure("modbusPortName", "asynPortName",
slaveAddress, modbusFunction, startAddress, length, dataType,
pollMsec, "plcType")
# Read Coils (Function Code 1)
# Reads 16 binary bits starting at offset 0, polling every 200
milliseconds.
# drvModbusAsynConfigure("READ_COILS", "PLC_NET", 0, 1, 0, 1, 0, 200,
"OldPLC")
# Write Coils (Function Code 5)
# Configures a write-only path for coils. pollMsec is 0 because writes
are instantaneous.
# drvModbusAsynConfigure("WRITE_COILS", "PLC_NET", 0, 5, 0, 1, 0, 0,
"OldPLC")
# Reads 11 read-only 16-bit registers starting at offset 10, polling
every 500 milliseconds.
# dataType=0 specifies standard 16-bit unsigned integers (UINT_16).
drvModbusAsynConfigure("READ_INPUTS", "BPS_Beck", 1, 4, 10, 11, 0,
500, "Beckhoff")
# Read Holding Registers (Function Code 3)
# Reads 1 read/write 16-bit register starting at offset 0, polling
# drvModbusAsynConfigure("READ_HOLDING", "PLC_NET", 0, 3, 0, 1, 0,
500, "OldPLC")
# Block E: Write Holding Registers (Function Code 6)
# Configures a write-only path for single registers. pollMsec is 0 for
on-demand writing.
# drvModbusAsynConfigure("WRITE_HOLDING", "PLC_NET", 0, 6, 0, 1, 0, 0,
"OldPLC")
# Enable ASYN_TRACEIO_HEX on octet server
# asynSetTraceIOMask("BPS_Beck",0,4)
# Enable ASYN_TRACE_ERROR and ASYN_TRACEIO_DRIVER on octet server
# asynSetTraceMask("BPS_Beck",0,9)
dbLoadRecords("../../db/BPS_Beck.db")
iocInit
Starting iocInit
## EPICS R7.0.10
## Rev. 2026-07-01T08:47+0200
## Rev. Date build date/time:
2026/07/24 09:33:00.992 drvModbusAsyn::doModbusIO port READ_INPUTS
error calling writeRead, error=asynManager::queueLockPort queueRequest
failed: port BPS_Beck not connected, nwrite=0/6, nread=0
epics>
Kind Regards
Luis
On 23/07/2026 16:24, Gabriel Fedel wrote:
Hi Luis,
Couldn't the firewall be blocking the EPICS application ?
Best Regards
Gabriel
*From:* Tech-talk <tech-talk-bounces at aps.anl.gov> on behalf of Luis
Alberto De Sousa Moreira via Tech-talk <tech-talk at aps.anl.gov>
*Sent:* Thursday, July 23, 2026 3:59 PM
*To:* Mark Rivers <rivers at cars.uchicago.edu>; tech-talk at aps.anl.gov
*Subject:* Re: Modbus Module issue
Hi Mark,
My other application is using the Modbus protocol, I used it to do the
initial testing on my system.
I tried the telnet command from my MSYS2 environment and it can
connect...
telnet 10.136.0.30 502
Trying 10.136.0.30...
Connected to 10.136.0.30.
Escape character is '^]'.
Kind Regards
Luis
Luis Moreira
EPFL SB SPC-II, PPH241 (Batiment PPH) Station 13
CH-1015 Lausanne, Switzerland
Tel. (+41) 21 693 58 37
E-Mail luis.moreira at epfl.ch
- Re: Modbus Module issue Luis Alberto De Sousa Moreira via Tech-talk
- Modbus Module issue Luis Alberto De Sousa Moreira via Tech-talk
- Re: Modbus Module issue Jörn Dreyer via Tech-talk
Re: Create record name manifest during build Jure Varlec via Tech-talk
2025
<2026>
2025
<2026>
