1994  1995  1996  1997  1998  1999  2000  2001  <2002>  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026  Index 1994  1995  1996  1997  1998  1999  2000  2001  <2002>  2003  2004  2005  2006  2007  2008  2009  2010  2011  2012  2013  2014  2015  2016  2017  2018  2019  2020  2021  2022  2023  2024  2025  2026
Subject: MEDM - alarm status not propagated for vis.calc
To: "Kenneth Evans, Jr." <[email protected]>
Cc: [email protected]
Date: Thu, 05 Dec 2002 17:26:31 -0500
Ken -
MEDM is supposed to allow use of the Alarm Status in the visibility calc.
I tried to use this feature, and it does not work.
Perusal of the code reveals that Alarm Status changes are not propagated
from a monitored channel into the Record for a display object, which means
this feature has never worked.
Appended below is a patch that produces the correct behavior.  The diff is
against medm V2.3.6Beta30, but the relevant code has not changed in
V3.0.2Beta2.
I should also point out that this code (and the similar handling of Alarm
Severity) only works because when records usually call db_post_events()
for .VAL with "DBE_VALUE" as well as "DBE_ALARM".
The code in setMonitorChanged() (in utils.c) only sets monitorValueChanged
for object with V_CALC, when is should also set monitorSeverityChanged
(which should probably be monitorAlarmChanged).
- brian
diff -c medm.2.3.6Beta30/medm/medmCA.c medm.2.3.6Beta30/medm/medmCA.c.orig
*** medm.2.3.6Beta30/medm/medmCA.c	Tue Nov 26 16:15:30 2002
--- medm.2.3.6Beta30/medm/medmCA.c.orig	Tue Sep 25 15:11:58 2001
*** 699,705 ****
  static void medmUpdateChannelCb(struct event_handler_args args) {
      Channel *pCh = (Channel *)ca_puser(args.chid);
      Boolean severityChanged = False;
-     Boolean statusChanged = False; /* bgmca */
      Boolean zeroAndNoneZeroTransition = False;
      Record *pr;
      double value;
--- 698,703 ----
*** 844,855 ****
  	severityChanged = True;
-   /* Mark status changed - bgmca */
-     if(pr->status != ((dataBuf *)(args.dbr))->d.status) {
- 	pr->status = ((dataBuf *)(args.dbr))->d.status;
- 	statusChanged = True;
    /* Set the new value into the record */
      pr->value = value;
--- 842,847 ----
*** 862,869 ****
      if(pCh->pr->updateValueCb) {
  	if(pr->monitorValueChanged) {
  	    pr->updateValueCb((XtPointer)pr);
! 	} else if(pr->monitorSeverityChanged &&
! 		  (statusChanged || severityChanged)) { /* bgmca */
  	} else if(pr->monitorZeroAndNoneZeroTransition &&
  	  zeroAndNoneZeroTransition) {
--- 854,860 ----
! 	} else if(pr->monitorSeverityChanged && severityChanged) {
Diff finished at Thu Dec  5 16:52:32