This looks like almost a no-op for RTEMS, so I see no problem. Are the changes to epicsTime.cpp a bug fix?
Diff comments:
> diff --git a/documentation/RELEASE_NOTES.html b/documentation/RELEASE_NOTES.html
> index 8ed4e04..f6daa49 100644
> --- a/documentation/RELEASE_NOTES.html
> +++ b/documentation/RELEASE_NOTES.html
> @@ -16,6 +16,38 @@
> <!-- Insert new items immediately below here ... -->
> +<h3>Replace EPICS_TIMEZONE with EPICS_TZ</h3>
> +<p>The <tt>EPICS_TIMEZONE</tt> environment parameter provided time-zone
> +information for the IOC's locale in the old ANSI format expected by VxWorks for
> +its <tt>TIMEZONE</tt> environment variable, and can also used by RTEMS to set
> +its <tt>TZ</tt> environment variable. However the <tt>TIMEZONE</tt> value has to
> +be updated every year since it contains the exact dates of the daylight-savings
> +time changes. The Posix TZ format that RTEMS uses contains rules that for
> +calculating those dates, thus its value would only need updating if the rules
> +(or the locale) are changed.</p>
> +<p>This release contains changes that replace the <tt>EPICS_TIMEZONE</tt>
> +environment parameter with one called <tt>EPICS_TZ</tt> and a routine for
> +VxWorks that calculates the <tt>TIMEZONE</tt> environment variable from the
> +current <tt>TZ</tt> value. This routine will be run once at start-up, when the
> +EPICS clock has synchronized to its NTP server. The calculations it contains
> +were worked out and donated to EPICS by Larry Hoff in 2009; it is unforunate
unforunate -> unfortunate
> +that it has taken 10 years for them to be integrated into Base.</p>
> +<p>The default value for the <tt>EPICS_TZ</tt> environment parameter is set in
> +the Base configure/CONFIG_SITE_ENV file, which contains example settings for
> +most EPICS sites that use VxWorks, and a link to a page describing the Posix TZ
> +format for any locations that I missed.</p>
> +<p>If a VxWorks IOC runs continuously without being rebooted from December 31st
> +to the start of daylight savings time the following year, its <tt>TIMEZONE</tt>
> +value will be wrong as it was calculated for the previous year. This only
> +affects times that are converted to a string on the IOC however and is easily
> +fixed; just run the command <tt>tz2timezone()</tt> on the VxWorks shell and the
> +calculation will be redone for the current year. IOCs that get rebooted at least
> +once before the start of summer time will not need this to be done.</p>
> <h3>Cleaning up with Multiple CA contexts in a Process</h3>
> <p>Bruno Martins reported a problem with the CA client library at shutdown in a
> diff --git a/src/libCom/RTEMS/rtems_init.c b/src/libCom/RTEMS/rtems_init.c
> index 2b909ab..dcb6daa 100644
> --- a/src/libCom/RTEMS/rtems_init.c
> +++ b/src/libCom/RTEMS/rtems_init.c
> @@ -581,25 +581,11 @@ Init (rtems_task_argument ignored)
> printf ("***** Can't set time: %s\n", rtems_status_text (sc));
> if (getenv("TZ") == NULL) {
> - const char *tzp = envGetConfigParamPtr(&EPICS_TIMEZONE);
> - if (tzp == NULL) {
> - printf("Warning -- no timezone information available -- times will be displayed as GMT.\n");
> - else {
> - char tz[10];
> - int minWest, toDst = 0, fromDst = 0;
> - if(sscanf(tzp, "%9[^:]::%d:%d:%d", tz, &minWest, &toDst, &fromDst) < 2) {
> - printf("Warning: EPICS_TIMEZONE (%s) unrecognizable -- times will be displayed as GMT.\n", tzp);
> - else {
> - char posixTzBuf[40];
> - char *p = posixTzBuf;
> - p += sprintf(p, "%cST%d:%.2d", tz[0], minWest/60, minWest%60);
> - if (toDst != fromDst)
> - p += sprintf(p, "%cDT", tz[0]);
> - epicsEnvSet("TZ", posixTzBuf);
> + const char *tzp = envGetConfigParamPtr(&EPICS_TZ);
> + if (!tzp || *tzp)
> + printf("Warning: No timezone information, times will be displayed in UTC.\n");
> + else
> + epicsEnvSet("TZ", tzp);
Should call tzset() after changing $TZ. cf. zoneset() iocsh function added on 7.0 branch (d70bfed75b469e6c671d3d0617f8bfd0c212b664).
> tzset();
> osdTimeRegister();
> diff --git a/src/libCom/osi/os/vxWorks/tz2timezone.c b/src/libCom/osi/os/vxWorks/tz2timezone.c
> new file mode 100644
> index 0000000..df8db85
> --- /dev/null
> +++ b/src/libCom/osi/os/vxWorks/tz2timezone.c
> @@ -0,0 +1,278 @@
> +* Copyright (c) 2009 Brookhaven Science Associates, as Operator of
> +* Brookhaven National Laboratory.
> +* Copyright (c) 2019 UChicago Argonne LLC, as Operator of Argonne
> +* National Laboratory.
> +* EPICS BASE is distributed subject to a Software License Agreement found
> +* in file LICENSE that is included with this distribution.
> + * Authors: Larry Hoff, Andrew Johnson <[email protected]>
> + * This file exports a single function "int tz2timezone(void)" which reads
> + * the TZ environment variable (defined by POSIX) and converts it to the
> + * TIMEZONE environment variable defined by ANSI. The latter is used by
> + * VxWorks "time" functions, is largely deprecated in other computing
> + * environments, has limitations, and is difficult to maintain. This holds
> + * out the possibility of "pretending" that VxWorks supports "TZ" - until
> + * such time as it actually does.
> + * For simplicity, only the "POSIX standard form" of TZ will be supported.
> + * Even that is complicated enough (see following spec). Furthermore,
> + * only the "M" form of DST start and stop dates are supported.
> + * TZ = zone[-]offset[dst[offset],start[/time],end[/time]]
> + * zone
> + * A three or more letter name for the timezone in normal (winter) time.
> + * [-]offset
> + * A signed time giving the offset of the time zone westwards from
> + * Greenwich. The time has the form hh[:mm[:ss]] with a one of two
> + * digit hour, and optional two digit minutes and seconds.
> + * dst
> + * The name of the time zone when daylight saving is in effect. It may
> + * be followed by an offset giving how big the adjustment is, required
> + * if different than the default of 1 hour.
> + * start/time,end/time
> + * Specify the start and end of the daylight saving period. The start
> + * and end fields indicate on what day the changeover occurs, and must
> + * be in this format:
> + * Mm.n.d
> + * This indicates month m, the n-th occurrence of day d, where
> + * 1 <= m <= 12, 1 <= n <= 5, 0 <= d <= 6, 0=Sunday
> + * The 5th occurrence means the last occurrence of that day in a
> + * month. So M4.1.0 is the first Sunday in April, M9.5.0 is the
> + * last Sunday in September.
> + * The time field indicates what hour the changeover occurs on the given
> + * day (TIMEZONE only supports switching on the hour).
> +#include <vxWorks.h>
> +#include <envLib.h> /* getenv() */
> +#include <stdio.h> /* printf() */
> +#include <string.h> /* strchr() */
> +#include <ctype.h> /* isalpha() */
> +#include <epicsTime.h>
> +/* for reference: TZ syntax, example, and TIMEZONE example
> + * std offset dst [offset],start[/time],end[/time]
> + * CST6CDT5,M3.2.0,M11.1.0
> + * EST+5EDT,M4.1.0/2,M10.5.0/2
> + * std <unused> offset start stop
> + * TIMEZONE=EST::300:030802:110102
> +static int extractDate(const char *tz, struct tm *current, char *s)
> + static const int startdays[] = {
> + 0, 31, 59, 90, 120, 151, 181, 212, 243, 273, 304, 334
> + static const int molengths[] = {
> + 31, 28, 31, 30, 31, 30, 31, 31, 30, 31, 30, 31
> + int month, week, weekday, hour=2; /* default=2AM */
> + int jan1wday, wday, mday;
> + /* Require 'M' format */
> + if (*++tz != 'M') {
> + printf("tz2timezone: Unsupported date type, need 'M' format\n");
> + return ERROR;
> + tz++;
> + if (sscanf(tz, "%d.%d.%d/%d", &month, &week, &weekday, &hour) < 3)
> + return ERROR; /* something important missing */
> + if (month == 0 || month>12 ||
> + week < 1 || week > 5 ||
> + weekday < 0 || weekday > 6 ||
> + hour < 0 || hour > 23)
> + return ERROR;
> + /* Now for some brute-force calendar calculations... */
> + /* start month is in "month", and the day is "weekday", but
> + we need to know when that weekday first occurs in that month */
> + /* Let's start with weekday on Jan. 1 */
> + jan1wday = (7 + current->tm_wday - (current->tm_yday % 7)) % 7;
> + /* We need to know if it is a leap year (and if it matters) */
> + /* Let's assume that we're working with a date between 1901 and 2099,
> + that way we don't have to think about the "century exception".
> + If this code is still running (unchanged) in 2100, I'll be stunned
> + (and 139 years old) */
> + wday = (jan1wday + startdays[month-1] +
> + ((month > 2 && (current->tm_year % 4 == 0)) ? 1 : 0)) % 7;
> + /* Let's see on what day-of-the-month the first target weekday occurs
> + (counting from 1). The result is a number between 1 and 7, inclusive. */
> + mday = 1 + ((7 + weekday - wday) % 7);
> + /* Next, we add the week offset. If we overflow the month, we subtract
> + one week */
> + mday += 7 * (week - 1);
> + if (mday > molengths[month-1])
> + mday -= 7;
> + /* Should I handle Feb 29? I'm willing to gamble that no one in their right
> + mind would schedule a time change to occur on Feb. 29. If so, we'll be a
> + week early */
> + sprintf(s, "%02d%02d%02d", month, mday, hour);
> + return OK;
> +static const char *getTime(const char *s, int *time)
> + /* Time format is [+/-]hh[:mm][:ss] followed by the next zone name */
> + *time = 0;
> + if (!isdigit((int) s[0]))
> + return s; /* no number here... */
> + if (!isdigit((int) s[1])) { /* single digit form */
> + *time = s[0] - '0';
> + return s + 1;
> + if (isdigit((int) s[1])) { /* two digit form */
> + *time = 10 * (s[0] - '0') + (s[1] - '0');
> + return s + 2;
> + return s; /* does not follow supported form */
> +int tz2timezone(void)
> + const char *tz = getenv("TZ");
> + /* Spec. says that zone names must be at least 3 chars.
> + * I've never seen a longer zone name, but I'll allocate
> + * 40 chars. If you live in a zone with a longer name,
> + * you may want to think about the benefits of relocation.
> + char zone[40];
> + char start[10], stop[10]; /* only really need 7 bytes now */
> + int hours = 0, minutes = 0, sign = 1;
> + /* This is more than enough, even with a 40-char zone
> + * name, and 4-char offset.
> + char timezone[100];
> + int i = 0; /* You *always need an "i" :-) */
> + epicsTimeStamp now;
> + struct tm current;
> + /* First let's get the current time. We need the year to
> + * compute the start/stop dates for DST.
> + if (epicsTimeGetCurrent(&now) ||
> + epicsTimeToTM(¤t, NULL, &now))
> + return ERROR;
> + /* Make sure TZ exists.
> + * Spec. says that ZONE must be at least 3 chars.
> + if ((!tz) || (strlen(tz) < 3))
> + return ERROR;
> + /* OK, now a bunch of brute-force parsing. My brain hurts if
> + * I try to think of an elegant regular expression for the
> + * string.
Could sscanf() avoid some of this pain?
> + /* Start extracting zone name, must be alpha */
> + while ((i < sizeof(zone) - 1) && isalpha((int) *tz)) {
> + zone[i++] = *tz++;
> + if (i < 3)
> + return ERROR; /* Too short, not a real zone name? */
> + zone[i] = 0; /* Nil-terminate (for now) */
> + /* Now extract offset time. The format is [+/-]hh[:mm[:ss]]
> + * Recall that TIMEZONE doesn't support seconds....
> + if (*tz == '-') {
> + sign = -1;
> + tz++;
> + else if (*tz == '+') {
> + tz++;
> + /* Need a digit now */
> + if (!isdigit((int) *tz))
> + return ERROR;
> + /* First get the hours */
> + tz = getTime(tz, &hours);
> + if (hours > 24)
> + return ERROR;
> + if (*tz == ':') { /* There is a minutes part */
> + /* Need another digit now */
> + if (!isdigit((int) *++tz))
> + return ERROR;
> + /* Extract the minutes */
> + tz = getTime(tz, &minutes);
> + if (minutes > 60)
> + return ERROR;
> + /* Skip any seconds part */
> + if (*tz == ':') {
> + int seconds;
> + tz = getTime(tz + 1, &seconds);
> + /* Extract any DST zone name, must be alpha */
> + if (isalpha((int) *tz)) {
> + zone[i++] = '/'; /* Separate the names */
> + zone[i] = 0; /* Nil-terminate */
> + minutes += hours * 60;
> + minutes *= sign;
> + /* Look for start/stop dates - require neither or both */
> + tz = strchr(tz, ',');
> + if (!tz) { /* No daylight savings time here */
> + /* Format the env. variable */
> + sprintf(timezone, "TIMEZONE=%s::%d", zone, minutes);
> + else {
> + if (extractDate(tz, ¤t, start) != OK)
> + return ERROR;
> + tz = strchr(tz + 1, ',');
> + if (!tz)
> + return ERROR;
> + if (extractDate(tz, ¤t, stop) != OK)
> + return ERROR;
> + sprintf(timezone, "TIMEZONE=%s::%d:%s:%s", zone, minutes, start, stop);
> + /* Make it live! */
> + putenv(timezone);
> + return OK;
https://code.launchpad.net/~anj/epics-base/+git/base-3.15/+merge/368570
Your team EPICS Core Developers is subscribed to branch epics-base:3.15.
- [Merge] ~anj/epics-base/+git/base-3.15:vxworks-tz-support into epics-base:3.15 Andrew Johnson via Core-talk
Re: [Merge] ~epics-core/epics-base/+git/make:rpath-origin into epics-base:7.0 mdavidsaver via Core-talk
[Merge] ~info-martin-konrad/epics-base:dont-nuke-global-cac-thread-id-in-exit-handler into epics-base:3.15 noreply--- via Core-talk
<2019>
2025
2026
Re: [Merge] ~anj/epics-base/+git/base-3.15:vxworks-tz-support into epics-base:3.15 Andrew Johnson via Core-talk
<2019>
2025
2026