Sorry for the usoft use. I have copied and
pasted the word and excel documents into this email
for those of you on UNIX.
A meeting was held from January 10 through January
12, 2000 to discuss the archive retrieval library, explore requirements for
higher physics applications, and to discuss the future of channel access.
Attendees:
Jeff Hill
[email protected]
Kay Kasemir
[email protected]
Bob Dalesio
[email protected]
Marty Kraimer
[email protected]
Bob Sass
[email protected]
John Galambos
[email protected]
Matt Bickley
[email protected]
David Brian
[email protected]
Chris Larrieu
[email protected]
Matthias Clausen
[email protected]
The goals of the archiving session were to make everyone
familiar with what had been done at DESY, JLAB, and LANL, determine what needed to be done to provide complete
archiving capabilities, develop a standard archive access library, and to
determine what would be required from a network protocol to support archive
data. To this end, a set of presentations were made concerning the source of
data to be archived as well as the users of archive data.
XARR – Chris Larrieu
XARR is an archive plotting tool that runs on UNIX and accesses archive
data from the old archive data source (ARR ascii version) and has a library to
support the binary channel_archiver data source. It fetches data that is
currently on disks that are locally mounted. The data source must be set in an
environment variable.
Some requirements to make this more useful to users was discussed. The
three major elements are:
1) A
Directory Server that is able to keep hierarchical relationships between
channels and groups. This service should be available over the network. It would
need to support the ability of channels to live in many groups, just as a single
channel can be thought of belonging to many different sets. For instance, a
dipole magnet power supply in sector A, belongs to bending magnets and
controllers in section A. We envision that requests for controllers and requests
for signals in sector A would both return a list that contained this magnet
power supply. With such a service, more generalized browsing tools for both
archive and current data could be developed. This would relieve the physicist or
operator from having to have predefined sets to see archive data and predefined
screens to view real time data.
2)
Requests that allow XARR to request various filters would prevent the
need for each tool to implement every filter that may be requested. A list of
filters were discussed at greater length during the archive data access
library.
3)
Requests that allow users to query data based on some relationship or
limits would allow users to search for events without looking through all of the
data. A request could be made to find all channels that moved by 2% when a
different value moved by 5%. This would allow the user to search for
relationships that were not previously understood in the process.
Xtract – Matt Bickley
Xtract is a tool that runs in the UNIX environment and allows users to
set up a data acquisition experiment. The tool allows the user to configure a
neseted set of control parameters moving through the control space at defined
steps, taking prescribed actions between steps and collecting some set of
channels into a buffer. It then provides some plotting capabilities.
Some requirements to improve the performance and capabilities of this
tool are:
1) Have
channel access deliver time synchronous sets of data during the collection
phase.
2) Have
some sort of buffer server that will take the request to collect data and
perform the data collection in the front-end computers.
3)
Produce a filter that allows this data to be placed into an archiver like
the channel archiver and then use the same tools that are available for archive
data viewing.
4)
Provide a way to produce a standard ascii format that can then be used by
some other tools like SDDS or Matlab.
Buffer Server – Bob Dalesio
This was presented as a possible extension to EPICS to support some of
the needs of applications for archive and synchronous data. The buffer server
would provide data in two ways: a single channel over time or a set of channels
at a single point in time. The buffer server could be used as a layer on top of
tools like the channel archiver or direct channel access.
Some requirements on channels access or some other protocol to support
such a tool:
1)
Provide a primitive data sample that includes statistical information for
a period in addition to timestamp. This would allow a large time interval to be
reduced to a single sample without loosing some of the potentially important
information about the interval. These would be duration of the statistics, mean
value, median value, high, low, average, standard deviation, and perhaps the
number of outliers from specified limits and the skew. Other data could be
envisioned in a statistical sample.
2)
Provide support for a time array. The request would specify a time range
and an optional statistical reduction period to use to reduce the amount of data
returned. The response would be a series of data, time stamp and status
triplets.
3)
Provide support for a set of channels at a single point in time. This
would require the ability to define a set, request to get synchronous sets
either from the present or at some point in the past from an archive file. The
set would have to have certain characteristics like the amount of time that is
considered within the same period. Support would also need to exist to put a
synchronous set. This would mean setting values in a single IOC or multiple IOCs
in as synchronously as possible.
Striptool modified for historical data viewing – Matthias
Clausen
Striptool was modified to access historical data as well as current data.
Many modifications were made to Striptool to give the user a seamless view of
archive and current data. At DESY, historical data can either be in an archive
file or in the front-end computer in an archive record. Striptool will now allow
the user to scroll back and forth in time. For plots which start at the present
time, the program will first access the archive record buffer and then the long
term archive. Algorithms are built in to average, tail, sharp, spline and
circular fit.
Requirements to better support this seamless access to data:
1) Have
network response to a single name include the ability to say that the data for
the channel is historical.
2)
Provide some data reduction and algorithmic fitting in the request to
reduce the communication time as well as the resource requirements on the
client.
3) Array
data needs to include the frequency – that is if there is a single time stamp
with many samples, the time distance between the samples needs to be a standard
attribute.
4) The
ability to handle an array of data, time stamp and status triplets would make it
possible to support front-end circular buffers to handle the first level of data
archiving. This real time data could also be available without long term
historical data.
Data Archiving at DESY – Matthias Clausen
Data is archived from many different control systems at DESY and needs to
be integrated at the viewer. The data being archived includes scalars, arrays
and multidimensional arrays. Scalars archived include analog input, digital
input and multibit binary inputs. Arrays include waveforms, subarrays, and data
logger messages (data sets consisting of an array of data and the corresponding
attributes). Multidimensional arrays include images and history buffers. It is
planned to have the archived data listed into a relational database allowing an
ODBC query to find what has been archived. Archive data is output in SDDS format
to take advantage of the data filtering and plotting capabilities from the
command line and to keep the structure of the current archive (1 channel per
month per file) which already has 4 years of data.
Requirements to support the archive uses here would include:
1)
Support for storing multidimensional arrays – which implies overcoming
the existing array size boundaries as well as storing the meta data to describe
the multiple dimensions.
2)
Support to extract bit information from multibit values implies that the
metadata describing the MBBI is also available from the archive interface.
3) To
archive data logging messages, the current string size limitations in the
database and channel access would need to be overcome. These messages should be
archived into all data stores as they are now. Should there be a way to specify
which group of channels that they affect – so that someone viewing archive data
could see a marker from these messages if they applied to the data being
viewed?
4) Again
we see the interest in querying what channels are archived over the network. The
use of ODBC makes this possible.
5)
Exporting the archive data in SDDS format to provide the ability to
manipulate the data from a script is an example of the need for operators to be
able to manipulate the data they retrieve interactively or at least
spontaneously – without pre-made programs that limit the flexibility of the
manipulation.
Projected Requirements for the NLC – Bob Sass
NLC anticipates a large volume of
archive data on the order of Petabytes (1015 bytes) /year. This probably means
multiple archive formats i.e. files plus multiple databases. Some may be
separate from the Channel Archiver but the use of databases e.g. Oracle by
the Archiver should be
possible.
Channel Archiver – Kay Kasemir
The channel archiver is a C++ archiving tool that is running under UNIX,
LINUX and Windows. It loads an ascii configuration on startupThe configuration
can be defined via a web interface. The interface provides channel and value
iterators.These iterators make the data source opaque to the application. In
order to change the data source for this set of tools, these channel and value
iterators need to be replaced. A CGI tool is supplied for retrieval that allows
the user to browse the archived data via a web browser. In addition, there is a
windows application for viewing archive files that are mounted.
This presentation was given with an eye toward defining a standard
interface for accessing archive data. The library for accessing archive data
follows.
Interface Library
It is agreed that access to archive data from application programs must
be through a common interface definition. A straw man will be worked out between
Chris Larrieu and Kay and presented to this group. The ability to access archive
data from a script will also be supported. The callable aspects are presented in
the next five items. The key elements missing involve the storage of the
data.
1)
Discovering the channels that are available in the archive. It would be
valuable to have some predefined groups or relationships that can be called into
an archive viewer. It was decided that this “directory service” should be a
separate entity that allowed the application to define arbitrary sets and
hierarchies that can be queried from various applications.
2) Initialize the range (channel_name(s),
time 0 – or special character for current time, time 1 as either the end time or
the duration) would be a request for data. The return would be a query
descriptor. The descriptor would include for each name: the time of the first
point, the time of the last point, the archive method, number of points, other
statistics to give a sense of the quality and density of the data, descriptor,
value type, and a list of the attributes that were archived. We could get more
than one response if there are multiple archivers or a buffers server.
3)
Transform_data would define a
set of sequential transformations that would be done on the data before
it is returned to the requestor. This would set a transformation through which
the data would go before being returned. There can be many such calls and they
would be done in order. (Can these be changed during operation – would be need a
remove transformation?)
4) Narrow
query would remove some of the attributes from the request list. (Do we really
need this?)
5)
Get_data – or use a channel and data iterator and leave the details of
the file traversal – network transmission hidden? Should request for attribute
data be a separate call? Does this become the new channel access data object? If
it is the new channel access data object, then we have the possibility of having
clients that are not bothered by the transition between historic and current
data.
Directory Service
The ability to
access relationships between channels and the sets in which they belong was
considered a general service that was worth creating. Several laboratories
have already provided some sort
of directory service. This is not to be confused with a name service. This
service provides some information about sets and hierarchical relationships of
sets. A common tool could provide the basis for generating sets to use in
current displays, archive sets, and data analysis sets. We would push to select
or develop a standard interface to a directory service and adopt a standard. It
was suggested that this tool use a free relational database like FreeDB and
mySQL. The use of Lightweight Directory Access Protocol (LDAP) was also
suggested. Chris Larrieu will be working on this (in what time scale??) Calls to
support include:
1)
channel_list (string set_name) which returns the channels that are
included in this set
2)
channel_list(regular _expression_) which returns the channels whose name
matches a regular _expression_.
3)
Set_list(string root) which returns all sets that are included in the
specified set.
4)
Set_list(string child) which returns all sets which are ancestors of this
child.
Standard Attributes
It has been clear that higher level tools cannot be shared unless there
is some standard set of attributes. In channel access these attributes have been
in the form of several sets of attributes: They included time, display, and
control attributes. Time attributes are: value, time stamp, alarm status, and
alarm severity. Display attributes change for discrete and analog values.
Display attributes for analog values include: display high, display low, hihi
alarm limit, high alarm limit, low alarm limit, lolo alarm limit, number of
digits to the right of the decimal point to display (precision), and the
engineering units as well as the fields included in the time attribute list. The
display attributes for discrete values is the number of states and a list of the
state strings for each state. The control list for an analog value includes the
display attributes as well as high control limit and low control limit. The
control list for a discrete value is the same as the display attributes. This
attribute list has been fixed and typically sent only on connection to clients,
to reduce the network traffic. This meant that clients using these attributes
for producing archives or displays would not register changes to these
attributes until a client was disconnected and connected again. A modification
that is planned for channel access will allow these attributes to be sent only
on change. In addition, we will also allow the dynamic grouping of attributes.
In this new environment, channel access will only send the attributes that have
changed. This will reduce the network traffic for existing applications as the
alarm status and severity rarely change, but are sent to nearly all standard
EPICS clients. Clients will need to be modified to respond to a change in the
attributes values. Jeff and Matthias will work to finalize this list of standard
attributes. Jeff or Kay will implement this data object – depending on their
available time. The list includes:
1) display_high
double
2) display_low
double
3) units
string
4) control_high
double
5) control_low
double
6) time
osi_time
7) alarm_status
8) alarm_severity
9) precision
unsigned integer
(number of decimal digits – old)
10) significant digits
unsigned integer
(total digits to display)
11) decimal_digits
unsigned integer
(number of decimal digits – new)
12) sample_frequency
double
13) descriptor
variable length string
14) trigger_offset
integer
15) array_bounds
??? – multi-dimensional arrays
16) host
17) user
18) application
19) process ID
20) value
any type
Standard Data Transformations (not to be confused with
STDs)
(who was going to work on this???)
As we discussed the access to archive data, it was clear that most people
making queries to this data would want to be able to perform some data
reduction. It was also clear that we wanted to be able to reduce the data at the
source in order to reduce the network traffic that would be required to send
this information over the wire in a distributed archive environment. It became
clear that there were several places where these transformations were made
readily available to the user and become invaluable tools for operations. The
most notable example was SDDS at APS. It was decided that we would supply a
standard set of transforms (perhaps stolen from SDDS) that would be available in
a callable library that was also accessable by a script. At any point in the
transform list, an SDDS output should be available to take advantage of the
other SDDS tools. The list includes binning algorithms which would be used for
reducing data across the wire, as well as computational transforms. The list
included:
1) moving
average
2)
digital Fourier transform (spelling)
3) chirpZ
transform (now infamous)
4)
decimation
5) single
value decomposition
6)
periodic
7)
interpolation – spline, linear, discrete, polynomial
8) trig
fit
9)
statistical – average, mean, standard deviation, skew, min, max, median,
number of outliers
10) rasterizing
11) infinite impulse response
filters
High Level Application Requirements
After paying particular attention to the uses of historical data in our
controls environment, we studied other high level applications to determine what
changes to the channel access protocol would better support these
applications.
Next Linear Collider / SLC Requirements – Bob Sass
The SLAC control group has been meeting to discuss the control system
required for the next linear collider. One key consideration for this control
system is that it has to provide all of the tools that the SLC operations has
found invaluable during their many years of operation.
Operator Scripting (Button Scripting)
Operators are able to put their console in learn mode and have the
commands that are pressed – turn into a script that can then be edited. The
script can either be invoked by name or executed from an operator display button
press. At SLC there are about 3,000 of these macros.
* A channel access requirement to monitor the actions from
one client. The DESY put logger into a string record is an example of monitoring
puts that could be translated into a macro. Having the user information included
in the attribute list would assist this.
* It was agreed that operators find scripting very useful. A
method for scripting should be accepted as the standard and included in EPICS
training.
Beam-based alignment
This is the alignment of the quads and sextapole magnets to measure the
offset eith respect to the readout center of the BPM. It is run on a time scale
of weeks or months. 100 pulses are read. The operator selects a range of devices
to produce the fit. The data acquisition is at 120 Hz for this 100 pulses. A 3x3
or 9x9 matrix is used. The output is the offset for the power supplies.
* Channel access requirements to support up to 9x9
matrices.
*Buffer server could handle the 100 pulse at 120 Hz data
collection.
*Channel access monitor to send the next X changes would also
support this.
Linac Auto Steering with Movers
Data is collected over many pulses and averaged. The bad data is removed
from the calculation. Mover motions must be synchronized within a couple of
pulse latency.
* Channel access requirement for synchronized puts.
* Standardization on transforms could aid in the averaging
portion
Machine Protection System
Has to run at the beam rate of 120 Hz. It will also use beam loss
monitors at 1 Hz. Latency required to read data is less that 1 pulse.
Beam-based feedback
This is run continuously to steer the beam. Matrices are computed and
sent to downstream and upstream loops on every pulse on a dedicated network like
a shared memory. Device support will interface to this. Feedback latency is 2
pulses.
Correlation Facility
X-Y plots with functionality similar to the JLAB XTRACT tool.
Linac Energy Management
Adjust quads under operator request. The results will be reviewed and the
changes made under operator control. Needs phase and amplitude from 3,000 RF
stations.
Optics and modeling
The current averaged bpm data will be used.
Required services to meet the requirements:
*120 Hz data acquisition
Is a buffer server useful for
averaged data?
What is the minimum latency
required by any application that will use the standard network?
*Contention resolution at 120 Hz will require multi-priority
channel access/database
*Synchronized device control across IOCs within 1 clock
tick.
Can they be told to set at some time in the future?
What is the maximum latency before the commands are completed?
*Support for 9x9 matrices
*A way to tell users to hold off in the case of device
contention.
*Booting and downloading of over 1,000 IOCs
Does this use flash memory to boot?
Incremental loading or online add would help
*120 Hz data scanning could use the buffer server to offer
prior data when an event occurred.
*At current specifications, 10 Gbytes per second will be
archived. Perhaps a buffer server will ease this requirement.
SNS – John Galambos
The SNS is a neutron spallation facility being built in Oak Ridge in a
collaboration between LBL, LANL, ANL, BNL and ORNL. One of the key design
constraints is to limit the beam loss so that tunnel access is not restricted
for an extended period of time. It
has a 60 Hz pulsed neutron source. The In the first 16.6667 msec period,
15 msecs are idle, and the 1.6667 msecs is used to fill the ring. There is 682 usecs between t0 and
the beginning of the accumulation cycle. There is 975 usec to accumulate and
after 250 nsec gap, there is 590 nsec of beam. The notes from the diagnostic
meeting where these timing requirements were discussed lives on a web site at:
http://recycle.lbl.snsbiw/. Information
on the applications discussed below can be found at http://www.ornl.gov/sns/mtgs/tdasw1/tdasw1.htm.
Linac Tuning
Horizontal and vertical corrections needed. The first corrector is
changed based on the first moment. All downstream power supplies will be
controlled on a model based correction program. This will run once per second
and is based on the TRACE3D model. (This will not include multi-particle space
charge tracking which is a computationally demanding and will take over 24 hours
to actually predict halo).
Steering
Select a subset of magnets and change the beam position.
RF Phase and Amplitude Correction
Vary the RF phase and amplitude for 10 points each at 60 Hz while
calculating dW. This will use the full current at a low duty factor. Each of 12
Klystrons will be run over 1000 different control values. Are these 1000 changes
made at the 60 Hz rate? How many channels are collected?
SNS Ring Steering
Transfer matrix needed for steering along with run-time reading of the
power supply read-backs.
SNS Ring Radiation and Beam Loss Monitors
100 ionization monitors are read every 1 usec and shut off beam. There
are also 10 paint can loss monitors sampling at the nsec rate that need to be
available to determine the beam loss within a pulse. We will need to keep track
of the source of beam loss over time to determine the possible causes.
SNS Ring Orbit Closure
Requires setting ramping power supplies within several pulses of each
other.
SNS Ring BPMs
Will require reading up to 100 bpms with 1K samples each at 60 Hz. We
will want to keep these available in memory for up to a minute? and to be able
to save these when an event occurs? Or deliver them to the operator after
running which transforms?
SNS Ring Beam Current
Wall current monitors are integrated at 60 Hz and should be kept in a
front-end buffer for up to one day.
SNS Ring Beam Profiles
These will be done using a flying
wire and a harp that is at the target and being read at 60 Hz.
SHS Ring Tune Measurement
An FFT of the BPM turn by turn data – once per minute or on the first 10
turns.
Jefferson Laboratory High Level Applications – David
Brian
Model server
Provides transfer matrices to other codes.
Orbit Lock and Energy Lock
These control strategies are run every 5 seconds during operation. They
are run every second during startup. They receive matrices from the model server
and then do synchronous puts into the data to change setpoints.
Auto Steer
Commissioning tool for beam steering. It uses the transfer matrices from
the model server. It requires that data it reads from the BPMs are from the same
pulse. Ideally, it would be able to do synchronous puts across the network.
Momentum Scaling Tool
Sets all of the quad magnets to known settings for know energies. No
synchronization is required.
LEM
Provides RF energy balance along the cavities to leave similar headroom
in each cavity. This is required as the energy gain between different cavities
can have as much as a 20% difference.
FFB
Takes out noise from the power lines. This runs on two of the three end
stations. It is run at 1KHz to keep the beam centered. It talks to orbit and
energy lock to prohibit interaction between the programs. It uses 12 inputs and
12 outputs.
Beam Energy Manager
Runs at a 1 Hz rate to control the energy of the beam delivered to the
halls. The goal is to control within 1 part in 10,000.
CM Log
Merges messages into an archive.
* If there was
support for unlimited string length, these messages could be archived on any
archiver
* There needs to be some way to
associate these messages with other channels – is this part of the set server?
If an archived message is being displayed – does it just put a paperclip in time
wherever it has a message to display?
Network Instruments – Kay Kasemir
This includes any intelligent device that receives setpoints and commands
and returns values and status. These could be channel access links, plcs,
labview etc….
*Require subscription with a guaranteed update rate –
notification if no data was received.
*Commands that require several parameters to be written need
synchronization.
*There is some need to process commands on a given start
time.
*For commands, it would be useful to be able to query the
device for its control values – one use would be to query the operator for the
parameters in a dialog box.
Redundant Lock Mechanism – Matthias Clausen
Some applications on the workstation require redundant operation. An
example is the alarm manager. The archiver could be modified to operate the same
way. In this situation, two or more machines are able to reach the same file
system. If one machine becomes unable to work, the other takes over.
Channel Access Requirements:
Jeff Hill
The requirements fell into the following topics. We went through the list
in an easiest to most contentious order.
New Data Descriptor
New Delivery Requirements
Large Matrix Support
CA Server Diagnostics
Data Descriptor Implementation
Diagnostics
A discussion was held on what online diagnostics could be added to
channel access to make the state of health of the system more apparent to users.
The current diagnostic, casr, does give a great deal of information on the state
of health of the clients connected to a given server. However, it would be nice
to be able to monitor these through channel access and set alarm and warning
limits on them. Values that are wanted include:
Notification when the server beacon rate changes
Per Client Diagnostics from the server
Event rate, memory usage, last
time event was sent, last time a put was received, time the client was started,
user name of the client, clients execution state
How is the data requested?
Server diagnostics
Total memory usage, overall event
rate, last time put was received, last time a monitor was sent, channel count,
search rate, connection rate.
What is the period for computing
the rate?
What about multiple servers in the
same location?
Client Diagnostics
Number of events per second being
received, number of channels connected, number of channels, last time an event
was received.
Data Descriptor Requirements
Process Variable Attributes –
Use well defined application types
Have built in standard attributes – listed earlier in the meeting
Allow new types to be added
Do the clients learn the servers native storage type?
We should move
conversions to clients
Application Defined Data Container
Support command completion
Support
message passing
Subscription update data packaging
Need well defined application type names.
Matrices
Number of dimensions
Number of elements in each dimension
Offset of first element in each dimension
What about sparse matrices?
Enumerated Data
Number of states
String per state
PV subscription
Send update messages on a periodic time (callback if late arriving)
Rate limit monitors (on the same offset for each requested interval)
Send a set of channels when some event occurs – calc like _expression_
Enable monitors on some condition
PV Read/Write
Read/Set group of attributes atomically
Read/Set client defined set of channels atomically
Event synchronize read/write on clock time or calc _expression_
Arm write with verification – then execute
Large Matrix Dilemma
Approach 1) lock record and copy in array
Slow client stops record processing – could lock with time limit
Client disconnecting with only have the array written – record is udf
Approach 2) allocate per client
large buffer in server
IOC memory is now vulnerable to rogue clients
To prevent fragmentation of memory, use fixed size buffers
This was discussed later in the
week and reappears later in the notes.
Between Dynamic Descriptors like GDD and CDEV data object, Compiled
Descriptors like the current dbr_types, or Abstract Base Class – it was decided
to use an abstract base class.
Bench marks of some prototype code show that like containers can be
unpacked in .1 usec on a 500 MHz Pentium. Unlike containers take .6 usecs.
Note that base class code will be sent to Chris Larrieu.
Bob Sass will look at IDL vs. a virtual base class in the
upcoming months.
Should we use IOP as the protocol – what action is required
and who does it for this?
CORBA will be examined by Bob Sass and Chris Larrieu with a
report forthcoming.
On Thursday and Friday Kay, Jeff, Marty and Bob continued to
discuss some of the issues from the meeting……….
Large Arrays – Part Deu
It was decided that channel access would allocate some number of fixed
size buffers to buffer the array and then put it into the record when the entire
array was received. Channel access would be using a high water mark for memory
usage so that other clients will have some headroom in memory if they need it.
When using large arrays, one will need to be careful about the number of clients
that are connecting to it and the frequency that they update it.
EPICS Release Schedule
3.14
Available for alpha release the first week of February
Features included are:
1)
Portable database and channel access server which allows the database to
run on platforms other than vxWorks.
2)
Support for tornado 2 and tornado 1 will be included
3) The
ability to log ca puts via dbaccess will be integrated into access control from
DESY (but not in the first alpha relese)
3.15
Available for alpha release by August and will include
1)
Support for large arrays
2)
Variable length characters strings
3)
Unlimited PV name length
4)
Portable server replacement of rsrv – multi thread locks, no gdd, use new
abstract base class
5) Put
confirmation
Synchronized Put Discussion
The need to somehow synchronize the putting of many parameters exists in
many applications. There are two scenarios: the channels are all in one IOC or
they are across several IOCs. Some discussion was held about the possibility of
locking the database while these values were set. It was agreed not to pursue
this strategy. The new feature that will be added to channel access to support
this is arm and set as well as put on event or clock time. For arm and set, the
new values will be loaded into the servers with verification that they have
arrived. The set command will include a time stamp and get a response indicating
when the set was performed. The client can at least determine if the puts were
in the time interval desired. The operation can be abandoned if any of the arm
commands returns late. Only notification can be given if the set commands
execute late. Another approach that will be supported is the ability to set a
value on an event. The event can either be some _expression_ in the format of a
calc record or a wall time that is in the future. An error is returned if the
wall time is already passed.
Data Storage for the Archive Requests
A discussion was held to examine the use of the abstract base class –
data object as the value to use for
the archive interface. The allocation of memory would need to be examined.
Excel Spreadsheet:
Subject |
Priority |
Categories |
Define C++ based client side
API |
High |
CAV4-Client-API |
unlimited matrix bounds |
High |
CAV4-Process-Entity-Paradigm |
unlimited string length |
High |
allow several PCAS
servers on one machine |
High |
Maintenance |
Convert old
client/serverto use osi routines |
High |
Maintenance |
EPICS_CA_ADDR_LIST
specifies port numbers |
High |
Maintenance |
if
possible, dont allow the server to use the last fd |
High |
Maintenance |
install PCAS as the IOC server |
High |
Maintenance |
abstract
base class for data description in the server API (backwards
compatible) |
High |
PCAS |
thread safe C++ server library |
High |
PCAS |
Implement C++ based client
side API |
Normal |
CAV4-Client-API |
write
logging (subscribe for name of client that is writing etc) |
Normal |
CAV4-Data-Acquisition |
application
extensible container types (msg passing, cmd compl) |
Normal |
application extensible PV
attribute set |
Normal |
directory
serivice resorce location update (detect name space collision) |
Low |
CAV4 Directory Service |
directory
service asynchronous query (implement client) |
Low |
directory
service asynchronous query (implement server) |
Low |
directory
service asynchronous query client side plug in (defne API) |
Low |
directory
service asynchronous query client side plug in (implement) |
Low |
directory
service PV location event subscription |
Low |
directory service redundancy |
Low |
directory
service server side update (implement client) |
Low |
directory
service server side update (implement server) |
Low |
directory
service server side update plug in (define API) |
Low |
directory
service server side update plug in (implement) |
Low |
directory service wild card
queies |
Low |
directory service wildcard
queries |
Low |
cancel
asynchronous write (put callback) while in progress |
Low |
CAV4-Client-API |
export process passive to
client API |
Low |
CAV4-Client-API |
2 channels
same name => effective 1 channel in client |
Low |
CAV4-Compression |
combine event
subscriptions on same PV in client |
Low |
CAV4-Compression |
move conversions to client |
Low |
CAV4-Compression |
protocol compression (level 1) |
Low |
CAV4-Compression |
protocol compression (level 2) |
Low |
CAV4-Compression |
application extensable event
types |
Low |
client adj monitor Q length |
Low |
client adj
server's dispatch priority and net QOS |
Low |
client sets event
subscription's min / max rate |
Low |
client sets server's
event queue length |
Low |
client
specified analog event subscription deadband |
Low |
dynamic
evaluation of event trigger criteria in event subscriupton |
Low |
built in PVs for server
diagnostics |
Low |
client discovers
N dimensional bounds of matrix |
Low |
N dimensional matrix
addressing |
Low |
replace IP broadcast with
IP multicast |
Low |
CAV4-WAN |
strengthened
security (kerberos SSH tuinnel) |
Low |
CAV4-WAN |