Subject: Re: [StreamDevice] parsing rapid inputs
Date: Thu, 31 May 2012 17:45:54 +0200
Pavel,
I think I know what's happening.
If the device sends \n\r and you define your terminator as \n, then the \r is still in the queue.
Normally this does not harm because StreamDevice flushes all input before sending a new output (command).
But sometimes, the computer is too fast. The \n may be still on the wire when StreamDevice tries to flush. Thus it arrives after the flush and appears as the first byte if the next input.
Thus setting your terminator properly (either in asyn or in StreamDevice) should help.
Note that InputEos of asyn is limited to 2 bytes (1 byte for most GPIB devices). StreamDevice supports arbitrarily long inTerminators.
When taking a new device into operation, I usually test it without any terminator setting (letting the read timeout terminate the input). Then I can see what type of terminator the device really sends (which may be different to the documentation!) and use that as the inputTerminator.
Dirk
Mark Rivers wrote:
I don’t know about the output EOS, that depends what the scope expects. But it looks like it is definitely sending you \n\r, so you should set the InputEos to “\n\r”.
*Sent:* Wednesday, May 30, 2012 9:09 AM
*To:* Mark Rivers
*Cc:* Dirk Zimoch; EPICS Tech Talk
*Subject:* Re: [StreamDevice] parsing rapid inputs
Hi Mark,
asynOctetSetInputEos("${PORT1}", -1, "\n")
asynOctetSetOutputEos("${PORT1}", -1, "\n")
Should I set them both to "\n\r"?
On Wed, May 30, 2012 at 6:00 PM, Mark Rivers <[email protected] <mailto:[email protected]>> wrote:
How have you set the input EOS on your asyn port? Have you overridden this by explicitly defining a terminator in your stream protocol file?
If you define the terminator as “\n\r” for the asyn port and don’t define it in your protocol file then I don’t think you should have this problem, because the read won’t complete until it finds and consume the \r (CR) character.
*From:* [email protected] <mailto:[email protected]> [mailto:[email protected] <mailto:[email protected]>] *On Behalf Of *Pavel Masloff
*Sent:* Wednesday, May 30, 2012 3:15 AM
*To:* Dirk Zimoch; EPICS Tech Talk
*Subject:* [StreamDevice] parsing rapid inputs
Hello,
I have run into a problem lately. I have sort of a slow device - a TDS2024 scope. So when I run my IOC, I expect StreamDevice to initialize my PVs. So there are ~ 20 PVs I want to initialize. And every once in a while I get the following error message in epics shell:
/2012/05/30 13:02:25.211 L2 TDS2024:probe_ch2: got "<0d>:CH2:PROBE 1" where ":CH2:PROBE " was expected
/This <0d> character (or CR) is driving me mad. This is because it was supposed to be the terminator of the previous input (here is the whole string together with the one above):
/2012/05/30 13:02:25.124 /dev/ttyUSB0 read 13
:CH1:PROBE 1\n
2012/05/30 13:02:25.211 L2 TDS2024:probe_ch2: got "<0d>:CH2:PROBE 1" where ":CH2:PROBE " was expected/
As you can see, there is an \r missing. So my <0d> comes as a part of the input / ":CH2:PROBE 1" /- so I get /"<0d>:CH2:PROBE 1" /instead which causes the error.
How can I fix this?
I have tried using the @mismatch handler, but it doesn't work within the @init handler.
And you will never know which PV will not initialize next.
As an comparison, my TPS2024 and TPS2024B scopes are fast enough to stumble upon this. No problem there.
Best regards,
Pavel Maslov, MS
Controls Engineer at Pulsed power Lab
Efremov Institute for Electro-Physical Apparatus
St. Petersburg, Russia
Mobile: +7 (951) 672 22 19
Land line: +7 (812) 461 01 01
Best regards,
Pavel Maslov, MS
Landline: +7 (812) 461 01 01
[StreamDevice] parsing rapid inputs Pavel Masloff
RE: [StreamDevice] parsing rapid inputs Mark Rivers
Re: [StreamDevice] parsing rapid inputs Pavel Masloff
Prev: Re: Proposed change in asyn - request for comments Eric Norum
Next: Re: Proposed change in asyn - request for comments Andrew Johnson
Prev: RE: [StreamDevice] parsing rapid inputs Mark Rivers
Next: Re: [StreamDevice] parsing rapid inputs Dirk Zimoch